Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-20 Thread Nick Soleil
 Robb Cary was dealing with a lot of large scale telecomm systems with CD 
Technologies, so his scary photos were probably not from solar projects, (if 
that is any comfort!)  He spoke of some projects with 50,000 2V industrial 
cells.  I have worked with him for a long time and served on the board of Solar 
Sebastopol with him 5-6 years ago.  I too have lost touch.  I tried to reach 
him 
four or five years ago but his office said that he was retired and his cell 
number was disconnected.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Darryl Thayer daryl_so...@yahoo.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wed, December 15, 2010 9:14:15 AM
Subject: Re: [RE-wrenches] Battery based hydrogen incidents


Yes they happen, Robb Cary of Battery Testing Co. has some frightening photos.  
I have lost contact with him however.  I have had an experiance, but I did not 
take pictures.  When you find the top of the battery and or battery enclousure 
blowen to smitherens it was a hydrogen explosion.  Sorry I am on road today, 
would love to comment more.  maybe later
Darryl

--- On Wed, 12/15/10, Warren Lauzon war...@wind-sun.com wrote:


From: Warren Lauzon war...@wind-sun.com
Subject: Re: [RE-wrenches] Battery based hydrogen incidents
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, December 15, 2010, 11:05 AM


 
In the 30+ years that we have been in the solar business, we have never seen 
or 
even heard of a single one.
  
From: Dana 
Sent: Wednesday, December 15, 2010 9:10 AM
To: 'RE-wrenches' 
Subject: [RE-wrenches] Battery based hydrogen incidents
  Ken – 
  
To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the 
fan 
into a 4” header with a matching 2.5” inlet as far away on the lowest portion 
of 
the battery box.
 
 
In 22+ years in off grid installations I have yet to see or even hear of one 
hydrogen explosion. I get repeatedly asked why we have to go to the efforts we 
go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of. 

  
Q - How many battery based hydrogen incidents have happened in our collective 
experience? 

  
  
  
Dana Orzel
Great Solar Works, Inc 
E - d...@solarwork.com 
V - 970.626.5253 
F - 970.626.4140 
C - 970.209.4076 
web - www.solarwork.com 
  
Responsible Technologies for Responsible People since 1988 
Do not ever belive anything, but seriously trust through action. 
  
From:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Tuesday, December 14, 2010 12:07 PM
To: Wrenches
Subject: [RE-wrenches] Battery Venting
  
Fellow Wrenches,

The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 
volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt 
Zephyr vent is good for about 5 CFM!   If you think you are venting enough, 
take 
some time and study this issue.

Kent Osterberg
Blue Mountain Solar 


 ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Northern Arizona Wind  Sun - Electricity from the sun since 1979

Online Solar Store
Free Solar Discussion Forum

-Inline Attachment Follows-


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 



  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org

Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-18 Thread Jeff Yago
30+ years experience in solar off-grid  battery backup systems, and 10 years before that designing and building heavy industrial battery-powered vehicles thatwere powered bytons of L-16 traction batteries. Here has been my experience:

1. Large industrial vehicle in corner of shop on charger, 30 feet away across shop a worker was grinding a weld and spark flew across shop and two L-16 batteries in bank exploded. Loudest sound I ever heard, but no fire. Lots of acid covered plastic chunks all over the place. Only tops of battery cells blew off, so no loss of acid.

2. A standard 12 volt RV/marine battery in small utility tool trailer which was kept charged by a 40 watt solar moduleblew off and caused acid damage to all wood walls and floor within 3 feet.After checking I found the battery was completely dry and all liquid electrolyte was gone. I think the lower cost charge controller went wako and kept on chargingfor days until all of the liquid had boiled off, then perhaps several of the cell plates warped from the heat and finally touched together causing a short and igniting the gasses building up inside the battery.


3. Two L-16 batteries sitting on shop floor and wired in series so I could re-charge with automotive shop type portable 12 volt charger. Charger had finished charging and shut off by timer switch. Although I knew better, instead of first un-plugging charger I "assumed" the alligator clips would no longer energized since the charger had timed off - wrong! When removing one of the clips there was a small spark and you could actually see the flame shoot out of the battery caps. Again, acid covered plastic pieces of the battery top all over and the loudest sound I ever heard but no fire.

