Re: [RE-wrenches] Mate 3s with legacy FX inverters

2023-12-12 Thread Roland Shackelford via RE-wrenches
We have numerous systems, with no programing or Mate display issues,
however the oldest FX series wont display correctly on Optics RE and wont
allow remote programability through Optics RE.


Roland Shackelford

President / Owner

NABCEP PVIP #091209-162

O 808.775.7410 | M 808.938.9239 |

45-487 Lehua St Honokaa, HI 96727

Power Solutions for Generations Renewable Energy Services, Inc.



" Where there is integrity, there will be trust. Where there is trust,
there will be an atmosphere for success." - Sadhguru


On Tue, Dec 12, 2023 at 6:45 AM Foxfire Energy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I think it depends on the firmware/age on the FX and the software revision
> on the Mate3s.. Talk to Chris at Outback if you can.
> --
> *From:* RE-wrenches  on behalf
> of Todd Cory via RE-wrenches 
> *Sent:* Tuesday, December 12, 2023 11:24 AM
> *To:* RE-wrenches 
> *Cc:* toddc...@finestplanet.com 
> *Subject:* [RE-wrenches] Mate 3s with legacy FX inverters
>
>
> Wrenches,
>
> I am receiving conflicting information about using a Mate 3s with legacy
> FX inverters. Has anyone done this and was the 3s able to function
> correctly?
>
> Thanks,
>
> Todd
>
>
>
> Sent from Finest Planet WebMail.
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark phantom loads

2023-11-03 Thread Roland Shackelford via RE-wrenches
Don,

We have had this happen when you auto calibrate the CT's and the CTs aren't
properly positioned to see exported energy from the Sol-Ark inverter.
Couple other times it took several calibrations and messing with opening
and closing the cts and double checking splices on extensions of CTS.

Good luck!


Roland Shackelford

President / Owner

NABCEP PVIP #091209-162

O 808.775.7410 | M 808.938.9239 |

45-487 Lehua St Honokaa, HI 96727

Power Solutions for Generations Renewable Energy Services, Inc.



" Where there is integrity, there will be trust. Where there is trust,
there will be an atmosphere for success." - Sadhguru


On Wed, Oct 25, 2023 at 11:18 AM don energysolarnow.com via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Just spent yesterday debugging a Sol-Ark 15 kW inverter phantom load
> weirdness.
> With Work Mode set at Limited Power To Home it seemed to get a bit schizo,
> pulling around 6kW in from the grid on leg L1 and around 13 kW on the other
> L2 leg, with 7kW of PV added. No house loads were involved. The monitoring
> called this a 13 kW load.
> I measured something like 50 amps on L2 and neutral; 120 Volts on L1 and
> 125 Volts on L2 at the house. My Fluke clamp-on amp meter does not say
> which way AC current is flowing. The utility meter showed it as  power
> coming in.
> At the main meter panel about 150 ft away from the house the voltages were
> better balanced; probably due to proximity to the utility transformer.
> Those leg voltages were balanced when the inverter was shut down.
> Oddly, this phantom loading decreased with decreasing PV production later
> in the day.
> Working with Sol-Ark tech support we (of course) downloaded new firmware,
> then changed Work Mode to Limited Power To Load. After a couple of resets
> this had the effect of allowing the inverter to cover just the loads in the
> battery-backed subpanel; not those at the house main panel where the CT
> sensors are located. The phantom 13kW load has not recurred.
> Has anyone seen an inverter try to mix import and export on different legs
> by creating phantom loads?
>
> Don Barch
> Energy Solar
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sunny Island AC-Coupled system integration with Fortress E-Vault

2023-10-25 Thread Roland Shackelford via RE-wrenches
Hey Michael,

Sorry to hear about your problems.

We have gone through several SMA SI issues that can be very difficult to
narrow down but found most of the time the issues are founded on miss
understanding the affects that different set points have on the over all
system operation.

In your system, I assume but want to confirm that the Sunny boys are set to
off grid mode? And they have hardwired communications with Sunny Islands
with the proper piggy back cards installed?

