Hi Mac, 
 
We fabricated and operate a similar sized (400 kWh) battery / inverter / 
generator hybrid system for BC Hydro, our power utility servicing a remote 
community. It has been online for 2 years now. 
 
Using Dekka / East Penn D-series batteries which we had custom built to our 
specs. 
 
A notable difference is we have 100 kW diesels and 60 kW inverter capacity in a 
120/208 SMA inverter config (stepped up to 14.4 kV distribution). The system 
works really well and it currently 100% uptime for last 12 months. This is an 
unattended system we are onsite to maintain every 2 months. No renewable input 
at this time. 
 
The sizing you have reported seems out of ratio. ~ 20 kW of charging power into 
a 400 kWh battery bank ie C/5. Depending on the loads the gen is carrying along 
with charging that could further reduce available charge capacity. That 
generator is going to have to run for a very long time to charge that battery. 
We call this the big battery blunder syndrome - which has caused many failures 
of such scale of system. 
 
Kevin

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Mac Lewis
Sent: March 11, 2014 7:27 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Huge battery bank recommendation


To clarify, this is for an off-grid application, 4 Sunny Islands, 30kW 
generator.


On Tue, Mar 11, 2014 at 9:16 AM, August Goers  aug...@luminalt.com wrote:


Mac, 

Is this for an off grid system? We're doing our first project with a Deka Unigy 
II battery system but they are AGM and I believe only good for grid tied 
battery backup or applications where you won't have a very deep depth of 
discharge:

http://www.dekabatteries.com/assets/base/0919c.pdf


Best,

August


August Goers

Principal

Luminalt Energy Corporation

o: 415.641.4000

m: 415.559.1525

www.luminalt.com

 



On Tue, Mar 11, 2014 at 6:24 AM, Mac Lewis  maclew...@gmail.com wrote:


Hi wrenches, 

I am consulting on a job that requires an 8000 Ahr battery bank.  This is quite 
a bit beyond my normal battery bank realm.  What would you recommend for this?

Thanks in advance


-- 





Mac Lewis



Yo solo sé que no sé nada. -Sócrates


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org







-- 





Mac Lewis



Yo solo sé que no sé nada. -Sócrates

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-12 Thread Mac Lewis
Hi Kirpal,

With regards to your question about what size solar system will be feeding
this large battery bank, we are still trying to optimize the design a bit.
 However, the the preliminary design was at about a 25 kW.  During peak
production, we expect about 500A(!) to be heading into the battery bank.
 Should be a fun project to see how it develops.

Thanks


On Tue, Mar 11, 2014 at 1:37 PM, Kirpal Khalsa solarwo...@gmail.com wrote:

 Ray.i do not have the link to the warrantyour salesman presented
 us with a variety of options ranging from 5 years upto 20 years.just
 like other manufacturers they had prorating levels with each option.If
 asked i am sure they will provide you with any information you want in
 regards to the warranty

 Allan.yes in fact we were also surprised with the low voltage settings
 that they specifyIn one system we installed a 3200Ah battery bank and
 trying to coordinate the settings they specify with the programmable
 settings offered in the Sunny Islands was an exercise in it selfThey
 have different terminology than is common in most RE system charging
 parametersmaking sure we were all talking about the same parameters was
 the hardest factorIf i remember correctly the absorb and equalize
 settings were almost the same per the manufacturer.
 I could not tell you much about the lead -selenium technology or the
 tubular positive plates with any expertise.
 The large system we installed these batteries on was specified to use the
 longest possible life span batteries  coupled with high cycling
 capabilityAt the time they were the only company we could find willing
 to put the 20 year warranty in writing apart from some sealed Unigy
 batteries which were far more expensive..This was a AC coupled grid
 interactive system and so the batteries are in standby 95%+ of the
 timeWe have a contract to do routine maintenance on the system and have
 only had to add water once per yeareven then it was not necessary but
 to set it on course till the next time we are scheduled to inspect, 1 year
 later.
 The customer has had very few power outages but did have one for 4 days
 last winter and the battery bank worked flawlesslyWe really like the
 clear cases for quick electrolyte level monitoring.  The cells have flip
 tops for easy access.
 My overall take on these batteries is that they are primarily designed for
 standby systems.  We haven't used them in an off grid configuration.  They
 have been in for 3 years with no sign of aging...I think they are a company
 that is only beginning to realize the possibility of the RE market and
 havent focused much effort in that direction in the past
 SBS was easy to work with, and provided good support for the seismic
 racking and spill containment systemwith more documentation than i am
 used to receiving from our main suppliers...
 Hope that helps...
 Cheers,



