[RE-wrenches] Recommendation for torque tools

2015-03-18 Thread Bill Loesch


Wrenches,

Do you have a favorite brand/model of torque wrenches when assembling 
mounts to manufacturer's specs? How do you handle calibration?


TIA,

--
Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094



-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.5751 / Virus Database: 4311/9328 - Release Date: 03/18/15

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Larry

Hi Jarmo,

I agree and recognize your urgency in making us aware of the proper use 
and charging of Li-ion batteries as well as the dangers of mistreating 
them. As an early adopter myself, I am very cautious in my approach even 
to the point of refusing to sell to some customers. Lithium battery 
technology is in a state of rapid evolution.


Not wanting to harp on the GBS brand that I sell, but one of your points 
goes to prove the safety of their integrated approach. You said, ...all 
it takes is one poor connection or broken temp sensor on one cell. The 
GBS EMS system has cell level sensors for temperature (and other data) 
and each sensor board requires constant communication with the CPU. If 
the EMS fails to communicate any information with any cell, the CPU 
immediately shuts down both safety solenoids, disconnecting the battery. 
With the non integrated systems, failures that don't report information 
to the management system could lead to disaster.


Please keep offering us the knowledge you are gaining as I am a firm 
believer that Lithium technology is a large part of the inevitable 
replacement the aged lead battery.


Larry Crutcher
Starlight Solar Power Systems
 


On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:

Hi:

I may sound like I'm a detractor against using Lion, but that's not it.

What I want to bring to light is that, being as the technology is new, 
not all the issues are known and there are things to learn for all 
early adopters in the foreseeable future.


From what I can gather the framework for the issues lies in that Lion 
technology is based on intercalation, that is, a reversible insertion 
and removal of Li molecules into compounds with microscopically 
layered structures.  This predicates that there must be no chemical 
reaction in the battery, but rather only the shelving of the highly 
reactive Li ions.  If there are any chemical reactions taking place, 
then in the least the battery performance is compromised and in the 
most there is a thermal event or worse


There are some very robust Lion battery packs, a favorite of mine 
being from a local company from Vancouver, (well Richmond, which is a 
suburb of Vancouver).  It's a small company, but they have designed, 
developed, built and successfully approved their 6 kWh Lion pack for 
use in large car ferries in Scandinavia.  The ferries have stacks of 
these packs in the 100's, in the MWh size.  It can be done.


What I'm advocating is that its best to work with companies that have 
the time, interest and resources to work through the wrinkles, and if 
not, then carefully put in reliable and precise BMS circuitry which 
includes things like fail safe circuits for single point failures of 
critical sensing circuits, the foremost of which is cell temperature. 
 When you're pushing large currents, all it takes is one poor 
connection or broken temp sensor on one cell..


Here's a link to the Lion battery pack manufacturer, Corvus,

http://corvus-energy.com/

I know they do a good job, but they're not cheap, for now...

JARMO

*
Jarmo Venalainen*  | *Schneider Electric **|  Xantrex Brand*  | 
*CANADA*  | *Sales Application Engineer* *
Phone:* +604-422-2528  | *Tech Support:* 800-670-0707  | *Mobile:* 
+604-505-0291 *
Email:* _jarmo.venalainen@schneider-electric.com_ 
mailto:jarmo.venalai...@schneider-electric.com | 
*Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:* 3700 
Gilmore Way, Burnaby, BC V5G4M1

http://www.xantrexrebate.com/
http://www.xantrex.com/ 	https://www.facebook.com/Xantrex 
https://twitter.com/Xantrex 	https://twitter.com/Xantrex







___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] outback radian question

2015-03-18 Thread jay peltz
HI All,

My question is. are there any known issues with the Radian interfacing with a 
generator?

I have a customer with flickering lights.
The lights are LED ( some dimmer/some on/off)

The generator supplier says that there are lots of problems with the Radian.
I've not heard this and don't believe it.

symptoms:
radian alone:  no flicker
generator alone: no flicker
generator/charging flicker.
different generator: no flicker.

So there is no doubt its the generator.

I'm trying to get more information to go back to the customer.

