Re: [RE-wrenches] Sunny Island DC wire size

2013-02-05 Thread Chris Schaefer
Jay, a pic would be sweet. We run into these issue a lot in the off-grid
world.
Thanks,
Christopher

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Monday, February 04, 2013 22:05
To: ho...@catamountsolar.com; RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island DC wire size

HI Howie,

I've seen someone use a single 4/0 fine stranded cable with a regular lug on
the end of it.
they then cut the top of the hole out to make in a sense a U shape.
Each side of the U fit into each side of the 2 hole barrel connector on the
SI.

Super slick iI thought.

I can send you a pic if you want.

jay

peltz power

On Feb 4, 2013, at 11:46 AM, Howie Michaelson wrote:

 Hi it has been more than a year since I wired up a Sunny Island 5048
 system and I'm trying to determine lug size for the DC conductors.  My
 memory is that the maxiumm wire size was (2) #1 conductors each for
 positive and negative.  Looking in the most recent SI manual states The
 Sunny Island has a MAX DC terminal rated for 2x #2/0 AWG for DC+, DC- and
 PE.  Not sure if that is a typo - anyone no definitively?  The tech
 support line has gotten to have as long a hold time as Outback, Xantrex,
 etc...
 
 Thanks,
 Howie
 -- 
 Howie Michaelson
 NABCEP Certified Solar PV InstallerT
 
 Catamount Solar, LLC
 Renewable Energy Systems Sales and Service
 VT Solar Electric  Hot Water Incentive Partner
 http://www.CatamountSolar.com
 802-272-0004
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread Dave Palumbo
Wrenchsters,

 

I have an Enphase 7.5kW system on a residence with utility Smart Metering,
both the PV Production Meter as well as the utility billing meter being
read every hour. This system has experienced many AC Frequency Out Of
Range events since the system was installed. Below is copied the Enphase
Event message. This particular event was for 5 minutes. Most of the events
(all events are AC Frequency Out Of Range) last 5 to 10 minutes but
occasionally they have lasted from 45 minutes to 64 minutes.

 

My question is: Could the use of the smart metering increase the likely hood
that AC Frequency events happen? Or is this just a coincidence and that we
are dealing with fluctuating utility power AC Frequency issues?

 

 

 

Started on: Mon February 04, 2013 12:49 PM EST

Cleared on: Mon February 04, 2013 12:54 PM EST 

 

Recommended action

 

This condition should correct itself. No action is required.

Details

 

The microinverter reports that the frequency coming from the utility is
either too low or too high as specified by applicable regional standards.

 

AC frequency is the frequency at which voltage varies on the utility grid.
Frequency Out of Range events are usually transient and self-correcting by
the utility.

 

When the microinverter detects an out of frequency condition, it must remain
offline until the utility has been within acceptable limits continuously for
a short period of time (seconds to minutes, varies by region). If during
that time the utility again exceeds or falls short of acceptable limits, the
five-minute timer must restart and the microinverter may not begin producing
power for an additional short period following the last out-of-bounds
condition.  

 

Best,

Dave

 

 

David Palumbo

Independent Power LLC 

462 Solar Way Drive

Hyde Park, VT 05655

www.independentpowerllc.com 

Vermont Solar Partner

25 Years Experience, (802) 888-7194 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread penobscotsolar
Dave,
  We have been having the same problem with an Enphase system in Maine. I
have been dealing directly with the third tier engineers at Enphase and
they are working on a software fix for this. Theevent itself is only a
fraction of a second but IEEE requirements are that the inverter shut
down for five minutes. I only found out about this problem when it
started for this customer. It sems that Enphase has already addressed
the problem with a software fix for the M-190's. The M-215 fix should
come, according to Enphase, by the end of March. It will be
automatically downloaded through the Enlighten router.
   It's a known issue with Smart Meters with Enphase, but should be
reconciled soon.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design
www.penobscotsolar.com



 Wrenchsters,



 I have an Enphase 7.5kW system on a residence with utility Smart Metering,
 both the PV Production Meter as well as the utility billing meter being
 read every hour. This system has experienced many AC Frequency Out Of
 Range events since the system was installed. Below is copied the Enphase
 Event message. This particular event was for 5 minutes. Most of the events
 (all events are AC Frequency Out Of Range) last 5 to 10 minutes but
 occasionally they have lasted from 45 minutes to 64 minutes.



 My question is: Could the use of the smart metering increase the likely
 hood
 that AC Frequency events happen? Or is this just a coincidence and that we
 are dealing with fluctuating utility power AC Frequency issues?



 



 Started on: Mon February 04, 2013 12:49 PM EST

 Cleared on: Mon February 04, 2013 12:54 PM EST



 Recommended action



 This condition should correct itself. No action is required.

 Details



 The microinverter reports that the frequency coming from the utility is
 either too low or too high as specified by applicable regional standards.



 AC frequency is the frequency at which voltage varies on the utility grid.
 Frequency Out of Range events are usually transient and self-correcting by
 the utility.