4. I remember about 10 years ago seeing an article about a major battery room explosion. Best I can remember the entire metal building blew up and photos looked like a bomb hit the building. Article indicated the building was full of large industrial batteries that were poorly maintained and over-charged, and they thought the room had totally filled with hydrogen gas.


Conclusions - 

The most likely place for an explosive level of hydrogen is INSIDE the batteries, not inside a well vented room or battery box, especially just after charging. However, wequit building battery boxes years agobecause the confinedbattery boxeswere always causing extensive battery terminal corrosion due to the higher concentrations of hydrogen and acid "mist" that settles all over the tops of the batteries in the confined space after repeated charging. Afterswitching to vented battery rooms we have had no other problems with corrosion and the batteries and terminals stay clean.

Stay safe, and remember, if you "taste" something salty in the air whilestanding around in a battery room - get out!

Jeff Yago

Netscape. Just the Net You Need.
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-17 Thread Joel Davidson
Here's a true story about another foolish but lucky guy. My Arkansas Ozark 
Mountain neighbor had a big 115 VDC windcharger and a battery bank of large 
2-volt cells inside a shed at the base of his 85 feet tower. One day he opened 
the door with a smoke in his mouth. The H2 (not the batteries) exploded, 
rocketing him out the door, and knocking him on his ass. He was a big, strong 
guy and didn't get hurt, but he swore he would never smoke around batteries 
again. (Preventive action - ventilate battery room before entering.)

  - Original Message - 
  From: Luke Christy 
  To: re-wrenches@lists.re-wrenches.org 
  Sent: Thursday, December 16, 2010 7:52 AM
  Subject: Re: [RE-wrenches] Battery based hydrogen incidents




  These descriptions of battery explosions certainly drive home the point that 
one should always always wear protective gear when working on batteries.


  I have  a story that may take the prize for the most foolish behavior yet 
described (thankfully I wasn't involved until the cleanup stage).
  In 2008 a neighbor of mine was filling a bank of 12 L-16s installed in a 
remote home here in So. Colorado. Apparently it didn't occur to him that it 
probably wasn't a good idea to smoke while adding water to gassing batteries. 
Two or three batteries into the job, sure enough, a spark fell off his lit 
cigarette, probably landed in or near the open cap of the cell he was filling, 
and the resulting explosion blew the top off of the L-16, also spraying 
electrolyte everywhere in the battery room. My neighbor (who shall remain 
nameless) was not wearing protective gear of any kind, and of course he had 
acid in his eyes and all over his face. He was alone at this house, 40+ miles 
from the nearest town, and close to ten miles from the closest neighbor. He 
managed to wash his eyes and face in a creek, and was somehow able to drive the 
ten miles to the neighbor's house, who then took him to a hospital. Amazingly, 
he came out of it without permanent eye damage or scarring, but that must be 
due to having had more than his share of luck that day.


  I had the job of cleaning up the mess and replacing the blown-up battery. One 
thing that stood out was the fact that the top of the battery disintegrated 
into dozens of very sharp shards of plastic. These were obviously thrown out 
with the explosion and could have easily caused serious injury themselves. The 
entire wall of the battery room was covered with tiny bits of plastic, plate 
particles, and electrolyte, almost making a cartoon-like outline of my 
neighbor, as he had been standing in front of the wall when the battery blew.


  Always wear your eye protection. (and it seems that smoking plus hydrogen 
equals bad things).




Luke Christy 

 NABCEP Certified PV Installer™: Certification #031409-25 (Luke Christy)
 CoSEIA Certified PV Installer (Luke Christy)

Solar Gain Services, LLC
Monte Vista, CO.
sgsrenewab...@gmail.com










--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread jay peltz
Hi Dana,

I've been 16 years all offgrid, no reports that I know of.

jay

peltz power
On Dec 15, 2010, at 8:10 AM, Dana wrote:

 Ken –
  
 To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the 
 fan into a 4” header with a matching 2.5” inlet as far away on the lowest 
 portion of the battery box.
  
  
 In 22+ years in off grid installations I have yet to see or even hear of one 
 hydrogen explosion. I get repeatedly asked why we have to go to the efforts 
 we go to for box and venting. I am not able to provide even one incident that 
 I have heard rumor of.
  
 Q - How many battery based hydrogen incidents have happened in our collective 
 experience?
  
