Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-30 Thread William Miller
Dan:

Thanks very much for the detailed analysis.  So the short answer is that a
48 v micro-inverter will be compatible with either module.  I am old school
and like a little more head room than that, especially since we have not
learned yet if inverter damage will occur on overvoltage.  I am anxious to
try the Power One units.  Anyone else tried these yet?

William




-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Exeltech
Sent: Monday, September 30, 2013 6:01 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Using legacy modules on micro-inverters

William,

PV temperature coefficient of voltage is a function of the number of cells
in series.  For 72 cell PV (or two 36-cell PV in series), the coefficient is
2X that of 36 cells.

Two SP75 in series, in an ambient temperature environment of -10C, and
presuming a cell temperature of -10C at reduced light and a low solar
altitude to minimize cell heating, would exhibit nominally 45.4Voc, and
35.6Vmpp respectively.

Two SP75 in series, in an ambient temperature environment of  38C, and
presuming 1000 W/m^2 orthogonal to the PV module at solar noon, would yield
nominally 36.6Voc, and 28.7Vmpp respectively.

Nominal cell temperature under the latter circumstances would be 69.3C,
presuming a rooftop mount, 6-8" above the roof surface, with 1.5 m/s or less
wind speed, and perfectly orthogonal to the sun at solar zenith.


Two SQ150 under the identical cold ambient conditions would exhibit 44.4
Voc, and 34.8Vmpp.

Two SQ150 under the identical hot ambient conditions would exhibit 36.1Voc,
and 28.3Vmpp.

Nominal cell temperature for the SQ150 under the latter circumstances would
be 70.5C, with the same presumptions as above.


Very slight differences exist between two SP75 in series, and one SQ150, but
as you alluded to below, they're close enough to be considered essentially
identical.



Regards,



Dan



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-30 Thread Exeltech
William,

PV temperature coefficient of voltage is a function of the number of cells in 
series.  For 72 cell PV (or two 36-cell PV in series), the coefficient is 2X 
that of 36 cells.

Two SP75 in series, in an ambient temperature environment of -10C, and 
presuming a cell temperature of -10C at reduced light and a low solar altitude 
to minimize cell heating, would exhibit nominally 45.4Voc, and 35.6Vmpp 
respectively.

Two SP75 in series, in an ambient temperature environment of  38C, and 
presuming 1000 W/m^2 orthogonal to the PV module at solar noon, would yield 
nominally 36.6Voc, and 28.7Vmpp respectively.

Nominal cell temperature under the latter circumstances would be 69.3C, 
presuming a rooftop mount, 6-8" above the roof surface, with 1.5 m/s or less 
wind speed, and perfectly orthogonal to the sun at solar zenith.


Two SQ150 under the identical cold ambient conditions would exhibit 44.4 Voc, 
and 34.8Vmpp.

Two SQ150 under the identical hot ambient conditions would exhibit 36.1Voc, and 
28.3Vmpp.

Nominal cell temperature for the SQ150 under the latter circumstances would be 
70.5C, with the same presumptions as above.


Very slight differences exist between two SP75 in series, and one SQ150, but as 
you alluded to below, they're close enough to be considered essentially 
identical.



Regards,



Dan




On Mon, 9/30/13, William Miller  wrote:

Subject: Re: [RE-wrenches] Using legacy modules on micro-inverters
To: "'RE-wrenches'" 
Date: Monday, September 30, 2013, 2:24 PM
 
Nick:
What is the upper voltage limit for the M250?  What happens when that voltage 
is exceeded?

I am trying to use Siemens SP75 modules (two in series) and Shell SQ-150-PC. 
Below are the specs.  Note that two SP75s in series, if you multiply the 
voltages by two, is identical to the SQ-150 except for the temperature 
compensation.  I am not sure what to do with the temperature compensation value 
if I put two SP175s insereis.  Do you know?
  
Our record low is -10 C and average high is 38C.  If I enter the data for the 
Shell, the calculator shows they are compatible with the M250.  Entering the 
data for two SP75s using -0.077 for Temp Comp (SP75) the tool says not.  If I 
use double (-0.154), then the two SP75s are compatible.  What is your 
determination?

Thanks,
William
  
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil
 Sent: Monday, September 30, 2013 9:56 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Using legacy modules on micro-inverters

Hi wrenches,The M250 is not limited to 60 cell modules only.  The M250 has an 
expanded voltage window which will allow for it to be paired with a wider range 
of modules.  Enphase has an online module
compatibility calculator which can be used for checking a specific pairing in a 
specific location, at:
 
http://enphase.com/module-compatibility-calculator-m250-update/. 

Keep in mind that many of the high efficiency, higher voltage, 72 cell modules 
will not be compatible.



