Re: [RE-wrenches] HV Module Testing

2019-04-11 Thread drake . chamberlin
Voc is 37.1
That times 1.25 is 46.38 V

It is less than 120 V, so I guess I can not test individual modules on
the 500 V setting. Is that the case? 

Thanks,

Drake 

- Original Message -
From:
 "RE-wrenches" 

To:
"RE-wrenches" 
Cc:

Sent:
Wed, 10 Apr 2019 15:51:42 -0700
Subject:
Re: [RE-wrenches] HV Module Testing

The IEC 62446 standard for IRT on PV is:

Voc@STC x 1.25 = 120 V to  ≤ 500 V, test to 500 V
Voc@STC x 1.25 = > 500 V, test to 1,000 V

They specify using one of two methods: 

1. With the array short circuited (a la the Seaward test meter style)

2. Testing both positive and negative to ground - both the negative
and positive leads need to be isolated (fuse open/breaker off, and
disconnected from parallel busbar connections).  In my experience,
putting the meter in series (meter positive to PV negative, meter
negative to ground) is usually sufficient for finding ground-faults.

Make sure the meter-to-ground connection is low resistance, and that
the connection point is something that is actually bonded to the
equipment grounding system. 

Temperature, humidity, and the amount of "glass" being tested will
have significant impacts on measured results, but you're really
looking for an outlier, assuming it isn't a hard fault that could've
been found with a DMM or a visual inspection.

Always a good idea to check with the module manufacturer to see if
they have documentation on their recommended procedure.

Cheers,

Brian Mehalic 
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org [1]

SEI Professional Services
http://www.s
eisolarpros.com [2]

On Wed, Apr 10, 2019 at 3:07 PM  wrote:

That is very helpful. If I do the high voltage test, can I test from
both positive to the frame and negative to the frame? 

Thanks,

Drake 

- Original Message -
From:
 "RE-wrenches" 

To:
"RE-wrenches" 
Cc:

Sent:
Wed, 10 Apr 2019 10:35:50 -0700
Subject:
Re: [RE-wrenches] HV Module Testing

Drake
I have performed test for manufactures and you must keep the test
voltage under the max rated voltage of the module, we have a bunch of
tests we do but in short, you need to see the modules up close, look
at the edges and back sheets look for green, brown or black spots, you
need to do testing both dry first then wet if it is a ground fault
concern. Most of the time the visual will find the issues but you
still want to verify what you think you see. Make sure you look at the
wiring to and from, the combiner box(s) or even the inverter(s).

On Wed, Apr 10, 2019 at 8:31 AM Drake
 wrote:

  Hello Wrenches, 

 We are troubleshooting an array of Orion modules, either 230s or
250s. The array is showing a ground fault. 

 We would like to test these modules with an insulation tester? 

 We would like to apply 500 V or 1000 V to each the + and – and test
resistance to ground. 
  
 Is this practice safe for individual PV modules? Is there anything I
should be aware of before attempting this?

 Thanks,

 Drake

Drake Chamberlin
Athens Electric LLC
 OH License 44810
 CO License 3773
 NABCEP Certified Solar PV 
 740-448-7328
http://athens-electric.com/ [7] 

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [8]

 Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[9]

 List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[10]

 List rules & etiquette:
www.re-wrenches.org/etiquette.htm [11]

 Check out or update participant bios:
www.members.re-wrenches.org [12]

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [13]

 Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[14]

 List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[15]

 List rules & etiquette:
www.re-wrenches.org/etiquette.htm [16]

 Check out or update participant bios:
www.members.re-wrenches.org [17]

 

Links:
--
[1] http://www.solarenergy.org
[2] http://www.seisolarpros.com
[3] mailto:drake.chamber...@redwoodalliance.org
[4] mailto:re-wrenches@lists.re-wrenches.org
[5] mailto:re-wrenches@lists.re-wrenches.org
[6] mailto:drake.chamber...@redwoodalliance.org
[7] http://athens-electric.com/
[8] mailto:RE-wrenches@lists.re-wrenches.org
[9]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[10]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[11] http://www.re-wrenches.org/etiquette.htm
[12] http://www.members.re-wrenches.org
[13] mailto:RE-wrenches@lists.re-wrenches.org
[14]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[15]
http:/