 Sunny Regards,
 Kirpal Khalsa
 NABCEP Certified PV Installation Professional
 Renewable Energy Systems
 www.oregonsolarworks.com
 541-218-0201 m
 541-299-0402 o


 On Tue, Mar 11, 2014 at 8:42 AM, Ray Walters r...@solarray.com wrote:

  Hi Kirpal;

 I see that the SBS batteries are rated to 1200 cycles to 80% DOD, but I
 can't find the warranty on their website. Do you have a link to that?

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer303 505-8760

 On 3/11/2014 9:26 AM, Kirpal Khalsa wrote:

 Mac...good morningthat is a big battery bank!We have used the SBS
 Batteries for large battery banksThey offer multiple warranty options
 including upto 20 years.  They are tubular plates with clear outer cases
 which make the electrolyte levels really easy to monitor and fillThey
 come with insulated cell interconnects with testing ports, they offer
 seismic racking custom designed to fit your battery bank, as well as spill
 containment trays and acid neutralizer kits for the spill containment
 trays.  We have been very happy with their performance.  They offer a 2V
 FLA cell at 4000Ah @ the 20 hr rate.  They are a high quality product made
 in the USA and worth looking at.
 Here is the link to their website.

 http://www.sbsbattery.com/products-services/by-product/batteries/batteries-flooded-wet-cell-batteries/flooded-wet-cell-batteries-stt-series-flooded-2v-cell.html
  Additionally they offer hydrogen gas alarms for battery rooms.

  I am curious - is this a solar integrated system, if so, what size
 array would be charging the batteries?
 Good luck!

  Sunny Regards,
 Kirpal Khalsa
 NABCEP Certified PV Installation Professional
 Renewable Energy Systems
 www.oregonsolarworks.com
 541-218-0201 m
 541-299-0402 o


 On Tue, Mar 11, 2014 at 8:05 AM, Ray Walters r...@solarray.com wrote:

 Consider the HUP Solar One battery, the 125-33.  It has 2490 AH at the
 20 hr rate.   The warranty is for 2100 cycles to 80% DOD.  Also most of the
 jumpers 

[RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Mac Lewis
Hi wrenches,

I am consulting on a job that requires an 8000 Ahr battery bank.  This is
quite a bit beyond my normal battery bank realm.  What would you recommend
for this?

Thanks in advance

-- 



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Jason Szumlanski
Not that I have an answer for you, but I'm curious, too. You need to
specify voltage to get a good answer.

Jason Szumlanski

Fafco Solar





On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:

 Hi wrenches,

 I am consulting on a job that requires an 8000 Ahr battery bank.  This is
 quite a bit beyond my normal battery bank realm.  What would you recommend
 for this?

 Thanks in advance

 --



 Mac Lewis


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Mac Lewis
Good point Jason.  To clarify this is a 48V system.

Thanks


On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski ja...@fafcosolar.comwrote:

 Not that I have an answer for you, but I'm curious, too. You need to
 specify voltage to get a good answer.

 Jason Szumlanski

 Fafco Solar





 On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:

 Hi wrenches,

 I am consulting on a job that requires an 8000 Ahr battery bank.  This is
 quite a bit beyond my normal battery bank realm.  What would you recommend
 for this?

