Re: [RE-wrenches] UL warns of counterfeit UL Mark on photovoltaic panels

2013-04-17 Thread Dave Click
Wrenches will especially enjoy the IMP and ISC values, pictured in the 
final image of the UL notice.



On 2013/4/16 13:29, Jason Szumlanski wrote:
Ray Johnson in Florida has done an excellent job documenting this 
fiasco on his blow in the article below and several other articles.


http://www.renewableenergyworld.com/rea/blog/post/2013/04/solar-contractors-installers-beware-of-the-panel-warranty-bait-switch

W
e lost several jobs to this company in the past due to unsustainable 
low competitive prices. I was sounding the alarm on this a couple of 
years ago - I thought they were dumping product on the market to 
establish their contracting/sales arm. It seems they were up to much 
more than that.


*Jason Szumlanski*

/Fafco Solar/



On Tue, Apr 16, 2013 at 11:16 AM, Nik Ponzio 
npon...@buildingenergyus.com mailto:npon...@buildingenergyus.com 
wrote:



http://www.ul.com/global/eng/pages/newsroom/publicnotices/detail/index.jsp?cpath=/global/eng/pages/newsroom/publicnotices/detail/data/ul-warns-of-counterfeit-ul-mark-on-photovoltaic_2013041507.xml


  UL warns of counterfeit UL Mark on photovoltaic panels (Release
  13PN-20)

*NORTHBROOK, IL - April 15, 2013 -* The following is a
notification from UL to Authorities Having Jurisdiction,
distributors, installers and users that the photovoltaic panels
identified below bear counterfeit UL Marks for the United States
and Canada . The photovoltaic (solar) panels have not been
evaluated by UL to the appropriate Standards for Safety and it is
unknown if these photovoltaic panels comply with UL's safety
requirements for the United States or Canada.

*Name of Product:*

ASP - Advanced Solar Photonics (also known as Bluechip Energy)
Models AP-240PK, AP-245MK and ASP-390M

Note that ASP is a tradename for the parent company Bluechip
Energy LLC

*Identification: */On the product:/   The products bear a
counterfeit UL Mark and one of the markings shown below:

Note that the labels include additional electrical rating
information, but the values may differ from that shown in the
photographs below.

*Photos of Product: *

*Photo of typical installation*

**

*Counterfeit nameplate from Model AP-240PK*

The nameplate label for Model AP-245MK is identical to the label
above except for Model number and electrical ratings.

**

*Counterfeit nameplate from Model ASP-390M*

**

*Sold at: *Known to be sold by SunWorks Solar and may be sold by
other distributors



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-17 Thread Garrison Riegel
Hi Ray,

Not saying he was right, but it was explained to me by an inspector that the
pipe electrode mentioned in 250.166(C) is different than a water main. The
justification being that 250.52(A)(1) lists requirements for a metal
underground water pipe electrode, while 250.52(A)(5) lists pipe electrode
separately.  I agree a water main fits the description of a pipe, but I
suppose it could depend on the mood of the inspector.  I've managed to avoid
it myself, but have heard horror stories of 4/0 GECs being required by
inspectors.

Good point about 250.53(D)(2) Supplemental Electrode Required.  Although it
does list a pipe again as a possible supplemental electrode to the water
main.  

250.166(C) just seems a little unclear with respect to a water main
electrode.  I have seen a number of sites that do not have a supplemental
electrode in addition to the water main, but I suppose you could simply
install a rod, bond it to the water main, and use #6 copper for the DC GEC.

Thanks,

Garrison



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, April 16, 2013 2:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

First, a water main is no longer allowed to be used as the primary grounding
electrode by itself, it needs an additional electrode added to it 25053(D)2.
You still are required to bond to it 250.104(A)1,  but it doesn't count as
the electrode.  Also, 250.166 (C) specifically lists pipe as one of the
exceptions.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 1:06 PM, Garrison Riegel wrote:
 Hi Ray and All,

 250.166 says the GEC must be sized as specified in (A) Not smaller 
 than the neutral conductor, or (B) Not smaller than the largest 
 conductor supplied by the system, except as permitted by (C) through (E).