 When the microinverter detects an out of frequency condition, it must
 remain
 offline until the utility has been within acceptable limits continuously
 for
 a short period of time (seconds to minutes, varies by region). If during
 that time the utility again exceeds or falls short of acceptable limits,
 the
 five-minute timer must restart and the microinverter may not begin
 producing
 power for an additional short period following the last out-of-bounds
 condition.  



 Best,

 Dave





 David Palumbo

 Independent Power LLC

 462 Solar Way Drive

 Hyde Park, VT 05655

 www.independentpowerllc.com

 Vermont Solar Partner

 25 Years Experience, (802) 888-7194



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread Dave Palumbo
Thanks Daryl. Does your system also sometimes stay off for longer periods
sometimes? My clients system can stay off for up to 64 minutes.

Dave

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
penobscotso...@midmaine.com
Sent: Tuesday, February 05, 2013 12:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase AC Frequency out of Range

Dave,
  We have been having the same problem with an Enphase system in Maine. I
have been dealing directly with the third tier engineers at Enphase and they
are working on a software fix for this. Theevent itself is only a fraction
of a second but IEEE requirements are that the inverter shut down for five
minutes. I only found out about this problem when it started for this
customer. It sems that Enphase has already addressed the problem with a
software fix for the M-190's. The M-215 fix should come, according to
Enphase, by the end of March. It will be automatically downloaded through
the Enlighten router.
   It's a known issue with Smart Meters with Enphase, but should be
reconciled soon.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design
www.penobscotsolar.com



 Wrenchsters,



 I have an Enphase 7.5kW system on a residence with utility Smart 
 Metering, both the PV Production Meter as well as the utility billing 
 meter being read every hour. This system has experienced many AC 
 Frequency Out Of Range events since the system was installed. Below 
 is copied the Enphase Event message. This particular event was for 5 
 minutes. Most of the events (all events are AC Frequency Out Of Range) 
 last 5 to 10 minutes but occasionally they have lasted from 45 minutes to
64 minutes.



 My question is: Could the use of the smart metering increase the 
 likely hood that AC Frequency events happen? Or is this just a 
 coincidence and that we are dealing with fluctuating utility power AC 
 Frequency issues?



 



 Started on: Mon February 04, 2013 12:49 PM EST

 Cleared on: Mon February 04, 2013 12:54 PM EST



 Recommended action



 This condition should correct itself. No action is required.

 Details



 The microinverter reports that the frequency coming from the utility 
 is either too low or too high as specified by applicable regional
standards.



 AC frequency is the frequency at which voltage varies on the utility grid.
 Frequency Out of Range events are usually transient and 
 self-correcting by the utility.



 When the microinverter detects an out of frequency condition, it must 
 remain offline until the utility has been within acceptable limits 
 continuously for a short period of time (seconds to minutes, varies by 
 region). If during that time the utility again exceeds or falls short 
 of acceptable limits, the five-minute timer must restart and the 
 microinverter may not begin producing power for an additional short 
 period following the last out-of-bounds condition.  



 Best,

 Dave





 David Palumbo

 Independent Power LLC

 462 Solar Way Drive

 Hyde Park, VT 05655

 www.independentpowerllc.com

 Vermont Solar Partner

 25 Years Experience, (802) 888-7194



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread Ryan Harkins
We see the same issue here in WI. Funny that you say 64 minutes, as some of the M215s show the error for 64 minutes for us routinely. Could that just be some designated error reporting length? Daryl, thanks for the Enphase update. Keep us updated if you can on the software fix.
Ryan HarkinsNABCEP Certified Solar PV Installer /Project Manager

PastedGraphic-3.pdf
Description: Adobe PDF document
Synergy Renewable Systems, LLCPO Box 58Stoughton, WI 53589PH: 608-712-7862ryan.hark...@energycraft.comwww.energycraft.com

On Feb 5, 2013, at 11:10 AM, Dave Palumbo wrote:Thanks Daryl. Does your system also sometimes stay off for longer periodssometimes? My clients system can stay off for up to 64 minutes.Dave-Original Message-From: re-wrenches-boun...@lists.re-wrenches.org[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Ofpenobscotso...@midmaine.comSent: Tuesday, February 05, 2013 12:01 PMTo: RE-wrenchesSubject: Re: [RE-wrenches] Enphase "AC Frequency out of Range"Dave, We have been having the same problem with an Enphase system in Maine. Ihave been dealing directly with the third tier engineers at Enphase and theyare working on a software fix for this. The"event" itself is only a fractionof a second but IEEE requirements are that the inverter shut down for fiveminutes. I only found out about this problem when it started for thiscustomer. It sems that Enphase has already addressed the problem with asoftware fix for the M-190's. The M-215 fix should come, according toEnphase, by the end of March. It will be automatically downloaded throughthe Enlighten router. It's a known issue with Smart Meters with Enphase, but should bereconciled soon.Daryl DeJoyNABCEP Certified PV installerPenobscot Solar Designwww.penobscotsolar.comWrenchsters,I have an Enphase 7.5kW system on a residence with utility Smart Metering, both the PV Production Meter as well as the utility billing meter being "read" every hour. This system has experienced many "AC Frequency Out Of Range" events since the system was installed. Below is copied the Enphase Event message. This particular event was for 5 minutes. Most of the events (all events are AC Frequency Out Of Range) last 5 to 10 minutes but occasionally they have lasted from 45 minutes to64 minutes.My question is: Could the use of the smart metering increase the likely hood that AC Frequency events happen? Or is this just a coincidence and that we are dealing with fluctuating utility power AC Frequency issues?Started on: Mon February 04, 2013 12:49 PM ESTCleared on: Mon February 04, 2013 12:54 PM ESTRecommended actionThis condition should correct itself. No action is required.DetailsThe microinverter reports that the frequency coming from the utility is either too low or too high as specified by applicable regionalstandards.AC frequency is the frequency at which voltage varies on the utility grid.Frequency Out of Range events are usually transient and self-correcting by the utility.When the microinverter detects an out of frequency condition, it must remain offline until the utility has been within acceptable limits continuously for a short period of time (seconds to minutes, varies by region). If during that time the utility again exceeds or falls short of acceptable limits, the five-minute timer must restart and the microinverter may not begin producing power for an additional short period following the last out-of-bounds condition. Best,DaveDavid PalumboIndependent Power LLC462 Solar Way DriveHyde Park, VT 05655www.independentpowerllc.comVermont Solar Partner25 Years Experience, (802) 888-7194___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions  settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions  settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions  settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:

Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread penobscotsolar
Dave,
   It doesn't happen often, and the longest I've seen him stay down is
about a half hour, but it seems to get progressively worse as time goes
on for some reason (initially only the five minutes, but longer down
times lately). This particular customer is difficult and picky, to
boot. I hope yours is a bit kinder. Mine seems to think we did him an
injustice of monumental proportions.
   We have had the utility out there logging events, meetings with the
utility and another solar company in Maine to discuss all this, and
have kept Enphase in the loop throughout. Enphase has responded in a
responsible and reasonable manner throughout.
   If you want to discuss this with Enphase, call and ask for Bret. He's
the engineer I previously dealt with, although he is second tier, he is
accessible.




 Thanks Daryl. Does your system also sometimes stay off for longer periods
 sometimes? My clients system can stay off for up to 64 minutes.

 Dave

 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
 penobscotso...@midmaine.com
 Sent: Tuesday, February 05, 2013 12:01 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Enphase AC Frequency out of Range

 Dave,
   We have been having the same problem with an Enphase system in Maine. I
 have been dealing directly with the third tier engineers at Enphase and
 they
 are working on a software fix for this. Theevent itself is only a
 fraction
 of a second but IEEE requirements are that the inverter shut down for five
 minutes. I only found out about this problem when it started for this
 customer. It sems that Enphase has already addressed the problem with a
 software fix for the M-190's. The M-215 fix should come, according to
 Enphase, by the end of March. It will be automatically downloaded through
 the Enlighten router.
It's a known issue with Smart Meters with Enphase, but should be
 reconciled soon.

 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 www.penobscotsolar.com



 Wrenchsters,



 I have an Enphase 7.5kW system on a residence with utility Smart
 Metering, both the PV Production Meter as well as the utility billing
 meter being read every hour. This system has experienced many AC
 Frequency Out Of Range events since the system was installed. Below
 is copied the Enphase Event message. This particular event was for 5
 minutes. Most of the events (all events are AC Frequency Out Of Range)
 last 5 to 10 minutes but occasionally they have lasted from 45 minutes
 to
 64 minutes.



 My question is: Could the use of the smart metering increase the
 likely hood that AC Frequency events happen? Or is this just a
 coincidence and that we are dealing with fluctuating utility power AC
 Frequency issues?



 



 Started on: Mon February 04, 2013 12:49 PM EST

 Cleared on: Mon February 04, 2013 12:54 PM EST



 Recommended action



 This condition should correct itself. No action is required.

 Details



 The microinverter reports that the frequency coming from the utility
 is either too low or too high as specified by applicable regional
 standards.



 AC frequency is the frequency at which voltage varies on the utility
 grid.
 Frequency Out of Range events are usually transient and
 self-correcting by the utility.



 When the microinverter detects an out of frequency condition, it must
 remain offline until the utility has been within acceptable limits
 continuously for a short period of time (seconds to minutes, varies by
 region). If during that time the utility again exceeds or falls short
 of acceptable limits, the five-minute timer must restart and the
 microinverter may not begin producing power for an additional short
 period following the last out-of-bounds condition.  



 Best,

 Dave





 David Palumbo

 Independent Power LLC

 462 Solar Way Drive

 Hyde Park, VT 05655

 www.independentpowerllc.com

 Vermont Solar Partner

 25 Years Experience, (802) 888-7194



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: 

Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread penobscotsolar
Will do. Enphase had originally projected the beginning of February for
the release of the fix. It is now projected for the end of March. I am
hoping it will be a done deal before this next season starts here in
Maine. It might be good incentive to try Power One, Exeltech or other
inverters. In all honesty, my interpretation is that the Enphase inverters
are very sensitive and respond quickly to these pings. I believe the
software fix will allow the inverters to ignore micro-events of less than
1/100th of a second or so (the length of the ping. I will keep the list
in the loop!

