Re: PDU recommendations

2013-06-24 Thread Måns Nilsson
Subject: Re: PDU recommendations Date: Sun, Jun 23, 2013 at 09:32:00PM -0400 
Quoting shawn wilson (ag4ve...@gmail.com):
 So, that's not a very good endorsement :)
 
 Idk why you'd use a fuse in a PDU.

MCB units age.  Especially with vibration.  A 10A MCB becomes a 9A MCB after 
some miles. 

Fuses don't. 

MCB units are good at protecting people since they trip quickly and 
aggressively. 

Fuses tend to linger before blowing, and thus are comparatively bad at 
protecting
people (longer shock) but better at protecting infrastructure (surge
and switch-on-transient resistance).

-- 
Måns Nilsson primary/secondary/besserwisser/machina
MN-1334-RIPE +46 705 989668
There's a little picture of ED MCMAHON doing BAD THINGS to JOAN RIVERS
in a $200,000 MALIBU BEACH HOUSE!!


signature.asc
Description: Digital signature


Re: PDU recommendations

2013-06-24 Thread Ryan - Lists
Does anyone on list have experience with the APC AP7920 switched rack PDU, or 
any of the horizontal rack mountables with management? We're looking at these 
for our remote sites.

Sent from my iPhone

On Jun 24, 2013, at 6:10 AM, Måns Nilsson mansa...@besserwisser.org wrote:

 Subject: Re: PDU recommendations Date: Sun, Jun 23, 2013 at 09:32:00PM -0400 
 Quoting shawn wilson (ag4ve...@gmail.com):
 So, that's not a very good endorsement :)
 
 Idk why you'd use a fuse in a PDU.
 
 MCB units age.  Especially with vibration.  A 10A MCB becomes a 9A MCB after 
 some miles. 
 
 Fuses don't. 
 
 MCB units are good at protecting people since they trip quickly and 
 aggressively. 
 
 Fuses tend to linger before blowing, and thus are comparatively bad at 
 protecting
 people (longer shock) but better at protecting infrastructure (surge
 and switch-on-transient resistance).
 
 -- 
 Måns Nilsson primary/secondary/besserwisser/machina
 MN-1334-RIPE +46 705 989668
 There's a little picture of ED MCMAHON doing BAD THINGS to JOAN RIVERS
 in a $200,000 MALIBU BEACH HOUSE!!



Re: PDU recommendations

2013-06-24 Thread Warren Bailey
We seem to always get calls from uplogix.. Check them out if you are 
considering managing pdu's etc. Their gear is pretty stout, and they have good 
to great support.


Sent from my Mobile Device.


 Original message 
From: Ryan - Lists rlambert.li...@gmail.com
Date: 06/24/2013 11:43 AM (GMT-08:00)
To: Måns Nilsson mansa...@besserwisser.org
Cc: North American Network Operators Group nanog@nanog.org
Subject: Re: PDU recommendations


Does anyone on list have experience with the APC AP7920 switched rack PDU, or 
any of the horizontal rack mountables with management? We're looking at these 
for our remote sites.

Sent from my iPhone

On Jun 24, 2013, at 6:10 AM, Måns Nilsson mansa...@besserwisser.org wrote:

 Subject: Re: PDU recommendations Date: Sun, Jun 23, 2013 at 09:32:00PM -0400 
 Quoting shawn wilson (ag4ve...@gmail.com):
 So, that's not a very good endorsement :)

 Idk why you'd use a fuse in a PDU.

 MCB units age.  Especially with vibration.  A 10A MCB becomes a 9A MCB after 
 some miles.

 Fuses don't.

 MCB units are good at protecting people since they trip quickly and 
 aggressively.

 Fuses tend to linger before blowing, and thus are comparatively bad at 
 protecting
 people (longer shock) but better at protecting infrastructure (surge
 and switch-on-transient resistance).