  Thanks in advance

 --



 Mac Lewis


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread penobscotsolar
Mac, for this type of large system we typically use Surrette/Rolls
2YS31.They are 2430 ah. When we get into battery banks this large we
typically only run two cells deep (front to back) for ease of maintenance.
I hope your customer has some free time on their hands for maintenance.
Remember, Surrette deep cycle batteries demand a higher than most charge
rate or you will find the life of the cell will be significantly shorter
than with proper charging. I'm sure your local battery distributor or
Jamie Surrette can send you the tech stuff on these batteries. Any way it
goes, this is a very big battery bank. Good luck!

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design



 Good point Jason.  To clarify this is a 48V system.

 Thanks


 On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski
 ja...@fafcosolar.comwrote:

 Not that I have an answer for you, but I'm curious, too. You need to
 specify voltage to get a good answer.

 Jason Szumlanski

 Fafco Solar





 On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:

 Hi wrenches,

 I am consulting on a job that requires an 8000 Ahr battery bank.  This
 is
 quite a bit beyond my normal battery bank realm.  What would you
 recommend
 for this?

  Thanks in advance

 --



 Mac Lewis


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





 --



 Mac Lewis

 *Yo solo sé que no sé nada. -Sócrates*
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Tump
Surrette YS 31s  2400Ahr X 3strings = 7200 2 volt IN plastic containment 
vessels. ~280Lbs/per
On Mar 11, 2014, at 9:24 AM, Mac Lewis wrote:

 Hi wrenches,
 
 I am consulting on a job that requires an 8000 Ahr battery bank.  This is 
 quite a bit beyond my normal battery bank realm.  What would you recommend 
 for this?
 
 Thanks in advance
 
 -- 
 
 
 
 Mac Lewis
 
 Yo solo sé que no sé nada. -Sócrates
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

 t...@swnl.net   www.SWNL.net
 Solarwinds Northernlights   
Serving Mid Coast Maine  Northern California
  207-832-7574   Cl. 610-517-8401  
 
   Blair TUMP May
  MAINE'S CHARTER 
   NABCEPCertified PV Installer 

     MAINE'S CHARTER 
   Trace Xantrex Certified Dealer / Installer
 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Roy Butler

  
  
We've used these batteries in a couple
  of high end off-grid jobs and they work great.
  Yes, they are around 280 pounds..but by afternoon, they're
  more like 325 ;-)
  
  The last system we installed had 48 of these. And as Tump said,
  allow plenty of time
  for watering...especially if you wind up with 72 cells.
  Roy Butler
NABCEP Certified Solar PV Installer
NYSERDA eligible PV  wind installer
IREC Certified Master Trainer for Small Wind Installer
Four Winds Renewable Energy, LLC
8902 Route 46, Arkport, NY 14807
607-324-9747  www.four-winds-energy.com

Join us at the 10th Annual Small Wind Conference
A Gathering of Installers, Manufacturers, Dealers,  Distributors
June 17 and 18, 2014 in Stevens Point, Wisconsin
www.smallwindconference.com

Although no trees were killed in the sending of this message, 
a large number of electrons were terribly inconvenienced.



  On 3/11/2014 10:10 AM, Tump wrote:

Surrette YS 31s 2400Ahr X 3strings = 7200 2 volt IN
  plastic containment vessels. ~280Lbs/per
  
On Mar 11, 2014, at 9:24 AM, Mac Lewis wrote:


  Hi wrenches,


I am consulting on a job that requires an 8000 Ahr
  battery bank. This is quite a bit beyond my normal
  battery bank realm. What would you recommend for this?


