Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-30 Thread Tump
This is a good representation of poor battery design. Reducing the # of strings 
by increasing the capacity of the battery should always be considered. Yes this 
is a cheap way to go but in the long run this type of install can be very 
expensive. Without someone as experienced as Jarmo, the installer may never 
have figured this out. LESS STRINGS  more Ahours = less interconnects  
potential for inductance and gives one far better performance charging  
discharging. One bad cell and one is chasing their tail for quite a while w/ 
this install.
On Jun 29, 2015, at 6:28 PM, jarmo.venalai...@schneider-electric.com wrote:

 Hi: 
 
 I'm not sure how much trouble this has caused, so that's why I asked the 
 question.  With large battery banks, it is possible to end up with a cabling 
 layout which has a potentially very large loop area as was the case at one of 
 the sites where I saw problems.  Here's a picture of the battery bank they 
 had created. 
 
 Mail Attachment.gif 
 
 The + and - cables were not run side by side and the rack is made out of 
 steel.  The inverters did not like it until we ran the cables along the 
 battery bank and then side by side.  Once that was done, things worked as 
 expected. 
 
 JARMO
 _
  
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
 Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
 +604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  |  
  Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
 Mail Attachment.gif
 Mail Attachment.gif Mail Attachment.gif   Mail Attachment.gif   
 Mail Attachment.gif
 
 
 
 *** Please consider the environment before printing this e-mail
 
 
 
 From: Ray Walters r...@solarray.com
 To:   RE-wrenches re-wrenches@lists.re-wrenches.org,
 Date: 06/29/2015 03:05 PM
 Subject:  Re: [RE-wrenches] Battery Bank to Inverter Wiring
 Sent by:  RE-wrenches re-wrenches-boun...@lists.re-wrenches.org
 
 
 
 
 This is fascinating because while I knew the DC cables had an AC  component, 
 I never realized how much inductance played in the volt drop to the inverter. 
  Thanks for bringing this to our attention Jarmo.  
 Which brings up another question based on Benn's question:  isn't the battery 
 itself part of the inductive loop?  and would the lead inside and steel cases 
 act to increase the inductance?  Should we consider changing battery layouts 
 not just to shorten cable lengths, but to counter inductance in the batteries 
 themselves?  If needed, we could actually wire the batteries to twist by 
 putting every other 2 v cell in the opposite row.  
 My guess is that it wouldn't be worth it, but I've been wrong many 
 times...
 
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer, 
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760 
 On 6/29/2015 3:55 PM, Benn Kilburn wrote: 
 What about when you have the (+) and (-) terminals at opposite ends of a 
 larger battery bank?  Sure you can run the conductors side-by-side once they 
 meet up on their way to the inverter, but would you consider the distance 
 between the end terminals a large loop?  
 Ideally the battery string is laid out so the end terminals are close 
 together and close to the inverter, but this isn't always the case. 
 
 Benn Kilburn 
 SkyFire Energy Inc.  
 780-906-7807 
 
 
 On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com wrote:
 
 Hi: 
 
 From the comments so far, it appears that within the wrenches group, good 
 practices are the rule and DC cables are kept side by side, so the problem I 
 mentioned hasn't come up much. 
 
 I have seen large loop battery cables a couple of times in solar installs 
 myself out on islands way down south.  Also on boats/RV's/motor homes. 
 
 Please keep the cable loop in mind when you do bench tests of inverters, as 
 it may screw up the results and make it seem like there is something wrong 
 with the inverter. 
 
 JARMO
 _
  
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
 Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
 +604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  |  
  Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
 mime-attachment.gif
 mime-attachment.gif mime-attachment.gif   mime-attachment.gif   
 mime-attachment.gif
 
 
 
 
 *** Please consider the environment before printing this e-mail
 
 
 From: b...@midnitesolar.com b...@midnitesolar.com
 To:   RE-wrenches re-wrenches@lists.re-wrenches.org,
 Date: 06/28/2015 10:30 PM
 Subject:  Re: [RE-wrenches] Battery Bank to Inverter Wiring
 Sent by:  RE-wrenches re-wrenches-boun...@lists.re-wrenches.org

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-29 Thread b...@midnitesolar.com
mailto:jarmo.venalai...@schneider-electric.com |
*Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:*
3700 Gilmore Way, Burnaby, BC V5G4M1
mime-attachment.gif http://www.xantrexrebate.com/
mime-attachment.gif http://www.xantrex.com/
mime-attachment.gif https://www.facebook.com/Xantrex
mime-attachment.gif https://twitter.com/Xantrex
mime-attachment.gif https://twitter.com/Xantrex




*** Please consider the environment before printing this e-mail



From:   b...@midnitesolar.com mailto:b...@midnitesolar.com
b...@midnitesolar.com mailto:b...@midnitesolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
mailto:re-wrenches@lists.re-wrenches.org,
Date:   06/28/2015 10:30 PM
Subject:Re: [RE-wrenches] Battery Bank to Inverter Wiring
Sent by:RE-wrenches
re-wrenches-boun...@lists.re-wrenches.org
mailto:re-wrenches-boun...@lists.re-wrenches.org







On 6/28/2015 9:20 AM, Allan Sindelar wrote:
I'm not an EE, but I can't see what difference twisting
would make in
the absence of a building/collapsing field as is normal with AC.

It is little known that with the typical inverters that use the
heavy power transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current
mixed in with that DC battery current.

The AC output current reflects back to the input as ripple
current.  This is why you want to
have at least short as possible Sbattery cable runs AND keep the
wires as close together as possible.

Twisting the battery cables may help a bit but that is probably
overkill.

