Re: [RE-wrenches] 200a manual xfer switch w/ small aux contact : who makes it?

2023-07-26 Thread Michael Morningstar via RE-wrenches
Ditto what William said about those micro-switches. They really need to be
fine tuned


On Wed, Jul 26, 2023 at 4:29 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Mick:
>
> Square D offers a set of auxiliary contacts on the double throw switches.
> It is ordered by adding a suffix to the model number. Check the footnotes
> in the Digest. My supplier at CED can hook you up and arrange a drop
> shipment. Eddie Jensen at 805-543-4700.
>
> Be careful though, these are micro switches that sometimes come
> mis-aligned such that they might barely trip when installed and then not
> quite trip later on. Exercise the switch and observe the throw to ensure it
> is positive.
>
> Good luck.
>
> William
>
> On Wed, Jul 26, 2023 at 3:26 PM Mick Abraham via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi, Mechanix~ My off grid project needs dual 40kW diesel generators with
>> easy manual selection between "A" or "B". The output from the manual switch
>> would feed AC into a set of XW Pro inverter/chargers.
>>
>> I seek a 200a manual xfer switch that can also changeover the 12v+
>> generator automation wire with the same handle. Schneider DTU324N is 3
>> phase (solid neutral) so that does get me a third blade but since the
>> trigger wire is only a few amps this p/n seems like overkill on size/weight
>> and on cost.
>>
>> The manual switch unit doesn't need to make or break live power because
>> folks always tend to shut down any nearby noisy engine before they do any
>> switching. We also don't need 100k short circuit current rating because the
>> machines can't fault as big as grid power can. Non-fusible seems best b/c
>> each genset will have a 200a main breaker. I'd prefer to buy the switch
>> inside a NEMA1 enclosure rather than getting a bare switch that would
>> require me to mount it into a housing. The project won't be code
>> inspected, so thanks in advance for any suggestions.
>>
>> The Wrench List is the Bomb!
>>
>> Mick Abraham, Proprietor
>> www.abrahamsolar.com
>>
>> Landline: 970-731-4675
>> Cell phone or for text messaging: 970-946-6584
>> ᐧ
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
>
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

Michael Morningstar


Morningstar Electric

PO Box 1494

Mount Shasta, CA 96067

530-921-0560

mjmornings...@gmail.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] 200a manual xfer switch w/ small aux contact : who makes it?

2023-07-26 Thread William Miller via RE-wrenches
Mick:

Square D offers a set of auxiliary contacts on the double throw switches.
It is ordered by adding a suffix to the model number. Check the footnotes
in the Digest. My supplier at CED can hook you up and arrange a drop
shipment. Eddie Jensen at 805-543-4700.

Be careful though, these are micro switches that sometimes come mis-aligned
such that they might barely trip when installed and then not quite trip
later on. Exercise the switch and observe the throw to ensure it is
positive.

Good luck.

William

On Wed, Jul 26, 2023 at 3:26 PM Mick Abraham via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi, Mechanix~ My off grid project needs dual 40kW diesel generators with
> easy manual selection between "A" or "B". The output from the manual switch
> would feed AC into a set of XW Pro inverter/chargers.
>
> I seek a 200a manual xfer switch that can also changeover the 12v+
> generator automation wire with the same handle. Schneider DTU324N is 3
> phase (solid neutral) so that does get me a third blade but since the
> trigger wire is only a few amps this p/n seems like overkill on size/weight
> and on cost.
>
> The manual switch unit doesn't need to make or break live power because
> folks always tend to shut down any nearby noisy engine before they do any
> switching. We also don't need 100k short circuit current rating because the
> machines can't fault as big as grid power can. Non-fusible seems best b/c
> each genset will have a 200a main breaker. I'd prefer to buy the switch
> inside a NEMA1 enclosure rather than getting a bare switch that would
> require me to mount it into a housing. The project won't be code
> inspected, so thanks in advance for any suggestions.
>
> The Wrench List is the Bomb!
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Landline: 970-731-4675
> Cell phone or for text messaging: 970-946-6584
> ᐧ
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] 200a manual xfer switch w/ small aux contact : who makes it?

2023-07-26 Thread Dave Angelini Offgrid Solar via RE-wrenches


You saw the back-up control switch from Schneider? Probably not what you 
want. https://solar.se.com/us/en/product/backup-control-switch/

Might be good for something else?

Whole home or partial home backup made easy. When paired with Schneider 
Electric
XW Pro inverters, the Backup Control Switch (BCS) automatically 
disconnects from the
grid during an outage, allowing the system to provide backup power to 
the home.
Certified to UL standards for USA, The Backup Control Switch is used for 
larger XW Pro
systems requiring up to 200 A rated MID or service entrance 
installation.