Thanks in advance
  
  
  -- 
  
  
  

  
  
  Mac Lewis
  
  

  "Yo solo
  s que no s nada."-Scrates
  

  
  ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Change email address  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List-Archive:
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm
  
  Check out participant bios:
  www.members.re-wrenches.org
  

  
  
  

  

  

  t...@swnl.net  www.SWNL.net
  
  

Solarwinds
  Northernlights
  
Serving Mid Coast Maine
   Northern California
 
  207-832-7574Cl.
610-517-8401
  
   Blair
"TUMP" May
  
 MAINE'S
  CHARTER 
  
 NABCEP "Certified PV
  Installer"


  MAINE'S CHARTER 
   Trace Xantrex
  "Certified" Dealer /
  Installer"
  
  

  



  

  

  
  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out 

Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread frenergy
As a side note, if you use the 2YS31 Surrettes, as I did for a single 48V 
string about a year ago.  You may want to have them shipped from Canada as a 
batch.  I'm almost certain that my pack of 24 2v cells was a mixture of 
manufacture dates, 3 of which were in the distribution chain for too long.  
So I have 3 cells that, despite the hours and hours and days of charging I 
cannot get above SG 1.252.  The rest of the cells are in the 1.268~1.275 range 
after EQ.  Yes, I've talked to Steve Higgins about this a couple timesso 
far, I don't have the answer I would like after having spent a very large chunk 
on $$ on what I'm hoping is a 15 year pack.

Bill
Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530.284.7849 / 6544 fax
  - Original Message - 
  From: Mac Lewis 
  To: RE-wrenches 
  Sent: Tuesday, March 11, 2014 6:45 AM
  Subject: Re: [RE-wrenches] Huge battery bank recommendation


  Good point Jason.  To clarify this is a 48V system.


  Thanks



  On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski ja...@fafcosolar.com 
wrote:

Not that I have an answer for you, but I'm curious, too. You need to 
specify voltage to get a good answer.


Jason Szumlanski


Fafco Solar
 





On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:

  Hi wrenches,


  I am consulting on a job that requires an 8000 Ahr battery bank.  This is 
quite a bit beyond my normal battery bank realm.  What would you recommend for 
this?


  Thanks in advance



  -- 







  Mac Lewis



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org








  -- 







  Mac Lewis


  Yo solo sé que no sé nada. -Sócrates



--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Change email address  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Ray Walters
Consider the HUP Solar One battery, the 125-33.  It has 2490 AH at the 
20 hr rate.   The warranty is for 2100 cycles to 80% DOD.  Also most of 
the jumpers are included (bus bars within each 12 v group)

We've had nothing but happy customers since we started using the HUPs.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/11/2014 8:01 AM, penobscotso...@midmaine.com wrote:

Mac, for this type of large system we typically use Surrette/Rolls
2YS31.They are 2430 ah. When we get into battery banks this large we
typically only run two cells deep (front to back) for ease of maintenance.
I hope your customer has some free time on their hands for maintenance.
Remember, Surrette deep cycle batteries demand a higher than most charge
rate or you will find the life of the cell will be significantly shorter
than with proper charging. I'm sure your local battery distributor or
Jamie Surrette can send you the tech stuff on these batteries. Any way it
goes, this is a very big battery bank. Good luck!

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design




Good point Jason.  To clarify this is a 48V system.

Thanks


On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski
ja...@fafcosolar.comwrote:


Not that I have an answer for you, but I'm curious, too. You need to
specify voltage to get a good answer.

Jason Szumlanski

Fafco Solar





On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:


Hi wrenches,

I am consulting on a job that requires an 8000 Ahr battery bank.  This
is
quite a bit beyond my normal battery bank realm.  What would you
recommend
for this?

  Thanks in advance

--



Mac Lewis



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





--



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread August Goers
Mac,

Is this for an off grid system? We're doing our first project with a Deka
Unigy II battery system but they are AGM and I believe only good for grid
tied battery backup or applications where you won't have a very deep depth
of discharge:

http://www.dekabatteries.com/assets/base/0919c.pdf

Best,

August

*August Goers*

Principal

Luminalt Energy Corporation

o: 415.641.4000

m: 415.559.1525

www.luminalt.com




On Tue, Mar 11, 2014 at 6:24 AM, Mac Lewis maclew...@gmail.com wrote:

 Hi wrenches,

 I am consulting on a job that requires an 8000 Ahr battery bank.  This is
 quite a bit beyond my normal battery bank realm.  What would you recommend
 for this?