 A water main [as in 250.52(A)(1)] is not listed as an exception in (C) 
 through (E). So if the GE is a water main wouldn't the GEC need to 
 be 4/0, if the battery cables were 4/0?  Not saying it makes sense, 
 especially if the water main is 3/4, but this has always made me wonder.

 Thoughts?

 Garrison Riegel
 Project Manager | Solar Service Inc
 [p] 847-677-0950 | garri...@solarserviceinc.com

 NABCEP Certified PV Installation ProfessionalT


 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray 
 Walters
 Sent: Tuesday, April 16, 2013 12:52 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

 Hi Drake;

 Read down a bit more and 250.166(C) and (D) limit the size of the GEC 
 to
 #4 or #6 max., depending on what electrode is used.
 This used to not be the case, and systems in the 90s had 4/0 cable to a
5/8
 electrode: which just like your 1/2 pipe example was absolutely
ridiculous.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760

 On 4/16/2013 9:31 AM, Drake wrote:

 So, in a standard battery system, with a charge control, ground fault 
 protection and an array, the DC system will likely need grounding. If 
 the DC system is grounded, then the battery cables are grounded also.
 In 250.166 (B) it says the grounding electrode conductor (GEC) shall 
 not be smaller than the largest conductor supplied by the system.

 If the battery cables are supplied by the system doesn't this imply 
 that the GEC should be the size of the battery cable?  This is the 
 logic that has led some inspectors to require a 4/0 copper wire to be 
 bonded to a 1/2 water pipe. This is, of course, technically absurd.
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

Re: [RE-wrenches] UL warns of counterfeit UL Mark on photovoltaic panels

2013-04-17 Thread Jason Szumlanski
Neat trick! Nice catch!

*Jason Szumlanski** *

*Fafco Solar* 
http://www.wisestamp.com/apps/wordpress?utm_source=extensionutm_medium=emailutm_term=wordpressutm_campaign=apps



On Wed, Apr 17, 2013 at 9:22 AM, Dave Click davecl...@fsec.ucf.edu wrote:

  Wrenches will especially enjoy the IMP and ISC values, pictured in the
 final image of the UL notice.


 On 2013/4/16 13:29, Jason Szumlanski wrote:

  Ray Johnson in Florida has done an excellent job documenting this fiasco
 on his blow in the article below and several other articles.


 http://www.renewableenergyworld.com/rea/blog/post/2013/04/solar-contractors-installers-beware-of-the-panel-warranty-bait-switch

 W
 e lost several jobs to this company in the past due to unsustainable low
 competitive prices. I was sounding the alarm on this a couple of years ago
 - I thought they were dumping product on the market to establish their
 contracting/sales arm. It seems they were up to much more than that.

   *Jason Szumlanski*

 *Fafco Solar*


 On Tue, Apr 16, 2013 at 11:16 AM, Nik Ponzio npon...@buildingenergyus.com
  wrote:


 http://www.ul.com/global/eng/pages/newsroom/publicnotices/detail/index.jsp?cpath=/global/eng/pages/newsroom/publicnotices/detail/data/ul-warns-of-counterfeit-ul-mark-on-photovoltaic_2013041507.xml

   UL warns of counterfeit UL Mark on photovoltaic panels (Release
 13PN-20)

 *NORTHBROOK, IL - April 15, 2013 -* The following is a notification from
 UL to Authorities Having Jurisdiction, distributors, installers and users
 that the photovoltaic panels identified below bear counterfeit UL Marks for
 the United States and Canada . The photovoltaic (solar) panels have not
 been evaluated by UL to the appropriate Standards for Safety and it is
 unknown if these photovoltaic panels comply with UL's safety requirements
 for the United States or Canada.