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-30 Thread Nick Soleil
Hi Wiliam,

The max voltage rating of the M250 is 48V.   When you ran the compatibility
checker, did you use 154mv/°C?  You can either input the mV/°C or the
%/°C.  You will need to be sure that you convert the 0.154 to 154mV.


On Mon, Sep 30, 2013 at 12:24 PM, William Miller wrote:

> Nick:
>
> ** **
>
> What is the upper voltage limit for the M250?  What happens when that
> voltage is exceeded?
>
> ** **
>
> I am trying to use Siemens SP75 modules (two in series) and Shell
> SQ-150-PC. Below are the specs.  Note that two SP75s in series, if you
> multiply the voltages by two, is identical to the SQ-150 except for the
> temperature compensation.  I am not sure what to do with the temperature
> compensation value if I put two SP175s insereis.  Do you know?
>
> ** **
>
> ** **
>
> *Qty*
>
> *Watts*
>
> *Ext*
>
> *Watts*
>
> *Pmax*
>
> *Vpmax*
>
> *Ipmax*
>
> *Isc*
>
> *Voc*
>
> *Temp Coefficient of Voc*
>
> Siemens PC4JF (Same as the SP75?)
>
> 12
>
> 75
>
> 900
>
> 75
>
> 75
>
> 17
>
> 4.4
>
> 4.8
>
> 21.7
>
> -0.077
>
> Shell SQ-150
>
> 3
>
> 150
>
> 450
>
> 150
>
> 150
>
> 34
>
> 4.4
>
> 4.8
>
> 43.4
>
> -0.161
>
> ** **
>
> Our record low is -10 C and average high is 38C.
>
> ** **
>
> If I enter the data for the Shell, the calculator shows they are
> compatible with the M250.  Entering the data for two SP75s using -0.077 for
> Temp Comp (SP75) the tool says not.  If I use double (-0.154), then the two
> SP75s are compatible.  What is your determination?
>
> ** **
>
> Thanks,****
>
> ** **
>
> William****
>
> ** **
>
> ** **
>
> ** **
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
> re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Nick Soleil
> *Sent:* Monday, September 30, 2013 9:56 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Using legacy modules on micro-inverters
>
> ** **
>
> Hi wrenches,
>
> The M250 is not limited to 60 cell modules only.  The M250 has an expanded
> voltage window which will allow for it to be paired with a wider range of
> modules.  Enphase has an online module compatibility calculator which can
> be used for checking a specific pairing in a specific location, at:
>
>  http://enphase.com/module-compatibility-calculator-m250-update/.  
>
> Keep in mind that many of the high efficiency, higher voltage, 72 cell
> modules will not be compatible.
>
> ** **
>
> ** **
>
> On Sat, Sep 28, 2013 at 6:45 AM, Jay Peltz  wrote:
>
> Hi Bill
>
> ** **
>
> Is there a new M250?
>
> Enphase shows the 250 at 48vdc max and states 60 cell only modules. 
>
> ** **
>
> That would be nice if it did both
>
> ** **
>
> Jay
>
> ** **
>
> Peltz power. 
>
> ** **
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

*
*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/>

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsol...@enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of the original message. 

<>___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-30 Thread William Miller
Nick:

 

What is the upper voltage limit for the M250?  What happens when that
voltage is exceeded?

 

I am trying to use Siemens SP75 modules (two in series) and Shell SQ-150-PC.
Below are the specs.  Note that two SP75s in series, if you multiply the
voltages by two, is identical to the SQ-150 except for the temperature
compensation.  I am not sure what to do with the temperature compensation
value if I put two SP175s insereis.  Do you know?

 

 


Qty

Watts

Ext

Watts

Pmax

Vpmax

Ipmax

Isc

Voc

Temp Coefficient of Voc


Siemens PC4JF (Same as the SP75?)

12

75

900

75

75

17

4.4

4.8

21.7

-0.077


Shell SQ-150

3

150

450

150

150

34

4.4

4.8

43.4

-0.161

 

Our record low is -10 C and average high is 38C.

 

If I enter the data for the Shell, the calculator shows they are compatible
with the M250.  Entering the data for two SP75s using -0.077 for Temp Comp
(SP75) the tool says not.  If I use double (-0.154), then the two SP75s are
compatible.  What is your determination?

 

Thanks,

 

William

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Soleil
Sent: Monday, September 30, 2013 9:56 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Using legacy modules on micro-inverters

 

Hi wrenches,

The M250 is not limited to 60 cell modules only.  The M250 has an expanded
voltage window which will allow for it to be paired with a wider range of
modules.  Enphase has an online module compatibility calculator which can be
used for checking a specific pairing in a specific location, at:

 http://enphase.com/module-compatibility-calculator-m250-update/.  