  
  
 Dana Orzel
 Great Solar Works, Inc
 E - d...@solarwork.com
 V - 970.626.5253
 F - 970.626.4140
 C - 970.209.4076
 web - www.solarwork.com
  
 Responsible Technologies for Responsible People since 1988
 Do not ever belive anything, but seriously trust through action.
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
 Sent: Tuesday, December 14, 2010 12:07 PM
 To: Wrenches
 Subject: [RE-wrenches] Battery Venting
  
 Fellow Wrenches,
 
 The discussion about battery venting reminds me of a useful and inexpensive 
 program, BattMV, for determining ventilation requirements per EN-50272.  
 EN-50272 is a European standard used to determine how much air flow is needed 
 for a room, I don't know of a equivalent standard used in the U.S.  It takes 
 a surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
 57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
 12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting 
 enough, take some time and study this issue.
 
 Kent Osterberg
 Blue Mountain Solar
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread Jonathan Hill
Me neither, in 30 years!
Jonathan Hill, solar applications engineerSierra Solar Systems563C Idaho Maryland RoadGrass Valley, CA 95945Celebrating our 30th year in solar!tech info and foreign orders:(530) 273-6754order line: (888) ON-SOLAR (US only)FAX:(530) 273-1760e-mail:mailto:solar...@sierrasolar.comworld wide web:http://www.sierrasolar.com
On Dec 15, 2010, at 8:58 AM, jay peltz wrote:Hi Dana,I've been 16 years all offgrid, no reports that I know of.jaypeltz powerOn Dec 15, 2010, at 8:10 AM, Dana wrote:Ken –To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan into a 4” header with a matching 2.5” inlet as far away on the lowest portion of the battery box.In 22+ years in off grid installations I have yet to see or even hear of one hydrogen explosion. I get repeatedly asked why we have to go to the efforts we go to for box and venting. I am not able to provide even one incident that I have heard rumor of.Q - How many battery based hydrogen incidents have happened in our collective experience?Dana OrzelGreat Solar Works, IncE -d...@solarwork.comV - 970.626.5253F - 970.626.4140C - 970.209.4076web -www.solarwork.com"Responsible Technologies for Responsible People since 1988"Do not ever belive anything, but seriously trust through action.From:re-wrenches-boun...@lists.re-wrenches.org[mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf OfKent OsterbergSent:Tuesday, December 14, 2010 12:07 PMTo:WrenchesSubject:[RE-wrenches] Battery VentingFellow Wrenches,The discussion about battery venting reminds me of a useful and inexpensive program,BattMV, for determining ventilation requirements per EN-50272. EN-50272 is a European standard used to determine how much air flow is needed for a room, I don't know of a equivalent standard used in the U.S. It takes a surprising amount of ventilation. For a 400-AH 48-volt L16 bank charged at 57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%. A 12-volt Zephyr vent is good for about 5 CFM! If you think you are venting enough, take some time and study this issue.Kent OsterbergBlue Mountain Solar___List sponsored by Home Power magazineList Address:RE-wrenches@lists.re-wrenches.orgOptions  settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions  settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules  etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread Warren Lauzon
In the 30+ years that we have been in the solar business, we have never seen or 
even heard of a single one.


From: Dana 
Sent: Wednesday, December 15, 2010 9:10 AM
To: 'RE-wrenches' 
Subject: [RE-wrenches] Battery based hydrogen incidents

Ken – 

 

To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan 
into a 4” header with a matching 2.5” inlet as far away on the lowest portion 
of the battery box.

 

 

In 22+ years in off grid installations I have yet to see or even hear of one 
hydrogen explosion. I get repeatedly asked why we have to go to the efforts we 
go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of.

 

Q - How many battery based hydrogen incidents have happened in our collective 
experience?

 

 

 

Dana Orzel

Great Solar Works, Inc

E - d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

Responsible Technologies for Responsible People since 1988

Do not ever belive anything, but seriously trust through action.

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Tuesday, December 14, 2010 12:07 PM
To: Wrenches
Subject: [RE-wrenches] Battery Venting

 

Fellow Wrenches,

The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting 
enough, take some time and study this issue.