The problem has to do with inductance in the battery cables. 
You can use as big of cable

as you can fit in to reduce resistance, but that will not help
to lower the inductance.
The problems you can sometimes have with high inductance is that
L-C resonance at the
inverter can raise the peak voltages seen at the inverter input
terminals and can be hard on
the inverter.

Then again,  the high frequency, lighter weight inverters will
typically keep most of that ripple
inside,  between the DC input and AC output and battery cable
inductance will not be as much
of a problem on the battery cables.

boB Gudgel




On 6/28/2015 9:20 AM, Allan Sindelar wrote:
As a matter of course I have always run the positive and
negative conductors of high-current cable pairs together, but
have never deliberately twisted them, and have never known of
any related problems.
The most obvious example of this would be 4/0 battery/inverter
cables in a 24V system, with a 250A GJ-class breaker or (prior
to that) a 300A or 400A Class T fuse. It's pretty tough to
thread a twisted pair of 4/0 USE/RHH/RHW cables through a 2
elbow or LB from inverter enclosure to battery enclosure.
I'm not an EE, but I can't see what difference twisting would
make in the absence of a building/collapsing field as is normal
with AC.
I have twisted AC conductors together in the past when clients
have expressed concerns about EMF from their equipment and
wiring, but only AC.
Allan

*Allan Sindelar*_
__allan@sindelarsolar.com_ mailto:al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.*
505 780-2738 tel:505%20780-2738 cell*

On 6/27/2015 2:40 AM, John wrote:
That is why for years we have been twisting those leads around
each other.  I was told it was to cancel out the opposing fields
on the wires, but for whatever the correct technical reason is, 
we have always twisted those heavy wires. John V.


*From:* RE-wrenches
[_mailto:re-wrenches-boun...@lists.re-wrenches.org_] *On Behalf
Of *_Jarmo.Venalainen@schneider-electric.com_
mailto:jarmo.venalai...@schneider-electric.com*
Sent:* Saturday, 27 June 2015 5:45 a.m.*
To:* RE-wrenches*
Subject:* [RE-wrenches] Battery Bank to Inverter Wiring

Hi:

From time to time over the years I've come across systems where
the routing of DC cables between the batteries and the inverter
has been the cause of  issues.

I'm not referring to wire thickness or quality of terminations. 
For the purposes of this discussion, just assume that wire

thickness and terminations are perfect.

What I am referring to is the routing of the positive and
negative battery cables.  In particular, the loop area within
the + and - cables as shown in the image below,

The problem I've seen in systems with a large loop in the setup
is that the inverter does not provide good surge power and can
even go into low voltage shutdown during large surges.

Recently

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-29 Thread Benn Kilburn
What about when you have the (+) and (-) terminals at opposite ends of a larger 
battery bank?  Sure you can run the conductors side-by-side once they meet up 
on their way to the inverter, but would you consider the distance between the 
end terminals a large loop? 
Ideally the battery string is laid out so the end terminals are close together 
and close to the inverter, but this isn't always the case. 

Benn Kilburn
SkyFire Energy Inc. 
780-906-7807


 On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com wrote:
 
 Hi: 
 
 From the comments so far, it appears that within the wrenches group, good 
 practices are the rule and DC cables are kept side by side, so the problem I 
 mentioned hasn't come up much. 
 
 I have seen large loop battery cables a couple of times in solar installs 
 myself out on islands way down south.  Also on boats/RV's/motor homes. 
 
 Please keep the cable loop in mind when you do bench tests of inverters, as 
 it may screw up the results and make it seem like there is something wrong 
 with the inverter. 
 
 JARMO
 _
  
 
 Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
 Sales Application Engineer 
 Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
 +604-505-0291 
 Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  |  
  Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
 mime-attachment.gif
 mime-attachment.gif mime-attachment.gif   mime-attachment.gif   
 mime-attachment.gif
 
 
 
 *** Please consider the environment before printing this e-mail
 
 
 
 From: b...@midnitesolar.com b...@midnitesolar.com
 To:   RE-wrenches re-wrenches@lists.re-wrenches.org,
 Date: 06/28/2015 10:30 PM
 Subject:  Re: [RE-wrenches] Battery Bank to Inverter Wiring
 Sent by:  RE-wrenches re-wrenches-boun...@lists.re-wrenches.org
 
 
 
 
 
 On 6/28/2015 9:20 AM, Allan Sindelar wrote:
 I'm not an EE, but I can't see what difference twisting would make in
 the absence of a building/collapsing field as is normal with AC.
 
 It is little known that with the typical inverters that use the heavy power 
 transformers,
 have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in with 
 that DC battery current.
 
 The AC output current reflects back to the input as ripple current.  This is 
 why you want to
 have at least short as possible Sbattery cable runs AND keep the wires as 
 close together as possible.
 
 Twisting the battery cables may help a bit but that is probably overkill.
 
 The problem has to do with inductance in the battery cables.  You can use as 
 big of cable
 as you can fit in to reduce resistance, but that will not help to lower the 
 inductance.
 The problems you can sometimes have with high inductance is that L-C 
 resonance at the
 inverter can raise the peak voltages seen at the inverter input terminals and 
 can be hard on
 the inverter.
 