We have two SMA SI offgrid system that we replaced lead acid batteries with
LFP and are successfully operating both in open loop communications. Both
are working well with minimal variation in SOC between SMA and batteries,
both do have separate DC charging sources and therefore have external
shunts enabled for monitoring the external charging sources (not sure if
this plays a factor). Both are properly regulating the AC coupled PV, but
took some adjustments to the SI charging parameters boost, full charge,
float and equalize, to get it working well, as well as we found VRLA
default battery SOC algorithm works better with LFP replacements.

Also one point of note is on any new battery programing the system attempts
to do a full charge and automatically sets battery SOC to 50%, how ever if
everything is programmed correctly it should just raise the battery to its
full voltage and hold it there, and it will then slowly auto correct the
SOC.

What did you set the max charge current for the batteries at?

Have the batteries discharged over a night and does this still happen when
the batteries are at a discharged state?

If you want to talk through details, you can reach me on my cell, just be
mindful of hawaii time.

Aloha,


Roland Shackelford

President / Owner

NABCEP PVIP #091209-162

O 808.775.7410 | M 808.938.9239 |

45-487 Lehua St Honokaa, HI 96727

Power Solutions for Generations Renewable Energy Services, Inc.



" Where there is integrity, there will be trust. Where there is trust,
there will be an atmosphere for success." - Sadhguru


On Tue, Oct 24, 2023 at 4:31 AM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Friends:
>
>
>
> This situation is as yet unresolved.  It is complicated enough I created a web
> page
> 
> to describe the scenario so I did not have to explain it over and over.  I
> submitted this to Fortress tech support.  They said they had likely not
> tested the Fortress compatibility with SI in an AC-Coupled system.
>
>
>
> While Fortress technicians and/or engineers ponder the situation I am
> brainstorming solutions.  One idea is to convert to a DC coupled system.
> DC Charge controllers will have intrinsically better voltage control.  The
> charge controller most likely suitable is the Schneider 600 volt 100 amp
> unit.  I would need two of them.  It is compatible with the existing string
> wiring.  In researching it many questions came up about that product’s
> suitability.  There is an integration guide for a Schneider system and
> Fortress but this would be a mixed system of Schneider and SMA.  Would I be
> able to apply closed loop communication to both systems?  Could the charge
> controllers work in open loop?  Has anyone tried anything like this?
>
>
>
> I will keep you apprised.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark arc fault issues

2022-05-10 Thread Roland Shackelford via RE-wrenches
We have had the same issues in the past, their newest firmware seems to
have fixed the issue.

Mahalo,

Roland Shackelford
President / Owner
Renewable Energy Services (RES), Inc. | www.renewablenergy.com |
Mobile:  808-938-9239 | Office:   808-775-7410 | Fax: 808-775-7756
NABCEP Certified PV Installation Professional #091209-162

" Where there is integrity, there will be trust. Where there is trust,
there will be an atmosphere for success." - Sadhguru

*Privileged And Confidential Communication.  This electronic transmission,
and any documents attached hereto, (a) are protected by the Electronic
Privacy Act (18 USC ?? 2510-2521), (b) may contain confidential and/or
legally privileged information, and (c) are for the sole use of the
intended recipient named above.  If you have received this electronic
message in error, please notify the sender and delete the electronic
message.  Any disclosure, copying, distribution, or use of the contents of
the information received in error is strictly prohibited.





On Tue, May 10, 2022 at 7:17 AM Eric Smiley via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> A general question for those who have installed Sol-Ark.
> We have a handful of systems that have consistently displayed arc-faults
> that, as best as we can determine, are false positives. Is this something
> others have experienced? We are trying to determine if this is a general
> problem with Sol-Ark or if we are having poor luck.
> Our other string inverter systems are not displaying this problem, which
> leads us to believe it isn't due to installer error.
>
> *Eric Smiley,* Project Manager
> e...@vecoop.ca
> T: 250.703.6004 <+12507036004>
> T: 888.386.0116 <+18883860116>
> *VIRIDIANENERGY.CA *
>
> * *
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org