Re: [RE-wrenches] Grid-tied Trace SW

2014-09-09 Thread Eric . Bentsen
Hi Russell,
The Trace SW4024 can sell it's full 4kW rating without any problem. The 
GTI was developed to add an extra layer 
of anti-islanding protection in 2002. The units that were previously 
approved for grid interconnection were allowed 
to be grandfathered in for the most part, and continue to sell back. 
This would be up to AHJ.
Rgds,
_
 

Eric Bentsen   |   Schneider Electric   |  Customer Care Center | Advanced 
Technical Support   |   Technical Support Engineer
Phone: 866-519-1470 option #1  |   Schneider Electric Support Center: 
+800-640-0770   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |
Address: 1660 Scenic Ave. Costa Mesa, CA 92626 

How am I doing? Please e-mail my manager with any feedback at: 
jim.hou...@schneider-electric.com
*** Please consider the environment before printing this e-mail 



From:
Russell Mueller r...@buffalosolartaos.com
To:
RE-wrenches@lists.re-wrenches.org, 
Date:
09/09/2014 07:43 AM
Subject:
[RE-wrenches] Grid-tied Trace SW
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



Hello Esteemed Wrenches,

I have a prospective client who has an old GTBB system using a Trace SW -- 
it was permitted and signed off by the utility way back when and has been 
operational ever since.  It's a Trace SW 4024 that's feeding the grid 
through a Trace T-240 transformer -- I didn't see a GTI.  All he wants me 
to do is replace his failing array (which would increase his array size 
from 1152W to 3300W) -- not pull a permit, not change the BOS other than 
to add a 2nd charge controller.

The original question that lead me to write this post is whether the 
SW4024 can handle the full 4kW sell-back onto the grid -- I couldn't find 
any specs on that on the web. 

But the question I have now is whether the Trace SW is UL1741 compliant. I 
didn't think to do an anti-islanding test before I left the site.  If it's 
not, then I'm thinking maybe I should insist that he change out his 
inverter for a modern one, or I'll pass on the job.  If it fails an 
anti-islanding test (which I'll do next time I'm in his neighborhood), 
then the dangers are obvious, and I don't want the liability.

What would you all do in this situation?  Do any of you have experience 
with grid-tied SWs -- any advice?

Thanks,

Russ

--
Russell Mueller
NM EE98 Electrical Contractor, license #382671
NM ER1J Journeyman Electrician
Photovoltaic Designer / Installer




BUFFALO SOLAR LLC
Taos, New Mexico
575-770-4877
r...@buffalosolartaos.com




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Grid-tied Trace SW

2014-09-09 Thread Eric . Bentsen
Hi William,
Please remember the GTI is not compatible with SW models manufactured 
prior to 2002. 
Rgds.
_
 

Eric Bentsen   |   Schneider Electric   |  Customer Care Center | Advanced 
Technical Support   |   Technical Support Engineer
Phone: 866-519-1470 option #1  |   Schneider Electric Support Center: 
+800-640-0770   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |
Address: 1660 Scenic Ave. Costa Mesa, CA 92626 

How am I doing? Please e-mail my manager with any feedback at: 
jim.hou...@schneider-electric.com
*** Please consider the environment before printing this e-mail 



From:
William Miller will...@millersolar.com
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org, 
Date:
09/09/2014 09:06 AM
Subject:
Re: [RE-wrenches] Grid-tied Trace SW
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



Russell:
 
I am curious, how do you perform anti-islanding tests?
 
The SW4024 should work great with a 3.3 kW array.  Due to battery and 
inverter inefficiencies you would never see the full 3.3 sell back any 
way, which is less than the rating of the inverter.
 
The SW4024 was UL listed at one time but the listing was removed due to 
failure to apply the testing regimen properly, if I remember correctly. We 
were not required to retrofit existing installations by adding the GTI, 
only to add them to pending installations.  Our utility lost a lot of 
applications during that era and years later, when forced to reapply, they 
accepted the SWs without GTIs.  If you really want one, I have one in the 
shop I would sell cheap, but I don’t have much faith in the design.
 
Lastly, I can’t comment on the efficiency of the SW versus a modern GTBB 
inverter.  That question would justify some research.  If the SW is 
significantly less efficient than, say, a Sunny Island, the impetus may be 
there to upgrade.
 
William Miller
 

Lic 773985
millersolar.com
805-438-5600
 
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
Behalf Of Russell Mueller
Sent: Tuesday, September 09, 2014 7:43 AM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Grid-tied Trace SW
 
Hello Esteemed Wrenches,
 
I have a prospective client who has an old GTBB system using a Trace SW -- 
it was permitted and signed off by the utility way back when and has been 
operational ever since.  It's a Trace SW 4024 that's feeding the grid 
through a Trace T-240 transformer -- I didn't see a GTI.  All he wants me 
to do is replace his failing array (which would increase his array size 
from 1152W to 3300W) -- not pull a permit, not change the BOS other than 
to add a 2nd charge controller.
 
The original question that lead me to write this post is whether the 
SW4024 can handle the full 4kW sell-back onto the grid -- I couldn't find 
any specs on that on the web. 
 
But the question I have now is whether the Trace SW is UL1741 compliant. I 
didn't think to do an anti-islanding test before I left the site.  If it's 
not, then I'm thinking maybe I should insist that he change out his 
inverter for a modern one, or I'll pass on the job.  If it fails an 
anti-islanding test (which I'll do next time I'm in his neighborhood), 
then the dangers are obvious, and I don't want the liability.
 
What would you all do in this situation?  Do any of you have experience 
with grid-tied SWs -- any advice?
 
Thanks,
 
Russ

--
Russell Mueller
NM EE98 Electrical Contractor, license #382671
NM ER1J Journeyman Electrician
Photovoltaic Designer / Installer




BUFFALO SOLAR LLC
Taos, New Mexico
575-770-4877
r...@buffalosolartaos.com
 
 



 

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] trace SW plus fan

2014-09-08 Thread Eric . Bentsen
Hi Jay,
The SWPlus has 2 fans, like the standard SW. Fairly straight forward to 
replace (drill out pop rivets thru cross member), but it has a different 
part # 460-0003-01-01. 
I will email off list with contact # for price and availability.
Specs, in case you wish to source elsewhere :
FAN, BOX, 135.5CFM/12VDC/3000RPM
Rgds,

_
 

Eric Bentsen   |   Schneider Electric   |  Customer Care Center | Advanced 
Technical Support   |   Technical Support Engineer
Phone: 866-519-1470 option #1  |   Schneider Electric Support Center: 
+800-640-0770   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |
Address: 1660 Scenic Ave. Costa Mesa, CA 92626 

How am I doing? Please e-mail my manager with any feedback at: 
jim.hou...@schneider-electric.com
*** Please consider the environment before printing this e-mail 



From:
jay peltz j...@asis.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
09/07/2014 07:08 PM
Subject:
[RE-wrenches] trace SW plus fan
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



Hi All,

I have a client with a SW Plus with a bad fan.
He wants it replaced ( I know I know, but the fan, not the unit!) as its 
affecting battery charging rates.

I've never done the Plus and don't know what the inside looks like, and 
therefore what I need or how hard/easy it is to replace the fan/s
Done plenty of SW's though.

Any help on this one?

thanks
jay

peltz power
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trace SW4024 LCD display problem

2014-06-27 Thread Eric . Bentsen
Hi Larry,
We may still have a few display boards left. 
Call in to the number below and we can check P  A.
Rgds,
Eric
_
 

Eric Bentsen   |   Schneider Electric   |  Customer Care Center | Advanced 
Technical Support   |   Technical Support Engineer
Phone: 866-519-1470 option #1  |   Schneider Electric Support Center: 
+800-640-0770   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |
Address: 1660 Scenic Ave. Costa Mesa, CA 92626 

How am I doing? Please e-mail my manager with any feedback at: 
jim.hou...@schneider-electric.com
*** Please consider the environment before printing this e-mail 



From:
Larry Crutcher,Starlight Solar Power Systems 
la...@starlightsolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
06/27/2014 03:34 AM
Subject:
[RE-wrenches] Trace SW4024 LCD display problem
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



I am looking for someone that can repair the SW4024 LCD control. The 
display is getting to dim to view.

Thank you,

Larry








___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Modified sine deterioration

2014-05-20 Thread Eric . Bentsen
Hi Drake,
Motor loads with control circuitry tend to have problems with MSW (phase 
detection or zero crossing). There are plenty of motor loads out there 
that are powered by modified sine wave, so it is not 
a hard fast rule that all motor loads have problems with MSW. You can look 
at the waveform on a scope. Under no load, it should have the appearance 
of a square wave with a ground-level step between each 1/2 cycle. Although 
the DR incorporated a robust design with good surge capability, they 
typically fail due to control board or AC board related issues. They are 
technically still repairable, although parts supplies are dwindling. The 
cost of true sine wave inverters has come down significantly in recent 
years. That way you don't need to worry about compatibility.
Rgds,
_
 

Eric Bentsen   |   Schneider Electric   |  Customer Care Center | Advanced 
Technical Support   |   Technical Support Engineer
Phone: 866-519-1470 option #1  |   Schneider Electric Support Center: 
+800-640-0770   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |
Address: 1660 Scenic Ave. Costa Mesa, CA 92626 

How am I doing? Please e-mail my manager with any feedback at: 
jim.hou...@schneider-electric.com
*** Please consider the environment before printing this e-mail 



From:
Drake drake.chamber...@redwoodalliance.org
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
05/20/2014 07:24 AM
Subject:
[RE-wrenches] Modified sine deterioration
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



Hello Wrenches,

We are diagnosing a system with a 20 year old Trace DR 1512 inverter. 
Recently a motor burned out that had been running on the system. I do 
understand that modified sine (modified square) wave inverters are hard on 
motors in general.