Thanks

jay

peltz power





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback quad stack X240 breaker tripping

2015-03-18 Thread Phil Undercuffler
There was a certification update the last year or so where UL standards on
transformers changed.  If you have an X240 that came with a 25, then it was
from the old math.  The X240s that ship under the new math have 20A
breakers.  Like you, I've installed tons of X240s with 25A breakers, but
either one works.

Phil

On Wed, Mar 18, 2015 at 1:18 PM, Jerry Shafer jerrysgarag...@gmail.com
wrote:

 Phil
 Please confirm i have built lots of ps2 and 4 seams to always have 25's on
 the x240 not 20's
 Jerry
 On Mar 18, 2015 10:04 AM, Phil Undercuffler solarp...@gmail.com wrote:

 The PSX-240 (independent unit in enclosure) has active cooling, so it has
 a higher capacity and therefore the 25A breaker.  The X-240 (bare xformer)
 should have a 20A.  The good news is, in OutBack Stacking the xformer is
 balancing the phases, which since there are inverters on both phases means
 that it typically is only processing 1-2kW or so, usually much less.

 Phil

 On Wed, Mar 18, 2015 at 10:34 AM, Allan Sindelar al...@sindelarsolar.com
  wrote:

  Kevin and Matt,
 Good advice from Matt. Just one detail: On the Outback PSX-240 (the
 independent unit with enclosure) the output breakers are 25A, not 20A. I
 suspect that the 2P
 breaker for the X-240 would be the same. As the unit often operates at
 close to its capacity, this could make a difference.
 Allan

  *Allan Sindelar*
 al...@sindelarsolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder (Retired), Positive Energy, Inc.
 *505 780-2738 505%20780-2738 cell*


  On 3/17/2015 2:56 PM, Kevin Pegg wrote:

 Thanks, Matt for the details here.

 I will be heading out to the site in the next little while and will
 report back what was found.

 Kevin

 -Original Message-
 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
 re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of *Matt James
 *Sent:* March 17, 2015 12:22 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Outback quad stack X240 breaker tripping

  Kevin,



 Not sure what happened on the dropped communication, but I had responded
 to you last week with some possible answers and things to check.  I think I
 made the mistake of replying directly to your email address and not sending
 to the entire Re-Wrenches forum, sorry for that as I know this is
 information that could be helpful to others as well.



 In any case, Tump is right -- on an existing system where everything has
 been working fine for some time but now isn’t, the key is to isolate,
 isolate, isolate.  Turn off all AC input, output and transformer breakers,
 then wake up each inverter by increasing the Power Save Level Master Adjust
 one step at a time.  Confirm proper AC voltage line to neutral at the
 inverter’s AC output terminals  – all breakers are still open.



 Close the breaker to the X240 balancing transformer, then close the AC
 output breakers of one inverter at a time, starting with the Master.
 Confirm that all inverters are on and have proper voltage and phasing by
 verifying proper AC voltage line to neutral, line to line as measured at
 the AC output terminals and to the output bus bars  – all inverters should
 show 120 L-N, and any inverters programmed as L1 Slaves should show 0v L-L
 to the Master and 240v L-L to L2 Slaves.  L2 slaves



 This establishes a baseline to ensure that all the power electronics,
 magnetics, wiring and programming are working properly.



 Next, start the generator and close all the input breakers.  Measure AC
 voltage at the inverter’s input terminals, confirm that each is seeing the
 proper voltage and phasing.  Verify that the inverters sync to and connect
 to the generator, and begin to charge.  Measure the AC current on both
 phases of the generator, and verify that they are balanced.



 Some potential issues are:

 1.   Bad X240 breaker.  Take a spare, 20A 2 pole DIN.

 2.   Transformer insulation damaged, typically by overheating.
 Rather unlikely, but possible.

 3.   Failed or mis-wired or mis-programmed inverter, likely on L2.
 Due to the distance to the site, consider taking a replacement board set
 with you.  Alternately, the system can operate on both legs with the other
 inverters, even if it’s an uneven number, through OutBack Stacking until
 you can schedule another trip.

 4.   Heavily imbalanced load or generator.



 If the charging currents on the generator are imbalanced, one possible
 solution is to disconnect the neutral from the generator at the power
 system end.  This presents a pure 240v load to the genset, which will force
 the currents to be balanced on both phases.