 Thanks in advance

 --



 Mac Lewis

 * Yo solo sé que no sé nada. -Sócrates *

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Mac Lewis
To clarify, this is for an off-grid application, 4 Sunny Islands, 30kW
generator.


On Tue, Mar 11, 2014 at 9:16 AM, August Goers aug...@luminalt.com wrote:

 Mac,

 Is this for an off grid system? We're doing our first project with a Deka
 Unigy II battery system but they are AGM and I believe only good for grid
 tied battery backup or applications where you won't have a very deep depth
 of discharge:

 http://www.dekabatteries.com/assets/base/0919c.pdf

 Best,

 August

 *August Goers*

 Principal

 Luminalt Energy Corporation

 o: 415.641.4000

 m: 415.559.1525

 www.luminalt.com




 On Tue, Mar 11, 2014 at 6:24 AM, Mac Lewis maclew...@gmail.com wrote:

 Hi wrenches,

 I am consulting on a job that requires an 8000 Ahr battery bank.  This is
 quite a bit beyond my normal battery bank realm.  What would you recommend
 for this?

 Thanks in advance

 --



 Mac Lewis

 * Yo solo sé que no sé nada. -Sócrates *

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org





-- 



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Kirpal Khalsa
Mac...good morningthat is a big battery bank!We have used the SBS
Batteries for large battery banksThey offer multiple warranty options
including upto 20 years.  They are tubular plates with clear outer cases
which make the electrolyte levels really easy to monitor and fillThey
come with insulated cell interconnects with testing ports, they offer
seismic racking custom designed to fit your battery bank, as well as spill
containment trays and acid neutralizer kits for the spill containment
trays.  We have been very happy with their performance.  They offer a 2V
FLA cell at 4000Ah @ the 20 hr rate.  They are a high quality product made
in the USA and worth looking at.
Here is the link to their website.
http://www.sbsbattery.com/products-services/by-product/batteries/batteries-flooded-wet-cell-batteries/flooded-wet-cell-batteries-stt-series-flooded-2v-cell.html
Additionally they offer hydrogen gas alarms for battery rooms.

I am curious - is this a solar integrated system, if so, what size array
would be charging the batteries?
Good luck!

Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-299-0402 o


On Tue, Mar 11, 2014 at 8:05 AM, Ray Walters r...@solarray.com wrote:

 Consider the HUP Solar One battery, the 125-33.  It has 2490 AH at the 20
 hr rate.   The warranty is for 2100 cycles to 80% DOD.  Also most of the
 jumpers are included (bus bars within each 12 v group)
 We've had nothing but happy customers since we started using the HUPs.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760


 On 3/11/2014 8:01 AM, penobscotso...@midmaine.com wrote:

 Mac, for this type of large system we typically use Surrette/Rolls
 2YS31.They are 2430 ah. When we get into battery banks this large we
 typically only run two cells deep (front to back) for ease of maintenance.
 I hope your customer has some free time on their hands for maintenance.
 Remember, Surrette deep cycle batteries demand a higher than most charge
 rate or you will find the life of the cell will be significantly shorter
 than with proper charging. I'm sure your local battery distributor or
 Jamie Surrette can send you the tech stuff on these batteries. Any way it
 goes, this is a very big battery bank. Good luck!

 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design



  Good point Jason.  To clarify this is a 48V system.

 Thanks


 On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski
 ja...@fafcosolar.comwrote:

  Not that I have an answer for you, but I'm curious, too. You need to
 specify voltage to get a good answer.

 Jason Szumlanski

 Fafco Solar





 On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis maclew...@gmail.com wrote:

  Hi wrenches,

 I am consulting on a job that requires an 8000 Ahr battery bank.  This
 is
 quite a bit beyond my normal battery bank realm.  What would you
 recommend
 for this?