Re: [RE-wrenches] HV Module Testing

2019-04-10 Thread Brian Mehalic
The IEC 62446 standard for IRT on PV is:

Voc@STC x 1.25 = 120 V to  ≤ 500 V, test to 500 V
Voc@STC x 1.25 = > 500 V, test to 1,000 V

They specify using one of two methods:

1. With the array short circuited (a la the Seaward test meter style)

2. Testing both positive and negative to ground - both the negative and
positive leads need to be isolated (fuse open/breaker off, and disconnected
from parallel busbar connections).  In my experience, putting the meter in
series (meter positive to PV negative, meter negative to ground) is usually
sufficient for finding ground-faults.

Make sure the meter-to-ground connection is low resistance, and that the
connection point is something that is actually bonded to the equipment
grounding system.

Temperature, humidity, and the amount of "glass" being tested will have
significant impacts on measured results, but you're really looking for an
outlier, assuming it isn't a hard fault that could've been found with a DMM
or a visual inspection.

Always a good idea to check with the module manufacturer to see if they
have documentation on their recommended procedure.

Cheers,

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Wed, Apr 10, 2019 at 3:07 PM 
wrote:

> That is very helpful. If I do the high voltage test, can I test from both
> positive to the frame and negative to the frame?
>
> Thanks,
>
> Drake
>
>
>
> - Original Message -
> From:
> "RE-wrenches" 
>
> To:
> "RE-wrenches" 
> Cc:
>
> Sent:
> Wed, 10 Apr 2019 10:35:50 -0700
> Subject:
> Re: [RE-wrenches] HV Module Testing
>
>
> Drake
> I have performed test for manufactures and you must keep the test voltage
> under the max rated voltage of the module, we have a bunch of tests we do
> but in short, you need to see the modules up close, look at the edges and
> back sheets look for green, brown or black spots, you need to do testing
> both dry first then wet if it is a ground fault concern. Most of the time
> the visual will find the issues but you still want to verify what you think
> you see. Make sure you look at the wiring to and from, the combiner box(s)
> or even the inverter(s).
>
> On Wed, Apr 10, 2019 at 8:31 AM Drake <
> drake.chamber...@redwoodalliance.org> wrote:
>
>> Hello Wrenches,
>>
>> We are troubleshooting an array of Orion modules, either 230s or 250s.
>> The array is showing a ground fault.
>>
>> We would like to test these modules with an insulation tester?
>>
>> We would like to apply 500 V or 1000 V to each the + and – and test
>> resistance to ground.
>>
>> Is this practice safe for individual PV modules? Is there anything I
>> should be aware of before attempting this?
>>
>> Thanks,
>>
>> Drake
>>
>> Drake Chamberlin
>>
>>
>>
>>
>>
>> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
>> Solar PV 740-448-7328*http://athens-electric.com/
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] HV Module Testing

2019-04-10 Thread jerrysgarage01
Current will pass through so just one hot leg to earth, be carefull not to 
overload the diodes, l have never had an issue but you never know. JerrySent 
from my Verizon, Samsung Galaxy smartphone
 Original message From: drake.chamber...@redwoodalliance.org 
Date: 4/10/19  3:07 PM  (GMT-08:00) To: RE-wrenches 
 Subject: Re: [RE-wrenches] HV Module 
Testing That is very helpful. If I do the high voltage test, can I test from 
both positive to the frame and negative to the frame? Thanks,Drake - 
Original Message -From: "RE-wrenches" 
To:"RE-wrenches" 
Cc:Sent:Wed, 10 Apr 2019 10:35:50 
-0700Subject:Re: [RE-wrenches] HV Module TestingDrakeI have performed test for 
manufactures and you must keep the test voltage under the max rated voltage of 
the module, we have a bunch of tests we do but in short, you need to see the 
modules up close, look at the edges and back sheets look for green, brown or 
black spots, you need to do testing both dry first then wet if it is a ground 
fault concern. Most of the time the visual will find the issues but you still 
want to verify what you think you see. Make sure you look at the wiring to and 
from, the combiner box(s) or even the inverter(s).On Wed, Apr 10, 2019 at 8:31 
AM Drake  wrote:

Hello Wrenches, 
We are troubleshooting an array of Orion modules, either 230s or 250s.
The array is showing a ground fault. 
We would like to test these modules with an insulation tester? 
We would like to apply 500 V or 1000 V to each the + and – and test
resistance to ground. 
 
