Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-04-03 Thread Jason Szumlanski
I'm talking about systems that exceed 52 IQ7+ microinverters. These systems
require an alternative AC load center. I have actually used the IQ combiner
to just house the Envoy in the past for simplicity's sake even though the
cost is somewhat higher. It is interesting to note that Enphase probably
did not anticipate this use case for the IQ combiner because they do not
include a knockout cover for the first PV string.

On Thu, Mar 28, 2019, 2:43 PM Christopher Warfel <
cwar...@entech-engineering.com> wrote:

> If you are using the IQ Combiner, the wiring diagram is on the inside
> cover.  Coming from the array, L1, L2 and G. Going to the utility
> interconnection, L1, L2, G, N.  L1, L2 into the 20a breakers, G to the G
> busbar, N to the N busbar.  It's all there and is a nice package I think.
> My personal preference is to use manufacturer's equipment instead of making
> my own. I don't know if the AHJ would complain about non-listed equipment
> in the case of making your own DAS center. The Envoy may need a button
> pushed once in a while.  I have asked customers to do this to save a trip.
> The Enphase "package" is safe for them to do that.  I hope I did not miss
> your question. Chris
> On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
>
> When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC
> conduit, is there any requirement to accompany the conductors with a ground
> wire? The envoy itself does not have a ground connection and the only
> exposed metallic part is the DIN rail.
>
> I'm thinking I need to mount a ground lug in the PVC box so the circuit
> conductors have a ground wire in the conduit. I have always used the IQ
> combiner even for larger systems because it was just easier. I'm
> considering changing to a regular PVC junction box with just an Envoy.
>
> While on the subject, if there is ample space within a load center, would
> it be permissible to mount the Envoy right inside the enclosure? 400A plus
> load centers in residential settings often have a lot of empty space!
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-04-01 Thread Nick Soleil
Hi Jason,


In the IQ Planning Guide, the reference to calculating the OCPD at 1.25 x the 
inverter continuous output current rating was in reference to sizing larger 
OCPDs for the Enphase Q Aggregators (branch aggregators.)  I did not intend to 
imply that smaller circuits should be installed on breakers smaller than 20A.  
20A breakers are sufficient for protecting a single branch circuit of IQ 
Microinverters, provided that the field wiring is sufficiently sized.


Cordially,

Nick Soleil

Enphase Energy Senior Product Manager, Envoy and Accessories

(707) 763-4784 x7267  // office

(707) 321-2937  // cell

Powering What’s Next™ | The Enphase Energy Management 
System<https://enphase.com/en-us/products-and-services/envoy>

NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315



From: RE-wrenches  on behalf of 
Jason Szumlanski 
Sent: Monday, April 1, 2019 3:55 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Enphase Envoy in PVC J-Box

EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading 
attachments.






Somewhat unrelated is the confusion about AC branch circuit OCPD in an Enphase 
IQ system. My understanding was that each branch circuit could be protected by 
a 20A breaker, but I always designed it for minimum branch circuit OCPD at 1.25 
x combined inverter output circuit rating. The Original IQ Combiner had 20A 
breakers preinstalled, so that was not an option. The IQ design guide states 
that for the Combiner+ and Combiner 3 that the installer should select breakers 
with the correct amp rating. The M series design guide stated that 1.25 x 
combined inverter output circuit rating should be used. But it seems that 
Enphase would approve of 20A circuit protection regardless of how the string is 
populated (up to the max).

Back to the original thread - I'm thinking that a grounding conductor should 
run with the circuit conductors and just terminate on a lug or ground bar even 
if it's all PVC. As for whether the DIN rail needs to be bonded - no idea on 
that one... I could argue that it is not exposed if it is behind the Envoy I 
suppose.

