Re: [RE-wrenches] var/ power factor

2010-05-16 Thread dan
Ok, I'll bite.First, some  diffnitions.. from Delmer's Standard (ISBN-13: 978-1-4180-6580-5):Apparent  Power (VA) is the value found by multiplying the applied voltage by the  total current of an AC circuit. Apparent power is measured in volt-amps  (VA) and should not be confused with true power, measured in watts."Power  Factor (PF) is a comparison of the true power (Resistive, or Watts) to  the Apparent power (Volt Amps) in an AC circuit.""Reactive  power (VARs or Volt Amps Reactive... sometimes called "wattless  power"), is calculated by multiplying reactive voltage by reactive  current. Which can be produced by inductive or capacitive loads.".  (The key concept here is the notion that there is funny reactive stuff going  on opposing input stuff).. there's also a  few different resistances to get your head around (I've tried to attach a  cheat Sheet from E2.. but I guess the file was too big, so it got kicked back... contact me off list and I can send it along)..anyway, Assuming you're in single phase parallel land  (AC).. : First, there's a pure resistance  measured in ohms (Greek letter omega), opposing current flow across any  purely resistive loads.. (power in this part of the circuit is measured  in watts.. current is in phase with voltage)...   there's also a current limiting property opposing current flow across  any inductive loads.. it's also measured in ohms, but is called XL.. or  Inductive Reactance... funny thing about this stuff is that it's not  really a resistance.. it's more of a reaction to magnetic fields.. so  the current wave form lags the voltage wave form by 90 degrees... Power  in this part of the circuit is tabbed VARsL...   similarly there's a resistance opposing current flow (or something like  it) in capacitive loads.. also measured in ohms. this resistance is  given the handle of Xc... or Capacitive Reactance. Power in  this part of the circuit is tabbed VARsc .. this current leads the voltage  wave form by 90 degrees, and is 180 degrees out of phase with any  inductive current .. so you can subtract the smaller from the larger,  and come up with a total VARs for the circuit.. which might be either inductive or  capacitive..  and because the relationship of either wave form is 90  degrees out of phase from resistive power, we can use right angle trig.  to keep tabs. Chuck Thompson (E1) taught us the phrase "ELI the ICE man"  to help us keep things straight.  Finally, there's Z (or total circuit impedance or "total opposition to  current flow in an AC circuit"), and is calculated from ohms, XL and Xc. Z can be substituted for R total circuit calculations... I think..--So--  The way I like to make sense of it.. when you  stuff AC power into a purely resistive circuit, it consumes watts.  the current wave form is in phase with the voltage wave form so the  resistive force pushes straight back on applied power... (twinkle,  twinkle little star, power = I squared R). When  you stuff AC power into a combination AC circuit (resistive, inductive,  and maybe capacitive.. like a motor), really funny things happen.. you  can still walk up and measure stuff with your meter (and you still see  Volts and Amps ), but you're seeing "apparent power".. (VA).. the  current wave form is likely not in phase with the voltage wave form, so  rather than there being a resistance opposing current flow directly,  there's now a "funny power" pushing back the on the applied power.. a  reactive power (VARs). which can be either inductive (lagging), or  capacitive (leading). that means VARs is oppositional to VA... And  Power Factor (PF) is the ratio of Watts/ Volt Amps (VA).So,  the way I see it, VA is total apparent power.. stuff you can see...  VARs is reactive power.. (funny power pushing back on applied power)...  So that means that if there is no VARs, (XL=Xc), there is no out  of phase (funny power) opposing input power... which would make the  Power Factor (PF= W/VA)=1. Now I have been known to be full of... beans, so if I've oopsied some, please chime in.. thanks. hope this helps. dbComments?Dan  BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP  #092907-44Dan BrownPresidentFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44


 Original Message 
Subject: Re: [RE-wrenches] var/ power factor
From: Kent Osterberg k...@coveoregon.com
Date: Fri, May 14, 2010 1:35 pm
To: RE-wrenches re-wrenches@lists.re-wrenches.org

