Re: Global Akamai Outage
On Sun, 25 Jul 2021 at 21:41, Mark Tinka wrote: > Are you speaking globally, or for NTT? Doesn't matter. And I'm not trying to say RPKI is a bad thing. I like that we have good AS:origin mapping that is verifiable and machine readable, that part of the solution will be needed for many applications which intend to improve the Internet by some metric. And of course adding any complexity will have some rearing problems, particularly if the problem it attempts to address is infrequently occurring, so it would be naive not to expect an increased rate of outages while maturing it. -- ++ytti
Re: Global Akamai Outage
On 7/25/21 17:32, Saku Ytti wrote: Steering dangerously off-topic from this thread, we have so far had more operational and availability issues from RPKI than from hijacks. And it is a bit more embarrassing to say 'we cocked up' than to say 'someone leaked to internet, it be like it do'. Are you speaking globally, or for NTT? Mark.
Re: Global Akamai Outage
> Very often the corrective and preventive actions appear to be > different versions and wordings of 'dont make mistakes', in this case: > > - Reviewing and improving input safety checks for mapping components > - Validate and strengthen the safety checks for the configuration > deployment zoning process > > It doesn't seem like a tenable solution, when the solution is 'do > better', since I'm sure whoever did those checks did their best in the > first place. So we must assume we have some fundamental limits what > 'do better' can achieve, we have to assume we have similar level of > outage potential in all work we've produced and continue to produce > for which we exert very little control over. > > I think the mean-time-to-repair actions described are more actionable > than the 'do better'. However Akamai already solved this very fast > and may not be very reasonable to expect big improvements to a 1h > start of fault to solution for a big organisation with a complex > product. > > One thing that comes to mind is, what if Akamai assumes they cannot > reasonably make it fail less often and they can't fix it faster. Is > this particular product/solution such that the possibility of having > entirely independent A+B sides, for which clients fail over is not > available? If it was a DNS problem, it seems like it might have been > possible to have entirely failed A, and clients automatically > reverting to B, perhaps adding some latencies but also allowing the > system to automatically detect that A and B are performing at an > unacceptable delta. formal verification
Re: Global Akamai Outage
On Sun, 25 Jul 2021 at 18:14, Jared Mauch wrote: > How can we improve response times when things are routed poorly? Time to > mitigate hijacks is improved my majority of providers doing RPKI OV, but > interprovider response time scales are much longer. I also think about the > two big CTL long haul and routing issues last year. How can you mitigate > these externalities. Steering dangerously off-topic from this thread, we have so far had more operational and availability issues from RPKI than from hijacks. And it is a bit more embarrassing to say 'we cocked up' than to say 'someone leaked to internet, it be like it do'. -- ++ytti
Re: Global Akamai Outage
Work hat is not on, but context is included from prior workplaces etc. > On Jul 25, 2021, at 2:22 AM, Saku Ytti wrote: > > It doesn't seem like a tenable solution, when the solution is 'do > better', since I'm sure whoever did those checks did their best in the > first place. So we must assume we have some fundamental limits what > 'do better' can achieve, we have to assume we have similar level of > outage potential in all work we've produced and continue to produce > for which we exert very little control over. I have seen a very strong culture around risk and risk avoidance whenever possible at akamai. Some minor changes are taken very seriously. I appreciate that on a daily basis, and when we make mistakes (I am human after all) are made, reviews of the mistakes and corrective steps are planned and followed up on. I'm sure this time will not be different. I also get how easy it is to be cynical about these issues. There's always someone with power who can break things, but those can also often fix them just as fast. Focus on how you can do a transactional routing change and roll it back, how you can test etc. This is why for years I told one vendor that had a line-by-line parser their system was too unsafe for operation. There's also other questions like: How can we improve response times when things are routed poorly? Time to mitigate hijacks is improved my majority of providers doing RPKI OV, but interprovider response time scales are much longer. I also think about the two big CTL long haul and routing issues last year. How can you mitigate these externalities. - Jared
Re: Global Akamai Outage
On 7/25/21 08:18, Saku Ytti wrote: Hey, Not a critique against Akamai specifically, it applies just the same to me. Everything seems so complex and fragile. Very often the corrective and preventive actions appear to be different versions and wordings of 'dont make mistakes', in this case: - Reviewing and improving input safety checks for mapping components - Validate and strengthen the safety checks for the configuration deployment zoning process It doesn't seem like a tenable solution, when the solution is 'do better', since I'm sure whoever did those checks did their best in the first place. So we must assume we have some fundamental limits what 'do better' can achieve, we have to assume we have similar level of outage potential in all work we've produced and continue to produce for which we exert very little control over. I think the mean-time-to-repair actions described are more actionable than the 'do better'. However Akamai already solved this very fast and may not be very reasonable to expect big improvements to a 1h start of fault to solution for a big organisation with a complex product. One thing that comes to mind is, what if Akamai assumes they cannot reasonably make it fail less often and they can't fix it faster. Is this particular product/solution such that the possibility of having entirely independent A+B sides, for which clients fail over is not available? If it was a DNS problem, it seems like it might have been possible to have entirely failed A, and clients automatically reverting to B, perhaps adding some latencies but also allowing the system to automatically detect that A and B are performing at an unacceptable delta. Did some of their affected customers recover faster than Akamai due to their own actions automated or manual? Can we learn something from how the airline industry has incrementally improved safety through decades of incidents? "Doing better" is the lowest hanging fruit any network operator can strive for. Unlike airlines, the Internet community - despite being built on standards - is quite diverse in how we choose to operate our own islands. So "doing better", while a universal goal, means different things to different operators. This is why we would likely see different RFO's and remedial recommendations from different operators for the "same kind of" outage. In most cases, continuing to "do better" may be most appealing prospect because anything better than that will require significantly more funding, in an industry where most operators are generally threading the P needle. Mark.