 --
 Måns Nilsson primary/secondary/besserwisser/machina
 MN-1334-RIPE +46 705 989668
 There's a little picture of ED MCMAHON doing BAD THINGS to JOAN RIVERS
 in a $200,000 MALIBU BEACH HOUSE!!



Re: PDU recommendations

2013-06-24 Thread Alain Hebert
Hi,

Yes.

They are good.

Nothing I would deploy in a large data center but for a few racks
they are perfect.

Beware that they are not built to be connected straight to the
internet =D.

The management module can reset depending on packet payload and
overall traffic.  They should always be behind some sort of firewall
with rules limiting its access.

PS: Ours are a few years old, I'm sure APC added some sort of
security since then, you may want to look 'em up.

Happy 24th to all.

-
Alain Hebertaheb...@pubnix.net   
PubNIX Inc.
50 boul. St-Charles
P.O. Box 26770 Beaconsfield, Quebec H9W 6G7
Tel: 514-990-5911  http://www.pubnix.netFax: 514-990-9443

On 06/24/13 14:41, Ryan - Lists wrote:
 Does anyone on list have experience with the APC AP7920 switched rack PDU, or 
 any of the horizontal rack mountables with management? We're looking at these 
 for our remote sites.

 Sent from my iPhone

 On Jun 24, 2013, at 6:10 AM, Måns Nilsson mansa...@besserwisser.org wrote:

 Subject: Re: PDU recommendations Date: Sun, Jun 23, 2013 at 09:32:00PM -0400 
 Quoting shawn wilson (ag4ve...@gmail.com):
 So, that's not a very good endorsement :)

 Idk why you'd use a fuse in a PDU.
 MCB units age.  Especially with vibration.  A 10A MCB becomes a 9A MCB after 
 some miles. 

 Fuses don't. 

 MCB units are good at protecting people since they trip quickly and 
 aggressively. 

 Fuses tend to linger before blowing, and thus are comparatively bad at 
 protecting
 people (longer shock) but better at protecting infrastructure (surge
 and switch-on-transient resistance).

 -- 
 Måns Nilsson primary/secondary/besserwisser/machina
 MN-1334-RIPE +46 705 989668
 There's a little picture of ED MCMAHON doing BAD THINGS to JOAN RIVERS
 in a $200,000 MALIBU BEACH HOUSE!!






Re: PDU recommendations

2013-06-24 Thread shawn wilson
Heh, I wouldn't dream of putting this type of device on the net - nothing
good can come from that.
On Jun 24, 2013 3:04 PM, Alain Hebert aheb...@pubnix.net wrote:

 Hi,

 Yes.

 They are good.

 Nothing I would deploy in a large data center but for a few racks
 they are perfect.

 Beware that they are not built to be connected straight to the
 internet =D.

 The management module can reset depending on packet payload and
 overall traffic.  They should always be behind some sort of firewall
 with rules limiting its access.

 PS: Ours are a few years old, I'm sure APC added some sort of
 security since then, you may want to look 'em up.

 Happy 24th to all.

 -
 Alain Hebertaheb...@pubnix.net
 PubNIX Inc.
 50 boul. St-Charles
 P.O. Box 26770 Beaconsfield, Quebec H9W 6G7
 Tel: 514-990-5911  http://www.pubnix.netFax: 514-990-9443

 On 06/24/13 14:41, Ryan - Lists wrote:
  Does anyone on list have experience with the APC AP7920 switched rack
 PDU, or any of the horizontal rack mountables with management? We're
 looking at these for our remote sites.
 
  Sent from my iPhone
 
  On Jun 24, 2013, at 6:10 AM, Måns Nilsson mansa...@besserwisser.org
 wrote:
 
  Subject: Re: PDU recommendations Date: Sun, Jun 23, 2013 at 09:32:00PM
 -0400 Quoting shawn wilson (ag4ve...@gmail.com):
  So, that's not a very good endorsement :)
 
  Idk why you'd use a fuse in a PDU.
  MCB units age.  Especially with vibration.  A 10A MCB becomes a 9A MCB
 after some miles.
 