 *Name of Product:*

 ASP - Advanced Solar Photonics (also known as Bluechip Energy)
 Models AP-240PK, AP-245MK and ASP-390M

 Note that ASP is a tradename for the parent company Bluechip Energy LLC

 *Identification:   **On the product:*   The products bear a counterfeit
 UL Mark and one of the markings shown below:







 Note that the labels include additional electrical rating information,
 but the values may differ from that shown in the photographs below.

 *Photos of Product: *

 *Photo of typical
 installation*

 * *

 *Counterfeit nameplate from Model AP-240PK*



 The nameplate label for Model AP-245MK is identical to the label above
 except for Model number and electrical ratings.

 **

 *Counterfeit nameplate from Model ASP-390M*

 * *

 *Sold at:  *Known to be sold by SunWorks Solar and may be sold by other
 distributors



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  
 settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:www.re-wrenches.org/etiquette.htm

 Check out participant bios:www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fuse sizing in battery circuits

2013-04-17 Thread Ray Walters
A metal underground water pipe is still a pipe in all cases, so I 
think I'm missing your inspector's logic.  A water main is always going 
to be made out of pipe, so I think the exception to 250.166 (C) should 
always apply. (unless some places make them square?;-) ) The difference 
in pipe between 250.52A1 and A5 is that one is a pipe set in the ground 
by an electrician with the sole purpose of being a grounding electrode, 
while the other is used for water and is set by the plumber.  The reason 
I heard that water lines into the house had to have supplementary 
grounding is that they often transition to PVC and so aren't always 
continuous metal.  They also might be cut and changed later by a 
plumber.  That also was a change from earlier code, that used to allow 
the water main to be used as the sole grounding electrode.  EIther way, 
250.166 does not make a distinction, it just says Pipe and would cover 
all GEC connections.


The 4/0 GEC horror stories probably are from earlier editions of the 
code.  BIll Brooks can tell us when that changed.  My guess is that it 
was a pre 2002 code requirement, as I saw that on 90s PV systems.
Your final suggested install should be code compliant with all the 
various NEC sections (IMHO); just use a lay in lug type pipe grounding 
clamp, to keep the GEC continuous to the rod.
Some of this code stuff makes you wonder whether we should have studied 
law to be a Wrench.(ugh)


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/17/2013 7:44 AM, Garrison Riegel wrote:

Hi Ray,

Not saying he was right, but it was explained to me by an inspector that the
pipe electrode mentioned in 250.166(C) is different than a water main. The
justification being that 250.52(A)(1) lists requirements for a metal
underground water pipe electrode, while 250.52(A)(5) lists pipe electrode
separately.  I agree a water main fits the description of a pipe, but I
suppose it could depend on the mood of the inspector.  I've managed to avoid
it myself, but have heard horror stories of 4/0 GECs being required by
inspectors.

Good point about 250.53(D)(2) Supplemental Electrode Required.  Although it
does list a pipe again as a possible supplemental electrode to the water
main.

250.166(C) just seems a little unclear with respect to a water main
electrode.  I have seen a number of sites that do not have a supplemental
electrode in addition to the water main, but I suppose you could simply
install a rod, bond it to the water main, and use #6 copper for the DC GEC.

Thanks,

Garrison



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Tuesday, April 16, 2013 2:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

First, a water main is no longer allowed to be used as the primary grounding
electrode by itself, it needs an additional electrode added to it 25053(D)2.
You still are required to bond to it 250.104(A)1,  but it doesn't count as
the electrode.  Also, 250.166 (C) specifically lists pipe as one of the
exceptions.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 1:06 PM, Garrison Riegel wrote:

Hi Ray and All,

250.166 says the GEC must be sized as specified in (A) Not smaller
than the neutral conductor, or (B) Not smaller than the largest
conductor supplied by the system, except as permitted by (C) through (E).

A water main [as in 250.52(A)(1)] is not listed as an exception in (C)
through (E). So if the GE is a water main wouldn't the GEC need to
be 4/0, if the battery cables were 4/0?  Not saying it makes sense,
especially if the water main is 3/4, but this has always made me wonder.

Thoughts?