Daryl




 We see the same issue here in WI.  Funny that you say 64 minutes, as some
 of the M215s show the error for 64 minutes for us routinely.  Could that
 just be some designated error reporting length?

 Daryl, thanks for the Enphase update.  Keep us updated if you can on the
 software fix.


 Ryan Harkins
 NABCEP Certified Solar PV Installer /
 Project Manager





 Synergy Renewable Systems, LLC
 PO Box 58
 Stoughton, WI 53589
 PH: 608-712-7862
 ryan.hark...@energycraft.com
 www.energycraft.com




 On Feb 5, 2013, at 11:10 AM, Dave Palumbo wrote:

 Thanks Daryl. Does your system also sometimes stay off for longer
 periods
 sometimes? My clients system can stay off for up to 64 minutes.

 Dave

 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
 penobscotso...@midmaine.com
 Sent: Tuesday, February 05, 2013 12:01 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Enphase AC Frequency out of Range

 Dave,
  We have been having the same problem with an Enphase system in Maine. I
 have been dealing directly with the third tier engineers at Enphase and
 they
 are working on a software fix for this. Theevent itself is only a
 fraction
 of a second but IEEE requirements are that the inverter shut down for
 five
 minutes. I only found out about this problem when it started for this
 customer. It sems that Enphase has already addressed the problem with a
 software fix for the M-190's. The M-215 fix should come, according to
 Enphase, by the end of March. It will be automatically downloaded
 through
 the Enlighten router.
   It's a known issue with Smart Meters with Enphase, but should be
 reconciled soon.

 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 www.penobscotsolar.com



 Wrenchsters,



 I have an Enphase 7.5kW system on a residence with utility Smart
 Metering, both the PV Production Meter as well as the utility billing
 meter being read every hour. This system has experienced many AC
 Frequency Out Of Range events since the system was installed. Below
 is copied the Enphase Event message. This particular event was for 5
 minutes. Most of the events (all events are AC Frequency Out Of Range)
 last 5 to 10 minutes but occasionally they have lasted from 45 minutes
 to
 64 minutes.



 My question is: Could the use of the smart metering increase the
 likely hood that AC Frequency events happen? Or is this just a
 coincidence and that we are dealing with fluctuating utility power AC
 Frequency issues?



 



 Started on: Mon February 04, 2013 12:49 PM EST

 Cleared on: Mon February 04, 2013 12:54 PM EST



 Recommended action



 This condition should correct itself. No action is required.

 Details



 The microinverter reports that the frequency coming from the utility
 is either too low or too high as specified by applicable regional
 standards.



 AC frequency is the frequency at which voltage varies on the utility
 grid.
 Frequency Out of Range events are usually transient and
 self-correcting by the utility.



 When the microinverter detects an out of frequency condition, it must
 remain offline until the utility has been within acceptable limits
 continuously for a short period of time (seconds to minutes, varies by
 region). If during that time the utility again exceeds or falls short
 of acceptable limits, the five-minute timer must restart and the
 microinverter may not begin producing power for an additional short
 period following the last out-of-bounds condition.  



 Best,

 Dave





 David Palumbo

 Independent Power LLC

 462 Solar Way Drive

 Hyde Park, VT 05655

 www.independentpowerllc.com

 Vermont Solar Partner

 25 Years Experience, (802) 888-7194



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 

Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread Dave Click
For these installations, do you guys have more information on the 
utilities' protocols that are causing problems with these inverters?


On 2013/2/5 12:51, penobscotso...@midmaine.com wrote:

Will do. Enphase had originally projected the beginning of February for
the release of the fix. It is now projected for the end of March. I am
hoping it will be a done deal before this next season starts here in
Maine. It might be good incentive to try Power One, Exeltech or other
inverters. In all honesty, my interpretation is that the Enphase inverters
are very sensitive and respond quickly to these pings. I believe the
software fix will allow the inverters to ignore micro-events of less than
1/100th of a second or so (the length of the ping. I will keep the list
in the loop!

Daryl





We see the same issue here in WI.  Funny that you say 64 minutes, as some
of the M215s show the error for 64 minutes for us routinely.  Could that
just be some designated error reporting length?

Daryl, thanks for the Enphase update.  Keep us updated if you can on the
software fix.


Ryan Harkins
NABCEP Certified Solar PV Installer /
Project Manager





Synergy Renewable Systems, LLC
PO Box 58
Stoughton, WI 53589
PH: 608-712-7862
ryan.hark...@energycraft.com
www.energycraft.com




On Feb 5, 2013, at 11:10 AM, Dave Palumbo wrote:


Thanks Daryl. Does your system also sometimes stay off for longer
periods
sometimes? My clients system can stay off for up to 64 minutes.