  Fuses don't.
 
  MCB units are good at protecting people since they trip quickly and
 aggressively.
 
  Fuses tend to linger before blowing, and thus are comparatively bad at
 protecting
  people (longer shock) but better at protecting infrastructure (surge
  and switch-on-transient resistance).
 
  --
  Måns Nilsson primary/secondary/besserwisser/machina
  MN-1334-RIPE +46 705 989668
  There's a little picture of ED MCMAHON doing BAD THINGS to JOAN RIVERS
  in a $200,000 MALIBU BEACH HOUSE!!
 
 





Re: PDU recommendations

2013-06-24 Thread Ryan - Lists
Oh, absolutely. These would be secured on a separate, private network with very 
specific access controls.

These remote sites are more branch than data center. Looking at a very 
limited amount of equipment (1-2 open telco racks/site).

Sent from my iPhone

On Jun 24, 2013, at 3:01 PM, Alain Hebert aheb...@pubnix.net wrote:

Hi,
 
Yes.
 
They are good.
 
Nothing I would deploy in a large data center but for a few racks
 they are perfect.
 
Beware that they are not built to be connected straight to the
 internet =D.
 
The management module can reset depending on packet payload and
 overall traffic.  They should always be behind some sort of firewall
 with rules limiting its access.
 
PS: Ours are a few years old, I'm sure APC added some sort of
 security since then, you may want to look 'em up.
 
Happy 24th to all.
 
 -
 Alain Hebertaheb...@pubnix.net   
 PubNIX Inc.
 50 boul. St-Charles
 P.O. Box 26770 Beaconsfield, Quebec H9W 6G7
 Tel: 514-990-5911  http://www.pubnix.netFax: 514-990-9443
 
 On 06/24/13 14:41, Ryan - Lists wrote:
 Does anyone on list have experience with the APC AP7920 switched rack PDU, 
 or any of the horizontal rack mountables with management? We're looking at 
 these for our remote sites.
 
 Sent from my iPhone
 
 On Jun 24, 2013, at 6:10 AM, Måns Nilsson mansa...@besserwisser.org wrote:
 
 Subject: Re: PDU recommendations Date: Sun, Jun 23, 2013 at 09:32:00PM 
 -0400 Quoting shawn wilson (ag4ve...@gmail.com):
 So, that's not a very good endorsement :)
 
 Idk why you'd use a fuse in a PDU.
 MCB units age.  Especially with vibration.  A 10A MCB becomes a 9A MCB 
 after some miles. 
 
 Fuses don't. 
 
 MCB units are good at protecting people since they trip quickly and 
 aggressively. 
 
 Fuses tend to linger before blowing, and thus are comparatively bad at 
 protecting
 people (longer shock) but better at protecting infrastructure (surge
 and switch-on-transient resistance).
 
 -- 
 Måns Nilsson primary/secondary/besserwisser/machina
 MN-1334-RIPE +46 705 989668
 There's a little picture of ED MCMAHON doing BAD THINGS to JOAN RIVERS
 in a $200,000 MALIBU BEACH HOUSE!!
 
 



Re: PDU recommendations

2013-06-24 Thread Ricky Beam
On Sun, 23 Jun 2013 11:37:43 -0400, shawn wilson ag4ve...@gmail.com  
wrote:

However, I figured I'd see if there was a better brand /
specific model recommendations for quality or bang / buck?


On Sun, 23 Jun 2013 12:02:27 -0400, Michael Loftis mlof...@wgops.com  
wrote:

(knock on wood) nothing in the
last 6-7 years has caused an outage.


APC's are what I've grown to love... mostly because they're cheap and  
plentiful (eBay!) The only issue I've had with them is flash corruption;  
sometimes they have to be reprogrammed after a power outage.  I'm using  
metered PDUs so it never effects the servers.


But I also have a set of ServerTech dual-feed units. The full monty of DC  
features. (in fact, what a number of colo providers use.)  I've not used  
them in years, 'tho -- lack of facilities to power them. (the electrician  
got a little happy cutting out old wiring in the current office and killed  
the two existing L6-30 drops.  everything else is L21-20.)