 Then again,  the high frequency, lighter weight inverters will typically keep 
 most of that ripple
 inside,  between the DC input and AC output and battery cable inductance will 
 not be as much
 of a problem on the battery cables.
 
 boB Gudgel
 
 
 
 
 On 6/28/2015 9:20 AM, Allan Sindelar wrote: 
 As a matter of course I have always run the positive and negative conductors 
 of high-current cable pairs together, but have never deliberately twisted 
 them, and have never known of any related problems. 
 The most obvious example of this would be 4/0 battery/inverter cables in a 
 24V system, with a 250A GJ-class breaker or (prior to that) a 300A or 400A 
 Class T fuse. It's pretty tough to thread a twisted pair of 4/0 USE/RHH/RHW 
 cables through a 2 elbow or LB from inverter enclosure to battery enclosure.
 I'm not an EE, but I can't see what difference twisting would make in the 
 absence of a building/collapsing field as is normal with AC. 
 I have twisted AC conductors together in the past when clients have expressed 
 concerns about EMF from their equipment and wiring, but only AC.
 Allan
 Allan Sindelar
 al...@sindelarsolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder (Retired), Positive Energy, Inc.
 505 780-2738 cell
 
  
 
 On 6/27/2015 2:40 AM, John wrote: 
 That is why for years we have been twisting those leads around each other.  I 
 was told it was to cancel out the opposing fields on the wires, but for 
 whatever the correct technical reason is,  we have always twisted those heavy 
 wires. John V. 
   
 From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
 Behalf Of jarmo.venalai...@schneider-electric.com
 Sent: Saturday, 27 June 2015 5:45 a.m.
 To: RE-wrenches
 Subject: [RE-wrenches] Battery Bank to Inverter Wiring 
   
 Hi: 
 
 From time to time over the years I've come across systems where the routing 
 of DC cables

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-29 Thread Ray Walters
This is fascinating because while I knew the DC cables had an AC 
component, I never realized how much inductance played in the volt drop 
to the inverter.  Thanks for bringing this to our attention Jarmo.
Which brings up another question based on Benn's question:  isn't the 
battery itself part of the inductive loop?  and would the lead inside 
and steel cases act to increase the inductance?  Should we consider 
changing battery layouts not just to shorten cable lengths, but to 
counter inductance in the batteries themselves?  If needed, we could 
actually wire the batteries to twist by putting every other 2 v cell 
in the opposite row.
My guess is that it wouldn't be worth it, but I've been wrong many 
times...


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 6/29/2015 3:55 PM, Benn Kilburn wrote:
What about when you have the (+) and (-) terminals at opposite ends of 
a larger battery bank?  Sure you can run the conductors side-by-side 
once they meet up on their way to the inverter, but would you consider 
the distance between the end terminals a large loop?
Ideally the battery string is laid out so the end terminals are close 
together and close to the inverter, but this isn't always the case.


Benn Kilburn
SkyFire Energy Inc.
780-906-7807


On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com 
mailto:jarmo.venalai...@schneider-electric.com wrote:



Hi:

From the comments so far, it appears that within the wrenches group, 
good practices are the rule and DC cables are kept side by side, so 
the problem I mentioned hasn't come up much.


I have seen large loop battery cables a couple of times in solar 
installs myself out on islands way down south.  Also on 
boats/RV's/motor homes.


Please keep the cable loop in mind when you do bench tests of 
inverters, as it may screw up the results and make it seem like there 
is something wrong with the inverter.


JARMO
_
*
Jarmo Venalainen*  | *Schneider Electric **|  Xantrex Brand*  | 
*CANADA*  | *Sales Application Engineer* *
Phone:* +604-422-2528  | *Tech Support:* 800-670-0707  | *Mobile:* 
+604-505-0291 *
Email:* _jarmo.venalainen@schneider-electric.com_ 
mailto:jarmo.venalai...@schneider-electric.com | 
*Site:*_www.Xantrex.com_ http://www.xantrex.com/ | *Address:* 3700 
Gilmore Way, Burnaby, BC V5G4M1

mime-attachment.gif http://www.xantrexrebate.com/
mime-attachment.gif http://www.xantrex.com/ 
mime-attachment.gif https://www.facebook.com/Xantrex 
mime-attachment.gif https://twitter.com/Xantrex 
mime-attachment.gif https://twitter.com/Xantrex





*** Please consider the environment before printing this e-mail



From: 	b...@midnitesolar.com mailto:b...@midnitesolar.com 
b...@midnitesolar.com mailto:b...@midnitesolar.com
To: 	RE-wrenches re-wrenches@lists.re-wrenches.org 
mailto:re-wrenches@lists.re-wrenches.org,

Date:   06/28/2015 10:30 PM
Subject:Re: [RE-wrenches] Battery Bank to Inverter Wiring
Sent by: 	RE-wrenches re-wrenches-boun...@lists.re-wrenches.org 
mailto:re-wrenches-boun...@lists.re-wrenches.org








On 6/28/2015 9:20 AM, Allan Sindelar wrote:
I'm not an EE, but I can't see what difference twisting would make in
the absence of a building/collapsing field as is normal with AC.

It is little known that with the typical inverters that use the heavy 
power transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed 
in with that DC battery current.


The AC output current reflects back to the input as ripple current. 
This is why you want to
have at least short as possible Sbattery cable runs AND keep the 
wires as close together as possible.


Twisting the battery cables may help a bit but that is probably overkill.

The problem has to do with inductance in the battery cables.  You can 
use as big of cable
as you can fit in to reduce resistance, but that will not help to 
lower the inductance.
The problems you can sometimes have with high inductance is that L-C 
resonance at the
inverter can raise the peak voltages seen at the inverter input 
terminals and can be hard on

the inverter.

Then again,  the high frequency, lighter weight inverters will 
typically keep most of that ripple
inside,  between the DC input and AC output and battery cable 
inductance will not be as much

of a problem on the battery cables.

boB Gudgel




On 6/28/2015 9:20 AM, Allan Sindelar wrote:
As a matter of course I have always run the positive and negative 
conductors of high-current cable pairs together, but have never 
deliberately twisted them, and have never known of any related problems.
The most obvious example of this would be 4/0 battery/inverter cables 
in a 24V system, with a 250A GJ-class breaker or (prior to that) a 
300A or 400A Class T fuse. It's pretty

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-29 Thread Roy Rakobitsch
In my experience, adding large electrolytic filter caps at the inverter
seems to help quite a bit with ac ripple issues and increases inverter
efficiency a bit as well.