Jason



On Thu, Mar 28, 2019 at 4:29 PM Nick Soleil 
mailto:nsol...@enphaseenergy.com>> wrote:

Hi Jason and Christopher,


We provide installation recommendations for installing an Envoy in a separate 
enclosure on pages 12-16 of our IQ Planning Guide found 
here.<https://enphase.com/sites/default/files/downloads/support/TechBrief-Planning-for-IQ-System.pdf#page=12>
 This tech brief doesn't address Jason's code questions, though.


Cordially,

Nick Soleil

Enphase Energy Senior Product Manager, Envoy and Accessories

(707) 763-4784 x7267  // office

(707) 321-2937  // cell

Powering What’s Next™ | The Enphase Energy Management 
System<https://enphase.com/en-us/products-and-services/envoy>

NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315



From: RE-wrenches 
mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 on behalf of Christopher Warfel 
mailto:cwar...@entech-engineering.com>>
Sent: Thursday, March 28, 2019 11:43 AM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Enphase Envoy in PVC J-Box

EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading 
attachments.





If you are using the IQ Combiner, the wiring diagram is on the inside cover.  
Coming from the array, L1, L2 and G. Going to the utility interconnection, L1, 
L2, G, N.  L1, L2 into the 20a breakers, G to the G busbar, N to the N busbar.  
It's all there and is a nice package I think.  My personal preference is to use 
manufacturer's equipment instead of making my own. I don't know if the AHJ 
would complain about non-listed equipment in the case of making your own DAS 
center. The Envoy may need a button pushed once in a while.  I have asked 
customers to do this to save a trip. The Enphase "package" is safe for them to 
do that.  I hope I did not miss your question. Chris

On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC 
conduit, is there any requirement to accompany the conductors with a ground 
wire? The envoy itself does not have a ground connection and the only exposed 
metallic part is the DIN rail.

I'm thinking I need to mount a ground lug in the PVC box so the circuit 
conductors have a ground wire in the conduit. I have always used the IQ 
combiner even for larger systems because it was just easier. I'm considering 
changing to a regular PVC junction box with just an Envoy.

While on the subject, if there is ample space within a load center, would it be 
permissible to mount the Envoy right inside the enclosure? 400A plus load 
centers in residential settings often have a lot of empty space!





__

Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-04-01 Thread Jason Szumlanski
Somewhat unrelated is the confusion about AC branch circuit OCPD in an
Enphase IQ system. My understanding was that each branch circuit could be
protected by a 20A breaker, but I always designed it for minimum branch
circuit OCPD at 1.25 x combined inverter output circuit rating. The
Original IQ Combiner had 20A breakers preinstalled, so that was not an
option. The IQ design guide states that for the Combiner+ and Combiner 3
that the installer should select breakers with the correct amp rating. The
M series design guide stated that 1.25 x combined inverter output circuit
rating should be used. But it seems that Enphase would approve of 20A
circuit protection regardless of how the string is populated (up to the
max).

Back to the original thread - I'm thinking that a grounding conductor
should run with the circuit conductors and just terminate on a lug or
ground bar even if it's all PVC. As for whether the DIN rail needs to be
bonded - no idea on that one... I could argue that it is not exposed if it
is behind the Envoy I suppose.

Jason



On Thu, Mar 28, 2019 at 4:29 PM Nick Soleil 
wrote:

> Hi Jason and Christopher,
>
>
> We provide installation recommendations for installing an Envoy in a
> separate enclosure on pages 12-16 of our IQ Planning Guide found here.
> <https://enphase.com/sites/default/files/downloads/support/TechBrief-Planning-for-IQ-System.pdf#page=12>
>  This
> tech brief doesn't address Jason's code questions, though.
>
>
> Cordially,
>
> Nick Soleil
>
> Enphase Energy Senior Product Manager, Envoy and Accessories
>
> (707) 763-4784 x7267  // office
>
> (707) 321-2937  // cell
>
> *Powering What’s Next*™* | *The Enphase Energy Management System
> <https://enphase.com/en-us/products-and-services/envoy>
>
> NABCEP Certified Solar PV Installer #03262011-300
>
> California C10 Licensed Electrician #986315
>
>
>
> --
> *From:* RE-wrenches  on behalf
> of Christopher Warfel 
> *Sent:* Thursday, March 28, 2019 11:43 AM
> *To:* re-wrenches@lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] Enphase Envoy in PVC J-Box
>
> *EXTERNAL EMAIL* - *Use caution when responding, clicking, and/or
> downloading attachments.*
>
>
>
>
>
> If you are using the IQ Combiner, the wiring diagram is on the inside
> cover.  Coming from the array, L1, L2 and G. Going to the utility
> interconnection, L1, L2, G, N.  L1, L2 into the 20a breakers, G to the G
> busbar, N to the N busbar.  It's all there and is a nice package I think.
> My personal preference is to use manufacturer's equipment instead of making
> my own. I don't know if the AHJ would complain about non-listed equipment
> in the case of making your own DAS center. The Envoy may need a button
> pushed once in a while.  I have asked customers to do this to save a trip.
> The Enphase "package" is safe for them to do that.  I hope I did not miss
> your question. Chris
> On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
>
> When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC
> conduit, is there any requirement to accompany the conductors with a ground
> wire? The envoy itself does not have a ground connection and the only
> exposed metallic part is the DIN rail.
>
> I'm thinking I need to mount a ground lug in the PVC box so the circuit
> conductors have a ground wire in the conduit. I have always used the IQ
> combiner even for larger systems because it was just easier. I'm
> considering changing to a regular PVC junction box with just an Envoy.
>
> While on the subject, if there is ample space within a load center, would
> it be permissible to mount the Envoy right inside the enclosure? 400A plus
> load centers in residential settings often have a lot of empty space!
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/da2ef7faff3c518f059fdaeefe6907a68f9fcecc?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org=1613865=8c5d3391ec9d7709>
>

Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-03-28 Thread Nick Soleil
Hi Jason and Christopher,


We provide installation recommendations for installing an Envoy in a separate 
enclosure on pages 12-16 of our IQ Planning Guide found 
here.<https://enphase.com/sites/default/files/downloads/support/TechBrief-Planning-for-IQ-System.pdf#page=12>
 This tech brief doesn't address Jason's code questions, though.


Cordially,

Nick Soleil

Enphase Energy Senior Product Manager, Envoy and Accessories

(707) 763-4784 x7267  // office

(707) 321-2937  // cell

Powering What’s Next™ | The Enphase Energy Management 
System<https://enphase.com/en-us/products-and-services/envoy>

NABCEP Certified Solar PV Installer #03262011-300

California C10 Licensed Electrician #986315



From: RE-wrenches  on behalf of 
Christopher Warfel 
Sent: Thursday, March 28, 2019 11:43 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Enphase Envoy in PVC J-Box

EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading 
attachments.





If you are using the IQ Combiner, the wiring diagram is on the inside cover.  
Coming from the array, L1, L2 and G. Going to the utility interconnection, L1, 
L2, G, N.  L1, L2 into the 20a breakers, G to the G busbar, N to the N busbar.  
It's all there and is a nice package I think.  My personal preference is to use 
manufacturer's equipment instead of making my own. I don't know if the AHJ 
would complain about non-listed equipment in the case of making your own DAS 
center. The Envoy may need a button pushed once in a while.  I have asked 
customers to do this to save a trip. The Enphase "package" is safe for them to 
do that.  I hope I did not miss your question. Chris

On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC 
conduit, is there any requirement to accompany the conductors with a ground 
wire? The envoy itself does not have a ground connection and the only exposed 
metallic part is the DIN rail.

I'm thinking I need to mount a ground lug in the PVC box so the circuit 
conductors have a ground wire in the conduit. I have always used the IQ 
combiner even for larger systems because it was just easier. I'm considering 
changing to a regular PVC junction box with just an Envoy.