Re: PDU recommendations

2013-06-24 Thread Mark Keymer
I was wondering if anyone had experience with Geist's outlet monitoring 
product?


I recently started using there basic PDU's and so far so good. But am 
wondering if anyone has feed back on Geist's outlet monitoring product.


Mark Keymer






Re: PDU recommendations

2013-06-23 Thread Andrew D Kirch

On 6/23/2013 11:37 AM, shawn wilson wrote:

We currently use Triplite stuff but they've got an issue where after a few
minutes, they stop accepting new tcp connections. We're adding a new 30A
circuit and I'm thinking of going with APC (ran them in the past and never
had any issues). However, I figured I'd see if there was a better brand /
specific model recommendations for quality or bang / buck?

Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.


Shawn,

I'd go with APC it's quite monitorable and most NMS packages including 
Zenoss (where I work) have extensions to monitor it. There's a half 
dozen open source ZenPacks for APC including UPS's and PDU's.


Andrew



Re: PDU recommendations

2013-06-23 Thread Michael Loftis
Personally have gotten sick of dealing with basically every other
vendors PDU out there but APC.  APC PDUs may not have every whiz-bang
feature but they work.  SNMP or SSH pretty solid.  You still probably
want them on a closed management network but problems even in the wild
'net with port 22 open in my experience have been rare.  Management
software upgrades are generally live, load left on/undisturbed.  I
still schedule them for downtime but (knock on wood) nothing in the
last 6-7 years has caused an outage.



Re: PDU recommendations

2013-06-23 Thread Nick Khamis
Hello Michael, does that mean you do not employ PDUs in your network?
I.e., found a UPS with sufficient number of outlets in the back. With
that in mind, could you make a recommendation for such a UPS-direct
for a VM environment.

Kind Regards,

Nick.



Re: PDU recommendations

2013-06-23 Thread Michael Loftis
No, I only use APC anymore for PDUs.  It's the others I've dealt with
I don't like.  There's quite a few I've never used but after the
painfully expensive experiences I've had with Tripp-Lite, Bay tech,
MGE (though I think they're part of Schneider or APC now), Liebert
(which at the time looked suspiciously the same as the Tripp-Lite's
but with a bigger price tag), and a couple others I'm certainly
forgetting.

I'd heard there were some bad batches that were DOA from APC, but
haven't personally experienced any myself.  I've had a couple
management cards in Symmetra LXes fail, and that same Symmetra chassis
had a power/inverter/charger module fail around the same time.

On Sun, Jun 23, 2013 at 9:13 AM, Nick Khamis sym...@gmail.com wrote:
 Hello Michael, does that mean you do not employ PDUs in your network?
 I.e., found a UPS with sufficient number of outlets in the back. With
 that in mind, could you make a recommendation for such a UPS-direct
 for a VM environment.

 Kind Regards,

 Nick.



-- 

Genius might be described as a supreme capacity for getting its possessors
into trouble of all kinds.
-- Samuel Butler



Re: PDU recommendations

2013-06-23 Thread tritran
APC is solid. Their newer line can provide outlet metering. WTI is also 
good...they support redundant circuits. I've seen Baytech died after just 
unplugging a server. 
--Original Message--
From: shawn wilson
To: North American Network Operators Group
Subject: PDU recommendations
Sent: Jun 23, 2013 8:37 AM

We currently use Triplite stuff but they've got an issue where after a few
minutes, they stop accepting new tcp connections. We're adding a new 30A
circuit and I'm thinking of going with APC (ran them in the past and never
had any issues). However, I figured I'd see if there was a better brand /
specific model recommendations for quality or bang / buck?

Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.




Re: PDU recommendations

2013-06-23 Thread Nick Hilliard
On 23/06/2013 20:05, trit...@cox.net wrote:
 APC is solid. Their newer line can provide outlet metering.