Dave

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
penobscotso...@midmaine.com
Sent: Tuesday, February 05, 2013 12:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase AC Frequency out of Range

Dave,
  We have been having the same problem with an Enphase system in Maine. I
have been dealing directly with the third tier engineers at Enphase and
they
are working on a software fix for this. Theevent itself is only a
fraction
of a second but IEEE requirements are that the inverter shut down for
five
minutes. I only found out about this problem when it started for this
customer. It sems that Enphase has already addressed the problem with a
software fix for the M-190's. The M-215 fix should come, according to
Enphase, by the end of March. It will be automatically downloaded
through
the Enlighten router.
   It's a known issue with Smart Meters with Enphase, but should be
reconciled soon.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design
www.penobscotsolar.com




Wrenchsters,



I have an Enphase 7.5kW system on a residence with utility Smart
Metering, both the PV Production Meter as well as the utility billing
meter being read every hour. This system has experienced many AC
Frequency Out Of Range events since the system was installed. Below
is copied the Enphase Event message. This particular event was for 5
minutes. Most of the events (all events are AC Frequency Out Of Range)
last 5 to 10 minutes but occasionally they have lasted from 45 minutes
to

64 minutes.




My question is: Could the use of the smart metering increase the
likely hood that AC Frequency events happen? Or is this just a
coincidence and that we are dealing with fluctuating utility power AC
Frequency issues?







Started on: Mon February 04, 2013 12:49 PM EST

Cleared on: Mon February 04, 2013 12:54 PM EST



Recommended action



This condition should correct itself. No action is required.

Details



The microinverter reports that the frequency coming from the utility
is either too low or too high as specified by applicable regional

standards.




AC frequency is the frequency at which voltage varies on the utility
grid.
Frequency Out of Range events are usually transient and
self-correcting by the utility.



When the microinverter detects an out of frequency condition, it must
remain offline until the utility has been within acceptable limits
continuously for a short period of time (seconds to minutes, varies by
region). If during that time the utility again exceeds or falls short
of acceptable limits, the five-minute timer must restart and the
microinverter may not begin producing power for an additional short
period following the last out-of-bounds condition.  



Best,

Dave





David Palumbo

Independent Power LLC

462 Solar Way Drive

Hyde Park, VT 05655

www.independentpowerllc.com

Vermont Solar Partner

25 Years Experience, (802) 888-7194



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: 

[RE-wrenches] Mobil inverter with Gen support

2013-02-05 Thread William Miller

Friends:

I am shopping for an inverter/charger that has true generator support and 
is available in a mobile configuration.  Can anyone suggest one?


I know Xantrex XW inverter were not available in mobile.  Outback FX do not 
have gen support.  I am looking to see if the Radian can be had in 
mobile.  I have heard the Sunny Island has gen support, but don't know yet 
if it is mobile capable.


Thanks in advance.

William Miller


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mobil inverter with Gen support

2013-02-05 Thread Roberto Kruse

  
  
William:
  
  Have a look at the Quattro inverter/charger from Victron Energy.
  
  Regards,
  


Roberto Kruse
Sistemas de Energa
t +506 2273 4545
f +506 2273 1010
email roberto.kr...@sercsa.com
www.sercsa.com
  



  
  El 5/2/2013 15:24, William Miller escribi:

Friends:
  
  
  I am shopping for an inverter/charger that has true generator
  support and is available in a mobile configuration. Can anyone
  suggest one?
  
  
  I know Xantrex XW inverter were not available in mobile. Outback
  FX do not have gen support. I am looking to see if the Radian can
  be had in mobile. I have heard the Sunny Island has gen support,
  but don't know yet if it is mobile capable.
  
  
  Thanks in advance.
  
  
  William Miller
  
  
  
  Miller Solar
  
  Voice :805-438-5600
  
  email: will...@millersolar.com
  
  http://millersolar.com
  
  License No. C-10-773985
  
  
  ___
  
  List sponsored by Home Power magazine
  
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  
  Options  settings:
  
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  
  List-Archive:
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  
  List rules  etiquette:
  
  www.re-wrenches.org/etiquette.htm
  
  
  Check out participant bios:
  
  www.members.re-wrenches.org
  
  


  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mobil inverter with Gen support

2013-02-05 Thread Larry Crutcher, Starlight Solar Power Systems
Hello William,

If by mobile you are referring to the neutral leg being switched then read on.

Depending on your definition of the term true, Magnum Energy has a very 
advanced AGS control for all their inverters, mobile and off grid. Two remotes 
are available. For the most advanced AGS control you will want the model ME-ARC 
remote and the ME-AGS-N. 

If you also install the ME-BMK (battery capacity meter), you can gen start and 
stop based on SoC. Very advanced and my favorite.

The manuals can be downloaded here for review: 
http://www.magnumenergy.com/Documents/DocsFront.htm


Larry Crutcher
Starlight Solar Power Systems



On Feb 5, 2013, at 2:24 PM, William Miller wrote:

Friends:

I am shopping for an inverter/charger that has true generator support and is 
available in a mobile configuration.  Can anyone suggest one?

I know Xantrex XW inverter were not available in mobile.  Outback FX do not 
have gen support.  I am looking to see if the Radian can be had in mobile.  I 
have heard the Sunny Island has gen support, but don't know yet if it is mobile 
capable.

Thanks in advance.