Roy Rakobitsch
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
Certified Advanced Tower Climbing, Safety  Rescue
Wind/PV Design Engineer
Windsine LLC
631-514-4166
www.windsine.org
On Jun 29, 2015 5:05 PM, Ray Walters r...@solarray.com wrote:

  This is fascinating because while I knew the DC cables had an AC
 component, I never realized how much inductance played in the volt drop to
 the inverter.  Thanks for bringing this to our attention Jarmo.
 Which brings up another question based on Benn's question:  isn't the
 battery itself part of the inductive loop?  and would the lead inside and
 steel cases act to increase the inductance?  Should we consider changing
 battery layouts not just to shorten cable lengths, but to counter
 inductance in the batteries themselves?  If needed, we could actually wire
 the batteries to twist by putting every other 2 v cell in the opposite
 row.
 My guess is that it wouldn't be worth it, but I've been wrong many
 times...

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer303 505-8760

 On 6/29/2015 3:55 PM, Benn Kilburn wrote:

 What about when you have the (+) and (-) terminals at opposite ends of a
 larger battery bank?  Sure you can run the conductors side-by-side once
 they meet up on their way to the inverter, but would you consider the
 distance between the end terminals a large loop?
 Ideally the battery string is laid out so the end terminals are close
 together and close to the inverter, but this isn't always the case.

 Benn Kilburn
 SkyFire Energy Inc.
 780-906-7807


 On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com
 wrote:

  Hi:

 From the comments so far, it appears that within the wrenches group, good
 practices are the rule and DC cables are kept side by side, so the problem
 I mentioned hasn't come up much.

 I have seen large loop battery cables a couple of times in solar
 installs myself out on islands way down south.  Also on boats/RV's/motor
 homes.

 Please keep the cable loop in mind when you do bench tests of inverters,
 as it may screw up the results and make it seem like there is something
 wrong with the inverter.

 JARMO

 _

 * Jarmo Venalainen*  |  * Schneider Electric **  |  Xantrex Brand*  |
 *CANADA*  |   *Sales Application Engineer*
 * Phone:* +604-422-2528  |   *Tech Support:* 800-670-0707  |   *Mobile:*
 +604-505-0291
 * Email:* *jarmo.venalai...@schneider-electric.com*
 jarmo.venalai...@schneider-electric.com  |   *Site:** www.Xantrex.com*
 http://www.xantrex.com/  |   *Address:* 3700 Gilmore Way, Burnaby, BC
 V5G4M1
   mime-attachment.gif http://www.xantrexrebate.com/
 mime-attachment.gif http://www.xantrex.com/ mime-attachment.gif
 https://www.facebook.com/Xantrex mime-attachment.gif
 https://twitter.com/Xantrex mime-attachment.gif
 https://twitter.com/Xantrex


 *** Please consider the environment before printing this e-mail



   From: b...@midnitesolar.com b...@midnitesolar.com  To: RE-wrenches 
 re-wrenches@lists.re-wrenches.org,   Date: 06/28/2015 10:30 PM  Subject: Re:
 [RE-wrenches] Battery Bank to Inverter Wiring  Sent by: RE-wrenches 
 re-wrenches-boun...@lists.re-wrenches.org
 --




 On 6/28/2015 9:20 AM, Allan Sindelar wrote:
 I'm not an EE, but I can't see what difference twisting would make in
 the absence of a building/collapsing field as is normal with AC.

 It is little known that with the typical inverters that use the heavy
 power transformers,
 have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in
 with that DC battery current.

 The AC output current reflects back to the input as ripple current.  This
 is why you want to
 have at least short as possible Sbattery cable runs AND keep the wires as
 close together as possible.

 Twisting the battery cables may help a bit but that is probably overkill.

 The problem has to do with inductance in the battery cables.  You can use
 as big of cable
 as you can fit in to reduce resistance, but that will not help to lower
 the inductance.
 The problems you can sometimes have with high inductance is that L-C
 resonance at the
 inverter can raise the peak voltages seen at the inverter input terminals
 and can be hard on
 the inverter.

 Then again,  the high frequency, lighter weight inverters will typically
 keep most of that ripple
 inside,  between the DC input and AC output and battery cable inductance
 will not be as much
 of a problem on the battery cables.

 boB Gudgel




 On 6/28/2015 9:20 AM, Allan Sindelar wrote:
 As a matter of course I have always run the positive and negative
 conductors of high-current cable pairs together, but have never

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-29 Thread jerrysgarage01
Wrenches
We always try to minimize in connection cables as well as home run cables to 
the shorted length possible, restating batteries to aid this should always be 
considered as well as positive and negative runs
Jerry


Sent via the Samsung Galaxy S™ III, an ATT 4G LTE smartphone

div Original message /divdivFrom: Ray Walters 
r...@solarray.com /divdivDate:06/29/2015  12:05 PM  (GMT-10:00) 
/divdivTo: RE-wrenches re-wrenches@lists.re-wrenches.org 
/divdivSubject: Re: [RE-wrenches] Battery Bank to Inverter Wiring 
/divdiv
/divThis is fascinating because while I knew the DC cables had an AC  
component, I never realized how much inductance played in the volt drop to the 
inverter.  Thanks for bringing this to our attention Jarmo.  
Which brings up another question based on Benn's question:  isn't the battery 
itself part of the inductive loop?  and would the lead inside and steel cases 
act to increase the inductance?  Should we consider changing battery layouts 
not just to shorten cable lengths, but to counter inductance in the batteries 
themselves?  If needed, we could actually wire the batteries to twist by 
putting every other 2 v cell in the opposite row.  
My guess is that it wouldn't be worth it, but I've been wrong many times...