Garrison Riegel
Project Manager | Solar Service Inc
[p] 847-677-0950 | garri...@solarserviceinc.com

NABCEP Certified PV Installation ProfessionalT


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray
Walters
Sent: Tuesday, April 16, 2013 12:52 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fuse sizing in battery circuits

Hi Drake;

Read down a bit more and 250.166(C) and (D) limit the size of the GEC
to
#4 or #6 max., depending on what electrode is used.
This used to not be the case, and systems in the 90s had 4/0 cable to a

5/8

electrode: which just like your 1/2 pipe example was absolutely

ridiculous.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/16/2013 9:31 AM, Drake wrote:

So, in a standard battery system, with a charge control, ground fault
protection and an array, the DC system will likely need grounding. If
the DC system is grounded, then the battery cables are grounded also.
In 250.166 (B) it says 

Re: [RE-wrenches] Outback wave form

2013-04-17 Thread Steve Jefferson
Bruce,

Please call me, I have a fix for your issue.

SMA America, LLC
Steve Jefferson
Supervisor, Service Line
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: steve.jeffer...@sma-america.com
www.SMA-America.com
 
This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bruce Erickson
Sent: Tuesday, April 16, 2013 11:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback wave form

I'm having a similar issue with a GRID-TIE inverter just now. SMA 5000US which, 
when it wakes up every morning, removes the date and time from the programming 
in the customers' Monitor brand kerosene heater. They have to re-enter it 
daily, which is annoying enough, but when they go out of town, they have to 
leave the inverter off to avoid coming home to a cold house.

So far SMA has had us move the breaker as far as possible from the heater 
breaker, to no avail. They had no other suggestions. I used a Panamax plug-in 
power conditioner with 50 dB of EMI filtering on the heater outlet, which has 
reduced the frequency of the problem to once a day, when it wakes up, from a 
few times a day. Trying a different heater is out of the question due to cost, 
so I'm stumped as how to avoid an unhappy customer, unless the answer is 
experimenting with more robust power conditioners.

Bruce Erickson
Mendocino Solar Service
PO Box 1252
Mendocino, CA 95460
707-937-1701
707-937-1741 fax
br...@mendocinosolar.com




On Apr 16, 2013, at 11:12 AM, Dave Palumbo wrote:

 Jeremy,
 
  What to look for? 
 
 Unfortunately, probably a different coffee maker. 
 I've gone through this with several different appliances over the 
 years on sine wave inverter output. Washing machines, refrigerators, 
 dishwashers it could be anything with electronics. Specific 
 manufacturers typically cannot be avoided in order to solve this 
 issue. Year to year manufacturers may change the design of their 
 appliances, so blanket statements on what works and what doesn't are 
 unreliable. All appliances (excepting a few) are designed to operate 
 on utility power, not inverter power. Inverter power (excepting 
 Exeltech and possibly others) typically has more distortion than 
 utility power. Some appliances cannot tolerate the simulated inverter 
 sine wave power. I always council my inverter customers that I cannot 
 guarantee that all appliances with work flawlessly and that some may not work 
 at all.
 I advise off-grid clients to buy appliances where there is a liberal 
 return policy.
 
 David Palumbo
 Independent Power LLC
 462 Solar Way Drive
 Hyde Park, VT 05655
 www.independentpowerllc.com
 Vermont Solar Partner
 25 Years Experience, (802) 888-7194
 
 
 
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of All Solar
 Sent: Tuesday, April 16, 2013 12:47 PM
 To: re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] Outback wave form
 
 Have a client with a new coffee maker that will not run from their new dual
 outback setup. Has anyone heard of this lately. We have had no problems with
 appliances and sine wave inverters. What to look for?
 
 Sent from Jeremy's IPhone.  Sorry for typos and shorthand!
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


Re: [RE-wrenches] Advanced PV Training Solar Living Institute - class needs students

2013-04-17 Thread SunHarvest
On the off-chance that anyone out there is interested in an advanced off-grid 
training class on the 25th  26th of this month for about $400 in Hopland, CA...