William Miller


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread Nick Soleil
Hi wrenches,

The frequency out of range issue is being caused by some utility meter's
communication ping.  This ping is actually affecting the utility voltage
and frequency, and can be viewed with a power quality analyzer.  It is
highly likely that this is affecting a wide variety of utility-interactive
inverters, but is only noticeable with the Enphase systems; due to the high
level of visibility that our Enlighten monitoring and reporting provides.

These changes required that the software undergo a new certification
process. We have completed our CSA certification of the new software, and
are validating it's functionality before pushing out the solution to our
entire population of microinverters.  We are in the process of beta testing
the software fix, and are hoping to have this resolved in February.

Thank you for your patience as we work to resolve this issue.


On Tue, Feb 5, 2013 at 9:24 AM, penobscotso...@midmaine.com wrote:

 Dave,
It doesn't happen often, and the longest I've seen him stay down is
 about a half hour, but it seems to get progressively worse as time goes
 on for some reason (initially only the five minutes, but longer down
 times lately). This particular customer is difficult and picky, to
 boot. I hope yours is a bit kinder. Mine seems to think we did him an
 injustice of monumental proportions.
We have had the utility out there logging events, meetings with the
 utility and another solar company in Maine to discuss all this, and
 have kept Enphase in the loop throughout. Enphase has responded in a
 responsible and reasonable manner throughout.
If you want to discuss this with Enphase, call and ask for Bret. He's
 the engineer I previously dealt with, although he is second tier, he is
 accessible.




  Thanks Daryl. Does your system also sometimes stay off for longer periods
  sometimes? My clients system can stay off for up to 64 minutes.
 
  Dave
 
  -Original Message-
  From: re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
  penobscotso...@midmaine.com
  Sent: Tuesday, February 05, 2013 12:01 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Enphase AC Frequency out of Range
 
  Dave,
We have been having the same problem with an Enphase system in Maine. I
  have been dealing directly with the third tier engineers at Enphase and
  they
  are working on a software fix for this. Theevent itself is only a
  fraction
  of a second but IEEE requirements are that the inverter shut down for
 five
  minutes. I only found out about this problem when it started for this
  customer. It sems that Enphase has already addressed the problem with a
  software fix for the M-190's. The M-215 fix should come, according to
  Enphase, by the end of March. It will be automatically downloaded through
  the Enlighten router.
 It's a known issue with Smart Meters with Enphase, but should be
  reconciled soon.
 
  Daryl DeJoy
  NABCEP Certified PV installer
  Penobscot Solar Design
  www.penobscotsolar.com
 
 
 
  Wrenchsters,
 
 
 
  I have an Enphase 7.5kW system on a residence with utility Smart
  Metering, both the PV Production Meter as well as the utility billing
  meter being read every hour. This system has experienced many AC
  Frequency Out Of Range events since the system was installed. Below
  is copied the Enphase Event message. This particular event was for 5
  minutes. Most of the events (all events are AC Frequency Out Of Range)
  last 5 to 10 minutes but occasionally they have lasted from 45 minutes
  to
  64 minutes.
 
 
 
  My question is: Could the use of the smart metering increase the
  likely hood that AC Frequency events happen? Or is this just a
  coincidence and that we are dealing with fluctuating utility power AC
  Frequency issues?
 
 
 
  
 
 
 
  Started on: Mon February 04, 2013 12:49 PM EST
 
  Cleared on: Mon February 04, 2013 12:54 PM EST
 
 
 
  Recommended action
 
 
 
  This condition should correct itself. No action is required.
 
  Details
 
 
 
  The microinverter reports that the frequency coming from the utility
  is either too low or too high as specified by applicable regional
  standards.
 
 
 
  AC frequency is the frequency at which voltage varies on the utility
  grid.
  Frequency Out of Range events are usually transient and
  self-correcting by the utility.
 
 
 
  When the microinverter detects an out of frequency condition, it must
  remain offline until the utility has been within acceptable limits
  continuously for a short period of time (seconds to minutes, varies by
  region). If during that time the utility again exceeds or falls short
  of acceptable limits, the five-minute timer must restart and the
  microinverter may not begin producing power for an additional short
  period following the last out-of-bounds condition.  
 
 
 
  Best,
 
  Dave
 
 
 
 
 
  David Palumbo
 
  Independent Power LLC
 
  462 Solar Way Drive
 
  Hyde Park, VT 05655
 
  

Re: [RE-wrenches] Hawaii Frequency Settings

2013-02-05 Thread Nick Soleil
Yes Mark,

Enphase sets the alternate grid parameters for HI remotely, and will send a
letter of confirmation directly to the utility on your behalf.  We have
preset grid parameters for HECO and MECO.


On Mon, Feb 4, 2013 at 3:44 PM, Mark Frye ma...@berkeleysolar.com wrote:

 Folks,

 ** **

 I was told that because the HI grid has poor frequency control, grid-tied
 inverters have to have their low frequency limit set to 57 Hz so they can
 ride out the worst low frequency events.

 ** **

 I find it hard to believe that this has been done for every single
 inverter installed in HI.

 ** **

 But, what do I know.

 ** **

 Can anyone shed some light on this?