   Thanks in advance

 --



 Mac Lewis


  ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 --



 Mac Lewis

 *Yo solo sé que no sé nada. -Sócrates*
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
 wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
 wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power 

Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread william
Mac:

 

One option is steel tray batteries.  Manufacturers include MK/Deka and
Hawker.  We are accepting delivery of 6 of the 1800 a/h Hawkers Friday.
They are 2600 pounds each.   We move them with a special narrow pallet jack.
Here’s some photos:

 

http://www.millersolar.com/public_html/MillerSolar/Portfolio/Commercial/Cal_
Trans/_cal_trans_gorda.html

 

The bank shown is VRLA and were a poor choice for the application.  They
failed in 8 years.  They will be replaced by FLA batteries with a watering
system.  We will leave the watering system turned off so we can inspect each
cell for consumption before watering.

 

Good luck,

 

William

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mac Lewis
Sent: Tuesday, March 11, 2014 6:25 AM
To: RE-wrenches
Subject: [RE-wrenches] Huge battery bank recommendation

 

Hi wrenches,

 

I am consulting on a job that requires an 8000 Ahr battery bank.  This is
quite a bit beyond my normal battery bank realm.  What would you recommend
for this?

 

Thanks in advance


 

-- 

 

 

 

Mac Lewis

Yo solo sé que no sé nada. -Sócrates

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Ray Walters

Hi Kirpal;

I see that the SBS batteries are rated to 1200 cycles to 80% DOD, but I 
can't find the warranty on their website. Do you have a link to that?


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 3/11/2014 9:26 AM, Kirpal Khalsa wrote:
Mac...good morningthat is a big battery bank!We have used the 
SBS Batteries for large battery banksThey offer multiple warranty 
options including upto 20 years.  They are tubular plates with clear 
outer cases which make the electrolyte levels really easy to monitor 
and fillThey come with insulated cell interconnects with testing 
ports, they offer seismic racking custom designed to fit your battery 
bank, as well as spill containment trays and acid neutralizer kits for 
the spill containment trays.  We have been very happy with their 
performance.  They offer a 2V FLA cell at 4000Ah @ the 20 hr rate. 
 They are a high quality product made in the USA and worth looking at.

Here is the link to their website.
http://www.sbsbattery.com/products-services/by-product/batteries/batteries-flooded-wet-cell-batteries/flooded-wet-cell-batteries-stt-series-flooded-2v-cell.html 


Additionally they offer hydrogen gas alarms for battery rooms.

I am curious - is this a solar integrated system, if so, what size 
array would be charging the batteries?

Good luck!

Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com http://www.oregonsolarworks.com
541-218-0201 m
541-299-0402 o


On Tue, Mar 11, 2014 at 8:05 AM, Ray Walters r...@solarray.com 
mailto:r...@solarray.com wrote:


Consider the HUP Solar One battery, the 125-33.  It has 2490 AH at
the 20 hr rate.   The warranty is for 2100 cycles to 80% DOD.
 Also most of the jumpers are included (bus bars within each 12 v
group)
We've had nothing but happy customers since we started using the HUPs.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760 tel:303%20505-8760


On 3/11/2014 8:01 AM, penobscotso...@midmaine.com
mailto:penobscotso...@midmaine.com wrote:

Mac, for this type of large system we typically use Surrette/Rolls
2YS31.They are 2430 ah. When we get into battery banks this
large we
typically only run two cells deep (front to back) for ease of
maintenance.
I hope your customer has some free time on their hands for
maintenance.
Remember, Surrette deep cycle batteries demand a higher than
most charge
rate or you will find the life of the cell will be
significantly shorter
than with proper charging. I'm sure your local battery
distributor or
Jamie Surrette can send you the tech stuff on these batteries.
Any way it
goes, this is a very big battery bank. Good luck!

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design



Good point Jason.  To clarify this is a 48V system.

Thanks


On Tue, Mar 11, 2014 at 7:44 AM, Jason Szumlanski
ja...@fafcosolar.com mailto:ja...@fafcosolar.comwrote:

Not that I have an answer for you, but I'm curious,
too. You need to
specify voltage to get a good answer.