Kent Osterberg
Blue Mountain Solar




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Northern Arizona Wind  Sun - Electricity from the sun since 1979

Online Solar Store
Free Solar Discussion Forum

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread Darryl Thayer
Yes they happen, Robb Cary of Battery Testing Co. has some frightening photos.  
I have lost contact with him however.  I have had an experiance, but I did not 
take pictures.  When you find the top of the battery and or battery enclousure 
blowen to smitherens it was a hydrogen explosion.  Sorry I am on road today, 
would love to comment more.  maybe later
Darryl

--- On Wed, 12/15/10, Warren Lauzon war...@wind-sun.com wrote:


From: Warren Lauzon war...@wind-sun.com
Subject: Re: [RE-wrenches] Battery based hydrogen incidents
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, December 15, 2010, 11:05 AM







In the 30+ years that we have been in the solar business, we have never seen or 
even heard of a single one.
 


 

From: Dana 
Sent: Wednesday, December 15, 2010 9:10 AM
To: 'RE-wrenches' 
Subject: [RE-wrenches] Battery based hydrogen incidents
 


Ken – 
 
To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan 
into a 4” header with a matching 2.5” inlet as far away on the lowest portion 
of the battery box.
 
 
In 22+ years in off grid installations I have yet to see or even hear of one 
hydrogen explosion. I get repeatedly asked why we have to go to the efforts we 
go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of.
 
Q - How many battery based hydrogen incidents have happened in our collective 
experience?
 
 
 

Dana Orzel
Great Solar Works, Inc
E - d...@solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
 
Responsible Technologies for Responsible People since 1988
Do not ever belive anything, but seriously trust through action.
 


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Tuesday, December 14, 2010 12:07 PM
To: Wrenches
Subject: [RE-wrenches] Battery Venting
 
Fellow Wrenches,

The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting 
enough, take some time and study this issue.

Kent Osterberg
Blue Mountain Solar


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Northern Arizona Wind  Sun - Electricity from the sun since 1979

Online Solar Store
Free Solar Discussion Forum

-Inline Attachment Follows-


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread Warren Lauzon
We have seen a few instances of the batteries themselves blowing, but not from 
hydrogen that we could tell. In one case a guy decided to fast charge his 
battery bank with a DC welding generator...

From: Allan Sindelar 
Sent: Wednesday, December 15, 2010 11:10 AM
To: re-wrenches@lists.re-wrenches.org 
Subject: Re: [RE-wrenches] Battery based hydrogen incidents

Knowledge of two incidents - sort of.
About ten years ago a Hydrocap on an L16 blew apart. Not our installation; I 
suspect that it became plugged up or overheated, as the array had been recently 
enlarged. Explosion was contained within the battery enclosure; just made a 
mess.

About four years ago a small 12V automotive battery used only to start a 6.5 
Onan generator blew up, causing modest permanent hearing damage to the 
homeowner. I wasn't there, and heard about it from her. This wasn't a venting 
issue, as the battery was on the floor in a ventilated room, but rather 
apparently a plugged cap in the battery itself. 

Otherwise, nothing.
Allan


Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com


On 12/15/2010 10:56 AM, Exeltech wrote: 
38+ years in RE.  Knowledge of one incident (an off-grid friend).

Very sunny day.  Very windy.  My friend had both PV and a wind 
generator (still does).  He had just stepped out of the room where the 
batteries were located when (as he described it) he heard something like a loud 
gunshot.  He went back inside to find one of the L16s exploded, top completely 
blown off, and case broken much of the way down one side.

Had the incident occurred only minutes earlier, injuries could have 
resulted.  He has since relocated his batteries to a dedicated (and vented) 
battery space.

Dan


--- On Wed, 12/15/10, Kent Osterberg mailto:k...@coveoregon.com wrote:


  From: Kent Osterberg mailto:k...@coveoregon.com
  Subject: Re: [RE-wrenches] Battery based hydrogen incidents
  To: RE-wrenches mailto:re-wrenches@lists.re-wrenches.org
  Date: Wednesday, December 15, 2010, 11:21 AM


  Sounds like, in general, that the off-grid industry has been 
fortunate to not have hydrogen explosions.  That's good.  No explosions here 
either.  But one shouldn't take that as evidence that it couldn't happen.  I 
don't believe this is a circumstance where it is better to be lucky than good.  
That's why I recommend doing the calculations.

  Kent Osterberg
  Blue Mountain Solar



  Dana wrote: 
Ken – 




To meet the flow have run 2 and 3 fans to meet the flow. 2” output 
from the fan into a 4” header with a matching 2.5” inlet as far away on the 
lowest portion of the battery box.