Re: Global Akamai Outage
Indeed. Worth rereading for that reason alone (or in particular). Miles Fidelman Hank Nussbacher wrote: On 23/07/2021 09:24, Hank Nussbacher wrote: From Akamai. How companies and vendors should report outages: [07:35 UTC on July 24, 2021] Update: Root Cause: This configuration directive was sent as part of preparation for independent load balancing control of a forthcoming product. Updates to the configuration directive for this load balancing component have routinely been made on approximately a weekly basis. (Further changes to this configuration channel have been blocked until additional safety measures have been implemented, as noted in Corrective and Preventive Actions.) The load balancing configuration directive included a formatting error. As a safety measure, the load balancing component disregarded the improper configuration and fell back to a minimal configuration. In this minimal state, based on a VIP-only configuration, it did not support load balancing for Enhanced TLS slots greater than 6145. The missing load balancing data meant that the Akamai authoritative DNS system for the akamaiedge.net zone would not receive any directive for how to respond to DNS queries for many Enhanced TLS slots. The authoritative DNS system will respond with a SERVFAIL when there is no directive, as during localized failures resolvers will retry an alternate authority. The zoning process used for deploying configuration changes to the network includes an alert check for potential issues caused by the configuration changes. The zoning process did result in alerts during the deployment. However, due to how the particular safety check was configured, the alerts for this load balancing component did not prevent the configuration from continuing to propagate, and did not result in escalation to engineering SMEs. The input safety check on the load balancing component also did not automatically roll back the change upon detecting the error. Contributing Factors: The internal alerting which was specific to the load balancing component did not result in blocking the configuration from propagating to the network, and did not result in an escalation to the SMEs for the component. The alert and associated procedure indicating widespread SERVFAILs potentially due to issues with mapping systems did not lead to an appropriately urgent and timely response. The internal alerting which fired and was escalated to SMEs was for a separate component which uses the load balancing data. This internal alerting initially fired for the Edge DNS system rather than the mapping system, which delayed troubleshooting potential issues with the mapping system and the load balancing component which had the configuration change. Subsequent internal alerts more clearly indicated an issue with the mapping system. The impact to the Enhanced TLS service affected Akamai staff access to internal tools and websites, which delayed escalation of alerts, troubleshooting, and especially initiation of the incident process. Short Term Completed: Akamai completed rolling back the configuration change at 16:44 UTC on July 22, 2021. Blocked any further changes to the involved configuration channel. Other related channels are being reviewed and may be subject to a similar block as reviews take place. Channels will be unblocked after additional safety measures are assessed and implemented where needed. In Progress: Validate and strengthen the safety checks for the configuration deployment zoning process Increase the sensitivity and priority of alerting for high rates of SERVFAILs. Long Term In Progress: Reviewing and improving input safety checks for mapping components. Auditing critical systems to identify gaps in monitoring and alerting, then closing unacceptable gaps. On 22/07/2021 19:34, Mark Tinka wrote: https://edgedns.status.akamai.com/ Mark. [18:30 UTC on July 22, 2021] Update: Akamai experienced a disruption with our DNS service on July 22, 2021. The disruption began at 15:45 UTC and lasted for approximately one hour. Affected customer sites were significantly impacted for connections that were not established before the incident began. Our teams identified that a change made in a mapping component was causing the issue, and in order to mitigate it we rolled the change back at approximately 16:44 UTC. We can confirm this was not a cyberattack against Akamai's platform. Immediately following the rollback, the platform stabilized and DNS services resumed normal operations. At this time the incident is resolved, and we are monitoring to ensure that traffic remains stable. -- In theory, there is no difference between theory and practice. In practice, there is. Yogi Berra Theory is when you know everything but nothing works. Practice is when everything works but no one knows why. In our lab, theory and practice
Re: Global Akamai Outage
On 25/07/2021 09:18, Saku Ytti wrote: Hey, Not a critique against Akamai specifically, it applies just the same to me. Everything seems so complex and fragile. Complex systems are apt to break and only a very limited set of tier-3 engineers will understand what needs to be done to fix it. KISS -Hank