 Feel free to contact me directly if you have any problems or questions.



 Best Regards,



 Matt James

 Applications Engineering Manager

 OutBack Power Technologies Inc.

 Direct:  (360) 618-4364

 Cell:  (360) 618-2869



 *From:* RE-wrenches 

Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Bruce Erickson
If a communication failure with a single cell (not even an actual fault) can 
cause total battery shutdown, does that lead to a lot of nuisance tripping?

Bruce Erickson
Mendocino Solar Service
PO Box 1252
Mendocino, CA 95460
707-937-1701
707-937-1741 fax
br...@mendocinosolar.com

Celebrating 20 Years in Solar! 1994-2014





On Mar 18, 2015, at 8:57 AM, Larry wrote:

 Hi Jarmo,
 
 I agree and recognize your urgency in making us aware of the proper use and 
 charging of Li-ion batteries as well as the dangers of mistreating them. As 
 an early adopter myself, I am very cautious in my approach even to the point 
 of refusing to sell to some customers. Lithium battery technology is in a 
 state of rapid evolution. 
 
 Not wanting to harp on the GBS brand that I sell, but one of your points goes 
 to prove the safety of their integrated approach. You said, ...all it takes 
 is one poor connection or broken temp sensor on one cell. The GBS EMS system 
 has cell level sensors for temperature (and other data) and each sensor board 
 requires constant communication with the CPU. If the EMS fails to communicate 
 any information with any cell, the CPU immediately shuts down both safety 
 solenoids, disconnecting the battery. With the non integrated systems, 
 failures that don't report information to the management system could lead to 
 disaster.
 
 Please keep offering us the knowledge you are gaining as I am a firm believer 
 that Lithium technology is a large part of the inevitable replacement the 
 aged lead battery.
 Larry Crutcher
 Starlight Solar Power Systems
  
 On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:
 Hi: 
 
 I may sound like I'm a detractor against using Lion, but that's not it. 
 
 What I want to bring to light is that, being as the technology is new, not 
 all the issues are known and there are things to learn for all early 
 adopters in the foreseeable future. 
 
 From what I can gather the framework for the issues lies in that Lion 
 technology is based on intercalation, that is, a reversible insertion and 
 removal of Li molecules into compounds with microscopically layered 
 structures.  This predicates that there must be no chemical reaction in the 
 battery, but rather only the shelving of the highly reactive Li ions.  If 
 there are any chemical reactions taking place, then in the least the battery 
 performance is compromised and in the most there is a thermal event or worse 
 
 There are some very robust Lion battery packs, a favorite of mine being from 
 a local company from Vancouver, (well Richmond, which is a suburb of 
 Vancouver).  It's a small company, but they have designed, developed, built 
 and successfully approved their 6 kWh Lion pack for use in large car ferries 
 in Scandinavia.  The ferries have stacks of these packs in the 100's, in the 
 MWh size.  It can be done. 
 
 What I'm advocating is that its best to work with companies that have the 
 time, interest and resources to work through the wrinkles, and if not, then 
 carefully put in reliable and precise BMS circuitry which includes things 
 like fail safe circuits for single point failures of critical sensing 
 circuits, the foremost of which is cell temperature.  When you're pushing 
 large currents, all it takes is one poor connection or broken temp sensor on 
 one cell.. 
 
 Here's a link to the Lion battery pack manufacturer, Corvus, 
 
 http://corvus-energy.com/ 
 
 I know they do a good job, but they're not cheap, for now... 
 
 JARMO 
 
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
 Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
 +604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  | 
   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
 Mail Attachment.gif
 Mail Attachment.gifMail Attachment.gif   
 Mail Attachment.gif   Mail Attachment.gif
 
 
 
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Larry
Not at all. The EMS boards are well built and are protected under a 
cover with the terminals. I have not had any failures of the EMS boards 
or any failure to communicate with them.


Larry

On 3/18/15 4:52 PM, Bruce Erickson wrote:
If a communication failure with a single cell (not even an actual 
fault) can cause total battery shutdown, does that lead to a lot of 
nuisance tripping?