In 22+ years in off grid installations I have yet to see or even 
hear of one hydrogen explosion. I get repeatedly asked why we have to go to the 
efforts we go to for box and venting. I am not able to provide even one 
incident that I have heard rumor of.



Q - How many battery based hydrogen incidents have happened in our 
collective experience?






Dana Orzel

Great Solar Works, Inc

E - wlmailhtml:/mc/compose?to=d...@solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com



Responsible Technologies for Responsible People since 1988

Do not ever belive anything, but seriously trust through action.



From: 
wlmailhtml:/mc/compose?to=re-wrenches-boun...@lists.re-wrenches.org 
[wlmailhtml:/mc/compose?to=re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Kent Osterberg
Sent: Tuesday, December 14, 2010 12:07 PM
To: Wrenches
Subject: [RE-wrenches] Battery Venting



Fellow Wrenches,

The discussion about battery venting reminds me of a useful and 
inexpensive program, BattMV, for determining ventilation requirements per 
EN-50272.  EN-50272 is a European standard used to determine how much air flow 
is needed for a room, I don't know of a equivalent standard used in the U.S.  
It takes a surprising amount of ventilation.  For a 400-AH 48-volt L16 bank 
charged at 57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down 
to 4%.  A 12-volt Zephyr vent is good for about 5 CFM!   If you think you are 
venting enough, take some time and study this issue.

Kent Osterberg
Blue Mountain Solar

   



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re

Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread R Ray Walters
H2S is slightly heavier than air, but I vent with the inlets on line with the 
tops of the battery, and the outlet at the highest point.
If there is a lot of space around the bottom of the batteries, I might lower 
the inlets some, but not enough for the airflow to contribute to much cooling 
effect. (I'm in the Rockies)

All these stories make even more of a stickler about having my crews wear 
safety glasses.

R. Walters
r...@solarray.com
Solar Engineer




On Dec 15, 2010, at 12:08 PM, Jonathan Hill wrote:

 Ray-
 Is H2S lighter or heavier than air? Should it be vented from the top or 
 bottom of the enclosure? Thanks.
 
 Jonathan Hill, solar applications engineer
 Sierra Solar Systems
 563C Idaho Maryland Road
 Grass Valley, CA 95945
 Celebrating our 30th year in solar!
 tech info and foreign orders:  (530) 273-6754 
 order line: (888) ON-SOLAR (US only)   FAX:  (530) 273-1760
 e-mail:  mailto:solar...@sierrasolar.com
 world wide web:  http://www.sierrasolar.com
 att6eade.png
 
 On Dec 15, 2010, at 10:48 AM, R Ray Walters wrote:
 
 I really think the real venting issue is H2S (hydrogen sulfide) gas, which 
 is deadly at high enough concentrations, causes head aches at lower 
 concentrations, and is just awful to smell at any concentration.
 I think you would have to literally design a battery box to explode to ever 
 get to the 4% concentration necessary. It would consist of a large battery 
 bank, ridiculously oversized charge source, 
 the enclosure lid would be barely above the terminals, and the enclosure 
 would be a refrigerator, or ice chest with excellent seals and gaskets all 
 the way around.
 Hydrogen is tough to contain, it can permeate right through many plastics, 
 metals, sheetrock, etc.
 Again despite article 480, the issue of venting is the H2S danger, and 
 accelerated corrosion, not explosion.
 I too, have had a hydrogen explosion, ( and cool colorless fire after!) but 
 it wasn't due to the enclosure venting at all. (short circuited battery, 
 lead terminal melted through battery case, ignition of hydrogen inside of 
 battery, boom, then jet whistle sound of fire burning through the hole)
 Article 480.9A should be revised from explosive mixture to dangerous 
 mixture.  H2S above 10ppm?
 I copied some toxicity info if anyone wants to see. 
 
 R. Walters
 r...@solarray.com
 Solar Engineer
 
 Long-term, low-level exposure may result in fatigue, loss of appetite, 
 headaches, irritability, poor memory, and dizziness. Chronic exposure to low 
 level H2S (around 2 ppm) has been implicated in increased miscarriage and 
 reproductive health issues among Russian and Finnish wood pulp workers,[11] 
 but the reports have not (as of circa 1995) been replicated.
 