Re: Global Akamai Outage
Hey, Not a critique against Akamai specifically, it applies just the same to me. Everything seems so complex and fragile. Very often the corrective and preventive actions appear to be different versions and wordings of 'dont make mistakes', in this case: - Reviewing and improving input safety checks for mapping components - Validate and strengthen the safety checks for the configuration deployment zoning process It doesn't seem like a tenable solution, when the solution is 'do better', since I'm sure whoever did those checks did their best in the first place. So we must assume we have some fundamental limits what 'do better' can achieve, we have to assume we have similar level of outage potential in all work we've produced and continue to produce for which we exert very little control over. I think the mean-time-to-repair actions described are more actionable than the 'do better'. However Akamai already solved this very fast and may not be very reasonable to expect big improvements to a 1h start of fault to solution for a big organisation with a complex product. One thing that comes to mind is, what if Akamai assumes they cannot reasonably make it fail less often and they can't fix it faster. Is this particular product/solution such that the possibility of having entirely independent A+B sides, for which clients fail over is not available? If it was a DNS problem, it seems like it might have been possible to have entirely failed A, and clients automatically reverting to B, perhaps adding some latencies but also allowing the system to automatically detect that A and B are performing at an unacceptable delta. Did some of their affected customers recover faster than Akamai due to their own actions automated or manual? On Sat, 24 Jul 2021 at 21:46, Hank Nussbacher wrote: > > On 23/07/2021 09:24, Hank Nussbacher wrote: > > From Akamai. How companies and vendors should report outages: > > [07:35 UTC on July 24, 2021] Update: > > Root Cause: > > This configuration directive was sent as part of preparation for > independent load balancing control of a forthcoming product. Updates to > the configuration directive for this load balancing component have > routinely been made on approximately a weekly basis. (Further changes to > this configuration channel have been blocked until additional safety > measures have been implemented, as noted in Corrective and Preventive > Actions.) > > The load balancing configuration directive included a formatting error. > As a safety measure, the load balancing component disregarded the > improper configuration and fell back to a minimal configuration. In this > minimal state, based on a VIP-only configuration, it did not support > load balancing for Enhanced TLS slots greater than 6145. > > The missing load balancing data meant that the Akamai authoritative DNS > system for the akamaiedge.net zone would not receive any directive for > how to respond to DNS queries for many Enhanced TLS slots. The > authoritative DNS system will respond with a SERVFAIL when there is no > directive, as during localized failures resolvers will retry an > alternate authority. > > The zoning process used for deploying configuration changes to the > network includes an alert check for potential issues caused by the > configuration changes. The zoning process did result in alerts during > the deployment. However, due to how the particular safety check was > configured, the alerts for this load balancing component did not prevent > the configuration from continuing to propagate, and did not result in > escalation to engineering SMEs. The input safety check on the load > balancing component also did not automatically roll back the change upon > detecting the error. > > Contributing Factors: > > The internal alerting which was specific to the load balancing > component did not result in blocking the configuration from propagating > to the network, and did not result in an escalation to the SMEs for the > component. > The alert and associated procedure indicating widespread SERVFAILs > potentially due to issues with mapping systems did not lead to an > appropriately urgent and timely response. > The internal alerting which fired and was escalated to SMEs was for > a separate component which uses the load balancing data. This internal > alerting initially fired for the Edge DNS system rather than the mapping > system, which delayed troubleshooting potential issues with the mapping > system and the load balancing component which had the configuration > change. Subsequent internal alerts more clearly indicated an issue with > the mapping system. > The impact to the Enhanced TLS service affected Akamai staff access > to internal tools and websites, which delayed escalation of alerts, > troubleshooting, and especially initiation of the incident process. > > Short Term > > Completed: > > Akamai completed rolling back the configuration change at 16:44 UTC > on July 22, 2021. >