  Todd,  You are getting credit for all the energy your system can produce. Turn off the humidify and you'll see the power factor go up to nearly 1.0. That's what the inverter is operating at, regardless of whether the humidifier is on or off.   Say the PF is 80% without the inverter running. That means the utility is providing some reactive power or VARs. With the inverter running, the real power delivered by the utility is reduced, but the reactive power is not 

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Square-D tells me they have tested the breakers to a higher voltage (can't 
recall now whether it was 80V or 125 VDC) but the listing is indeed for 48 
Volts.  24V battery systems are useful for a lot of applications, but the 
unfortunate lack of a 5A breaker means we can not use them to derive a Class 2 
supply, which would make them about 10x as useful to me.



On May 15, 2010, at 9:22 , jay peltz wrote:

 Hi Rebekah,
 
 The 48v is a max rating not a nominal rating.
 So yes only good for 12 and 24v systems.
 
 However with CBI breakers I don't understand why the need for QO for DC 
 anymore?
 
 jay
 
 peltz power
 On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
 
 Hi,
 One thing to be clear about is whether these are listed for 48 volt 
 systems, or for max 48 volts?
 I was under the impression that they were max 48 volts, meaning you really 
 shouldn't use them on a system 24volts nominal.
 
 Rebekah Hren
 North Carolina
  
 
 
 http://thecarbonfreehome.com/
 
 --- On Sat, 5/15/10, Kurt Albershardt i...@es-ee.com wrote:
 
 From: Kurt Albershardt i...@es-ee.com
 Subject: Re: [RE-wrenches] AC breakers used in DC applications
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Saturday, May 15, 2010, 12:59 AM
 
 The Square-D catalogs are marginally clear on which breakers are listed for 
 DC and for what voltages, but when I tried to select an appropriate load 
 center for a DC application earlier this year I quickly ran into a number of 
 conflicts in their catalogs.  Here is the response from Schneider tech 
 support (Case# 4845778 on 1/19/10 in case anyone runs into problems with an 
 inspector):
 
 
 
 The load center catalog numbers listed below are UL LISTED, File E6294, for 
 use on 48 V dc systems. The load centers listed ARE NOT MARKED for use on 
 this voltage system, however are suitable for the application. QO branch 
 breakers, 10-70 ampere (1 and 2 pole) are also UL LISTED for use on 48V dc 
 systems. Short circuit current rating is limited to 5,000 amperes when used 
 on 48V dc.
 QO24L70F, S or RB QO612L100F, S, DF, DS, DFCU, DSCU, RB, TRB or RBCU 
 QO816L100F, S, DF, DS, DFCU, DSCU, RB or RBCU
 QO112L125G or QO11224L125G QO116L125G QO11624L125G QO120L125G QO12024L125G 
 QO124L125G or QO12030L150G QO124L150G QO130L150G or QO112L200G or QO130L200G 
 or QO13040L200G QO142L225G or
 GRB or GRB
 or GRB
 GRB
 GRB GRB GRB or GRB QO142L225GRB
 
 
 I can email the PDF to anyone who needs a copy.
 
  
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Voltage is not the issue here, it is current, and battery fault currents can be 
staggering - far more than one would ever encounter in a typical AC system fed 
from a distribution transformer.  I have seen a 200A Class T fail to act on an 
48V inverter fault which resulted in welding the metal tabs of the fuse holder 
(which had been greased with copper-laden Penetrox E) to their sockets.  That 
indicates a fault current well north of 200,000 amps, quite possibly sseveral 
times that.   A fire ensued, which triggered the gas protection system and 
fortunately resulted in almost no peripheral damage.  It did cost about $10k to 
recharge and recertify the Inergen system.  The inverter manufacturer was quite 
cagey on warranty replacement until they saw the photos - at which point a 
replacement miraculously arrived by overnight air.