My question is, does the quality of the Mayan Pyramid sine wave 
deteriorate with time as the capacitors dry up, or for any other reason? 
Would the power quality be expected to have declined on an old unit like 
this?

Thanks,

Drake 

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV 
740-448-7328
http://athens-electric.com/ 


__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charge Controller with Configurable Maximum Output Current

2014-01-03 Thread Eric . Bentsen
Hi Jason,
Both the XW MPPT60 (865-1030-1) and MPPT80 (865-1032) models can have the 
charge % adjusted using the SCP (865-1050). 
Advanced SettingsCharger SettingsMax Chg Rate
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Jason Szumlanski ja...@fafcosolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
01/03/2014 11:38 AM
Subject:
[RE-wrenches] Charge Controller with Configurable Maximum Output Current
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



What commonly available MPPT controllers have a user configurable current 
output limit? (other than Outback FM##)

Jason Szumlanski
Fafco Solar


__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SW repair

2013-12-04 Thread Eric . Bentsen
Hi Brian,
  The fan drive circuit is on the control board. If the control board 
needs to be replaced, it could get pricey. 
Tekris Power Electronics in Farmingdale, NJ may be able to repair at 
component level, give them a call. 
732-938-4996
Alternately, there are some former Trace techs that may be able to repair 
at a component level, you need to email them for a quote :
phantompowerservices.com

Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Brian Mehalic br...@solarenergy.org
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
12/04/2013 07:31 AM
Subject:
[RE-wrenches] SW repair
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Howdy-
Have a friend with stacked Trace SWs.  The fan on one is running nearly 
continuously, so two questions:

Anything in the settings that could cause this (it isn't related to the 
load, which is usually low and evenly split between the two 120 legs)?

How about repairs?  The concern is it will fail...I've never changed out 
any internal parts on SWs, and a few posts on the internet made it sound 
like the fan is a pain in the butt.  Any reputable repair shops in the 
Southeast or east coast?

Thanks!

Brian Mehalic 
NABCEP Certified Solar PV Installation Professional™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-11 Thread Eric . Bentsen
Hi Wrenches,
 There is no implication other than confirming how the disco 
is tested, and thus certified. It probably makes no difference 
electrically which position the
 unit is mounted, but AHJs may have differing opinions on whether this 
would be permitted. 
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Bob-O Schultze bo...@electronconnection.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
11/11/2013 10:09 AM
Subject:
Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Dan,
I think this thread applied not to OCDs but to an unfused 600VDC 
disconnect can mounted on a roof which is less than vertical.
Bob-O
On Nov 11, 2013, at 9:21 AM, Exeltech wrote:

Wrenches,

There appears to be some misinformation getting into this thread.

The trip mechanism within standard thermal over-current protective 
devices (OCP devices) is mechanically spring-loaded, and is triggered by 
heat.

Eric mentions below that Square D breakers are tested in a vertical 
orientation only - the implication being that's their only UL certified 
position.  If this were true, it would imply the breakers cannot be used 
in any other orientation.  This would potentially limit the Square D OCP 
market to sub-panels and other enclosures where the devices are vertical. 
Inasmuch as the vast majority of panelboards I've encountered in my 40+ 
years in this industry have the breakers stacked horizontally, it would 
not be a wise business decision for the manufacturer to self-inflict such 
a limitation on their product.

This also does not mean any such limitation (real or not) applies to all 
breakers.

By way of example, OCP devices work in a horizontal position, stacked 
pancake style in a main panelboard, as well as vertically oriented 
side-by-side in a sub-panel.  In either orientation, they are  in full 
compliance with UL 489, (UL Standard for Circuit Breakers, Switches, and 
Circuit Breaker Enclosures).  If an OCP device *was* 
positionally-sensitive, UL Standards require this sensitivity to be noted 
in the documentation accompanying the device.  Further to that point, UL 
489 Section 7.1.1.13 states: In determining if a circuit breaker complies 
with the test requirements, the device shall be mounted or supported as in 
service and tested under conditions approximating those of intended 
operation, except as otherwise noted.

Mounting position notwithstanding, a greater concern would be the ambient 
temperature of a rooftop location, whereby summer heat would tend to make 
the OCP device more sensitive than necessary, potentially causing it to 
trip at an amperage below that of its UL ratings.  While a nuisance, a 
more serious issue arises when operating the OCP device in cold ambient 
conditions, whereby the device may allow MORE than its rated trip current 
to flow.

Per UL 489, OCP devices are tested at either 25C or 40C ambient.  Again 
per UL 489, if an OCP device is to be used in ambient conditions other 
than those two ranges, the acceptable temperature range for that OCP 
device shall be marked on the body of the device.

In UL 489, Supplemental Annex, Section 2, Subsection 2.3.3, mechanical 
vibration testing is conducted with OCP devices oriented vertically, 
horizontally, and inclined 30 degrees from vertical, with all devices 
energized up to 200% of the device rated current during the testing.

Given the preceding, and per implication of UL 489 testing methods, OCP 
devices are NOT positionally sensitive.

In conclusion, if you DO install a rooftop OCP system, and for proper 
protection, please ensure the OCP devices utilized are rated for the 
worst-case ambient temperatures involved.


Regards to all,


Dan Lepinski




At 09:33 AM 11/8/2013, you wrote:

Hi Kirpal,

All Square D safety switches are UL tested in the Vertical position ONLY, 
so if someone is trying to install a switch in any other position other 
than vertical, that will be between them and the inspector.

Hope this helps. 

Eric


Eric Bentsen  |  Schneider Electric   |  Solar Business  |   UNITED STATES 
 |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   Email: 
eric.bent...@schneider-electric.com  |  Site: 
www.schneider-electric.com/solar   |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] Square D Disconnects mounted on the slope of the roof.

2013-11-08 Thread Eric . Bentsen
Hi Kirpal,
All Square D safety switches are UL tested in the Vertical position ONLY, 
so if someone is trying to install a switch in any other position other 
than vertical, that will be between them and the inspector. Hope this 
helps.
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Kirpal Khalsa solarwo...@gmail.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
11/07/2013 01:42 PM
Subject:
[RE-wrenches] Square D Disconnects mounted on the slope of the roof.
Sent by:
re-wrenches-boun...@lists.re-wrenches.org




Hi Folks!!!
Anyone aware of minimum slope requirements for Square D 321RB 
disconnectsCan they be mounted on rails parallel to the slope of the 
roof like Outback and Midnite solar combiner boxes(down to a 3/12 pitch)
I can't seem to find any notes stating the limitations in manufacturer 
documentation.. They are NEMA 3 of course
Thanks in advance for any direction you can provide

Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o





__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Hidden freight damage

2013-11-04 Thread Eric . Bentsen
Hi Luke,
Shipping damage is a direct loss to profit, so the carrier will want to 
have reasonable proof 
confirming they are actually responsible. Anyone can say it was delivered 
that way.
 If it is necessary to have the delivery person sit there 
while you unpack everything, so be it. Do not sign anything until then. 
Sometimes, the manufacturer may step up and cover shipping damage 
to keep the customer happy. 

Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Luke Christy sgsrenewab...@gmail.com
To:
re-wrenches@lists.re-wrenches.org re-wrenches@lists.re-wrenches.org
Date:
11/04/2013 08:47 AM
Subject:
[RE-wrenches] Hidden freight damage
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Wrenches,

We have been in business for about 8 years, and up until now, the shipping 
gods have smiled upon me, but apparently my luck has run out, as I've had 
2 costly shipping nightmares within a month,  and I'm just wondering what 
other Wrenches have done to protect themselves from the liability involved 
in trusting expensive shipments to the freight carriers.  Here's my 
situation:

I recently had a pallet of modules shipped, and it arrived with multiple 
broken modules, due apparently to careless handling,and having had 
something heavy set on top of the pallet.  I have my freight shipments 
sent to a neighboring business which is kind enough to receive them for 
me, since they have many full time staff who are always available during 
business hours to fork shipments off a truck.  In this case the forklift 
driver did not notice the damage (it was not immediately evident), and the 
delivery was signed for.  However, upon picking up the pallet an hour 
later, I  realized that the shipment was damaged, called the freight 
company immediately to notify them of the damage, and subsequently filed a 
detailed written claim. 

I just got notice that my claim was denied by the carrier, evidently 
without considering any of the photos or the written explanation I 
submitted with the claim. They simply cited that the shipment had been 
signed for without noting damage. 
It is clear to me that the carrier was responsible for the damage, yet 
apparently because the damage was hidden and the BOL was signed, they can 
leave me holding the bag for a significant amount of money. 

This particular incident could have been worse, but it is the first time 
I've had it happen and it certainly makes me worried about future 
deliveries. It suddenly seems like an unacceptable liability to have 
others sign for my deliveries without a thorough inspection. 

I asked my distributor whether the shipments have any insurance on them, 
and the person I spoke with didn't know the answer. So my $50 Ebay 
shipment is insured, but my $50,000 worth of equipment isn't? My insurance 
agent says that I can make a claim on my commercial insurance, but advised 
against it in this case, since the loss was only around $1K, and is 
guaranteed to raise my future premiums.

I know that things get damaged or lost all the time in shipment, and I'm 
wondering how other businesses handle it.  Businesses that do larger 
volume must have damaged freight all the time.  Is it just impossible to 
get freight companies to take responsibility for damage that is not 
immediately evident, since they are acting as judge on their own behalf? 
Do you just refuse to sign the bill of lading until you've examined all 
the contents of the packages (this is a logistical nightmare in most 
cases)?  Do you just chalk it up to the cost of doing business and/or make 
claims to your commercial insurance? 