While on the subject, if there is ample space within a load center, would it be 
permissible to mount the Envoy right inside the enclosure? 400A plus load 
centers in residential settings often have a lot of empty space!





___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-03-28 Thread Wayne Irwin
If you locate the envoy in a metal enclosure the WiFi connection will most 
likely not work.

From: RE-wrenches  on behalf of 
Christopher Warfel 
Sent: Thursday, March 28, 2019 2:43:04 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Enphase Envoy in PVC J-Box


If you are using the IQ Combiner, the wiring diagram is on the inside cover.  
Coming from the array, L1, L2 and G. Going to the utility interconnection, L1, 
L2, G, N.  L1, L2 into the 20a breakers, G to the G busbar, N to the N busbar.  
It's all there and is a nice package I think.  My personal preference is to use 
manufacturer's equipment instead of making my own. I don't know if the AHJ 
would complain about non-listed equipment in the case of making your own DAS 
center. The Envoy may need a button pushed once in a while.  I have asked 
customers to do this to save a trip. The Enphase "package" is safe for them to 
do that.  I hope I did not miss your question. Chris

On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC 
conduit, is there any requirement to accompany the conductors with a ground 
wire? The envoy itself does not have a ground connection and the only exposed 
metallic part is the DIN rail.

I'm thinking I need to mount a ground lug in the PVC box so the circuit 
conductors have a ground wire in the conduit. I have always used the IQ 
combiner even for larger systems because it was just easier. I'm considering 
changing to a regular PVC junction box with just an Envoy.

While on the subject, if there is ample space within a load center, would it be 
permissible to mount the Envoy right inside the enclosure? 400A plus load 
centers in residential settings often have a lot of empty space!





___
List sponsored by Redwood Alliance

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org<http://www.members.re-wrenches.org>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-03-28 Thread Christopher Warfel
If you are using the IQ Combiner, the wiring diagram is on the inside 
cover.  Coming from the array, L1, L2 and G. Going to the utility 
interconnection, L1, L2, G, N.  L1, L2 into the 20a breakers, G to the G 
busbar, N to the N busbar.  It's all there and is a nice package I 
think.  My personal preference is to use manufacturer's equipment 
instead of making my own. I don't know if the AHJ would complain about 
non-listed equipment in the case of making your own DAS center. The 
Envoy may need a button pushed once in a while.  I have asked customers 
to do this to save a trip. The Enphase "package" is safe for them to do 
that.  I hope I did not miss your question. Chris


On 3/28/2019 12:55 PM, Jason Szumlanski wrote:
When mounting an Envoy on the supplied DIN rail in a PVC box wired via 
PVC conduit, is there any requirement to accompany the conductors with 
a ground wire? The envoy itself does not have a ground connection and 
the only exposed metallic part is the DIN rail.


I'm thinking I need to mount a ground lug in the PVC box so the 
circuit conductors have a ground wire in the conduit. I have always 
used the IQ combiner even for larger systems because it was just 
easier. I'm considering changing to a regular PVC junction box with 
just an Envoy.


While on the subject, if there is ample space within a load center, 
would it be permissible to mount the Envoy right inside the enclosure? 
400A plus load centers in residential settings often have a lot of 
empty space!




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Enphase Envoy in PVC J-Box

2019-03-28 Thread Jason Szumlanski
When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC
conduit, is there any requirement to accompany the conductors with a ground
wire? The envoy itself does not have a ground connection and the only
exposed metallic part is the DIN rail.

I'm thinking I need to mount a ground lug in the PVC box so the circuit
conductors have a ground wire in the conduit. I have always used the IQ
combiner even for larger systems because it was just easier. I'm
considering changing to a regular PVC junction box with just an Envoy.

While on the subject, if there is ample space within a load center, would
it be permissible to mount the Envoy right inside the enclosure? 400A plus
load centers in residential settings often have a lot of empty space!
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org