On May 15, 2010, at 9:43 , Drake Chamberlin wrote:

 I did see a QO breaker fail to trip on a 24 volt DC system with only battery 
 voltage behind it.  It burned a #12 wire completely in two.  
 
 
 The 48v is a max rating not a nominal rating.
 So yes only good for 12 and 24v systems.
 
 However with CBI breakers I don't understand why the need for QO for DC 
 anymore?
 
 jay
 
 peltz power
 On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
 Drake Chamberlin
 Athens Electric
 OH License 44810
 CO License 3773
 NABCEP TM  Certified PV Installer 
 Office - 740-448-7328
 Mobile - 740-856-9648
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Small (QO or Airpax-type) breakers in a distribution bank should be front ended 
with a suitable DC master breaker or fuse that has the capability to interrupt 
the available fault current.  Ideally, the series combination should be rated 
but at a minimum, a coordination study should be undertaken.

I like to have primary protection on each string, as close to the battery as 
possible - preferably bolted to the battery terminal.  Cable limiters are nice, 
but a TPL style fuse is easier to get.



On May 16, 2010, at 16:13 , Kurt Albershardt wrote:

 Voltage is not the issue here, it is current, and battery fault currents can 
 be staggering - far more than one would ever encounter in a typical AC system 
 fed from a distribution transformer.  I have seen a 200A Class T fail to act 
 on an 48V inverter fault which resulted in welding the metal tabs of the fuse 
 holder (which had been greased with copper-laden Penetrox E) to their 
 sockets.  That indicates a fault current well north of 200,000 amps, quite 
 possibly several times that.   A fire ensued, which triggered the gas 
 protection system and fortunately resulted in almost no peripheral damage.  
 It did cost about $10k to recharge and recertify the Inergen system.  The 
 inverter manufacturer was quite cagey on warranty replacement until they saw 
 the photos - at which point a replacement miraculously arrived by overnight 
 air.
 
 
 
 On May 15, 2010, at 9:43 , Drake Chamberlin wrote:
 
 I did see a QO breaker fail to trip on a 24 volt DC system with only battery 
 voltage behind it.  It burned a #12 wire completely in two.  
 
 
 The 48v is a max rating not a nominal rating.
 So yes only good for 12 and 24v systems.
 
 However with CBI breakers I don't understand why the need for QO for DC 
 anymore?
 
 jay
 
 peltz power
 On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
 Drake Chamberlin
 Athens Electric
 OH License 44810
 CO License 3773
 NABCEP TM  Certified PV Installer 
 Office - 740-448-7328
 Mobile - 740-856-9648
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread R Ray Walters
My understanding was that the din mountable QOU breakers were rated to 125 vDC, 
and are internally the same as the QO. The difference was the connectors, and 
the mounting method.
I've used the QOUs reliably at 120 v nom on an EV, (but don't try this at home, 
kids)
We still use the QOs sometimes based on cost and availability, but I don't use 
them on anything over 24 v nominal anymore. 
They were handiest in that one breaker line could cover AC and low volt DC.
With MPPT high voltage arrays, and some of Midnite Solar's new products (Mini 
DC  Baby DC boxes), though, we've found less and less of a place for the 
venerable QO line.

R. Walters
r...@solarray.com
Solar Engineer




On May 16, 2010, at 2:25 PM, Kurt Albershardt wrote:

 Square-D tells me they have tested the breakers to a higher voltage (can't 
 recall now whether it was 80V or 125 VDC) but the listing is indeed for 48 
 Volts.  24V battery systems are useful for a lot of applications, but the 
 unfortunate lack of a 5A breaker means we can not use them to derive a Class 
 2 supply, which would make them about 10x as useful to me.
 
 
 
 On May 15, 2010, at 9:22 , jay peltz wrote:
 
 Hi Rebekah,
 
 The 48v is a max rating not a nominal rating.
 So yes only good for 12 and 24v systems.
 