*Bruce Erickson*
Mendocino Solar Service
PO Box 1252
Mendocino, CA 95460
707-937-1701
707-937-1741 fax
br...@mendocinosolar.com mailto:br...@mendocinosolar.com

/Celebrating 20 Years in Solar!/1994-2014







___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Jerry Shafer
We use elite batteries with BMS no problems, the BMS sensor does seem to
run warm we are now setting up 4, 100 Ah banks with no problems so far.
Jerry
On Mar 18, 2015 1:52 PM, Bruce Erickson br...@mendocinosolar.com wrote:

 If a communication failure with a single cell (not even an actual fault)
 can cause total battery shutdown, does that lead to a lot of nuisance
 tripping?

 *Bruce Erickson*
 Mendocino Solar Service
 PO Box 1252
 Mendocino, CA 95460
 707-937-1701
 707-937-1741 fax
 br...@mendocinosolar.com

 *Celebrating 20 Years in Solar!* 1994-2014





 On Mar 18, 2015, at 8:57 AM, Larry wrote:

  Hi Jarmo,

 I agree and recognize your urgency in making us aware of the proper use
 and charging of Li-ion batteries as well as the dangers of mistreating
 them. As an early adopter myself, I am very cautious in my approach even to
 the point of refusing to sell to some customers. Lithium battery technology
 is in a state of rapid evolution.

 Not wanting to harp on the GBS brand that I sell, but one of your points
 goes to prove the safety of their integrated approach. You said, ...all
 it takes is one poor connection or broken temp sensor on one cell. The
 GBS EMS system has cell level sensors for temperature (and other data) and
 each sensor board requires constant communication with the CPU. If the EMS
 fails to communicate any information with any cell, the CPU immediately
 shuts down both safety solenoids, disconnecting the battery. With the non
 integrated systems, failures that don't report information to the
 management system could lead to disaster.

 Please keep offering us the knowledge you are gaining as I am a firm
 believer that Lithium technology is a large part of the inevitable
 replacement the aged lead battery.

 Larry Crutcher
 Starlight Solar Power Systems


 On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:

 Hi:

 I may sound like I'm a detractor against using Lion, but that's not it.

 What I want to bring to light is that, being as the technology is new, not
 all the issues are known and there are things to learn for all early
 adopters in the foreseeable future.

 From what I can gather the framework for the issues lies in that Lion
 technology is based on intercalation, that is, a reversible insertion and
 removal of Li molecules into compounds with microscopically layered
 structures.  This predicates that there must be no chemical reaction in the
 battery, but rather only the shelving of the highly reactive Li ions.  If
 there are any chemical reactions taking place, then in the least the
 battery performance is compromised and in the most there is a thermal event
 or worse

 There are some very robust Lion battery packs, a favorite of mine being
 from a local company from Vancouver, (well Richmond, which is a suburb of
 Vancouver).  It's a small company, but they have designed, developed, built
 and successfully approved their 6 kWh Lion pack for use in large car
 ferries in Scandinavia.  The ferries have stacks of these packs in the
 100's, in the MWh size.  It can be done.

 What I'm advocating is that its best to work with companies that have the
 time, interest and resources to work through the wrinkles, and if not, then
 carefully put in reliable and precise BMS circuitry which includes things
 like fail safe circuits for single point failures of critical sensing
 circuits, the foremost of which is cell temperature.  When you're pushing
 large currents, all it takes is one poor connection or broken temp sensor
 on one cell..

 Here's a link to the Lion battery pack manufacturer, Corvus,

 http://corvus-energy.com/

 I know they do a good job, but they're not cheap, for now...

 JARMO


 * Jarmo Venalainen*  |  * Schneider Electric **  |  Xantrex Brand*  |
 *CANADA*  |   *Sales Application Engineer*
 * Phone:* +604-422-2528  |   *Tech Support:* 800-670-0707  |   *Mobile:*
 +604-505-0291
 * Email:* *jarmo.venalai...@schneider-electric.com*
 jarmo.venalai...@schneider-electric.com  |   *Site:** www.Xantrex.com*
 http://www.xantrex.com/  |   *Address:* 3700 Gilmore Way, Burnaby, BC
 V5G4M1
   Mail Attachment.gif http://www.xantrexrebate.com/  Mail
 Attachment.gif http://www.xantrex.com/ Mail Attachment.gif
 https://www.facebook.com/Xantrex Mail Attachment.gif
 https://twitter.com/Xantrex Mail Attachment.gif
 https://twitter.com/Xantrex




___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 

Re: [RE-wrenches] outback radian question

2015-03-18 Thread Kevin Pegg
This sounds like the exact same issue with the FX and VFX inverters. Meter the 
power quality while under charge - nasty. We found a lot of computerized 
control systems on furnaces and boilers would either reject the power and not 
power up, or would behave erratically, some would be ok if you powered it up 
before generator on, some not. They were fine on inverter, fine on generator, 
but under charge bad. 