Would appreciate your thoughts / experiences with this issue. 
Thanks. - Luke

Luke Christy
 
NABCEP Certified PV Installation Professional™: Certification #031409-25 
NABCEP Certified Solar Heating Installer™: Certification #ST032611-03  
CoSEIA Certified PV Installer 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
sgsrenewab...@gmail.com
719.588.3044
www.sgsrenewables.com

 







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

__
This email has been scanned by the Symantec Email Security.cloud

Re: [RE-wrenches] Trace 2548 intermittent power problem...55 not 25

2013-10-17 Thread Eric . Bentsen
Hi Eric,
Sounds like a bad control board. 
Swap the inverter and you should be back in business.

Rgds,

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
SunHarvest e...@harvesthesun.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
10/17/2013 11:28 AM
Subject:
[RE-wrenches] Trace 2548 intermittent power problem...55 not 25
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



I was looking at a scratch pad note where I wrote 25 instead of 55...Yes, 
it is a SW5548. Definitely not set to Search...it's in On mode. I've 
checked error codes. No Yes messages. I am wondering about a firmware 
upgrade although I have serious doubt that will clear up the problem.
 
I guess I will try the swap and see if that does the trick.
 
On the genny, I try to stay away from genset service but I can definitely 
check some of the more simple items like check oil  coolant.
 
Thanks guys.
 
 - Original Message - 
From: Allan Sindelar 
To: RE-wrenches 
Sent: Thursday, October 17, 2013 10:36 AM
Subject: Re: [RE-wrenches] Trace 2548 intermittent power problem

Eric,
A Trace 2548 with automatic generator start? I don't believe there ever 
was such a thing. I suspect that you're referring to either a SW4048 or 
SW5548. If so, your first step is to check the error codes, some of which 
are found in Menu Heading 2 (for generator-related issues) and the rest in 
Heading 5. Any Yes message as you scroll through them is a good hint. 

This inverter is at least 13 years in service, likely more. Sounds like a 
pre-GTI Y2K system. The units are remarkably robust and reliable, but it 
may well have a glitch in the firmware or voltage/frequency sensors. The 
extra inverter is your ace in the hole, once you determine what the issue 
is.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
On 10/17/2013 10:41 AM, SunHarvest wrote:
 
I have encountered a Trace 2548 in seemingly good working condition. I was 
called out to troubleshoot a Grid-tied, battery back-up system with the 
following problem:
 
- Upon loss of grid power there is about a 5 second lapse (no power to 
house) before the BB system engages. Power to the critical loads panel 
from the Trace is restored after the 5 second lapse.
- After another 5 seconds the Trace will disconnect power to the loads. 
This on-off cycle continues until grid power is restored.
 
After checking voltage  S.G. values, I determined that the 11 year old 
batteries needed to be replaced and I assumed this was the cause of the 
Trace on-off cycling.
I also found that half of his PV array had bad BP modules. BP replaced all 
of the modules under somewhat of a warranty. So, new modules, new 
batteries, and a new Outback FM60 charge controller. After all upgrades I 
ran through a simulated power outage again and the intermittent power 
problem persists!
 
He also has gen support enabled - connection to an Onan RV Genset BGE NHE 
(??) - and when I start the genny from the inverter, by selecting On not 
Auto, the genset fires right up but only stays on for about 30 seconds 
before it too shuts off and enters a cycling between auto-starting from 
the inverter and shutting down.
 
This behavior is beyond me. So, I'm seeking help from the pros. Anyone 
know what's going on here? The customer has another Trace 2548, unused, 
sitting in a box. So, if I needed to I could swap out the inverter and see 
if that makes a difference...?
 
Eric
SunHarvest
(530)798-3738


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios

Re: [RE-wrenches] GTBB resistance

2013-10-10 Thread Eric . Bentsen
Hi All,
Following this post with much interest, as this affects everyone that 
wants to reduce reliance on a utility grid 
 that is already overburdened, If TOU metering was done away with, it 
would eliminate buy low and sell high, 
which is a wash when you consider battery replacement cost (due to 
excessive cycling).
GTBB is an excellent way for individuals to do their part in conserving 
energy. The fact that utility companies 
are putting up such a battle is indicative of one thing.money (is 
there any other motive?).  Everyone concerned 
should contact their lawmakers in Congress to pass a federal law so these 
utility companies will stop obstructing 
clean energy.
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Dan Fink danbo...@gmail.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
10/10/2013 11:22 AM
Subject:
Re: [RE-wrenches] GTBB resistance
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Ray;

We always run a variety of made-up financial scenarios in our Intro to 
Off-Grid classes.we usually end up around 35 to 70 cents per kWh. 

Or another way to put ita monthly 'battery bill' of $25 to $120 
depending on battery bank size, and how many years they pamper it to 
lastor torture it to premature death.

The GTBB backlash from the utilities is just more smoke and 
mirrors.I'll try to get something up on HuffPost before I leave for 
Canada next week.

Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342

 


On Thu, Oct 10, 2013 at 11:43 AM, Ray Walters r...@solarray.com wrote:
Just to add to Phil's comments:  I've been calculating total life cost of 
battery storage  (KWH x cycle life x %DOD)  and the costs are 15 to 35 
cents/ KWH to cycle a battery.  Its even higher for sealed batteries and 
Li+.  It would have to be an amazing cost difference in the TOU rates to 
beat the battery cost plus all the losses of AC charging/ discharging a 
battery.
I agree with Phil, as I've seen utilities obstruct solar since the 1980s. 
 Unfortunately their attitude has still not changed.
Its pretty dumb too; battery storage could help improve the reliability of 
the grid.
You can't retire yet folks,  we have another battle to fight.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760


On 10/10/2013 12:13 AM, Phil Undercuffler wrote:
 However, arbitrage (buying low and selling high) is one of the lousiest 
economic models for energy storage. Yes, perhaps you can make a buck or 
two if the delta is big enough. However, that's like driving forty miles 
in your 4x4 to use a dollar coupon instead of shopping at the grocery 
store down the block. There are just better ways to make a buck.

At the end of the day, what should matter in NEM is what generated the 
energy that is exported. The customer should be able to maintain their 
battery by charging from grid, solar, or any combination. The batteries 
are not a balloon -- energy used to charge them doesn't come rushing back 
out. Batteries are like a bucket -- if the inverter can only sell what 
flows over the top, then it takes solar input to begin flowing.

Ultimately, it's going to take a chorus of voices to get the CPUC to tell 
the utilities to shape up and stop obstructing these systems.  If people 
stay silent, the utilities get their way. It's your industry, it's your 
business.  It's your choice.

Phil Undercuffler
OutBack Power
425-319-2821


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules

Re: [RE-wrenches] parallel stacking SW

2013-10-04 Thread Eric . Bentsen
Hi William,
In theory, this would be possible, but you have to consider the 60A 
transfer relay rating, so if we are dealing with SW5548 (5.5kW) models,
you will only add approx 1700W of power (per set) before nuisance tripping 
a 60A breaker.
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
William Miller will...@millersolar.com
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date:
10/03/2013 10:49 PM
Subject:
Re: [RE-wrenches] parallel stacking SW
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Mac:
 
I approached this problem some years ago and posted about it on this 
forum. What I heard is that, yes, it can be done.  The actual process is 
known by a few former Trace engineers and could not be divulged due to 
confidentiality agreements signed when Outback split off from Xantrex (or 
Trace, if that is what it was called at the time).  If you know a former 
Trace Engineer, you might be able to wrest the information out of them if 
the stature of limitations has expired.
 
Of course I was not satisfied with “this information is only is for some 
to know,” so I worked on the problem.  My idea is to connect two inverters 
in series and then feed them into the AC1 inputs of two more inverters in 
parallel.  Since the SW inverters can provide true “Gen Support” mode, the 
downstream inverters can assist the upstream inverters, therefore 
providing the gross power of all four inverters.  See this page for a 
drawing.Look about halfway down the page for Cascading SW inverters.
 
Now I have come up with some pretty strange ideas in my time, but I think 
this is one of the more wacky, but actually possible solutions.  I never 
had the chance to test this scheme, but I would love to know if it would 
actually work.
 
William
 
PS:  Just as I was finishing this email I remembered the situation I was 
trying to correct. The other idea is here:  Link  I don’t recommend this 
technique for the reasons stated on the web site, but there may the germ 
of an idea that may work.  It would have to do with feeding a transformer 
from opposite ends with paralleled inverters.  How to keep them in sync…
 
Good Luck,
 
William Miller
 
 
 
From: re-wrenches-boun...@lists.re-wrenches.org [
mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Wednesday, October 02, 2013 8:01 AM
To: RE-wrenches
Subject: [RE-wrenches] parallel stacking SW
 
Hi wrenches,
 
I have some folks that I'm meeting in a couple of days that have 4 Trace 
SW 5048 inverters.  It's a very large, older compound-style installation 
that the original installer has bailed on.  They have it set up so that 
there is a common battery bank and each pair of series stacked inverters 
are independently feeding 2 separate 120/240 busses.  One of these 120/240 
services gets utilized very heavily, and one isn't really used at all.  Is 
it possible with this type of inverter, to have all four inverters feeding 
a common AC bus, two feed Phase A and the other two feeding phase B?
 
I know that is possible to series stack and to parallel stack this 
inverter, but can you do both at the same time?
 
If so, does anyone have a pin out to a parallel stacking cable?
 
Thanks in advance
 
-- 
 
 
 
Mac Lewis
Yo solo sé que no sé nada. -Sócrates

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trace SWs in Energy Management Mode

2013-10-04 Thread Eric . Bentsen
Hi Brian,
LBX would be better for the way this customer is using the system, because 
it only connects
 to the grid when the batteries get low. Unfortunately, the timers do not 
affect LBX, so charging 
may occur during the peak rateor it may not :C)

Rgds,

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Brian Mehalic br...@solarenergy.org
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
10/04/2013 12:04 PM
Subject:
[RE-wrenches] Trace SWs in Energy Management Mode
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Have a friend that is on an electric co-op where peak $/kWh is 4x the 
off-peak rate.  Peak hours are 6-10 am in the winter and 12-6 pm in the 
summer.