 ** **

 Thanks,

 ** **

 Mark Frye

 Berkeley Solar Electric Systems

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

*
*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

1420 North McDowell

Petaluma, CA 94954

www.enphase.com http://www.enphaseenergy.com/

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsol...@enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 

image002.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mobil inverter with Gen support

2013-02-05 Thread William Miller

Larry:

By true generator support, I do not mean generator start functions.  I mean 
the ability of the inverter to sense when the attached generator is being 
asked to provide beyond rated amperage and syncing with the generator and 
assisting in powering loads.  Does the Magnum do this?  I read the manual 
and did not see this function.


William Miller

PS:  Xantrex SW, Xantrex XW, Outback Radian and Sunny Island all do 
this.  I don't think any of them provide neutral switching.


Wm



At 02:22 PM 2/5/2013, you wrote:

Hello William,

If by mobile you are referring to the neutral leg being switched then read on.

Depending on your definition of the term true, Magnum Energy has a very 
advanced AGS control for all their inverters, mobile and off grid. Two 
remotes are available. For the most advanced AGS control you will want the 
model ME-ARC remote and the ME-AGS-N.


If you also install the ME-BMK (battery capacity meter), you can gen start 
and stop based on SoC. Very advanced and my favorite.


The manuals can be downloaded here for review: 
http://www.magnumenergy.com/Documents/DocsFront.htm



Larry Crutcher
Starlight Solar Power Systems



On Feb 5, 2013, at 2:24 PM, William Miller wrote:

Friends:

I am shopping for an inverter/charger that has true generator support and 
is available in a mobile configuration.  Can anyone suggest one?


I know Xantrex XW inverter were not available in mobile.  Outback FX do 
not have gen support.  I am looking to see if the Radian can be had in 
mobile.  I have heard the Sunny Island has gen support, but don't know yet 
if it is mobile capable.


Thanks in advance.

William Miller


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5582 - Release Date: 02/04/13 
22:19:00


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Mobil inverter with Gen support

2013-02-05 Thread Larry Crutcher, Starlight Solar Power Systems
I see. That feature is coming this year in 3 new inverter models from Magnum. 
They will share up to full output with the generator. The 12 volt will be 3kW, 
the other two will be 24v, 4kW, one with dual AC inputs.

Xantrex has one 3kW 12 volt model with gen support but I have seen quite a few 
failures so I do not recommend them. Also, they are made in China while the 
Magnums are US made. 
If interested see here:
http://www.xantrex.com/power-products/inverter-chargers/freedom-sw-12v_newgen.aspx

Larry Crutcher
Starlight Solar Power Systems




On Feb 5, 2013, at 4:23 PM, William Miller wrote:

Larry:

By true generator support, I do not mean generator start functions.  I mean the 
ability of the inverter to sense when the attached generator is being asked to 
provide beyond rated amperage and syncing with the generator and assisting in 
powering loads.  Does the Magnum do this?  I read the manual and did not see 
this function.

William Miller

PS:  Xantrex SW, Xantrex XW, Outback Radian and Sunny Island all do this.  I 
don't think any of them provide neutral switching.

Wm



At 02:22 PM 2/5/2013, you wrote:
 Hello William,
 
 If by mobile you are referring to the neutral leg being switched then read on.
 
 Depending on your definition of the term true, Magnum Energy has a very 
 advanced AGS control for all their inverters, mobile and off grid. Two 
 remotes are available. For the most advanced AGS control you will want the 
 model ME-ARC remote and the ME-AGS-N.
 
 If you also install the ME-BMK (battery capacity meter), you can gen start 
 and stop based on SoC. Very advanced and my favorite.
 
 The manuals can be downloaded here for review: 
 http://www.magnumenergy.com/Documents/DocsFront.htm
 
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 On Feb 5, 2013, at 2:24 PM, William Miller wrote:
 
 Friends:
 
 I am shopping for an inverter/charger that has true generator support and is 
 available in a mobile configuration.  Can anyone suggest one?
 
 I know Xantrex XW inverter were not available in mobile.  Outback FX do not 
 have gen support.  I am looking to see if the Radian can be had in mobile.  I 
 have heard the Sunny Island has gen support, but don't know yet if it is 
 mobile capable.
 
 Thanks in advance.
 
 William Miller
 
 
 Miller Solar
 Voice :805-438-5600
 email: will...@millersolar.com
 http://millersolar.com
 License No. C-10-773985
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 No virus found in this incoming message.
 Checked by AVG - www.avg.com
 Version: 8.5.455 / Virus Database: 271.1.1/5582 - Release Date: 02/04/13 
 22:19:00

Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase AC Frequency out of Range

2013-02-05 Thread penobscotsolar
Thanks for the succinct explanation Nick. I look forward to the fix. Like
you, I believe this is happening with other inverters, but lacking the
level of monitoring available with Enphase, people just aren't aware it is
happening.

Daryl



 Hi wrenches,

 The frequency out of range issue is being caused by some utility meter's
 communication ping.  This ping is actually affecting the utility voltage
 and frequency, and can be viewed with a power quality analyzer.  It is
 highly likely that this is affecting a wide variety of utility-interactive
 inverters, but is only noticeable with the Enphase systems; due to the
 high
 level of visibility that our Enlighten monitoring and reporting provides.