Ended up swapping out a lot of inverters since customers were not so keen on 
certain loads not operating properly when under generator charge. 

Kevin

-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]On
Behalf Of jay peltz
Sent: March 18, 2015 5:32 PM
To: RE-wrenches
Subject: [RE-wrenches] outback radian question


HI All,

My question is. are there any known issues with the Radian interfacing with a 
generator?

I have a customer with flickering lights.
The lights are LED ( some dimmer/some on/off)

The generator supplier says that there are lots of problems with the Radian.
I've not heard this and don't believe it.

symptoms:
radian alone:  no flicker
generator alone: no flicker
generator/charging flicker.
different generator: no flicker.

So there is no doubt its the generator.

I'm trying to get more information to go back to the customer.

Thanks

jay

peltz power





___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] outback radian question

2015-03-18 Thread Kirpal Khalsa
Are LED's on dimmers and non dimmers flickering or just dimmer switch
connected lightsi have had problems with LED's on dimmer switches even
with LED specific dimmer switches. ..
Just an idea. ...
On Mar 18, 2015 7:39 PM, jay peltz j...@asis.com wrote:

 HI All,

 My question is. are there any known issues with the Radian interfacing
 with a generator?

 I have a customer with flickering lights.
 The lights are LED ( some dimmer/some on/off)

 The generator supplier says that there are lots of problems with the
 Radian.
 I've not heard this and don't believe it.

 symptoms:
 radian alone:  no flicker
 generator alone: no flicker
 generator/charging flicker.
 different generator: no flicker.

 So there is no doubt its the generator.

 I'm trying to get more information to go back to the customer.

 Thanks

 jay

 peltz power





 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] outback radian question

2015-03-18 Thread Jerry Shafer
I have not had any issues with either the FX or Radian. I have had lots of
bad gennys fields failed, over under voltage, Check programming possible
overloading of the genny
Jerry
On Mar 18, 2015 4:39 PM, jay peltz j...@asis.com wrote:

 HI All,

 My question is. are there any known issues with the Radian interfacing
 with a generator?

 I have a customer with flickering lights.
 The lights are LED ( some dimmer/some on/off)

 The generator supplier says that there are lots of problems with the
 Radian.
 I've not heard this and don't believe it.

 symptoms:
 radian alone:  no flicker
 generator alone: no flicker
 generator/charging flicker.
 different generator: no flicker.

 So there is no doubt its the generator.

 I'm trying to get more information to go back to the customer.

 Thanks

 jay

 peltz power





 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Max Balchowsky
We're leaning toward the LiFePO4 batteries (low internal resistance) GBS have  
a medium high resistance so they warm faster and have a lower C rate 
efficiency, were gathering info as we go.. Max Balchowsky
Design Engineer
Golden Bridge Development
1048 Irvine Ave Suite 217
Newport Beach, Ca. 92660
760-403-6810Building a Better Future For The Next Generation

  From: Larry la...@starlightsolar.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org 
 Sent: Wednesday, March 18, 2015 8:57 AM
 Subject: Re: [RE-wrenches] Load testing Lithium battery bank
   
 Hi Jarmo,
 
 I agree and recognize your urgency in making us aware of the proper use and 
charging of Li-ion batteries as well as the dangers of mistreating them. As an 
early adopter myself, I am very cautious in my approach even to the point of 
refusing to sell to some customers. Lithium battery technology is in a state of 
rapid evolution. 
 