Is this practice safe for individual PV modules? Is there anything I
should be aware of before attempting this?
Thanks,
DrakeDrake ChamberlinAthens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV 
740-448-7328http://athens-electric.com/


___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & 
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:www.re-wrenches.org/etiquette.htm
Check out or update participant bios:www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] HV Module Testing

2019-04-10 Thread drake . chamberlin

That is very helpful. If I do the high voltage test, can I test from
both positive to the frame and negative to the frame? 

Thanks,

Drake 

- Original Message -
From: "RE-wrenches" 
To:"RE-wrenches" 
Cc:
Sent:Wed, 10 Apr 2019 10:35:50 -0700
Subject:Re: [RE-wrenches] HV Module Testing

Drake
I have performed test for manufactures and you must keep the test
voltage under the max rated voltage of the module, we have a bunch of
tests we do but in short, you need to see the modules up close, look
at the edges and back sheets look for green, brown or black spots, you
need to do testing both dry first then wet if it is a ground fault
concern. Most of the time the visual will find the issues but you
still want to verify what you think you see. Make sure you look at the
wiring to and from, the combiner box(s) or even the inverter(s).

On Wed, Apr 10, 2019 at 8:31 AM Drake
 wrote:

 Hello Wrenches, 

 We are troubleshooting an array of Orion modules, either 230s or
250s. The array is showing a ground fault. 

 We would like to test these modules with an insulation tester? 

 We would like to apply 500 V or 1000 V to each the + and – and test
resistance to ground. 
  
 Is this practice safe for individual PV modules? Is there anything I
should be aware of before attempting this?

 Thanks,

 Drake

Drake Chamberlin
Athens Electric LLC
 OH License 44810
 CO License 3773
 NABCEP Certified Solar PV 
 740-448-7328
http://athens-electric.com/ [2] 

 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org [3]

 Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[4]

 List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[5]

 List rules & etiquette:
www.re-wrenches.org/etiquette.htm [6]

 Check out or update participant bios:
www.members.re-wrenches.org [7]

 

Links:
--
[1] mailto:drake.chamber...@redwoodalliance.org
[2] http://athens-electric.com/
[3] mailto:RE-wrenches@lists.re-wrenches.org
[4]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[5]
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
[6] http://www.re-wrenches.org/etiquette.htm
[7] http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] HV Module Testing

2019-04-10 Thread Jerry Shafer
Drake
I have performed test for manufactures and you must keep the test voltage
under the max rated voltage of the module, we have a bunch of tests we do
but in short, you need to see the modules up close, look at the edges and
back sheets look for green, brown or black spots, you need to do testing
both dry first then wet if it is a ground fault concern. Most of the time
the visual will find the issues but you still want to verify what you think
you see. Make sure you look at the wiring to and from, the combiner box(s)
or even the inverter(s).

On Wed, Apr 10, 2019 at 8:31 AM Drake 
wrote:

> Hello Wrenches,
>
> We are troubleshooting an array of Orion modules, either 230s or 250s. The
> array is showing a ground fault.
>
> We would like to test these modules with an insulation tester?
>
> We would like to apply 500 V or 1000 V to each the + and – and test
> resistance to ground.
>
> Is this practice safe for individual PV modules? Is there anything I
> should be aware of before attempting this?
>
> Thanks,
>
> Drake
>
> Drake Chamberlin
>
>
>
>
>
> *Athens Electric LLC OH License 44810 CO License 3773 NABCEP Certified
> Solar PV 740-448-7328 *http://athens-electric.com/
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org