 These changes required that the software undergo a new certification
 process. We have completed our CSA certification of the new software, and
 are validating it's functionality before pushing out the solution to our
 entire population of microinverters.  We are in the process of beta
 testing
 the software fix, and are hoping to have this resolved in February.

 Thank you for your patience as we work to resolve this issue.


 On Tue, Feb 5, 2013 at 9:24 AM, penobscotso...@midmaine.com wrote:

 Dave,
It doesn't happen often, and the longest I've seen him stay down is
 about a half hour, but it seems to get progressively worse as time goes
 on for some reason (initially only the five minutes, but longer down
 times lately). This particular customer is difficult and picky, to
 boot. I hope yours is a bit kinder. Mine seems to think we did him an
 injustice of monumental proportions.
We have had the utility out there logging events, meetings with the
 utility and another solar company in Maine to discuss all this, and
 have kept Enphase in the loop throughout. Enphase has responded in a
 responsible and reasonable manner throughout.
If you want to discuss this with Enphase, call and ask for Bret. He's
 the engineer I previously dealt with, although he is second tier, he is
 accessible.




  Thanks Daryl. Does your system also sometimes stay off for longer
 periods
  sometimes? My clients system can stay off for up to 64 minutes.
 
  Dave
 
  -Original Message-
  From: re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
  penobscotso...@midmaine.com
  Sent: Tuesday, February 05, 2013 12:01 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] Enphase AC Frequency out of Range
 
  Dave,
We have been having the same problem with an Enphase system in
 Maine. I
  have been dealing directly with the third tier engineers at Enphase
 and
  they
  are working on a software fix for this. Theevent itself is only a
  fraction
  of a second but IEEE requirements are that the inverter shut down for
 five
  minutes. I only found out about this problem when it started for this
  customer. It sems that Enphase has already addressed the problem with
 a
  software fix for the M-190's. The M-215 fix should come, according to
  Enphase, by the end of March. It will be automatically downloaded
 through
  the Enlighten router.
 It's a known issue with Smart Meters with Enphase, but should be
  reconciled soon.
 
  Daryl DeJoy
  NABCEP Certified PV installer
  Penobscot Solar Design
  www.penobscotsolar.com
 
 
 
  Wrenchsters,
 
 
 
  I have an Enphase 7.5kW system on a residence with utility Smart
  Metering, both the PV Production Meter as well as the utility billing
  meter being read every hour. This system has experienced many AC
  Frequency Out Of Range events since the system was installed. Below
  is copied the Enphase Event message. This particular event was for 5
  minutes. Most of the events (all events are AC Frequency Out Of
 Range)
  last 5 to 10 minutes but occasionally they have lasted from 45
 minutes
  to
  64 minutes.
 
 
 
  My question is: Could the use of the smart metering increase the
  likely hood that AC Frequency events happen? Or is this just a
  coincidence and that we are dealing with fluctuating utility power AC
  Frequency issues?
 
 
 
  
 
 
 
  Started on: Mon February 04, 2013 12:49 PM EST
 
  Cleared on: Mon February 04, 2013 12:54 PM EST
 
 
 
  Recommended action
 
 
 
  This condition should correct itself. No action is required.
 
  Details
 
 
 
  The microinverter reports that the frequency coming from the utility
  is either too low or too high as specified by applicable regional
  standards.
 
 
 
  AC frequency is the frequency at which voltage varies on the utility
  grid.
  Frequency Out of Range events are usually transient and
  self-correcting by the utility.
 
 
 
  When the microinverter detects an out of frequency condition, it must
  remain offline until the utility has been within acceptable limits
  continuously for a short period of time (seconds to minutes, varies
 by
  region). If during that time the utility again exceeds or falls short
  of acceptable limits, the five-minute timer must restart 

[RE-wrenches] Simplified permit process

2013-02-05 Thread Allan Sindelar

  
  
A bill has been introduced in our 60-day state legislative session
to direct our statewide licensing agency to develop a consistent set
of permitting standards for PV systems. Like many states, we suffer
a confusing matrix of differing local standards, costs and
requirements. I would like to testify at a legislative committee
hearing in favor of a common standard.

We have our own matrix spreadsheet, and we have the Solar ABCs'
Expedited Process as developed by Bill Brooks and others. What I'm
looking for are links to the best short, nontechnical and easily
read articles about how the permit process has become a large
portion of the cost of all PV systems, how it's holding back the
adoption and growth of PV, how the Obama administration has
recognized this as one of the structural barriers to more renewables
adoption, and the like. The best I can find will get printed out and
given to the legislators.

I have seen many of these articles, on Renewable Energy World and
other media, but have never saved them, of course. That's why I'm
asking for this assistance. Many of us are facing the same issues in
our jurisdictions.

Thank you,
Allan
-- 
  
  
  Allan Sindelar
  al...@positiveenergysolar.com
NABCEP Certified Photovoltaic
  Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc.
  3209 Richards Lane (note new address)
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com
  
  
  
   
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org