That's an improvement then.  Raritan has had this feature for years, with
visibility via SNMP.  This was one of the reasons I dumped APC a couple of
years ago.

Nick




Re: PDU recommendations

2013-06-23 Thread Seth Mattinen

On 6/23/13 12:08 PM, Nick Hilliard wrote:

That's an improvement then.  Raritan has had this feature for years, with
visibility via SNMP.  This was one of the reasons I dumped APC a couple of
years ago.



The APC metered-by-outlet series are relatively new. I figured it was 
inevitable when I was scrolling through the menus on a new genreation 2 
PDU a while back and it listed outlet metering in the menu (although it 
didn't do anything).


~Seth



Re: PDU recommendations

2013-06-23 Thread Eric Clark
Raritan has a good line, the usual features, we use a lot of 2U, 208v,30A units 
with 20xc13 which is a good config these days

Their central management software, while not perfect, is excellent for pdu 
control
On Jun 23, 2013, at 8:37 AM, shawn wilson ag4ve...@gmail.com wrote:

 We currently use Triplite stuff but they've got an issue where after a few
 minutes, they stop accepting new tcp connections. We're adding a new 30A
 circuit and I'm thinking of going with APC (ran them in the past and never
 had any issues). However, I figured I'd see if there was a better brand /
 specific model recommendations for quality or bang / buck?
 
 Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.




RE: PDU recommendations

2013-06-23 Thread Petter Bruland
We're replacing TrippLite with APC. Had two TrippLite SNMP/Web cards stop 
working at random times, and need to be reset. Pain when the datacenter is far 
away. On a different note TrippLite support has been super awesome.

The APC line we went with, model # escaping me at the moment, only had overall 
unit AMP load indicator. But their SNMP access is nice, for custom graphs in 
Cacti etc, and being able to remote bounce an outlet.

We did have a few WTI, the really old ones, which did not store the config in 
flash, thus needed to be reconfigured via serial after power outage. Even with 
that annoyance, they had much faster response time from telnet (I know, 
old) turning on/off outlets than either of APC or TrippLite.

-Petter


From: trit...@cox.net [trit...@cox.net]
Sent: Sunday, June 23, 2013 12:05 PM
To: shawn wilson; North American Network Operators Group
Subject: Re: PDU recommendations

APC is solid. Their newer line can provide outlet metering. WTI is also 
good...they support redundant circuits. I've seen Baytech died after just 
unplugging a server.
--Original Message--
From: shawn wilson
To: North American Network Operators Group
Subject: PDU recommendations
Sent: Jun 23, 2013 8:37 AM

We currently use Triplite stuff but they've got an issue where after a few
minutes, they stop accepting new tcp connections. We're adding a new 30A
circuit and I'm thinking of going with APC (ran them in the past and never
had any issues). However, I figured I'd see if there was a better brand /
specific model recommendations for quality or bang / buck?

Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.





RE: PDU recommendations

2013-06-23 Thread shawn wilson
Thanks, I think the amount of love for the APC stuff confirmed my
experience. I'll look at the Raritan PDUs as I like their KVMs but if I
have to use their software or a WebUI to manage it (I use AddleLink for
remote to the KVM because I don't like proprietary management) I won't use
their PDU.

AFAIK (I'll obviously confirm), the circuit is 208VAC and the plug is the
dual phase NMEA type.
On Jun 23, 2013 3:41 PM, Petter Bruland petter.brul...@allegiantair.com
wrote:

 We're replacing TrippLite with APC. Had two TrippLite SNMP/Web cards stop
 working at random times, and need to be reset. Pain when the datacenter is
 far away. On a different note TrippLite support has been super awesome.

 The APC line we went with, model # escaping me at the moment, only had
 overall unit AMP load indicator. But their SNMP access is nice, for custom
 graphs in Cacti etc, and being able to remote bounce an outlet.

 We did have a few WTI, the really old ones, which did not store the config
 in flash, thus needed to be reconfigured via serial after power outage.
 Even with that annoyance, they had much faster response time from telnet
 (I know, old) turning on/off outlets than either of APC or TrippLite.