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 6/29/2015 3:55 PM, Benn Kilburn wrote:
What about when you have the (+) and (-) terminals at opposite ends of a larger 
battery bank?  Sure you can run the conductors side-by-side once they meet up 
on their way to the inverter, but would you consider the distance between the 
end terminals a large loop? 
Ideally the battery string is laid out so the end terminals are close together 
and close to the inverter, but this isn't always the case. 

Benn Kilburn
SkyFire Energy Inc. 
780-906-7807


On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com wrote:

Hi: 

From the comments so far, it appears that within the wrenches 
group, good practices are the rule and DC cables are kept side by side, so the 
problem I mentioned hasn't come up much. 

I have seen large loop battery cables a couple of times in solar installs 
myself out on islands way down south.  Also on boats/RV's/motor homes. 

Please keep the cable loop in mind when you do bench tests of inverters, as it 
may screw up the results and make it seem like there is something wrong with 
the inverter.   

JARMO
_
 

Jarmo Venalainen  |   Schneider Electric |  Xantrex 
  Brand  |   CANADA  |   Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com  |   
Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
mime-attachment.gif
mime-attachment.gif   mime-attachment.gif   
mime-attachment.gif   mime-attachment.gif


*** Please consider the environment before printing this e-mail



From:   b...@midnitesolar.com b...@midnitesolar.com 

To: RE-wrenches re-wrenches@lists.re-wrenches.org,
Date:   06/28/2015 10:30 PM
Subject:Re: [RE-wrenches] Battery Bank to Inverter 
Wiring
Sent by:RE-wrenches 
re-wrenches-boun...@lists.re-wrenches.org




On 6/28/2015 9:20 AM, Allan Sindelar wrote:
I'm not an EE, but I can't see what difference twisting would make in
the absence of a building/collapsing field as is normal with AC.

It is little known that with the typical inverters that use the heavy power 
transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in with 
that DC battery current.

The AC output current reflects back to the input as ripple current.  This is 
why you want to
have at least short as possible Sbattery cable runs AND keep the wires as close 
together as possible.

Twisting the battery cables may help a bit but that is probably overkill.

The problem has to do with inductance in the battery cables. You can use as big 
of cable
as you can fit in to reduce resistance, but that will not help to 
lower the inductance.
The problems you can sometimes have with high inductance is that 
L-C resonance at the
inverter can raise the peak voltages seen at the inverter input terminals and 
can be hard on
the inverter.

Then again,  the high frequency, lighter weight inverters will typically keep 
most of that ripple
inside,  between the DC input and AC output and battery cable inductance will 
not be as much
of a problem on the battery cables.

boB Gudgel




On 6/28/2015 9:20 AM, Allan Sindelar wrote: 
As a matter of course I have always run the positive and negative 
conductors of high-current cable

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-29 Thread Jarmo . Venalainen
Hi:

It's not possible to have no loop area at all, but cables should be run in 
ways to minimize the loop area.

If you run the + or - along the side of the batteries for example, then 
that has the effect of minimizing the total loop.

JARMO
_
 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  | 
  Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 








*** Please consider the environment before printing this e-mail




From:
Benn Kilburn b...@skyfireenergy.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date:
06/29/2015 02:55 PM
Subject:
Re: [RE-wrenches] Battery Bank to Inverter Wiring
Sent by:
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org



What about when you have the (+) and (-) terminals at opposite ends of a 
larger battery bank?  Sure you can run the conductors side-by-side once 
they meet up on their way to the inverter, but would you consider the 
distance between the end terminals a large loop? 
Ideally the battery string is laid out so the end terminals are close 
together and close to the inverter, but this isn't always the case. 

Benn Kilburn
SkyFire Energy Inc. 
780-906-7807


On Jun 29, 2015, at 10:28 AM, jarmo.venalai...@schneider-electric.com 
wrote:

Hi: 

From the comments so far, it appears that within the wrenches group, good 
practices are the rule and DC cables are kept side by side, so the problem 
I mentioned hasn't come up much. 

I have seen large loop battery cables a couple of times in solar 
installs myself out on islands way down south.  Also on boats/RV's/motor 
homes. 

Please keep the cable loop in mind when you do bench tests of inverters, 
as it may screw up the results and make it seem like there is something 
wrong with the inverter. 

JARMO
_
 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  | 
  Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 
mime-attachment.gif 
mime-attachment.gif 
mime-attachment.gif 
mime-attachment.gif 
mime-attachment.gif



*** Please consider the environment before printing this e-mail



From: 
b...@midnitesolar.com b...@midnitesolar.com 
To: 
RE-wrenches re-wrenches@lists.re-wrenches.org, 
Date: 
06/28/2015 10:30 PM 
Subject: 
Re: [RE-wrenches] Battery Bank to Inverter Wiring 
Sent by: 
RE-wrenches re-wrenches-boun...@lists.re-wrenches.org





On 6/28/2015 9:20 AM, Allan Sindelar wrote:
I'm not an EE, but I can't see what difference twisting would make in
the absence of a building/collapsing field as is normal with AC.

It is little known that with the typical inverters that use the heavy 
power transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in 
with that DC battery current.

The AC output current reflects back to the input as ripple current.  This 
is why you want to
have at least short as possible Sbattery cable runs AND keep the wires as 
close together as possible.