 Not wanting to harp on the GBS brand that I sell, but one of your points goes 
to prove the safety of their integrated approach. You said, ...all it takes is 
one poor connection or broken temp sensor on one cell. The GBS EMS system has 
cell level sensors for temperature (and other data) and each sensor board 
requires constant communication with the CPU. If the EMS fails to communicate 
any information with any cell, the CPU immediately shuts down both safety 
solenoids, disconnecting the battery. With the non integrated systems, failures 
that don't report information to the management system could lead to disaster.
 
 Please keep offering us the knowledge you are gaining as I am a firm believer 
that Lithium technology is a large part of the inevitable replacement the aged 
lead battery.
 Larry Crutcher
Starlight Solar Power Systems
  

On 3/17/15 6:11 PM, jarmo.venalai...@schneider-electric.com wrote:
  
Hi: 
 
 I may sound like I'm a detractor against using Lion, but that's not it. 
 
 What I want to bring to light is that, being as the technology is new, not all 
the issues are known and there are things to learn for all early adopters in 
the foreseeable future. 
 
 From what I can gather the framework for the issues lies in that Lion 
technology is based on intercalation, that is, a reversible insertion and 
removal of Li molecules into compounds with microscopically layered structures. 
 This predicates that there must be no chemical reaction in the battery, but 
rather only the shelving of the highly reactive Li ions.  If there are any 
chemical reactions taking place, then in the least the battery performance is 
compromised and in the most there is a thermal event or worse 
 
 There are some very robust Lion battery packs, a favorite of mine being from a 
local company from Vancouver, (well Richmond, which is a suburb of Vancouver).  
It's a small company, but they have designed, developed, built and successfully 
approved their 6 kWh Lion pack for use in large car ferries in Scandinavia.  
The ferries have stacks of these packs in the 100's, in the MWh size.  It can 
be done. 
 
 What I'm advocating is that its best to work with companies that have the 
time, interest and resources to work through the wrinkles, and if not, then 
carefully put in reliable and precise BMS circuitry which includes things like 
fail safe circuits for single point failures of critical sensing circuits, the 
foremost of which is cell temperature.  When you're pushing large currents, all 
it takes is one poor connection or broken temp sensor on one cell.. 
 
 Here's a link to the Lion battery pack manufacturer, Corvus, 
 
 http://corvus-energy.com/ 
 
 I know they do a good job, but they're not cheap, for now... 
 
 JARMO 
 
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  |   
Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
  
|   |
|   |   |   |  |

 
  
 
 
 
 
 
| 
  |

 
 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



  ___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback quad stack X240 breaker tripping

2015-03-18 Thread Phil Undercuffler
The PSX-240 (independent unit in enclosure) has active cooling, so it has a
higher capacity and therefore the 25A breaker.  The X-240 (bare xformer)
should have a 20A.  The good news is, in OutBack Stacking the xformer is
balancing the phases, which since there are inverters on both phases means
that it typically is only processing 1-2kW or so, usually much less.

Phil

On Wed, Mar 18, 2015 at 10:34 AM, Allan Sindelar al...@sindelarsolar.com
wrote:

  Kevin and Matt,
 Good advice from Matt. Just one detail: On the Outback PSX-240 (the
 independent unit with enclosure) the output breakers are 25A, not 20A. I
 suspect that the 2P
 breaker for the X-240 would be the same. As the unit often operates at
 close to its capacity, this could make a difference.
 Allan

  *Allan Sindelar*
 al...@sindelarsolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder (Retired), Positive Energy, Inc.
 *505 780-2738 505%20780-2738 cell*


  On 3/17/2015 2:56 PM, Kevin Pegg wrote:

 Thanks, Matt for the details here.

 I will be heading out to the site in the next little while and will report
 back what was found.

 Kevin

 -Original Message-
 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
 re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of *Matt James
 *Sent:* March 17, 2015 12:22 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Outback quad stack X240 breaker tripping

  Kevin,



 Not sure what happened on the dropped communication, but I had responded
 to you last week with some possible answers and things to check.  I think I
 made the mistake of replying directly to your email address and not sending
 to the entire Re-Wrenches forum, sorry for that as I know this is
 information that could be helpful to others as well.



 In any case, Tump is right -- on an existing system where everything has
 been working fine for some time but now isn’t, the key is to isolate,
 isolate, isolate.  Turn off all AC input, output and transformer breakers,
 then wake up each inverter by increasing the Power Save Level Master Adjust
 one step at a time.  Confirm proper AC voltage line to neutral at the
 inverter’s AC output terminals  – all breakers are still open.