He has relocated an older system from his previous house to his new one; 
circuits were separated out to sub-panel that is connected to the inverter 
AC output.  The reinstallation is very professional.

Two Trace SW4024 in series (04/96)
120/240 Vac Grid connected to AC1 of each inverter
575 Ah battery bank
Two C40s with digital displays, ~ 4.5 kW STC array total
Trimetric

The goal is to not use any utility energy during peak times, unless the 
low battery voltage setting is reached, and in general to run as an 
off-grid system, minimizing charge time from the grid during off-peak 
hours as well.  The assumption (I know it's a tough one, but I'm coming in 
after the transition) is that the PV array should at least be able to 
provide the bulk of the load; using the grid to charge the batteries to 
ensure they are regularly filled and to maximize their life expectancy. 
 The customer is also managing loads actively.

It's been a few years, but I used to work on these all the time; however 
it was usually off-grid with a genset, or fixing poorly maintained Y2K 
systems which were always in float. I'm attempting to use the energy 
management mode.

Inverter settings:
Clocks: Time is accurate
Grid AC1 amps AC: 60
Max charge amps AC: 10 (each inverter)

Grid usage: FLT
Set start charge time: 23:00
Start bulk time: 23:10
Set end charge time: 05:00
Set float volts DC: 25.4
Bulk volts DC: 28.8
Absorb time: 1.5 hours
Low battery cut-out: 22 
Low battery cut-in: 25.4

Okay, programmed the system, both inverters are inverting, AC1 is blinking 
green, looks good.  Then a well pump kicks on, registers 70 A DC on the 
Trimetric.  This causes inverter 1 to go into bulk charging and pass 
through about 10 additional amps from the grid to the load (inverter 2 
continued to inverter about 10 amps for the load).  Inverter 1 soon cycled 
into float, then went back to what invertering (amber light) and green 
blinking AC1 (which is what I want it to be at).  

Had to leave, both the customer and I had other obligations.

He took a picture of the inverter sat 11:15 pm, and they were in bulk, 
battery voltage rising...exactly as planned.  But then in the next set of 
pictures, taken at 7 am, after the end of the charge time, they were in 
float, not inverting, even though, based on the Trimetric readings at 11 
(64%, 85A charging), and the fact that charging would have been active all 
night, they were not in anyway at a low voltage condition (Trimetric 
readings am readings were 85%, trickle charge, 25.6 V).

Something seems amiss.  Any suggestions or insight?

Thanks!

Brian Mehalic 
NABCEP Certified Solar PV Installation Professional™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant

Re: [RE-wrenches] Trace SWs in Energy Management Mode

2013-10-04 Thread Eric . Bentsen
Hi Brian,
That is the issue.LBX mode is the only way the SW can disconnect from 
a qualified source of AC, thus maximizing solar production. The best way 
is 
to get approved to sell, which probably won't happen with an inverter that 
old.
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Brian Mehalic br...@solarenergy.org
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
10/04/2013 01:39 PM
Subject:
Re: [RE-wrenches] Trace SWs in Energy Management Mode
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Thanks, I was thinking about using LBX, but the customer is really not too 
excited about it.  And based on the manual, Energy Management Mode seems 
like it fits the bill, but it doesn't seem to be going back into 
stand-alone/inverter mode when the timer is supossed to turn off.


Brian Mehalic 
NABCEP Certified Solar PV Installation Professional™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org


On Fri, Oct 4, 2013 at 3:42 PM, eric.bent...@schneider-electric.com 
wrote:

Hi Brian, 
LBX would be better for the way this customer is using the system, because 
it only connects 
 to the grid when the batteries get low. Unfortunately, the timers do not 
affect LBX, so charging 
may occur during the peak rateor it may not :C) 

Rgds, 

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 



From: 
Brian Mehalic br...@solarenergy.org 
To: 
RE-wrenches re-wrenches@lists.re-wrenches.org 
Date: 
10/04/2013 12:04 PM 
Subject: 
[RE-wrenches] Trace SWs in Energy Management Mode 
Sent by: 
re-wrenches-boun...@lists.re-wrenches.org





Have a friend that is on an electric co-op where peak $/kWh is 4x the 
off-peak rate.  Peak hours are 6-10 am in the winter and 12-6 pm in the 
summer. 

He has relocated an older system from his previous house to his new one; 
circuits were separated out to sub-panel that is connected to the inverter 
AC output.  The reinstallation is very professional. 

Two Trace SW4024 in series (04/96) 
120/240 Vac Grid connected to AC1 of each inverter 
575 Ah battery bank 
Two C40s with digital displays, ~ 4.5 kW STC array total 
Trimetric 

The goal is to not use any utility energy during peak times, unless the 
low battery voltage setting is reached, and in general to run as an 
off-grid system, minimizing charge time from the grid during off-peak 
hours as well.  The assumption (I know it's a tough one, but I'm coming in 
after the transition) is that the PV array should at least be able to 
provide the bulk of the load; using the grid to charge the batteries to 
ensure they are regularly filled and to maximize their life expectancy. 
 The customer is also managing loads actively. 

It's been a few years, but I used to work on these all the time; however 
it was usually off-grid with a genset, or fixing poorly maintained Y2K 
systems which were always in float. I'm attempting to use the energy 
management mode. 

Inverter settings: 
Clocks: Time is accurate 
Grid AC1 amps AC: 60 
Max charge amps AC: 10 (each inverter) 

Grid usage: FLT 
Set start charge time: 23:00 
Start bulk time: 23:10 
Set end charge time: 05:00 
Set float volts DC: 25.4 
Bulk volts DC: 28.8 
Absorb time: 1.5 hours 
Low battery cut-out: 22  
Low battery cut-in: 25.4 

Okay, programmed the system, both inverters are inverting, AC1 is blinking 
green, looks good.  Then a well pump kicks on, registers 70 A DC on the 
Trimetric.  This causes inverter 1 to go into bulk charging and pass 
through about 10 additional amps from the grid to the load (inverter 2 
continued to inverter about 10 amps for the load).  Inverter 1 soon cycled 
into float, then went back to what invertering (amber light) and green 
blinking AC1 (which is what I want it to be at).   

Had to leave, both the customer and I had other obligations. 

He took a picture of the inverter sat 11:15 pm, and they were in bulk, 
battery voltage rising...exactly as planned.  But then in the next set of 
pictures, taken at 7 am, after the end of the charge time, they were in 
float, not inverting, even though, based on the Trimetric

Re: [RE-wrenches] Search mode

2013-09-10 Thread Eric . Bentsen
Hi Jesse,
With my XW4024, I have (2) GFCI recepticles within 2 ft of the PDP. 
I am required to set search to 90W before it enters search mode, but if I 
cut the breakers that feed the GFCIs, I can
 set search to min value (25W) and it will remain in search mode.
Most folks do not use search because certain loads require continuous AC, 
i.e. the clock on your microwave, or a fridge,etc.
The power draw in search is 8W, and no load draw when inverting is approx 
25W.
Hope that helps,
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Jesse Dahl dahlso...@gmail.com
To:
Wrenches RE-wrenches@lists.re-wrenches.org
Date:
09/08/2013 03:39 PM
Subject:
[RE-wrenches] Search mode
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Hello,

A friend of mine in the woods just put in a new xantrax inverter and is 
having a search mode problem. They can't get 25W search mode to work and 
are stuck with using the 50W setting. So they've had to put a few 
incandescents in to make this setting work. His calls to tech support have 
been less then helpful. 

Advice I can pass on?

Thanks as always!

Jesse

Sent from my iPhone
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Fw: Conext inverter

2013-08-29 Thread Eric . Bentsen
Hi Allen,
Conext SW is available in 24V models only (not 12V). 
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar al...@positiveenergysolar.com
To:
jay peltz j...@asis.com
Cc:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/28/2013 06:51 PM
Subject:
Re: [RE-wrenches] Conext inverter
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Jay,
No, it's the first new product since Schneider bought Xantrex and soon 
realized that they had to put in a lot of effort to develop the line that 
they paid way too much for. 

This series is intended for off grid and GTWB, is not able to sell back, 
is sine wave, 120/240, 12/24V only, to be marketed as much to the 
developing world as the US, and will be promoted as a lower cost 
competitor to Magnum's PAE. That's about all I know about it. Info is at 
http://www.schneider-electric.com/products/ww/en/7000-solar-off-grid-and-back-up/7010-inverters-chargers/61645-conext-sw/?BUSINESS=7
 
and  
http://www.schneider-electric.com/products/ww/en/7000-solar-off-grid-and-back-up/7030-monitoring/62089-conext-combox/?BUSINESS=7
.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
On 8/28/2013 7:34 PM, jay peltz wrote:
HI Allan, 

I think you have me here.

I was under the impression that this is just a new name for what is the 
old XW series?


jay

peltz power


On Aug 28, 2013, at 5:24 PM, Allan Sindelar wrote:

Wrenches,
When a new product comes out I usually wait for a few reviews on this list 
before using it. That would have been the case with the new Schneider 
Conext series, the low-cost 120/240 SW off grid unit. But I was talking 
with Tom Carpenter of Midnite about other issues and he happened to speak 
quite highly of the unit he was bench testing. So I'm asking: has anyone 
worked with this unit yet? What's the feedback, please?
Allan
-- 
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Xantrex XW system stability

2013-08-26 Thread Eric . Bentsen
Hi Kevin,
We have found that network (Cat5) cables shorter than 2m (6.5 ft) causes 
network reflections that contribute to network instability in multi-unit 
XW systems. Do not rule out a bad or intermittent network cable either. 
Also, confirm the inverters have the same firmware and the latest.
It is not necessary to have the controllers in-network, but it allows 
Enhanced Grid operation, which does a better job of keeping batteries full 
when 
selling. For off grid, they can be in a separate network if you want to 
monitor them with a dedicated SCP, but you will need to supply network 
power 
for Xanbus (AUX port can be used for this).

Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Kevin Pegg kp...@energyalternatives.ca
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/22/2013 10:18 AM
Subject:
[RE-wrenches] Xantrex XW system stability
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Hello Wrenches, 

Curious how others are finding the stability of larger Xantrex XW 
deployments? We have an installation with 12 Xanbus devices (4 x XW6048, 6 
x XW-MPPT60, 1 x AGS, 1 x SCP) and it keeps crashing. Power cycle the 
whole system and it's fine for a few weeks and then it crashes again. 

I find with smaller deployments under 5 Xanbus devices the stability is 
much better, but still get the occasional customer call with a system gone 
haywire and a power cycle fixes. 

This particular installation is in the high arctic darn near the north 
pole and sending a tech up there next week to resolve. Needless to say, 
it's an expensive ordeal to get up there. 

Kevin


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV Assist

2013-08-16 Thread Eric . Bentsen
Hi William,
In off grid applications, you want to have sufficient RE to keep up with 
load demand 
and only run the generator when RE cannot keep up. However, having too 
much RE is a waste because it will
 result in energy not harvested (if regulating), however, diversion 
controllers can allow the excess energy to be utilized
 (i.e. water heating).
Running the gen up to the bulk level replaces approx 80% of capacity, and 
maximizes fuel consumption, allowing RE to get the
 batteries charged the last 20%. Automatic gen start capability with 
staggered start voltages allow you to target 50% discharge 
more accurately, and minimizes user interaction. Try to calculate the 
total daily kWhrs and match the demand with RE as 
closely as possible. 
Hope that helps,
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Jay Peltz j...@asis.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/16/2013 02:01 PM
Subject:
Re: [RE-wrenches] PV Assist
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Hi William 

Thx helps a lot. 
I can only say how I do it. 
I'll give the client some options, including the change of appliances and 
usually the price difference makes the sale one way or the other. 

Funny reminds me of the old days, only with much smaller loads/$. 

Good luck

Jay



Sent from my iPhone

On Aug 16, 2013, at 12:49 PM, William Miller will...@millersolar.com 
wrote:

Jay:
 
There are four systems in question.  In three the loads are year round and 
one is summer only AC loads.  The year round loaded systems have loads day 
and night.
 
One is a highway maintenence station with at least 4 residences.
One is a family compound with two homes with electric ranges, water 
heaters, AC units (I know its stupid, lord knows I've tried to convince 
them to change appliances.)
One is an animal rescue operation with heater loads.
One is a large home with 5 very small, very new, very sophisticated and 
frugal AC units
 
I know it is silly to move these loads off-grid, but people do it and they 
will hire someone to work on the systems.  It may as well be me, doing the 
best I can to use the resources as wisely as possible.
 
William
 
PS:  It always happens like this:  I get a call from a client with 
problems.  Well, of course their expensive battery bank died and it died 
because of wasteful appliances.  The prescription is a new, expensive 
battery bank and, at the same time, new, expensive, efficient appliances. 
They complain can't afford both and they have to have the batteries, so 
that is what they get.  Repeat every two years.  Sad
 
Wm
 
 
From: re-wrenches-boun...@lists.re-wrenches.org [
mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
Sent: Friday, August 16, 2013 12:22 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] PV Assist

Hi William

I feel it's impossible to discuss without more specifics. 

For example if the extreme loads are only every ( just run the genny) so 
often vs seasonal ( maybe AC coupling makes more sense vs cycling a 
extremely expensive battery 4 x day),  vs year round vs what is do able 
etc

I would be curious to know what some of the parameters are, as I'm sure 
others as well

Jay

Peltz power. 





Sent from my iPhone

On Aug 16, 2013, at 10:53 AM, William Miller will...@millersolar.com 
wrote:

Friends:
 
We have been receiving a flurry of requests for design of off-grid systems 
where the loads are enormous, relative to normal off-grid requirements. It 
is obvious that the size of PV and battery arrays to power these loads is 
beyond what is practical.  We have dubbed these systems Generator/battery 
with PV assist, or PV assist for short.
 
These systems will cycle batteries multiple times per day.  It is my 
understanding that the extra battery cycels will shorten battery life. 
Since generator run is expected, we are willing to increase generator run 
time in order to prolong battery life.
 
The parameters I suggest are an aggressive load start and a very high 
battery start parameter.  This will prevent deep discharge of the battery 
bank.  I know shallow discharge is not the norm, but I don't believe 
shallow cycling is a problem as long is it as at the top of the voltage 
window, i.e. the batteries achieve absorption at least once per day.
 
We know a load start ciuld result in an abbreviated run time, curtailing 
absorption period, but we are assuming there will be a battery votage 
start at least once per day allowing full absorption.
 
Has anyone else considered these issues, and what conclusions did you make
 
I am

Re: [RE-wrenches] Mouse pee in the SW

2013-08-15 Thread Eric . Bentsen
Hi William,
Fluid intrusion can be very problematic and lead to highly erratic 
behavior, if not a complete shutdown.
If an IC was internally damaged by moisture allowing for an undesirable 
current path, then a chipset may 
solve the issue. It may be a challenge to clean sufficiently unless you 
remove (unsolder) the DIP sockets (big job). 
 However, if other components were damaged, it may require a complete 
control board replacement. 
We still have them available, if you want pricing, email me off list.
eric.bent...@schneider-electric.com
Rgds,

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
William Miller will...@millersolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/15/2013 02:37 PM
Subject:
[RE-wrenches] Mouse pee in the SW
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Friends:
 
I had a mouse take up residency in an SW inverter (SW4024).  It peed on 
the top circuit board and chewed on one wire, at least that we found.  We 
have had this happen before and solved the problem by cleaning and drying. 
 
 
This time the mouse pee was minimal and cleaned off easily and what 
appeared to be throughly.  However we can't get the inverter to work 
reliably.  Sometimes it works and sometimes it does not.  The overload 
light is solid and the error light flashes.  The controls work on some 
menus and not on others.  If I shut the inverter down it won't come back 
on.  I take off the cover, look around, connect and disconnect ribon 
cables and it comes back on, only to go out a day later.
 
I have a spare display and chipset.  I am considering changing out one 
then the other.
 
Any adivce would be appreciated.
 
As always, I am very grateful to all of you.  It seems I have been 
receiving more advice than I have been giving lately so I look forwards to 
the opportuntiy to reciprocate.
 
Sincerely,
 
William Miller

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SW AGS

2013-08-07 Thread Eric . Bentsen
Hi Eric,
 Sounded like bad batteries to me also (I think he called in this AM). He 
has (2) XW6048 units that are 
capable of 200ADC between them, and he also has 1260Ah of flooded 
capacity. DC Start V is set for 46.5V, so if we assume he was close to 50% 

discharge (depending on load), it should take almost 2 hours to reach the 
bulk voltage (80% replaced). His batteries were ramping up to bulk 
in just a couple of minutes, meaning the batteries were not absorbing the 
charge. I have heard varying opinions on the symptoms of sulfation, 
but it does sound like a battery issue (5 yrs old). He was advised to 
equalize to try and recover them (he has never done this), or replace 
them.
Rgds,

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
SunHarvest e...@harvesthesun.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 12:39 PM
Subject:
[RE-wrenches] SW AGS
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



I read through the archives on the XW AGS thread but have a query on 
behalf of a customer with an SW AGS issue. I'm heading out to the remote 
site tomorrow and would like, if possible, to show up knowing what I might 
be up against.
 
The customer recently replaced his AGS for his two SW 6048s and then 
upgraded his firmware a week later. He reported that his problem with the 
AGS began after firmware upgrade. Here's the particular issue:
 
AGS will try to start the 15.8kW Multi-Quip genny due to low battery 
voltage (event 306 DCV start). After about 5 minutes the AGS will stop the 
genny due to battery absorption level reached (event 313 ABS stop). The 
AGS will go through this event 306/313 cycle on and off until the 
homeowner shuts down the AGS. To me this sounds like bad batteries. But, 
the homeowner says this cycling does not occur when he manually starts the 
generator. This doesn't sound like a complicated problem but so far I'm 
unfamiliar with the SW AGS. So, I would greatly appreciate any insight you 
guys can offer me.
 
Thanks!!
 
Eric
SunHarvest
001.530.798.3738 (Cell)

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trojan L-16s

2013-08-07 Thread Eric . Bentsen
Hi Allen,
I am going by experience, not only with my own (4) Workaholic L16s, but 
when dealing with customers in the field.
 I would like to get some feedback from other wrenches on this.
 Maybe it is coincidence, but there seems to be a correlation. Maybe the 
taller batteries 
experience sulfation easier?
 