Twisting the battery cables may help a bit but that is probably overkill.

The problem has to do with inductance in the battery cables.  You can use 
as big of cable
as you can fit in to reduce resistance, but that will not help to lower 
the inductance.
The problems you can sometimes have with high inductance is that L-C 
resonance at the
inverter can raise the peak voltages seen at the inverter input terminals 
and can be hard on
the inverter.

Then again,  the high frequency, lighter weight inverters will typically 
keep most of that ripple
inside,  between the DC input and AC output and battery cable inductance 
will not be as much
of a problem on the battery cables.

boB Gudgel




On 6/28/2015 9:20 AM, Allan Sindelar wrote: 
As a matter of course I have always run the positive and negative 
conductors of high-current cable pairs together, but have never 
deliberately twisted them, and have never known of any related problems. 
The most obvious example of this would be 4/0 battery/inverter cables in a 
24V system, with a 250A GJ-class breaker or (prior to that) a 300A or 400A 
Class T fuse. It's pretty tough to thread a twisted pair of 4/0 
USE/RHH/RHW cables through a 2 elbow or LB from inverter enclosure to 
battery enclosure.
I'm not an EE, but I can't see what difference twisting would make in the 
absence of a building/collapsing field as is normal with AC. 
I have twisted AC conductors together in the past when clients have 
expressed concerns about EMF from their equipment and wiring, but only AC.
Allan
Allan Sindelar
al

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-28 Thread Allan Sindelar

  
  
As a matter of course I have always run the positive and negative
conductors of high-current cable pairs together, but have never
deliberately twisted them, and have never known of any related
problems. 
The most obvious example of this would be 4/0 battery/inverter
cables in a 24V system, with a 250A GJ-class breaker or (prior to
that) a 300A or 400A Class T fuse. It's pretty tough to thread a
twisted pair of 4/0 USE/RHH/RHW cables through a 2" elbow or LB from
inverter enclosure to battery enclosure.
I'm not an EE, but I can't see what difference twisting would make
in the absence of a building/collapsing field as is normal with AC.

I have twisted AC conductors together in the past when clients have
expressed concerns about EMF from their equipment and wiring, but
only AC.
Allan


  
  
  
  
  
  
  
  
  
  
  
Allan Sindelar
  al...@sindelarsolar.com
  NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive
  Energy,
  Inc.
505 780-2738 cell


 
  

On 6/27/2015 2:40 AM, John wrote:


  
  
  
  
  
That
is why for years we have been twisting those leads around
each other.  I was told it was to cancel out the opposing
fields on the wires, but for whatever the correct technical
reason is,  we have always twisted those heavy
wires. John V.
 
From: RE-wrenches
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On
  Behalf Of jarmo.venalai...@schneider-electric.com
Sent: Saturday, 27 June 2015 5:45 a.m.
To: RE-wrenches
Subject: [RE-wrenches] Battery Bank to Inverter
    Wiring
 
Hi:
  
  
  From
time to time over the years I've come across systems where
the routing of DC cables between the batteries and the
inverter has been the cause of  issues. 
  
  I'm
not referring to wire thickness or quality of terminations.
 For the purposes of this discussion, just assume that wire
thickness and terminations are perfect. 
  
  What
I am referring to is the routing of the positive and
negative battery cables.  In particular, the loop area
within the + and - cables as shown in the image below,
  
  
  
  The
problem I've seen in systems with a large loop in the setup
is that the inverter does not provide good surge power and
can even go into low voltage shutdown during large surges.
  
  
  Recently
this happened again and I wanted to get a better feel for
it, so I did some math.   
  
  For
a cable length of about 12', the loop is an inductor which
has a value of inductance of about 1 uH for side by side
cables and as much as 6 uH for cables about 1 foot apart.  
  
  
  This
inductance is greatly multiplied by any ferrous metal in the
loop and can easily be in the range of 10's to 100's of uH.
 Examples being cables which run in steel conduits or along
the steel frame of a motor home. 
  
  Inductance
causes a voltage drop proportional to the rate at which the
current is changing.  To get an idea of how large that rate
can be for typical inverters, I did surge tests with a 5kW
inverter and found that the rate of change of current can be
as high as 100A per milli-second or 100,000 Amps/second.
  
  
  Given
that, the voltage drop of the wire inductance is then ,
Vdrop = (rate of change of current) x (inductance), 
  
  Vdrop
for 1 uH = (100,000 A/s) x (0.01 H) = 0.1V 
  Vdrop
for 10 uH = (100,000 A/s) x (0.01 H) = 1.0V 
  Vdrop
for 100 uH = (100,000 A/s) x (0.01 H) = 10.0V    clearly
this is a problem. 
  
  Have
any of the wrenches had systems with this issue?  If so, how
often. 
  
  
  JARMO
  
  
  
   
  _
  
  
  Jarmo Venalainen
 |   Schneider Electric  
  |  Xantrex Brand  |   C

Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-28 Thread b...@midnitesolar.com


On 6/28/2015 9:20 AM, Allan Sindelar wrote:
I'm not an EE, but I can't see what difference twisting would make in
the absence of a building/collapsing field as is normal with AC.

It is little known that with the typical inverters that use the heavy 
power transformers,
have a lot of AC 120 Hz (or 100 Hz for 50 Hz systems) current mixed in 
with that DC battery current.


The AC output current reflects back to the input as ripple current.  
This is why you want to
have at least short as possible Sbattery cable runs AND keep the wires 
as close together as possible.


Twisting the battery cables may help a bit but that is probably overkill.