 -Petter

 
 From: trit...@cox.net [trit...@cox.net]
 Sent: Sunday, June 23, 2013 12:05 PM
 To: shawn wilson; North American Network Operators Group
 Subject: Re: PDU recommendations

 APC is solid. Their newer line can provide outlet metering. WTI is also
 good...they support redundant circuits. I've seen Baytech died after just
 unplugging a server.
 --Original Message--
 From: shawn wilson
 To: North American Network Operators Group
 Subject: PDU recommendations
 Sent: Jun 23, 2013 8:37 AM

 We currently use Triplite stuff but they've got an issue where after a few
 minutes, they stop accepting new tcp connections. We're adding a new 30A
 circuit and I'm thinking of going with APC (ran them in the past and never
 had any issues). However, I figured I'd see if there was a better brand /
 specific model recommendations for quality or bang / buck?

 Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.





RE: PDU recommendations

2013-06-23 Thread Chris Dunn
Been at a place where they have hundreds of APC's in production, all monitored 
and reporting back. Hardly a lick of trouble. 
Love the fact you can reboot the management interface in the rare case there is 
a hang and it does not affect the status of the outlets.
-ChrisD.


-Original Message-
From: shawn wilson [mailto:ag4ve...@gmail.com] 
Sent: Sunday, June 23, 2013 10:38 AM
To: North American Network Operators Group
Subject: PDU recommendations

We currently use Triplite stuff but they've got an issue where after a few 
minutes, they stop accepting new tcp connections. We're adding a new 30A 
circuit and I'm thinking of going with APC (ran them in the past and never had 
any issues). However, I figured I'd see if there was a better brand / specific 
model recommendations for quality or bang / buck?

Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.




Re: PDU recommendations

2013-06-23 Thread Nick Khamis
And now for the stupid question. Is there an APC UPS in a U form factor
with sufficient
outlets that can act kind of like a PDU, only better?

PS If it has stonith capabilities ever better!!!

Kind Regards,

Nick.



RE: PDU recommendations

2013-06-23 Thread Trey Valenta
I'll also throw out recommendations for ServTech PDUs. They have an affordable 
line of PDUs with static transfer switches that are particularly attractive for 
all your single-power-supply devices.

Chris Dunn chrisdu...@gmail.com wrote:

Been at a place where they have hundreds of APC's in production, all
monitored and reporting back. Hardly a lick of trouble. 
Love the fact you can reboot the management interface in the rare case
there is a hang and it does not affect the status of the outlets.
-ChrisD.


-Original Message-
From: shawn wilson [mailto:ag4ve...@gmail.com] 
Sent: Sunday, June 23, 2013 10:38 AM
To: North American Network Operators Group
Subject: PDU recommendations

We currently use Triplite stuff but they've got an issue where after a
few minutes, they stop accepting new tcp connections. We're adding a
new 30A circuit and I'm thinking of going with APC (ran them in the
past and never had any issues). However, I figured I'd see if there was
a better brand / specific model recommendations for quality or bang /
buck?

Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.


Re: PDU recommendations

2013-06-23 Thread Blake Dunlap
Nick, he meant he was using APC PDUs, not APC UPSs with PDU functionality...


APC is also the PDU vendor I would recommend.


On Sun, Jun 23, 2013 at 6:40 PM, Nick Khamis sym...@gmail.com wrote:

 And now for the stupid question. Is there an APC UPS in a U form factor
 with sufficient
 outlets that can act kind of like a PDU, only better?

 PS If it has stonith capabilities ever better!!!

 Kind Regards,

 Nick.




Re: PDU recommendations

2013-06-23 Thread Caruso, Anthony
I used an APC (I think) 1U PDU at a client a few years back.  The bugger was it 
wasn't deep, so after the cabinet started getting really populated, the back 
outlets were a PITA.  We started using the full-height back of the cabinet PDU 
strips (one on each side for A  B power respectively) after that SNAFU.