 Close the breaker to the X240 balancing transformer, then close the AC
 output breakers of one inverter at a time, starting with the Master.
 Confirm that all inverters are on and have proper voltage and phasing by
 verifying proper AC voltage line to neutral, line to line as measured at
 the AC output terminals and to the output bus bars  – all inverters should
 show 120 L-N, and any inverters programmed as L1 Slaves should show 0v L-L
 to the Master and 240v L-L to L2 Slaves.  L2 slaves



 This establishes a baseline to ensure that all the power electronics,
 magnetics, wiring and programming are working properly.



 Next, start the generator and close all the input breakers.  Measure AC
 voltage at the inverter’s input terminals, confirm that each is seeing the
 proper voltage and phasing.  Verify that the inverters sync to and connect
 to the generator, and begin to charge.  Measure the AC current on both
 phases of the generator, and verify that they are balanced.



 Some potential issues are:

 1.   Bad X240 breaker.  Take a spare, 20A 2 pole DIN.

 2.   Transformer insulation damaged, typically by overheating.
 Rather unlikely, but possible.

 3.   Failed or mis-wired or mis-programmed inverter, likely on L2.
 Due to the distance to the site, consider taking a replacement board set
 with you.  Alternately, the system can operate on both legs with the other
 inverters, even if it’s an uneven number, through OutBack Stacking until
 you can schedule another trip.

 4.   Heavily imbalanced load or generator.



 If the charging currents on the generator are imbalanced, one possible
 solution is to disconnect the neutral from the generator at the power
 system end.  This presents a pure 240v load to the genset, which will force
 the currents to be balanced on both phases.



 Feel free to contact me directly if you have any problems or questions.



 Best Regards,



 Matt James

 Applications Engineering Manager

 OutBack Power Technologies Inc.

 Direct:  (360) 618-4364

 Cell:  (360) 618-2869



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Kevin Pegg
 *Sent:* Monday, March 16, 2015 10:51 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Outback quad stack X240 breaker tripping



 Thanks for everyone's advise on this one. I've done as much as I can
 working with the caretaker remotely and will need to attend myself with
 some test gear to fully diagnose. This site is remote (10h of driving then
 1h boat ride). I generally make a point of avoiding Outback product so feel
 much better informed to diagnose when onsite - later in the 

Re: [RE-wrenches] Outback quad stack X240 breaker tripping

2015-03-18 Thread Jerry Shafer
Phil
Please confirm i have built lots of ps2 and 4 seams to always have 25's on
the x240 not 20's
Jerry
On Mar 18, 2015 10:04 AM, Phil Undercuffler solarp...@gmail.com wrote:

 The PSX-240 (independent unit in enclosure) has active cooling, so it has
 a higher capacity and therefore the 25A breaker.  The X-240 (bare xformer)
 should have a 20A.  The good news is, in OutBack Stacking the xformer is
 balancing the phases, which since there are inverters on both phases means
 that it typically is only processing 1-2kW or so, usually much less.

 Phil

 On Wed, Mar 18, 2015 at 10:34 AM, Allan Sindelar al...@sindelarsolar.com
 wrote:

  Kevin and Matt,
 Good advice from Matt. Just one detail: On the Outback PSX-240 (the
 independent unit with enclosure) the output breakers are 25A, not 20A. I
 suspect that the 2P
 breaker for the X-240 would be the same. As the unit often operates at
 close to its capacity, this could make a difference.
 Allan

  *Allan Sindelar*
 al...@sindelarsolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder (Retired), Positive Energy, Inc.
 *505 780-2738 505%20780-2738 cell*


  On 3/17/2015 2:56 PM, Kevin Pegg wrote:

 Thanks, Matt for the details here.

 I will be heading out to the site in the next little while and will
 report back what was found.

 Kevin

 -Original Message-
 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
 re-wrenches-boun...@lists.re-wrenches.org]*On Behalf Of *Matt James
 *Sent:* March 17, 2015 12:22 PM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Outback quad stack X240 breaker tripping

  Kevin,



 Not sure what happened on the dropped communication, but I had responded
 to you last week with some possible answers and things to check.  I think I
 made the mistake of replying directly to your email address and not sending
 to the entire Re-Wrenches forum, sorry for that as I know this is
 information that could be helpful to others as well.