The problem has to do with inductance in the battery cables.  You can 
use as big of cable
as you can fit in to reduce resistance, but that will not help to lower 
the inductance.
The problems you can sometimes have with high inductance is that L-C 
resonance at the
inverter can raise the peak voltages seen at the inverter input 
terminals and can be hard on

the inverter.

Then again,  the high frequency, lighter weight inverters will typically 
keep most of that ripple
inside,  between the DC input and AC output and battery cable inductance 
will not be as much

of a problem on the battery cables.

boB Gudgel




On 6/28/2015 9:20 AM, Allan Sindelar wrote:
As a matter of course I have always run the positive and negative 
conductors of high-current cable pairs together, but have never 
deliberately twisted them, and have never known of any related problems.
The most obvious example of this would be 4/0 battery/inverter cables 
in a 24V system, with a 250A GJ-class breaker or (prior to that) a 
300A or 400A Class T fuse. It's pretty tough to thread a twisted pair 
of 4/0 USE/RHH/RHW cables through a 2 elbow or LB from inverter 
enclosure to battery enclosure.
I'm not an EE, but I can't see what difference twisting would make in 
the absence of a building/collapsing field as is normal with AC.
I have twisted AC conductors together in the past when clients have 
expressed concerns about EMF from their equipment and wiring, but only AC.

Allan

*Allan Sindelar*
al...@sindelarsolar.com mailto:al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

**

On 6/27/2015 2:40 AM, John wrote:


That is why for years we have been twisting those leads around each 
other.  I was told it was to cancel out the opposing fields on the 
wires, but for whatever the correct technical reason is,  we have 
always twisted those heavy wires. John V.


*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] 
*On Behalf Of *jarmo.venalai...@schneider-electric.com

*Sent:* Saturday, 27 June 2015 5:45 a.m.
*To:* RE-wrenches
*Subject:* [RE-wrenches] Battery Bank to Inverter Wiring

Hi:

From time to time over the years I've come across systems where the 
routing of DC cables between the batteries and the inverter has been 
the cause of  issues.


I'm not referring to wire thickness or quality of terminations.  For 
the purposes of this discussion, just assume that wire thickness and 
terminations are perfect.


What I am referring to is the routing of the positive and negative 
battery cables.  In particular, the loop area within the + and - 
cables as shown in the image below,


The problem I've seen in systems with a large loop in the setup is 
that the inverter does not provide good surge power and can even go 
into low voltage shutdown during large surges.


Recently this happened again and I wanted to get a better feel for 
it, so I did some math.


For a cable length of about 12', the loop is an inductor which has a 
value of inductance of about 1 uH for side by side cables and as much 
as 6 uH for cables about 1 foot apart.


This inductance is greatly multiplied by any ferrous metal in the 
loop and can easily be in the range of 10's to 100's of uH.  Examples 
being cables which run in steel conduits or along the steel frame of 
a motor home.


Inductance causes a voltage drop proportional to the rate at which 
the current is changing.  To get an idea of how large that rate can 
be for typical inverters, I did surge tests with a 5kW inverter and 
found that the rate of change of current can be as high as 100A per 
milli-second or 100,000 Amps/second.


Given that, the voltage drop of the wire inductance is then , Vdrop = 
(rate of change of current) x (inductance),


Vdrop for 1 uH = (100,000 A/s) x (0.01 H) = 0.1V
Vdrop for 10 uH = (100,000 A/s) x (0.01 H) = 1.0V
Vdrop for 100 uH = (100,000 A/s) x (0.01 H) = 10.0V  clearly this 
is a problem.


Have any of the wrenches had systems with this issue?  If so, how often.


JARMO




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address

[RE-wrenches] Battery Bank to Inverter Wiring

2015-06-27 Thread Jarmo . Venalainen
Hi:

From time to time over the years I've come across systems where the 
routing of DC cables between the batteries and the inverter has been the 
cause of  issues.

I'm not referring to wire thickness or quality of terminations.  For the 
purposes of this discussion, just assume that wire thickness and 
terminations are perfect.

What I am referring to is the routing of the positive and negative battery 
cables.  In particular, the loop area within the + and - cables as shown 
in the image below,


The problem I've seen in systems with a large loop in the setup is that 
the inverter does not provide good surge power and can even go into low 
voltage shutdown during large surges.

Recently this happened again and I wanted to get a better feel for it, so 
I did some math. 

For a cable length of about 12', the loop is an inductor which has a value 
of inductance of about 1 uH for side by side cables and as much as 6 uH 
for cables about 1 foot apart. 

This inductance is greatly multiplied by any ferrous metal in the loop and 
can easily be in the range of 10's to 100's of uH.  Examples being cables 
which run in steel conduits or along the steel frame of a motor home.

Inductance causes a voltage drop proportional to the rate at which the 
current is changing.  To get an idea of how large that rate can be for 
typical inverters, I did surge tests with a 5kW inverter and found that 
the rate of change of current can be as high as 100A per milli-second or 
100,000 Amps/second.

Given that, the voltage drop of the wire inductance is then , Vdrop = 
(rate of change of current) x (inductance), 

Vdrop for 1 uH = (100,000 A/s) x (0.01 H) = 0.1V
Vdrop for 10 uH = (100,000 A/s) x (0.01 H) = 1.0V
Vdrop for 100 uH = (100,000 A/s) x (0.01 H) = 10.0Vclearly this is 
a problem.

Have any of the wrenches had systems with this issue?  If so, how often.


JARMO


 
_
 


Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  | 
  Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: 
+604-505-0291 
Email: jarmo.venalai...@schneider-electric.com  |   Site: www.Xantrex.com 
|   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 








*** Please consider the environment before printing this e-mail
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-27 Thread John
That is why for years we have been twisting those leads around each other.
I was told it was to cancel out the opposing fields on the wires, but for
whatever the correct technical reason is,  we have always twisted those
heavy wires. John V.