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar al...@positiveenergysolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 12:59 PM
Subject:
Re: [RE-wrenches] Trojan L-16s
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Eric,
I kept this in my inbox for awhile, and finally had to ask - where did you 
get this information? I have never heard this recommendation - to charge a 
taller flooded lead acid battery to a higher voltage just because it's 
taller. I guess I see the apparent logic - more gassing addresses a 
potential for more stratification of the electrolyte - but if true, why 
have I never seen this in any battery service guide? What's your source? 
And has anyone else heard of this?
Thanks, Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
On 7/16/2013 7:53 AM, eric.bent...@schneider-electric.com wrote:

Hi Drake, 
The L16 is quite popular in RE apps...but they typically require a bit 
higher charge voltage to reach the correct SOC than their shorter 
counterparts (i.e. T105 golf cart), 
because they are a taller battery (stands to reason .specific 
gravity). Make sure they are in a vented enclosure if off-gassing will 
be an issue. 
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 



__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SW AGS

2013-08-07 Thread Eric . Bentsen
It's an XW system.SW doesn't have event codes. 
Starting the gen manually just means it will keep running until he stops 
it.
We need to see how much current is flowing, and what's going on with 
battery voltage.
If you are going to the site, give me a call when you get there.
866-519-1470
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
SunHarvest e...@harvesthesun.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 02:08 PM
Subject:
Re: [RE-wrenches] SW AGS
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Sounds like you talked to the right guy, that's his info...except that he 
has, according to what he told me, an SW not an XW. I'm assuming he's 
maybe at 50% capacity on his original 1260Ah bank based on everything he 
told me this morning. He did say that his bank will last him through the 
night and that he has some pretty hefty air conditioning loads. He also 
said he had equalized in the past but not in the last 18 months. I'm just 
not convinced that his batteries are shot. But all this battery talk may 
be beside the point if he's not experiencing the same on/off cycling 
problem when he manually starts the genny, right? That is, assuming the 
disco settings remain in effect regardless of start mechanism. Thanks for 
indulging me tocayo.
 
Eric
SunHarvest
001.530.798.3738 (Cell)
- Original Message - 
From: eric.bent...@schneider-electric.com 
To: RE-wrenches 
Sent: Wednesday, August 07, 2013 12:54 PM
Subject: Re: [RE-wrenches] SW AGS


Hi Eric, 
 Sounded like bad batteries to me also (I think he called in this AM). He 
has (2) XW6048 units that are 
capable of 200ADC between them, and he also has 1260Ah of flooded 
capacity. DC Start V is set for 46.5V, so if we assume he was close to 50% 

discharge (depending on load), it should take almost 2 hours to reach the 
bulk voltage (80% replaced). His batteries were ramping up to bulk 
in just a couple of minutes, meaning the batteries were not absorbing the 
charge. I have heard varying opinions on the symptoms of sulfation, 
but it does sound like a battery issue (5 yrs old). He was advised to 
equalize to try and recover them (he has never done this), or replace 
them. 
Rgds, 

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 



From: 
SunHarvest e...@harvesthesun.com 
To: 
RE-wrenches re-wrenches@lists.re-wrenches.org 
Date: 
08/07/2013 12:39 PM 
Subject: 
[RE-wrenches] SW AGS 
Sent by: 
re-wrenches-boun...@lists.re-wrenches.org




I read through the archives on the XW AGS thread but have a query on 
behalf of a customer with an SW AGS issue. I'm heading out to the remote 
site tomorrow and would like, if possible, to show up knowing what I might 
be up against. 
  
The customer recently replaced his AGS for his two SW 6048s and then 
upgraded his firmware a week later. He reported that his problem with the 
AGS began after firmware upgrade. Here's the particular issue: 
  
AGS will try to start the 15.8kW Multi-Quip genny due to low battery 
voltage (event 306 DCV start). After about 5 minutes the AGS will stop the 
genny due to battery absorption level reached (event 313 ABS stop). The 
AGS will go through this event 306/313 cycle on and off until the 
homeowner shuts down the AGS. To me this sounds like bad batteries. But, 
the homeowner says this cycling does not occur when he manually starts the 
generator. This doesn't sound like a complicated problem but so far I'm 
unfamiliar with the SW AGS. So, I would greatly appreciate any insight you 
guys can offer me. 
  
Thanks!! 
  
Eric
SunHarvest
001.530.798.3738 (Cell) 

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org

[RE-wrenches] Fw: Trojan L-16s

2013-08-07 Thread Eric . Bentsen
Hi Allen,
Now that you have me thinking.if you look at the charge recommendation 
for T-105 and L16, according to Trojan,
 they are giving us a range of 2.35-2.45V per cell @77degF.
If there is no variable other than temperature, why the range?
http://www.trojanbatteryre.com/PDF/datasheets/L16REA_TrojanRE_Data_Sheets.pdf
http://www.trojanbatteryre.com/PDF/datasheets/T105_TrojanRE_Data_Sheets.pdf

Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 

- Forwarded by Eric Bentsen/Canada/Schneider on 08/07/2013 01:53 PM 
-

From:
Eric Bentsen/Canada/Schneider
To:
al...@positiveenergysolar.com, RE-wrenches 
re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 01:41 PM
Subject:
Re: [RE-wrenches] Trojan L-16s


Hi Allen,
I am going by experience, not only with my own (4) Workaholic L16s, but 
when dealing with customers in the field.
 I would like to get some feedback from other wrenches on this.
 Maybe it is coincidence, but there seems to be a correlation. Maybe the 
taller batteries 
experience sulfation easier?
 
Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar al...@positiveenergysolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 12:59 PM
Subject:
Re: [RE-wrenches] Trojan L-16s
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Eric,
I kept this in my inbox for awhile, and finally had to ask - where did you 
get this information? I have never heard this recommendation - to charge a 
taller flooded lead acid battery to a higher voltage just because it's 
taller. I guess I see the apparent logic - more gassing addresses a 
potential for more stratification of the electrolyte - but if true, why 
have I never seen this in any battery service guide? What's your source? 
And has anyone else heard of this?
Thanks, Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 
On 7/16/2013 7:53 AM, eric.bent...@schneider-electric.com wrote:

Hi Drake, 
The L16 is quite popular in RE apps...but they typically require a bit 
higher charge voltage to reach the correct SOC than their shorter 
counterparts (i.e. T105 golf cart), 
because they are a taller battery (stands to reason .specific 
gravity). Make sure they are in a vented enclosure if off-gassing will 
be an issue. 
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 



__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpegimage/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SW AGS

2013-08-07 Thread Eric . Bentsen
Hi Chris,
Stop absorb ramps up to the BULK voltage, which replaces approx 80% of 
capacity. Running the gen thru the 
absorption stage will allow for a full charge, but is a waste of fuel 
(most of abs is at reduced rate), and users want to 
charge the rest of the way with RE. The SW uses Absorption Time for stop 
parameter, but if set to 0 would accomplish
 the same as stop absorb.
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Chris Worcester ch...@solarwindworks.com
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 03:17 PM
Subject:
Re: [RE-wrenches] SW AGS
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Now there is a useful setting, just being a little sarcastic, this would 
be hard to diagnose. Was that available on the SW’s AGS menu too?
 
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Office 530-582-4503
Cell 530-448-9692
Fax 530-582-4603
www.solarwindworks.com
ch...@solarwindworks.com
 
From: re-wrenches-boun...@lists.re-wrenches.org [
mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Wednesday, August 07, 2013 2:30 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] SW AGS
 
HI Eric,
 
Sounds like the stop absorb might have been enabled.
This will stop the AGS when the battery volts reach absorb setpoint.
 
But has no impact if starting the generator manually.
 
jay
 
peltz power
 
 


Sounds like you talked to the right guy, that's his info...except that he 
has, according to what he told me, an SW not an XW. I'm assuming he's 
maybe at 50% capacity on his original 1260Ah bank based on everything he 
told me this morning. He did say that his bank will last him through the 
night and that he has some pretty hefty air conditioning loads. He also 
said he had equalized in the past but not in the last 18 months. I'm just 
not convinced that his batteries are shot. But all this battery talk may 
be beside the point if he's not experiencing the same on/off cycling 
problem when he manually starts the genny, right? That is, assuming the 
disco settings remain in effect regardless of start mechanism. Thanks for 
indulging me tocayo.
 
Eric
SunHarvest
001.530.798.3738 (Cell)
- Original Message -
From: eric.bent...@schneider-electric.com
To: RE-wrenches
Sent: Wednesday, August 07, 2013 12:54 PM
Subject: Re: [RE-wrenches] SW AGS
 

Hi Eric, 
 Sounded like bad batteries to me also (I think he called in this AM). He 
has (2) XW6048 units that are 
capable of 200ADC between them, and he also has 1260Ah of flooded 
capacity. DC Start V is set for 46.5V, so if we assume he was close to 50% 

discharge (depending on load), it should take almost 2 hours to reach the 
bulk voltage (80% replaced). His batteries were ramping up to bulk 
in just a couple of minutes, meaning the batteries were not absorbing the 
charge. I have heard varying opinions on the symptoms of sulfation, 
but it does sound like a battery issue (5 yrs old). He was advised to 
equalize to try and recover them (he has never done this), or replace 
them. 
Rgds, 

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 

Mail Attachment.jpeg
*** Please consider the environment before printing this e-mail 



From:
SunHarvest e...@harvesthesun.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/07/2013 12:39 PM
Subject:
[RE-wrenches] SW AGS
Sent by:
re-wrenches-boun...@lists.re-wrenches.org
 




I read through the archives on the XW AGS thread but have a query on 
behalf of a customer with an SW AGS issue. I'm heading out to the remote 
site tomorrow and would like, if possible, to show up knowing what I might 
be up against. 
  