-T

On Jun 23, 2013, at 7:27 PM, Blake Dunlap iki...@gmail.com wrote:

 Nick, he meant he was using APC PDUs, not APC UPSs with PDU functionality...


 APC is also the PDU vendor I would recommend.


 On Sun, Jun 23, 2013 at 6:40 PM, Nick Khamis sym...@gmail.com wrote:

 And now for the stupid question. Is there an APC UPS in a U form factor
 with sufficient
 outlets that can act kind of like a PDU, only better?

 PS If it has stonith capabilities ever better!!!

 Kind Regards,

 Nick.





This email message and any attachments are for the sole use of the intended 
recipient(s) and contain confidential and/or privileged information. Any 
unauthorized review, use, disclosure or distribution is prohibited. If you are 
not the intended recipient, please contact the sender by reply e-mail and 
destroy all copies of the original message and any attachments.



Re: PDU recommendations

2013-06-23 Thread tritran
Eaton have 1U UPS that provide the same runtime as a 2U APC. Are they any good?

--Original Message--
From: Nick Khamis
To: Chris Dunn
Cc: North American Network Operators Group
Subject: Re: PDU recommendations
Sent: Jun 23, 2013 4:40 PM

And now for the stupid question. Is there an APC UPS in a U form factor
with sufficient
outlets that can act kind of like a PDU, only better?

PS If it has stonith capabilities ever better!!!

Kind Regards,

Nick.





Re: PDU recommendations

2013-06-23 Thread Luke S. Crawford
I also have had good experience with (used) servertech/century/power 
tower (I think all the same brand)  -  very inexpensive;  if you are in 
santa clara I have some spare 2u 16 port 208v (20a/c19) units.


Here is something a buddy wrote up when we were wiring them to the 
user-accessable power on/off menu:


http://blog.prgmr.com/xenophobia/2012/02/notes-on-setting-up-a-sentry-p.html


My new rack is all avocent PM3001-401 units.Used, of course;  but 
the feature I was after was per-port power monitoring.


I haven't quite gotten 'em all the way figured out yet.   One thing I 
see as a negative (but might be positive?) is that they have fuses, not 
breakers.I don't know if this provides better protection;  I do know 
that when my buddy overloaded one of them in testing, I had to replace 
fuses, rather than just switching a breaker back.   (also, when a 
different buddy plugged a ancient desktop (so old the PSU wasn't 
auto-switch)  with the power input switch set to 110 in, it blew some of 
the fuses in the PDU (and took out the rack)  - it didn't damage any of 
the other servers on the pdu (other than taking out the PDU;  but 
everything came back up when I swapped it with my spare.)


Also note, uh, the servertech and the avocent and I think all the other 
PDUs I've seen can reboot the management interface without flipping the 
outlets.  I did it a bunch when I was getting familiar with the avocent.


Yeah.  I think I need to give fewer buddies access to production.


Nobody takes hardware seriously enough.  I can find people I trust with 
root, and that trust doesn't seem misplaced.But I let them touch the 
hardware?  and they fuck it up.So I end up doing almost all the 
hardware stuff myself.




On 06/23/2013 04:48 PM, Trey Valenta wrote:

I'll also throw out recommendations for ServTech PDUs. They have an affordable 
line of PDUs with static transfer switches that are particularly attractive for 
all your single-power-supply devices.





RE: PDU recommendations

2013-06-23 Thread Bill Breckenridge
We have switched to Chatsworth products PDU line - robust and dependable in 
over 100 redundant installs - all outlet/environmental/SNMP and other options 
well behaved with plug-ins as well tech support is easier to access/escalate

Bill

-Original Message-
From: Petter Bruland [mailto:petter.brul...@allegiantair.com] 
Sent: Sunday, June 23, 2013 3:42 PM
To: trit...@cox.net; shawn wilson; North American Network Operators Group
Subject: RE: PDU recommendations

We're replacing TrippLite with APC. Had two TrippLite SNMP/Web cards stop 
working at random times, and need to be reset. Pain when the datacenter is far 
away. On a different note TrippLite support has been super awesome.