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of jarmo.venalai...@schneider-electric.com
Sent: Saturday, 27 June 2015 5:45 a.m.
To: RE-wrenches
Subject: [RE-wrenches] Battery Bank to Inverter Wiring

 

Hi: 

From time to time over the years I've come across systems where the routing
of DC cables between the batteries and the inverter has been the cause of
issues. 

I'm not referring to wire thickness or quality of terminations.  For the
purposes of this discussion, just assume that wire thickness and
terminations are perfect. 

What I am referring to is the routing of the positive and negative battery
cables.  In particular, the loop area within the + and - cables as shown in
the image below, 


The problem I've seen in systems with a large loop in the setup is that the
inverter does not provide good surge power and can even go into low voltage
shutdown during large surges. 

Recently this happened again and I wanted to get a better feel for it, so I
did some math.   

For a cable length of about 12', the loop is an inductor which has a value
of inductance of about 1 uH for side by side cables and as much as 6 uH for
cables about 1 foot apart.   

This inductance is greatly multiplied by any ferrous metal in the loop and
can easily be in the range of 10's to 100's of uH.  Examples being cables
which run in steel conduits or along the steel frame of a motor home. 

Inductance causes a voltage drop proportional to the rate at which the
current is changing.  To get an idea of how large that rate can be for
typical inverters, I did surge tests with a 5kW inverter and found that the
rate of change of current can be as high as 100A per milli-second or 100,000
Amps/second. 

Given that, the voltage drop of the wire inductance is then , Vdrop = (rate
of change of current) x (inductance), 

Vdrop for 1 uH = (100,000 A/s) x (0.01 H) = 0.1V 
Vdrop for 10 uH = (100,000 A/s) x (0.01 H) = 1.0V 
Vdrop for 100 uH = (100,000 A/s) x (0.01 H) = 10.0Vclearly this is a
problem. 

Have any of the wrenches had systems with this issue?  If so, how often. 


JARMO 


 

_ 

Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |
Sales Application Engineer 
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile:
+604-505-0291 
Email:  mailto:jarmo.venalai...@schneider-electric.com
jarmo.venalai...@schneider-electric.com  |   Site: http://www.xantrex.com/
www.Xantrex.com  |   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1 


 http://www.xantrexrebate.com/ 


 http://www.xantrex.com/ 

 https://www.facebook.com/Xantrex 

 https://twitter.com/Xantrex 

 https://twitter.com/Xantrex 




*** Please consider the environment before printing this e-mail

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Bank to Inverter Wiring

2015-06-27 Thread Jerry Shafer
Wrenches
Going back many many years, twisting the pairs together was the preferred
way to run the cables between the inverter and batteries, this seamed to
reduce noise, I have personally seen improvement of audio conditions. Doing
this on the AC side does the opposite and creates noise on sound mixers and
powered amps.
Jerry

On Fri, Jun 26, 2015 at 7:45 AM, jarmo.venalai...@schneider-electric.com
wrote:

 Hi:

 From time to time over the years I've come across systems where the
 routing of DC cables between the batteries and the inverter has been the
 cause of  issues.

 I'm not referring to wire thickness or quality of terminations.  For the
 purposes of this discussion, just assume that wire thickness and
 terminations are perfect.

 What I am referring to is the routing of the positive and negative battery
 cables.  In particular, the loop area within the + and - cables as shown in
 the image below,


 The problem I've seen in systems with a large loop in the setup is that
 the inverter does not provide good surge power and can even go into low
 voltage shutdown during large surges.

 Recently this happened again and I wanted to get a better feel for it, so
 I did some math.

 For a cable length of about 12', the loop is an inductor which has a value
 of inductance of about 1 uH for side by side cables and as much as 6 uH for
 cables about 1 foot apart.

 This inductance is greatly multiplied by any ferrous metal in the loop and
 can easily be in the range of 10's to 100's of uH.  Examples being cables
 which run in steel conduits or along the steel frame of a motor home.

 Inductance causes a voltage drop proportional to the rate at which the
 current is changing.  To get an idea of how large that rate can be for
 typical inverters, I did surge tests with a 5kW inverter and found that the
 rate of change of current can be as high as 100A per milli-second or
 100,000 Amps/second.

 Given that, the voltage drop of the wire inductance is then , Vdrop =
 (rate of change of current) x (inductance),

 Vdrop for 1 uH = (100,000 A/s) x (0.01 H) = 0.1V
 Vdrop for 10 uH = (100,000 A/s) x (0.01 H) = 1.0V
 Vdrop for 100 uH = (100,000 A/s) x (0.01 H) = 10.0Vclearly this is
 a problem.

 Have any of the wrenches had systems with this issue?  If so, how often.


 JARMO




 _

 * Jarmo Venalainen*  |  * Schneider Electric **  |  Xantrex Brand*  |
 *CANADA*  |   *Sales Application Engineer*
 * Phone:* +604-422-2528  |   *Tech Support:* 800-670-0707  |   *Mobile:*
 +604-505-0291
 * Email:* *jarmo.venalai...@schneider-electric.com*
 jarmo.venalai...@schneider-electric.com  |   *Site:** www.Xantrex.com*
 http://www.xantrex.com/  |   *Address:* 3700 Gilmore Way, Burnaby, BC
 V5G4M1
   http://www.xantrexrebate.com/  http://www.xantrex.com/
 https://www.facebook.com/Xantrex https://twitter.com/Xantrex
 https://twitter.com/Xantrex


 *** Please consider the environment before printing this e-mail

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org