 0.00047 ppm is the recognition threshold, the concentration at which 50% of 
 humans can detect the characteristic odor of hydrogen sulfide,[12] normally 
 described as resembling a rotten egg.
 Less than 10 ppm has an exposure limit of 8 hours per day.
 10–20 ppm is the borderline concentration for eye irritation.
 50–100 ppm leads to eye damage.
 At 100–150 ppm the olfactory nerve is paralyzed after a few inhalations, and 
 the sense of smell disappears, often together with awareness of 
 danger.[13][14]
 320–530 ppm leads to pulmonary edema with the possibility of death.
 530–1000 ppm causes strong stimulation of the central nervous system and 
 rapid breathing, leading to loss of breathing.
 800 ppm is the lethal concentration for 50% of humans for 5 minutes exposure 
 (LC50).
 Concentrations over 1000 ppm cause immediate collapse with loss of 
 breathing, even after inhalation of a single breath.
 
 
 
 On Dec 15, 2010, at 10:21 AM, Kent Osterberg wrote:
 
 Sounds like, in general, that the off-grid industry has been fortunate to 
 not have hydrogen explosions.  That's good.  No explosions here either.  
 But one shouldn't take that as evidence that it couldn't happen.  I don't 
 believe this is a circumstance where it is better to be lucky than good.  
 That's why I recommend doing the calculations.
 
 Kent Osterberg
 Blue Mountain Solar
 
 
 
 Dana wrote:
 
 Ken –
  
 To meet the flow have run 2 and 3 fans to meet the flow. 2” output from 
 the fan into a 4” header with a matching 2.5” inlet as far away on the 
 lowest portion of the battery box.
  
  
 In 22+ years in off grid installations I have yet to see or even hear of 
 one hydrogen explosion. I get repeatedly asked why we have to go to the 
 efforts we go to for box and venting. I am not able to provide even one 
 incident that I have heard rumor of.
  
 Q - How many battery based hydrogen incidents have happened in our 
 collective experience?
  
  
  
 Dana Orzel
 Great Solar Works, Inc
 E - d...@solarwork.com
 V - 970.626.5253
 F - 970.626.4140
 C - 970.209.4076
 web - www.solarwork.com
  
 Responsible Technologies for Responsible People since 1988
 Do not ever belive anything, but seriously trust through action.
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 

Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-15 Thread Joel Davidson
I have sold thousands of off-grid PV systems and hundreds of on-grid PV systems 
with batteries. In 1984, one customer located 30 miles north of New Orleans 
with an off-grid PV system and T-105 batteries reported that a battery 
exploded. The cause was a clogged cell cap vent that trapped H2 that was 
ignited by transient current from a nearby lightning strike (that also 
destroyed his charge controller). About 6 months later another nearby lightning 
strike fried another controller. The PV array was a few hundred feet from the 
home. The owner wired the PV array and home equipment ground rods together and 
made sure that cap vent holes were kept clean. Subsequent lightning storms 
caused no problems.

The only exploded battery that I actually saw was also in the 1980s at a Sears 
service station. An automobile battery had exploded and tore a hole in the car 
engine hood.

Joel Davidson

- Original Message - 
  From: Dana 
  To: 'RE-wrenches' 
  Sent: Wednesday, December 15, 2010 8:10 AM
  Subject: [RE-wrenches] Battery based hydrogen incidents


  Ken - 

   

  To meet the flow have run 2 and 3 fans to meet the flow. 2 output from the 
fan into a 4 header with a matching 2.5 inlet as far away on the lowest 
portion of the battery box.

   

   

  In 22+ years in off grid installations I have yet to see or even hear of one 
hydrogen explosion. I get repeatedly asked why we have to go to the efforts we 
go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of.

   

  Q - How many battery based hydrogen incidents have happened in our collective 
experience?

   

   

   

  Dana Orzel

  Great Solar Works, Inc

  E - d...@solarwork.com

  V - 970.626.5253

  F - 970.626.4140

  C - 970.209.4076

  web - www.solarwork.com

   

  Responsible Technologies for Responsible People since 1988

  Do not ever belive anything, but seriously trust through action.

   

  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
  Sent: Tuesday, December 14, 2010 12:07 PM
  To: Wrenches
  Subject: [RE-wrenches] Battery Venting

   

  Fellow Wrenches,

  The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt Zephyr vent is good for about 5 CFM!   If you think you are venting 
enough, take some time and study this issue.

  Kent Osterberg
  Blue Mountain Solar



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org