The customer recently replaced his AGS for his two SW 6048s and then 
upgraded his firmware a week later. He reported that his problem with the 
AGS began after firmware upgrade. Here's the particular issue: 
  
AGS will try to start the 15.8kW Multi-Quip genny due to low battery 
voltage (event 306 DCV start). After about 5 minutes the AGS will stop the 
genny due to battery absorption level reached (event 313 ABS stop). The 
AGS will go through this event 306/313 cycle on and off until the 
homeowner shuts down the AGS. To me this sounds like bad batteries. But, 
the homeowner says this cycling

Re: [RE-wrenches] BIG dual axis trackers

2013-08-01 Thread Eric . Bentsen
Hi ,
Deger 5000HD and Sentinel Solar make large trackers. 
http://www.dommelvalley.ca/data/DEGERtraker-5000HD-dommelvalley.pdf
http://www.sentinelsolar.com/

Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Chris Daum ch...@oasismontana.com
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date:
08/01/2013 10:06 AM
Subject:
[RE-wrenches] BIG dual axis trackers
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Dear people:
 
Does anyone have a line on a really large dual axis tracker--something 
that would hold 25 or 30 modules in the ~250W range?  I've seen some 
really big commercial units, but I have a client wanting a dual axis 
tracker that'll hold 25 of the Helios 255s.
 
THANKS!
 
Chris Daum
Oasis Montana Inc.
406-777-4309
406-777-0830 fax
www.oasismontana.com 

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] C60 setpoint question

2013-08-01 Thread Eric . Bentsen
Hi Allen,
The absorption time is actually only 1 hour for the C-series controllers. 
Battery manufacturers are always the final authority on 
how their batteries should be charged. If they say you can charge at 
14.2-14.4V indefinitely, then increase the float setting.
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar al...@positiveenergysolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
08/01/2013 01:20 PM
Subject:
[RE-wrenches] C60 setpoint question
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Wrenches,
Eden, our main off grid field tech, came across a situation about which I 
want to ask the group for advice, please.

The system: existing old/funky off grid 12V residential system, done by 
others over many years; this was our first visit. Owner out of state, 
currently rented, owner's complaint is that the old Heart 2800 EMS 
inverter is shutting down at times. Six four year old Concorde SunXtender 
PVX-3050Ts, so 900 rated amp-hours in three strings at 12V. Approximately 
830 watts of a hodgepodge of older modules, but well below rated output at 
present, though no obvious failures. Trace C60 charge controller. Our 
assessment after a site visit is that the batteries have been chronically 
undercharged and are showing signs of premature sulfation.

With AGM batteries such as these, we have been encouraged (by Midnite tech 
support and others) to set really long absorption times - we have some 
systems with six-hour absorptions. The logic is that theese batteries can 
tolerate - indeed thrive on - staying at absorption voltage of 14.2 - 14.4 
V (for 12 V nominal) indefinitely, and given the fickle nature of off grid 
PV charging, this maximizes the likelihood of their getting full most 
days. This logic makes total sense to me.

Most modern MPPT charge controllers have a programmable absorption time, 
and some have a done amps (a.k.a. float transition current), to allow them 
to transition to float if the charge current necessary to maintain 
absorption voltage drops below a set threshold (typically 1-3% of battery 
capacity). The C60 has neither, but rather has a nonadjustable two-hour 
timed absorption. This brings the question: is there any good reason that 
the float voltage on the C60 should not be set to the same voltage as the 
bulk/absorption voltage, such that they never drop into float? When 
sufficient input is available to get the batteries full, they are just 
allowed to stay in absorption mode indefinitely, slowly getting the energy 
necessary to reach 100%.

We have installed many Concorde AGM batteries, but never with an old 
C-series controller. This idea seems wacky, but the more I think about it, 
the more I can't see any problem with it. What do the rest of you advise?
Thanks, Allan

-- 
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified PV Installation Professional 
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc., a Certified B CorporationTM
3209 Richards Lane
Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com
 

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-24 Thread Eric . Bentsen
Hi Jay,
This has happened to me personally, and to other customers I have dealt 
with over the years. In my case, I got my hands 
on (4) used Interstate Workaholic L16 batteries. I was unable to achieve 
an acceptable SG because the voltage would not
climb above 14V (using 20A charger). I used a clamp-on DC amp meter to 
verify a full 20A going into the batteries, but the voltage
 would not climb any higher. It was as if energy was being lost within the 
batteries. When I separated the bank into sets of two, 
the ratio of current-to-capacity was improved and I was able to equalize 
the daylights out of them, and eventually recovered 
their performance. I have heard of the condition where the battery has low 
SOC, and the charger causes the voltage to increase 
very quickly, but I cannot definitely attribute that to sulfation. It 
sounds more like an internal open circuit condition. I do know it 
usually results in the need to replace the batteries. 
Rgds
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
jay peltz j...@asis.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
07/23/2013 07:33 PM
Subject:
Re: [RE-wrenches] Tri-Star MPPT
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Hi Eric,

While agree with most all your assessments, 
Can you please elaborate on the sulfation causes the voltage not to 
climb?

This is quite counter to what I have seen and what the battery people say?

Thanks

Jay

Peltz power

Sent from my iPad

On Jul 23, 2013, at 2:48 PM, eric.bent...@schneider-electric.com wrote:


Hi William, 

 If the SG was 1.26, of course the battery voltage would increase 
quickly to 30V (which is high for warm weather, BTW). 
 It has been my experience that sulfation causes the voltage NOT to climb. 
Especially when you have a very large bank, and a 
 relatively small amount of solar. 
 Sometimes it is necessary to reduce the bank size into smaller sets to 
equalize them and recover their performance. 
This method of reducing bank size is also effective to compare performance 
and weed out a potentially bad battery. 
 Systems that have a lot of capacity, with a relatively small amount of 
charge current usually creates problems, because 
 the load demand exceeds solar production. 
 This results in batteries that operate with partial SOC, which is when 
sulfation is most prevalent. With (8) L16s, you have approx 
 800Ahrs of capacity (24V bank). It would take significantly more than 8A 
of charge current to properly care for a bank that size. 

Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 



__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-24 Thread Eric . Bentsen
Hi Larry,
Looking at the Rolls Solar Battery User Manual regarding corrective 
equalization, on pg. 9 line 5, it reads :
 If severely sulfated, it may take many hours for the specific gravity to 
rise. 
 In William's case, the SG is full.  This condition where the batteries do 
not seem to be absorbing the charge happens
 more often with sealed batteries. Maybe it is related to the degree of 
sulfation.
Rgds
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Larry Crutcher,Starlight Solar Power Systems 
la...@starlightsolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
07/24/2013 05:29 AM
Subject:
Re: [RE-wrenches] Tri-Star MPPT
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Jay, 

I saw that comment also. The more hardened lead sulfate becomes, the more 
resistant the battery is to the electrochemical process and therefore less 
current is drawn from the charge source. This decrease of load allows the 
charge voltage to rise more rapidly. This rapid rise is usually a first 
indicator of sulfated batteries. A healthy battery, charged at the proper 
rate, will always have a gradual, linear rise in voltage.

Just FYI, I am a hands on guy and my experience with servicing batteries 
is somewhat unique to our wrench group having designed, installed and 
serviced many hundreds of battery systems. Lead sulfation and it's cause 
and prevention has been an interest of mine because it is so prevalent. 

Larry

On Jul 23, 2013, at 9:32 PM, jay peltz j...@asis.com wrote:

Hi Eric,

While agree with most all your assessments, 
Can you please elaborate on the sulfation causes the voltage not to 
climb?

This is quite counter to what I have seen and what the battery people say?

Thanks

Jay

Peltz power

Sent from my iPad

On Jul 23, 2013, at 2:48 PM, eric.bent...@schneider-electric.com wrote:


Hi William, 

 If the SG was 1.26, of course the battery voltage would increase 
quickly to 30V (which is high for warm weather, BTW). 
 It has been my experience that sulfation causes the voltage NOT to climb. 
Especially when you have a very large bank, and a 
 relatively small amount of solar. 
 Sometimes it is necessary to reduce the bank size into smaller sets to 
equalize them and recover their performance. 
This method of reducing bank size is also effective to compare performance 
and weed out a potentially bad battery. 
 Systems that have a lot of capacity, with a relatively small amount of 
charge current usually creates problems, because 
 the load demand exceeds solar production. 
 This results in batteries that operate with partial SOC, which is when 
sulfation is most prevalent. With (8) L16s, you have approx 
 800Ahrs of capacity (24V bank). It would take significantly more than 8A 
of charge current to properly care for a bank that size. 

Rgds,
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re

Re: [RE-wrenches] Battery bank during peak times

2013-06-25 Thread Eric . Bentsen
Hi Jesse,
If the customer wants PV with battery storage capability, this can 
certainly reduce their utility bill. I agree that just charging off the 
grid 
during non-peak hours would not be very efficient, but when you add solar 
energy with storage to the equation, this can make a difference.
Rgds,
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Jesse Dahl dahlso...@gmail.com
To:
RE-wrenches RE-wrenches@lists.re-wrenches.org
Date:
06/24/2013 08:51 PM
Subject:
[RE-wrenches] Battery bank during peak times
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Hello,

I was contacted by a local co-op about installing a PV system at their 
office.  At first they wanted a straight grid-tied system, and after 
they received the bid they changed their minds and now want a battery 
based system price. What they want now is a system that will allow them to 
draw the battery bank down starting at 5pm during their peak demand time. 
Has anyone worked on or installed a system of this type?


Thanks as always!


Jesse

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] generator support mode

2013-06-21 Thread Eric . Bentsen
Hi Lee,
The MC version is similar to the standard SW, but does not have grid usage 
menu (no sell/lbx), and does not give AC1 priority (assuming both inputs 
are present). It will support the generator with battery power whenever 
the load exceeds the AC2 Amps setting in Menu 11.
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
i...@solarplexus1.com i...@solarplexus1.com
To:
RE-wrenches@lists.re-wrenches.org
Date:
06/21/2013 07:29 AM
Subject:
[RE-wrenches] generator support mode
Sent by:
re-wrenches-boun...@lists.re-wrenches.org




 I have a project using an SW4024 inverter that uses the 
generator support mode with a smaller hydro AC generator.   Worked well, 
but one of the to inverters died. There are plenty of new SWs on the 
internet, but all the new ones are SW4024MC2.   Apparently the SELL mode 
does not exist in the MC2 version and Auto Gen Start is an option.   Does 
anyone know if the good old generator support is available in the MC2 
version, or has it been scrapped along with the SELL mode. 