The advanced off-grid course (PV 290) needs more participants lest it should be 
postponed until October. Just thought I'd post because I was planning to take 
this course...

Eric
SunHarvest

- Original Message - 
  From: Jesse Dahl 
  To: RE-wrenches 
  Sent: Friday, April 12, 2013 7:49 PM
  Subject: Re: [RE-wrenches] Advanced PV Training Recommendations


  The MREA (Midwest renewable energy association) offers classes, some on-line 
now. Really good Instructors. 


  www.midwestrenew.org


  Jesse

  Sent from my iPhone

  On Apr 12, 2013, at 8:03 PM, jay peltz j...@asis.com wrote:


HI Eric,


I'm going to advise you to look at SEI
Solar energy international.


http://www.solarenergy.org/


Full disclosure, I teach part time from them.


Cheers,


jay


peltz power


On Apr 12, 2013, at 12:46 PM, SunHarvest wrote:


  Wrenchers -

  I am in need of hands-on advanced training for my own continuing 
education. I have a California C46 solar contractor's license and plenty of 
experience designing and installing systems. But, as you all know, there are 
always more details to master, code issues to be clarified, and new 
technologies coming down the pike. I'd like to focus on off-grid and on-grid 
w/BB systems over straight grid-tie.

  I'm looking at Solar Living Institute as that's here in NorCal, where I 
live.

  Are there any training schools/programs that you guys would recommend?

  My main requirements are that the instructor has 20+ years of hands-on 
experience and that the training is hands-on and fully comprehensive. I am 
interested in getting NABCEP certified but I'm more concerned with getting 
professional, in-depth training than with qualifying for NABCEP exam 
requirements.

  Thanks!

  Eric
  SunHarvest


  - Original Message -
From: John Berdner
To: RE-wrenches
Sent: Thursday, April 04, 2013 11:44 AM
Subject: Re: [RE-wrenches] Combining conductors


Larry:

Yes, you can parallel conductors (there is an NEC limit on minimum size 
allowed to parallel).
You just add the ampacity of the two conductors.
To convince yourself you can also check Table 8 Conductor Properties 
and sum the cross sectional areas of all the parallel conductors to see the 
equivalency to a single larger conductor.

Best Regards,

John Berdner
General Manager, North America

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new 
address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher, 
Starlight Solar Power Systems
Sent: Thursday, April 04, 2013 9:51 AM
To: RE-wrenches
Subject: [RE-wrenches] Combining conductors

Wrenches,

Here's a tough one for me to understand. I am installing 2 volt AGM 
batteries. There are two terminals for each battery polarity. I have some 
height limits so I need to use the minimum wire size. Here's my question: If I 
combine two identical conductors, what is the equivalent single conductor size? 

I found one rule of thumb that says doubling like conductors creates 
a AWG decrease of 3. Example: two #2 will be equivalent to 2/0. Is this true?

Thank you,

Larry Crutcher
Starlight Solar Power Systems







CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended 
only for the use of the individual or entity who is the intended recipient and 
may contain information that is privileged, confidential and exempt from 
disclosure or any type of use under applicable law. If the reader of this 
e-mail is not the intended recipient, or the employee, agent, or representative 
responsible for delivering the e-mail to the intended recipient, you are hereby 
notified that any dissemination, distribution, copying, or other use of this 
e-mail is strictly prohibited. If you have received this e-mail in error, 
please reply immediately to the sender. 
P  Please think of the environment before printing this email







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:

Re: [RE-wrenches] Outback wave form

2013-04-17 Thread Ray Walters
The old 50uF cap trick worked on Trace SW Inverters as well to run other 
Hi Efficiency washers.  I thought it was the zero crossing issue, but 
what you're showing for PF makes more sense.  I knew the caps worked, I 
just didn't fully understand why.  Thanks, Larry.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 4/17/2013 1:09 PM, Larry Crutcher, Starlight Solar Power Systems wrote:

We experience issues like this from time to time. PF seems to be the culprit. Have 
you measured it or looked at the waveform yet?  How an inverter deals with PF seems 
to vary broadly. For example, the Splendide XC2100 washer/dryer will not work on a 
Magnum Energy and a few other sine wave inverters. However,  it will run on a low 
cost GoPower or Samlex sine wave inverter. Below is a scope trace of 
voltage/current of the Magnum inverter  Splendide washer. Upper trace is 
voltage





By adding a 50uF run capacitor inline, it somewhat tames the current phase and 
the sine wave so the Magnum can operate the washer.