Jason Szumlanski

Fafco Solar





On Tue, Mar 11, 2014 at 9:24 AM, Mac Lewis
maclew...@gmail.com mailto:maclew...@gmail.com wrote:

Hi wrenches,

I am consulting on a job that requires an 8000 Ahr
battery bank.  This
is
quite a bit beyond my normal battery bank realm.
 What would you
recommend
for this?

  Thanks in advance

--



Mac Lewis


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Change email address  settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
http://www.members.re-wrenches.org




--



Mac Lewis

*Yo solo sé que no sé nada. -Sócrates*

Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Allan Sindelar

  
  
Kirpal,
  I reviewed the link; thank you for this referral. I was surprised
  by the specified charge settings: while there's no bulk/absorption
  setting given, equalize is 2.33 - 2.40 vpc, or 53.5 - 57.6 v on a
  48 v bank. This is what I would expect with VRLA batteries, not
  flooded, as it's barely skirting the edge of the gassing range. Is
  this something specific to lead-selenium technology? Is it unique
  to the tubular positive plates? Is it specified for industrial
  (regular recharge from grid) as opposed to "opportunity charging"
  typical with PV? Please help us understand from your experience
  with them.
  Allan
  
  






  

  

  
  
  
Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified PV
Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder, Positive Energy, Inc.
A
Certified B CorporationTM
3209
Richards Lane
  Santa Fe, New Mexico 87507
505 424-1112 office 780-2738 cell
www.positiveenergysolar.com

  

  On 3/11/2014 9:26 AM, Kirpal Khalsa wrote:


  Mac...good morningthat is a big battery
bank!We have used the SBS Batteries for large battery
banksThey offer multiple warranty options including upto 20
years. They are tubular plates with clear outer cases which
make the electrolyte levels really easy to monitor and
fillThey come with insulated cell interconnects with testing
ports, they offer seismic racking custom designed to fit your
battery bank, as well as spill containment trays and acid
neutralizer kits for the spill containment trays. We have been
very happy with their performance. They offer a 2V FLA cell at
4000Ah @ the 20 hr rate. They are a high quality product made
in the USA and worth looking at. 

  Here is the link to their website. 
http://www.sbsbattery.com/products-services/by-product/batteries/batteries-flooded-wet-cell-batteries/flooded-wet-cell-batteries-stt-series-flooded-2v-cell.html
  

Additionally they offer hydrogen gas alarms for battery
  rooms.


I am curious - is this a solar integrated system, if so,
  what size array would be charging the batteries? 
Good luck!
  
  

  Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-299-0402 o



On Tue, Mar 11, 2014 at 8:05 AM, Ray
  Walters r...@solarray.com
  wrote:
  
Consider the HUP Solar One battery, the 125-33. It has 2490
AH at the 20 hr rate.  The warranty is for 2100 cycles to
80% DOD. Also most of the jumpers are included (bus bars
within each 12 v group)
We've had nothing but happy customers since we started using
the HUPs.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

  

On 3/11/2014 8:01 AM, penobscotso...@midmaine.com wrote:

  Mac, for this type of large system we typically use
  Surrette/Rolls
  2YS31.They are 2430 ah. When we get into battery banks
  this large we
  typically only run two cells deep (front to back) for
  ease of maintenance.
  I hope your customer has some free time on their hands
  for maintenance.
  Remember, Surrette deep cycle batteries demand a
  higher than most charge
  rate or you will find the life of the cell will be
  significantly shorter
  than with proper charging. I'm sure your local battery
  distributor or
  Jamie Surrette can send you the tech stuff on these
  batteries. Any way it
  goes, this is a very big battery bank. Good luck!
  