The APC line we went with, model # escaping me at the moment, only had overall 
unit AMP load indicator. But their SNMP access is nice, for custom graphs in 
Cacti etc, and being able to remote bounce an outlet.

We did have a few WTI, the really old ones, which did not store the config in 
flash, thus needed to be reconfigured via serial after power outage. Even with 
that annoyance, they had much faster response time from telnet (I know, 
old) turning on/off outlets than either of APC or TrippLite.

-Petter


From: trit...@cox.net [trit...@cox.net]
Sent: Sunday, June 23, 2013 12:05 PM
To: shawn wilson; North American Network Operators Group
Subject: Re: PDU recommendations

APC is solid. Their newer line can provide outlet metering. WTI is also 
good...they support redundant circuits. I've seen Baytech died after just 
unplugging a server.
--Original Message--
From: shawn wilson
To: North American Network Operators Group
Subject: PDU recommendations
Sent: Jun 23, 2013 8:37 AM

We currently use Triplite stuff but they've got an issue where after a few 
minutes, they stop accepting new tcp connections. We're adding a new 30A 
circuit and I'm thinking of going with APC (ran them in the past and never had 
any issues). However, I figured I'd see if there was a better brand / specific 
model recommendations for quality or bang / buck?

Specs: 30A 24+ port 0U, managed (with ssh), lcd use display.






Re: PDU recommendations

2013-06-23 Thread shawn wilson
So, that's not a very good endorsement :)

Idk why you'd use a fuse in a PDU.

The management interface can be rebooted without taking anything down on
the TrippLite but it's at a colo and it *shouldn't* time out like it does.
I think of this like a vehicle computer - if it goes down, you might still
drive for a little but get ready for a crash.
On Jun 23, 2013 9:00 PM, Luke S. Crawford l...@prgmr.com wrote:

 I also have had good experience with (used) servertech/century/power tower
 (I think all the same brand)  -  very inexpensive;  if you are in santa
 clara I have some spare 2u 16 port 208v (20a/c19) units.

 Here is something a buddy wrote up when we were wiring them to the
 user-accessable power on/off menu:

 http://blog.prgmr.com/**xenophobia/2012/02/notes-on-**
 setting-up-a-sentry-p.htmlhttp://blog.prgmr.com/xenophobia/2012/02/notes-on-setting-up-a-sentry-p.html


 My new rack is all avocent PM3001-401 units.Used, of course;  but the
 feature I was after was per-port power monitoring.

 I haven't quite gotten 'em all the way figured out yet.   One thing I see
 as a negative (but might be positive?) is that they have fuses, not
 breakers.I don't know if this provides better protection;  I do know
 that when my buddy overloaded one of them in testing, I had to replace
 fuses, rather than just switching a breaker back.   (also, when a different
 buddy plugged a ancient desktop (so old the PSU wasn't auto-switch)  with
 the power input switch set to 110 in, it blew some of the fuses in the PDU
 (and took out the rack)  - it didn't damage any of the other servers on the
 pdu (other than taking out the PDU;  but everything came back up when I
 swapped it with my spare.)

 Also note, uh, the servertech and the avocent and I think all the other
 PDUs I've seen can reboot the management interface without flipping the
 outlets.  I did it a bunch when I was getting familiar with the avocent.

 Yeah.  I think I need to give fewer buddies access to production.


 Nobody takes hardware seriously enough.  I can find people I trust with
 root, and that trust doesn't seem misplaced.But I let them touch the
 hardware?  and they fuck it up.So I end up doing almost all the
 hardware stuff myself.



 On 06/23/2013 04:48 PM, Trey Valenta wrote:

 I'll also throw out recommendations for ServTech PDUs. They have an
 affordable line of PDUs with static transfer switches that are particularly
 attractive for all your single-power-supply devices.