(Special thanks to Al for the discovery and photos)

Larry Crutcher
Starlight Solar Power Systems


On Apr 16, 2013, at 9:46 AM, All Solar allso...@scswifi.net wrote:

Have a client with a new coffee maker that will not run from their new dual 
outback setup. Has anyone heard of this lately. We have had no problems with 
appliances and sine wave inverters. What to look for?

Sent from Jeremy's IPhone.  Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] BP SX mods and inverter failure?

2013-04-17 Thread jason pozner
Hi all,

I know the BP SX module failure has come up often on past posts, but I was
wondering if anyone has seen the failures effecting the systems inverters.
I have inherited several systems from an installer who is no longer in the
area.  I have been picking up the task of replacing the failed/or failing
modules over the last few years.  The two catastrophic failures of the
modules I have seen (melted j-boxes, and spidered glass) have also been
connected to a inverter (2 different models) that has failed.  The OCP has
checked out, ground fault fuses intact, no evidence of hot/melted wires
(other than the failed mods).  This could be coincidence , or not?
Questions of replacing the inverter, and having the remaining modules still
in service is a concern.  Just seeing if any of you have seen anything
similar. Also  wondering if anyone has some insight unto trying to test
mods that don't have the signature burn marks, or come up with a compelling
case for a full array replacement.  It seems my last BP contact is no
longer with them, and not sure how this round will turn out.

Thanks,

Jay Poz
www.nunatakenergy.com
970-349-3432
NABCEP Certified PV Installer:
Cert.#031310-177
IREC Affiliated Instructor
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase compatibility heads up

2013-04-17 Thread Nick Soleil
Hi William,

You can use the Sharp 235s with M190s.  The M190s will work with all 60
cell and 72 cell products.


On Tue, Apr 16, 2013 at 4:54 PM, William Miller will...@millersolar.comwrote:

 Colleagues:

 I had occasion today to use the Enphase on-line compatibility calculator.
  My client bought some modules and M190 inverters from an E-bay vendor.
  The exact module model number was not listed on the compatibility list so
 I was recommended by Enphase to use the calculator.

 The result showed the module was compatible only with the M215 inverter.
  Further research revealed that the calculator will never indicate
 compatibility with M190s even if your module is indeed compatible.  The
 reason I was given for this is that since Enphase no longer makes M190s the
 calculator would not recommend them.

 This is silly since we still encounter M190s in the field.  Be aware of
 this situation if you ever need to use the calculator.  I informed the
 customer support person of this concern and recommended that this tool be
 corrected to show all compatibilities.  I don't know if they will change
 this, but I hope so.

 By the way does anyone know if the Sharp NU-US235F9 BX modules will work
 with the Enphase M190? It appears so, but I don't want to recommend
 something that does not work.

 Thanks,

 William




 Miller Solar
 Voice :805-438-5600
 email: will...@millersolar.com
 http://millersolar.com
 License No. C-10-773985

 __**_
 List sponsored by Home Power magazine

 List Address: 
 re-wrenc...@lists.re-wrenches.**orgRE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/**options.cgi/re-wrenches-re-**wrenches.orghttp://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: http://lists.re-wrenches.org/**pipermail/re-wrenches-re-**
 wrenches.orghttp://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.**htmhttp://www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

*
*http://www.enphase.com/commercial?utm_source=emailutm_medium=sigutm_campaign=Comm2012

1420 North McDowell

Petaluma, CA 94954

www.enphase.com http://www.enphaseenergy.com/

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsol...@enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 

image002.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback wave form

2013-04-17 Thread Exeltech
Wrenches,

While the addition of a capacitor may resolve issues associated with various
inverter/appliance/motor combinations, please make sure the capacitor(s) get
switched OUT of the circuit (disconnected) when the load itself is disconnected.