  Daryl DeJoy
 

Re: [RE-wrenches] Huge battery bank recommendation

2014-03-11 Thread Kirpal Khalsa
Ray.i do not have the link to the warrantyour salesman presented us
with a variety of options ranging from 5 years upto 20 years.just like
other manufacturers they had prorating levels with each option.If asked
i am sure they will provide you with any information you want in regards to
the warranty

Allan.yes in fact we were also surprised with the low voltage settings
that they specifyIn one system we installed a 3200Ah battery bank and
trying to coordinate the settings they specify with the programmable
settings offered in the Sunny Islands was an exercise in it selfThey
have different terminology than is common in most RE system charging
parametersmaking sure we were all talking about the same parameters was
the hardest factorIf i remember correctly the absorb and equalize
settings were almost the same per the manufacturer.
I could not tell you much about the lead -selenium technology or the
tubular positive plates with any expertise.
The large system we installed these batteries on was specified to use the
longest possible life span batteries  coupled with high cycling
capabilityAt the time they were the only company we could find willing
to put the 20 year warranty in writing apart from some sealed Unigy
batteries which were far more expensive..This was a AC coupled grid
interactive system and so the batteries are in standby 95%+ of the
timeWe have a contract to do routine maintenance on the system and have
only had to add water once per yeareven then it was not necessary but
to set it on course till the next time we are scheduled to inspect, 1 year
later.
The customer has had very few power outages but did have one for 4 days
last winter and the battery bank worked flawlesslyWe really like the
clear cases for quick electrolyte level monitoring.  The cells have flip
tops for easy access.
My overall take on these batteries is that they are primarily designed for
standby systems.  We haven't used them in an off grid configuration.  They
have been in for 3 years with no sign of aging...I think they are a company
that is only beginning to realize the possibility of the RE market and
havent focused much effort in that direction in the past
SBS was easy to work with, and provided good support for the seismic
racking and spill containment systemwith more documentation than i am
used to receiving from our main suppliers...
Hope that helps...
Cheers,



Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-299-0402 o


On Tue, Mar 11, 2014 at 8:42 AM, Ray Walters r...@solarray.com wrote:

  Hi Kirpal;

 I see that the SBS batteries are rated to 1200 cycles to 80% DOD, but I
 can't find the warranty on their website. Do you have a link to that?

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer303 505-8760

 On 3/11/2014 9:26 AM, Kirpal Khalsa wrote:

 Mac...good morningthat is a big battery bank!We have used the SBS
 Batteries for large battery banksThey offer multiple warranty options
 including upto 20 years.  They are tubular plates with clear outer cases
 which make the electrolyte levels really easy to monitor and fillThey
 come with insulated cell interconnects with testing ports, they offer
 seismic racking custom designed to fit your battery bank, as well as spill
 containment trays and acid neutralizer kits for the spill containment
 trays.  We have been very happy with their performance.  They offer a 2V
 FLA cell at 4000Ah @ the 20 hr rate.  They are a high quality product made
 in the USA and worth looking at.
 Here is the link to their website.

 http://www.sbsbattery.com/products-services/by-product/batteries/batteries-flooded-wet-cell-batteries/flooded-wet-cell-batteries-stt-series-flooded-2v-cell.html
  Additionally they offer hydrogen gas alarms for battery rooms.

  I am curious - is this a solar integrated system, if so, what size array
 would be charging the batteries?
 Good luck!

  Sunny Regards,
 Kirpal Khalsa
 NABCEP Certified PV Installation Professional
 Renewable Energy Systems
 www.oregonsolarworks.com
 541-218-0201 m
 541-299-0402 o


 On Tue, Mar 11, 2014 at 8:05 AM, Ray Walters r...@solarray.com wrote:

 Consider the HUP Solar One battery, the 125-33.  It has 2490 AH at the 20
 hr rate.   The warranty is for 2100 cycles to 80% DOD.  Also most of the
 jumpers are included (bus bars within each 12 v group)
 We've had nothing but happy customers since we started using the HUPs.

 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760


 On 3/11/2014 8:01 AM, penobscotso...@midmaine.com wrote:

 Mac, for this type of large system we typically use Surrette/Rolls
 2YS31.They are 2430 ah. When we get into battery banks this large we