 Generator support mode--where some inverter AC output can 
be added to the generator AC input to meet a load larger than the 
generator could otherwise handle.  Not just where the inverter backs off 
the battery charger enough to use full generator input for the load.

 Any insight on the MC2 version would be helpful. 

Lee Tavenner
Solar Plexus
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


__
This email has been scanned by the Symantec Email Security.cloud service.
__


image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 690.55 - maximum operating voltage

2013-06-11 Thread Eric . Bentsen
Hi Bob,
I would rather it be worded maximum normal operating voltage. 
Maximum operating voltage would be the recommended BULK voltage for the 
battery type being utilized. 
Equalization is a maintenance procedure, which is why it calls for 
separate listing. 
It must also include polarity of grounded conductor.

Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Bob Clark bcl...@solar-wind.us
To:
'RE-Wrenches' re-wrenches@lists.re-wrenches.org
Date:
06/10/2013 08:08 PM
Subject:
[RE-wrenches] NEC 690.55 - maximum operating voltage
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



RE_Wrenches:
 
Can someone tell me what is being referred to in NEC 690.55 when it says 
“Photovoltaic power systems employing energy storage shall also be marked 
with the “maximum operating voltage, . . .” ?
 
We have an off-grid system which employs energy storage [i.e.; batteries]; 
so I need to know what exactly is referred to when this section mentions 
“maximum operating voltage” so I can put it on a sign.
 
Bob Clark
SolarWind Energy Systems, LLC

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Damage

2013-06-10 Thread Eric . Bentsen
Hi Will,
Flooded (or wet cell batteries) are typically much more forgiving than a 
sealed battery. Check S.G. (≈1.265 at rest) and load test. 
Equalize if necessary (if .05 difference in S.G. cell-to-cell).
Eric
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Will White william.wh...@realgoods.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
06/10/2013 05:23 AM
Subject:
[RE-wrenches] Battery Damage
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Wrenches,
 
I have a customer who’s got a 24V off grid system with one string of 12 
two volt, 2000AH Power Battery brand flooded lead batteries.  The bank is 
about four years old and has been working great except the customer forgot 
to water the batteries for an extended period.  When I went out to service 
them the plates were exposed and I had to add about a gallon of water per 
battery.  These batteries have a large amount of water over the plates 
usually so I’m guessing that about 1-2” of the top of the plates were 
exposed which is about 10% of the total plate surface.
 
So here’s the question.  The bank seems to be working fine, is it likely 
that permanent damage was done?  Is there a good way to test for damage? 
Is there anything I can to do mitigate any damage done?
 
Thanks,
Will
 
__
Will White
Regional Field Operations Manager �C New England
 
Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com
 
 

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V charging with 60 cell modules

2013-06-06 Thread Eric . Bentsen
Hi Allan,

The C-series behaves in the same way as if you were to connect the module 
directly to the battery, 
then watch a DC volt meter and disconnect/reconnect when the bulk voltage 
is reached to hold the battery 
at that level. It will hold at the bulk level for 1 hour, then transition 
to float.
If left connected without disconnecting, the voltage would eventually 
climb to Voc (approx 36VDC). So, while it is not 
going to be as efficient as the MPPT controller in the bulk/absorption 
stages, once the PWM controller transitions to float, 
it will operate right about the sweet spot (Vmp). The question was making 
a single 24V module work with a 24V battery.
 PWM is the only way to do it, as the MPPT requires a higher PV voltage 
due to the use of a buck transformer.
 I will certainly pass on any recommendations for improvement to our 
engineering team, and 
I appreciate the feedback.

Eric Bentsen

_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Allan Sindelar al...@positiveenergysolar.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
06/04/2013 10:35 AM
Subject:
Re: [RE-wrenches] 24V charging with 60 cell modules
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Eric,
Please explain further, as what you wrote makes no sense to me. Mac didn't 
indicate whether he wanted to charge a flooded battery (~29.2V) or sealed 
(~28.4V). The C-series of PWM controllers has a fixed two-hour absorption, 
which it only counts down once the bulk voltage is reached. If the bulk 
voltage setpoint is above the MPP of the module, as it is in this case, 
how can it ever reach float, as you suggest?

And further, this is spec-sheet calculation. In all but the coldest winter 
weather, the Vmp of the module will be lower still as the module 
temperature rises above 25ºC, and is likely to be even below the float 
voltage in hot weather. And in the winter, if the battery is also cold, it 
will need a higher voltage still to get fully charged.

So I'm with Bob-O on this one. You can't charge a 24V battery with a 20V 
module. Please tell us how I'm wrong.
Thanks, Allan

P.S. - And while I'm on a virtual roll, please tell your engineering folks 
to build a charge controller with a higher voltage input window. I don't 
mean 600 volts at $1,500 or whatever it is; just higher than 150V. On a 
48V system, we're stuck with series strings of three modules if we use the 
lowest-cost-per-watt 60-cell modules. That means that systems have to be 
designed with arrays in ~750-watt increments. Give us another 50-100V or 
so of headroom, so we can design with strings in multiples of 3, 4, or 5. 
Outback, are you listening too? The Midnite Classic does this for us... 
Thanks.

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com 


On 6/4/2013 10:43 AM, eric.bent...@schneider-electric.com wrote:

Hi Mac, 

A PWM charge controller, such as the C35, will work in this application, 
because it will 
act like a switch that connects the panel to the battery. While the bulk 
voltage will likely be slightly 
higher than Vmp, once the controller transitions to float, which is approx 
27V for most battery types, 
it should allow the module to operate very close to Vmp. 
Typically, MPPT controllers require a higher Vmp than the target charge 
voltage. 

Eric Bentsen
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 



From: 
Mac Lewis maclew...@gmail.com 
To: 
RE-wrenches re-wrenches@lists.re-wrenches.org 
Date: 
06/04/2013 08:05 AM 
Subject: 
[RE-wrenches] 24V charging with 60 cell modules 
Sent by: 
re-wrenches-boun...@lists.re-wrenches.org




Hello wrenches, 

Is there a good method to charge 24V battery bank with single 60 cell 
modules?  Ideally, I'd like to charge a 24 V bank with a Kyocera 
245GX-LFB.  However, at NOTC the Vmp is 26.8V.  Any good way to do this? 

Thanks in advance.
-- 



Mac Lewis
Yo solo sé que no sé nada. -Sócrates

Re: [RE-wrenches] Old Modules for GIT system?

2013-06-05 Thread Eric . Bentsen
Hi Dana,
If the Trace model is SW, it will not be approved for selling if it was 
manufactured prior to 2002 (non-GTI model). If the batteries need to be 
replaced, the added expense may be considerable depending on the size of 
the bank. I guess it depends if the customer really wants backup. You may 
want to consider reconfiguring the array in series and go with a grid 
interactive inverter, such as the Conext TX2800, which will work fine with 
a 1.9kW array (24 in series). Other replies to this post indicate the 
array is not easily accessible, which can present it's own set of issues. 
I guess it boils down to what the customer wants. You can always sell the 
Trace inverter to someone off grid and use the proceeds toward a new 
grid-tie inverter. 
Eric 
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Dana d...@solarwork.com
To:
'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date:
06/04/2013 02:04 PM
Subject:
[RE-wrenches] Old Modules for GIT system?
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



I have a client eat has a 24 - Solarex  SX 80 PV module system that was 
off grid, Trace inverter, APT Power panel and an very aged L-16 battery 
bank. 
The utility came in and he wants to go grid tie. It is or was only 960 
watt originally. I realize that an array rewire is in order and it may 
only be a 1 KW system but he is interested in getting the equipment 
upgraded.
Has anyone done a grid tie with such a small array and with modules this 
old?
Any thoughts on installing sealed batteries and leaving it alone? 
 

Dana Orzel 
Great Solar Works, Inc -  NABCEP # 051112-136
d...@solarwork.com  - www.solarwork.com 
O - 970.626.5253F - 970.626.4140   C - 208.721.7003 
Responsible Technologies for Responsible People since 1988 
 
 

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V charging with 60 cell modules

2013-06-04 Thread Eric . Bentsen
Hi Mac,

A PWM charge controller, such as the C35, will work in this application, 
because it will 
act like a switch that connects the panel to the battery. While the bulk 
voltage will likely be slightly
higher than Vmp, once the controller transitions to float, which is approx 
27V for most battery types,
it should allow the module to operate very close to Vmp. 
Typically, MPPT controllers require a higher Vmp than the target charge 
voltage.

Eric Bentsen
_
 


Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED 
STATES  |   Technical Support Representative 
Phone: +(650) 351-8237 ext. 001#  |   
Email: eric.bent...@schneider-electric.com  |   Site: 
www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
Livermore, CA 94551 


*** Please consider the environment before printing this e-mail 




From:
Mac Lewis maclew...@gmail.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org
Date:
06/04/2013 08:05 AM
Subject:
[RE-wrenches] 24V charging with 60 cell modules
Sent by:
re-wrenches-boun...@lists.re-wrenches.org



Hello wrenches,

Is there a good method to charge 24V battery bank with single 60 cell 
modules?  Ideally, I'd like to charge a 24 V bank with a Kyocera 
245GX-LFB.  However, at NOTC the Vmp is 26.8V.  Any good way to do this?

Thanks in advance.
-- 



Mac Lewis

Yo solo sé que no sé nada. -Sócrates

__
This email has been scanned by the Symantec Email Security.cloud service.
__
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



image/jpeg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org