Failure to do so could under some circumstances cause the inverter control-loop
circuitry to go unstable, leading to unpredictable inverter operation, and 
possible
damage/failure in the power system.  Disconnecting the capacitor with the load
alleviate this possibility.


Regards to all...


Dan Lepinski



--- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems 
la...@starlightsolar.com wrote:

From: Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com
Subject: Re: [RE-wrenches] Outback wave form
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, April 17, 2013, 2:09 PM

We experience issues like this from time to time. PF seems to be the culprit. 
Have you measured it or looked at the waveform yet?  How an inverter deals with 
PF seems to vary broadly. For example, the Splendide XC2100 washer/dryer will 
not work on a Magnum Energy and a few other sine wave inverters. However,  it 
will run on a low cost GoPower or Samlex sine wave inverter. Below is a scope 
trace of voltage/current of the Magnum inverter  Splendide washer. Upper trace 
is voltage




By adding a 50uF run capacitor inline, it somewhat tames the current phase and 
the sine wave so the Magnum can operate the washer. 



(Special thanks to Al for the discovery and photos)

Larry Crutcher
Starlight Solar Power Systems


On Apr 16, 2013, at 9:46 AM, All Solar allso...@scswifi.net wrote:

Have a client with a new coffee maker that will not run from their new dual 
outback setup. Has anyone heard of this lately. We have had no problems with 
appliances and sine wave inverters. What to look for?

Sent from Jeremy's IPhone.  Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




-Inline Attachment Follows-

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback wave form

2013-04-17 Thread Larry Crutcher, Starlight Solar Power Systems
Thanks Dan. I should have mentioned that this fix is for the washer only and 
should be installed in a switchable circuit inside the washer or on the washer 
only circuit.

Larry 



On Apr 17, 2013, at 12:51 PM, Exeltech exelt...@yahoo.com wrote:

Wrenches,

While the addition of a capacitor may resolve issues associated with various
inverter/appliance/motor combinations, please make sure the capacitor(s) get
switched OUT of the circuit (disconnected) when the load itself is disconnected.

Failure to do so could under some circumstances cause the inverter control-loop
circuitry to go unstable, leading to unpredictable inverter operation, and 
possible
damage/failure in the power system.  Disconnecting the capacitor with the load
alleviate this possibility.


Regards to all...


Dan Lepinski



--- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems 
la...@starlightsolar.com wrote:

From: Larry Crutcher, Starlight Solar Power Systems la...@starlightsolar.com
Subject: Re: [RE-wrenches] Outback wave form
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, April 17, 2013, 2:09 PM

We experience issues like this from time to time. PF seems to be the culprit. 
Have you measured it or looked at the waveform yet?  How an inverter deals with 
PF seems to vary broadly. For example, the Splendide XC2100 washer/dryer will 
not work on a Magnum Energy and a few other sine wave inverters. However,  it 
will run on a low cost GoPower or Samlex sine wave inverter. Below is a scope 
trace of voltage/current of the Magnum inverter  Splendide washer. Upper trace 
is voltage




By adding a 50uF run capacitor inline, it somewhat tames the current phase and 
the sine wave so the Magnum can operate the washer. 



(Special thanks to Al for the discovery and photos)

Larry Crutcher
Starlight Solar Power Systems


On Apr 16, 2013, at 9:46 AM, All Solar allso...@scswifi.net wrote:

Have a client with a new coffee maker that will not run from their new dual 
outback setup. Has anyone heard of this lately. We have had no problems with 
appliances and sine wave inverters. What to look for?

Sent from Jeremy's IPhone.  Sorry for typos and shorthand!
___i



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback wave form

2013-04-17 Thread Mac Lewis
Wrenches, regarding installing these capacitors in parallel with the load,
how do you size the capacitor, from a input current or power perspective,
and also a capacitance rating perspective?