Flexible Installation
* Whole home backup or subpanel backup with up to 200
A rating
* Service entrance rated when installed with a main breaker
* Top or bottom entry for grid input
* Optional non-backup circuit, making it easy to backup an
existing panel and remove select non-critical loads
* Configurable for export limiting with integrated meter
Reliable
* Fast 50 ms transfer from grid connected to backup power
operation
* Reliable backup power and load starting performance
with the compatible XW Pro inverters
* Connect up to 4 XW Pro inverters for up to 27 kW
continuous and 48 kW peak backup power capability
* Outdoor rated enclosure
* 10 year limited warranty

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridso...@sti.net
text 209 813 0060

On 2023-07-26 3:24 pm, Mick Abraham via RE-wrenches wrote:

Hi, Mechanix~ My off grid project needs dual 40kW diesel generators 
with easy manual selection between "A" or "B". The output from the 
manual switch would feed AC into a set of XW Pro inverter/chargers.


I seek a 200a manual xfer switch that can also changeover the 12v+ 
generator automation wire with the same handle. Schneider DTU324N is 3 
phase (solid neutral) so that does get me a third blade but since the 
trigger wire is only a few amps this p/n seems like overkill on 
size/weight and on cost.


The manual switch unit doesn't need to make or break live power because 
folks always tend to shut down any nearby noisy engine before they do 
any switching. We also don't need 100k short circuit current rating 
because the machines can't fault as big as grid power can. Non-fusible 
seems best b/c each genset will have a 200a main breaker. I'd prefer to 
buy the switch inside a NEMA1 enclosure rather than getting a bare 
switch that would require me to mount it into a housing. The project 
won't be code inspected, so thanks in advance for any suggestions.


The Wrench List is the Bomb!

Mick Abraham, Proprietor
www.abrahamsolar.com [1]

Landline: 970-731-4675
Cell phone or for text messaging: 970-946-6584
ᐧ
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
--
[1] http://www.abrahamsolar.com___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] 200a manual xfer switch w/ small aux contact : who makes it?

2023-07-26 Thread Darryl Thayer via RE-wrenches
I have seen such equipment from generator suppliers, they will be reversing
contactors,  Look for reversing disconnecting switches I have used them
from SQ D and Eaton, and GE.

On Wed, Jul 26, 2023 at 5:26 PM Mick Abraham via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi, Mechanix~ My off grid project needs dual 40kW diesel generators with
> easy manual selection between "A" or "B". The output from the manual switch
> would feed AC into a set of XW Pro inverter/chargers.
>
> I seek a 200a manual xfer switch that can also changeover the 12v+
> generator automation wire with the same handle. Schneider DTU324N is 3
> phase (solid neutral) so that does get me a third blade but since the
> trigger wire is only a few amps this p/n seems like overkill on size/weight
> and on cost.
>
> The manual switch unit doesn't need to make or break live power because
> folks always tend to shut down any nearby noisy engine before they do any
> switching. We also don't need 100k short circuit current rating because the
> machines can't fault as big as grid power can. Non-fusible seems best b/c
> each genset will have a 200a main breaker. I'd prefer to buy the switch
> inside a NEMA1 enclosure rather than getting a bare switch that would
> require me to mount it into a housing. The project won't be code
> inspected, so thanks in advance for any suggestions.
>
> The Wrench List is the Bomb!
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Landline: 970-731-4675
> Cell phone or for text messaging: 970-946-6584
> ᐧ
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] 200a manual xfer switch w/ small aux contact : who makes it?

2023-07-26 Thread Mick Abraham via RE-wrenches
Hi, Mechanix~ My off grid project needs dual 40kW diesel generators with
easy manual selection between "A" or "B". The output from the manual switch
would feed AC into a set of XW Pro inverter/chargers.

I seek a 200a manual xfer switch that can also changeover the 12v+
generator automation wire with the same handle. Schneider DTU324N is 3
phase (solid neutral) so that does get me a third blade but since the
trigger wire is only a few amps this p/n seems like overkill on size/weight
and on cost.

The manual switch unit doesn't need to make or break live power because
folks always tend to shut down any nearby noisy engine before they do any
switching. We also don't need 100k short circuit current rating because the
machines can't fault as big as grid power can. Non-fusible seems best b/c
each genset will have a 200a main breaker. I'd prefer to buy the switch
inside a NEMA1 enclosure rather than getting a bare switch that would
require me to mount it into a housing. The project won't be code
inspected, so thanks in advance for any suggestions.

The Wrench List is the Bomb!

Mick Abraham, Proprietor
www.abrahamsolar.com

Landline: 970-731-4675
Cell phone or for text messaging: 970-946-6584
ᐧ
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org