 However with CBI breakers I don't understand why the need for QO for DC 
 anymore?
 
 jay
 
 peltz power
 On May 15, 2010, at 6:28 AM, Rebekah Hren wrote:
 
 Hi,
 One thing to be clear about is whether these are listed for 48 volt 
 systems, or for max 48 volts?
 I was under the impression that they were max 48 volts, meaning you really 
 shouldn't use them on a system 24volts nominal.
 
 Rebekah Hren
 North Carolina
  
 
 
 http://thecarbonfreehome.com/
 
 --- On Sat, 5/15/10, Kurt Albershardt i...@es-ee.com wrote:
 
 From: Kurt Albershardt i...@es-ee.com
 Subject: Re: [RE-wrenches] AC breakers used in DC applications
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Saturday, May 15, 2010, 12:59 AM
 
 The Square-D catalogs are marginally clear on which breakers are listed for 
 DC and for what voltages, but when I tried to select an appropriate load 
 center for a DC application earlier this year I quickly ran into a number 
 of conflicts in their catalogs.  Here is the response from Schneider tech 
 support (Case# 4845778 on 1/19/10 in case anyone runs into problems with an 
 inspector):
 
 
 
 The load center catalog numbers listed below are UL LISTED, File E6294, for 
 use on 48 V dc systems. The load centers listed ARE NOT MARKED for use on 
 this voltage system, however are suitable for the application. QO branch 
 breakers, 10-70 ampere (1 and 2 pole) are also UL LISTED for use on 48V dc 
 systems. Short circuit current rating is limited to 5,000 amperes when used 
 on 48V dc.
 QO24L70F, S or RB QO612L100F, S, DF, DS, DFCU, DSCU, RB, TRB or RBCU 
 QO816L100F, S, DF, DS, DFCU, DSCU, RB or RBCU
 QO112L125G or QO11224L125G QO116L125G QO11624L125G QO120L125G QO12024L125G 
 QO124L125G or QO12030L150G QO124L150G QO130L150G or QO112L200G or 
 QO130L200G or QO13040L200G QO142L225G or
 GRB or GRB
 or GRB
 GRB
 GRB GRB GRB or GRB QO142L225GRB
 
 
 I can email the PDF to anyone who needs a copy.
 
  
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Solmetric Suneye 210

2010-05-16 Thread Marco Mangelsdorf
Has anyone had any experience with the fairly new Solmetric Suneye 210
shading analysis tool?

 

Feedback and observations?

 

Or how about with their earlier version the Suneye 110?

 

Thanks,

marco

 

provision_highres_solar_logo2 with C-26351

Marco Mangelsdorf, President
69 Railroad Avenue, A-7
Hilo, Hawai'i 96720
(808) 969-3281, 934-7462 facsimile
 http://www.provisiontechnologies.com www.provision-solar.com

 

 

 

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread William Miller

Kurt

Fascinating story and valuable information.  This is the kind of real world 
experience we need to draw on.  Reality can change quickly under extreme 
conditions and one's education is not complete without this understanding.


Thanks for this post.

William Miller

PS:  You are fortunate your client had a proper fire suppression system.  I 
doubt many of us can count on that to minimize damage.


Wm



At 03:13 PM 5/16/2010, you wrote:
Voltage is not the issue here, it is current, and battery fault currents 
can be staggering - far more than one would ever encounter in a typical AC 
system fed from a distribution transformer.  I have seen a 200A Class T 
fail to act on an 48V inverter fault which resulted in welding the metal 
tabs of the fuse holder (which had been greased with copper-laden Penetrox 
E) to their sockets.  That indicates a fault current well north of 200,000 
amps, quite possibly sseveral times that.   A fire ensued, which triggered 
the gas protection system and fortunately resulted in almost no peripheral 
damage.  It did cost about $10k to recharge and recertify the Inergen 
system.  The inverter manufacturer was quite cagey on warranty replacement 
until they saw the photos - at which point a replacement miraculously 
arrived by overnight air.


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org