On Wed, Apr 17, 2013 at 1:51 PM, Exeltech exelt...@yahoo.com wrote:

 Wrenches,

 While the addition of a capacitor may resolve issues associated with
 various
 inverter/appliance/motor combinations, please make sure the capacitor(s)
 get
 switched OUT of the circuit (disconnected) when the load itself is
 disconnected.

 Failure to do so could under some circumstances cause the inverter
 control-loop
 circuitry to go unstable, leading to unpredictable inverter operation, and
 possible
 damage/failure in the power system.  Disconnecting the capacitor with the
 load
 alleviate this possibility.


 Regards to all...


 Dan Lepinski



 --- On *Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems 
 la...@starlightsolar.com* wrote:


 From: Larry Crutcher, Starlight Solar Power Systems 
 la...@starlightsolar.com

 Subject: Re: [RE-wrenches] Outback wave form
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Wednesday, April 17, 2013, 2:09 PM


 We experience issues like this from time to time. PF seems to be the
 culprit. Have you measured it or looked at the waveform yet?  How an
 inverter deals with PF seems to vary broadly. For example, the Splendide
 XC2100 washer/dryer will not work on a Magnum Energy and a few other sine
 wave inverters. However,  it will run on a low cost GoPower or Samlex sine
 wave inverter. Below is a scope trace of voltage/current of the Magnum
 inverter  Splendide washer. Upper trace is voltage




 By adding a 50uF run capacitor inline, it somewhat tames the current phase
 and the sine wave so the Magnum can operate the washer.



 (Special thanks to Al for the discovery and photos)

 Larry Crutcher
 Starlight Solar Power Systems


 On Apr 16, 2013, at 9:46 AM, All Solar 
 allso...@scswifi.nethttp://mc/compose?to=allso...@scswifi.net
 wrote:

 Have a client with a new coffee maker that will not run from their new
 dual outback setup. Has anyone heard of this lately. We have had no
 problems with appliances and sine wave inverters. What to look for?

 Sent from Jeremy's IPhone.  Sorry for typos and shorthand!
 ___
 List sponsored by Home Power magazine

 List Address: 
 RE-wrenches@lists.re-wrenches.orghttp://mc/compose?to=RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 -Inline Attachment Follows-


 ___
 List sponsored by Home Power magazine

 List Address: 
 RE-wrenches@lists.re-wrenches.orghttp://mc/compose?to=RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*

Yo solo sé que no sé nada. -Sócrates
*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Cleaning Modules

2013-04-17 Thread Corey Shalanski
Greetings Wrenches,

I am wondering if anyone can offer tried-and-true tips for cleaning
modules: tools, materials, methods?

--
Corey Shalanski
Joule Energy http://joule-energy.com/
New Orleans, LA
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] ground mount options?

2013-04-17 Thread Chris Anderson
Schletter has a nice small kit package if you are looking for something in
AL.
Terrasmart is also a favorite of ours for challenging soil conditions -
their ground screws go through anything. Great team over there too.
Sunlink LGMS flies up if you have good flat soil. Pricey at small sizes but
cost effective for larger projects.

On Thu, Apr 18, 2013 at 12:23 AM, Jesse Dahl dahlso...@gmail.com wrote:

 Hello,

 I've been asked to put together a proposal for a local community and the
 only option is a ground mount (pole mount would work too).  I've looked at
 a few options today and was wondering if anyone has any opinions on the DPW
 Power Peak mounting system?

 Also, I would be interested in any other ground mount options that people
 like/recommend.  I've used the two-tier mount on a few projects and the DPW
 MPM and liked them good enough, but I'm always interested in trying new
 mounts.

 Thanks!


 Jesse

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 

Regards,

Chris Anderson
Chief Technology Officer
Borrego Solar Systems
1115 Westford Street, 2nd floor
Lowell, MA  01851
M: 603-732-2411
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org