 In any case, Tump is right -- on an existing system where everything has
 been working fine for some time but now isn’t, the key is to isolate,
 isolate, isolate.  Turn off all AC input, output and transformer breakers,
 then wake up each inverter by increasing the Power Save Level Master Adjust
 one step at a time.  Confirm proper AC voltage line to neutral at the
 inverter’s AC output terminals  – all breakers are still open.



 Close the breaker to the X240 balancing transformer, then close the AC
 output breakers of one inverter at a time, starting with the Master.
 Confirm that all inverters are on and have proper voltage and phasing by
 verifying proper AC voltage line to neutral, line to line as measured at
 the AC output terminals and to the output bus bars  – all inverters should
 show 120 L-N, and any inverters programmed as L1 Slaves should show 0v L-L
 to the Master and 240v L-L to L2 Slaves.  L2 slaves



 This establishes a baseline to ensure that all the power electronics,
 magnetics, wiring and programming are working properly.



 Next, start the generator and close all the input breakers.  Measure AC
 voltage at the inverter’s input terminals, confirm that each is seeing the
 proper voltage and phasing.  Verify that the inverters sync to and connect
 to the generator, and begin to charge.  Measure the AC current on both
 phases of the generator, and verify that they are balanced.



 Some potential issues are:

 1.   Bad X240 breaker.  Take a spare, 20A 2 pole DIN.

 2.   Transformer insulation damaged, typically by overheating.
 Rather unlikely, but possible.

 3.   Failed or mis-wired or mis-programmed inverter, likely on L2.
 Due to the distance to the site, consider taking a replacement board set
 with you.  Alternately, the system can operate on both legs with the other
 inverters, even if it’s an uneven number, through OutBack Stacking until
 you can schedule another trip.

 4.   Heavily imbalanced load or generator.



 If the charging currents on the generator are imbalanced, one possible
 solution is to disconnect the neutral from the generator at the power
 system end.  This presents a pure 240v load to the genset, which will force
 the currents to be balanced on both phases.



 Feel free to contact me directly if you have any problems or questions.



 Best Regards,



 Matt James

 Applications Engineering Manager

 OutBack Power Technologies Inc.

 Direct:  (360) 618-4364

 Cell:  (360) 618-2869



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Kevin Pegg
 *Sent:* Monday, March 16, 2015 10:51 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] Outback quad stack X240 breaker tripping



 Thanks for everyone's advise on this one. I've done as much as I can
 working with the caretaker remotely and will need to attend myself with
 some test gear to fully 

Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Luke Christy
Larry,

I've been checking out the [current] viability of Li+ technologies for RE 
systems, and I'm encouraged to hear of the success you've apparently had. 
What is the typical kWh size of the battery packs you've been putting together? 
Are you sourcing the GBS batteries directly from the manufacturer?

I appreciate both your and Jarmo's comments about the safety concerns with this 
rapidly evolving technology.  
Feeling good about the long term safety of a large RE-scale Li-ion battery pack 
for my customers has been a major stumbling block for me thus far. 

Thanks,
-Luke


Luke Christy

NABCEP Certified PV Installation Professional™: Certification #031409-25 
NABCEP Certified Solar Heating Installer™: Certification #ST032611-03   
CoSEIA Certified PV Installer 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
sgsrenewab...@gmail.com
719.588.3044
www.sgsrenewables.com

   







___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Load testing Lithium battery bank

2015-03-18 Thread Larry

Hi Chris,

Thanks for the recommendation. I received a quote from Comrent$1800 
to rent a load for 1 week. Ouch! I'll go with the $10 water elements and 
a little fabrication time. I have AH counters and controllers to stop 
the discharge.


Thank you,

Larry Crutcher
Starlight Solar Power Systems

On 3/17/15 2:38 PM, Chris Mason wrote:
Load banks are for rent, I am in the generator business and it is a 
common requirement to provide a load bank upon installation.

http://www.comrent.com/Solutions/load-bank-rentals.html


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org