Keep in mind that many of the high efficiency, higher voltage, 72 cell
modules will not be compatible.

 

 

On Sat, Sep 28, 2013 at 6:45 AM, Jay Peltz  wrote:

Hi Bill

 

Is there a new M250?

Enphase shows the 250 at 48vdc max and states 60 cell only modules. 

 

That would be nice if it did both

 

Jay

 

Peltz power. 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-30 Thread Nick Soleil
Hi wrenches,

The M250 is not limited to 60 cell modules only.  The M250 has an expanded
voltage window which will allow for it to be paired with a wider range of
modules.  Enphase has an online module compatibility calculator which can
be used for checking a specific pairing in a specific location, at:

 http://enphase.com/module-compatibility-calculator-m250-update/.

Keep in mind that many of the high efficiency, higher voltage, 72 cell
modules will not be compatible.



On Sat, Sep 28, 2013 at 6:45 AM, Jay Peltz  wrote:

> Hi Bill
>
> Is there a new M250?
> Enphase shows the 250 at 48vdc max and states 60 cell only modules.
>
> That would be nice if it did both
>
> Jay
>
> Peltz power.
>
>
>
> Sent from my iPhone
>
> On Sep 27, 2013, at 10:14 AM, "Bill Brooks"  wrote:
>
> William,
>
> ** **
>
> Just to add one more thing. I said that the M215 does not match well, but
> if you have them on hand, they would still work. You will probably power
> limit in the spring and fall, but the rest of the year you will probably do
> fine. The M250 has a higher operating voltage for 72-cell arrangements. The
> M215 is more suited for 60-cell modules and circuits.
>
> ** **
>
> Bill.
>
> ** **
>
> ** **
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *William Miller
> *Sent:* Thursday, September 26, 2013 10:01 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Using legacy modules on micro-inverters
>
> ** **
>
> Friends:
>
> ** **
>
> I am trying to upgrade a long time off-grid client to a grid-connected
> installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.
> It is my understanding that putting two of the PC4JFs in series is exactly
> one SQ-150.  I don’t have spec sheets for the PC4JFs but I am told they are
> an SP75.  If I use the data for the SP75 and multiply the voltages by two I
> get exactly a SQ-150P.
>
> ** **
>
> Anyway, putting two 36 modules together makes one 72 cell module.  This
> would likely work with an Enphase M190 but those are no longer
> manufactured.  Same with the M215.  Power One makes a micro that meets the
> predicted voltage window.
>
> ** **
>
> I did this a while ago with pairs of SR100s.  It worked great.  Anyone try
> this with even older modules, like those cited???
>
> ** **
>
> Thanks in advance.
>
> ** **
>
> William Miller
>
> ** **
>
> ___
>
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 

Cordially,

*Nick Soleil*

*Field Applications Engineer
*

*Enphase Energy*

Mobile: (707) 321-2937


**

*Enphase Commercial Solar.*
*Limitless.*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

*
*<http://www.enphase.com/commercial?utm_source=email&utm_medium=sig&utm_campaign=Comm2012>

1420 North McDowell

Petaluma, CA 94954

www.enphase.com <http://www.enphaseenergy.com/>

P: (707) 763-4784 x7267

F: (707) 763-0784

E: nsol...@enphaseenergy.com

[image: nabcep logo] Certified Solar PV Installer #03262011-300

“Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion
to fission. And it just so happens that there’s an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it’s wireless! .”

- William McDonough



This email message is for the sole use of the intended recipient(s) and may 
contain confidential and/or privileged information. If you are not an intended 
recipient, you may not review, use, copy, disclose or distribute this message. 
If you received this message in error, please contact the sender by reply email 
and destroy all copies of

Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-28 Thread August Goers
All -

If you haven't already seen it, you might want to try playing with the
numbers on Enphase's online calculator:

http://enphase.com/module-compatibility-calculator-m250-update/

-August

*August Goers*

Principal

Luminalt Energy Corporation

o: 415.641.4000

m: 415.559.1525

www.luminalt.com




On Sat, Sep 28, 2013 at 6:45 AM, Jay Peltz  wrote:

> Hi Bill
>
> Is there a new M250?
> Enphase shows the 250 at 48vdc max and states 60 cell only modules.
>
> That would be nice if it did both
>
> Jay
>
> Peltz power.
>
>
>
> Sent from my iPhone
>
> On Sep 27, 2013, at 10:14 AM, "Bill Brooks"  wrote:
>
> William,
>
> ** **
>
> Just to add one more thing. I said that the M215 does not match well, but
> if you have them on hand, they would still work. You will probably power
> limit in the spring and fall, but the rest of the year you will probably do
> fine. The M250 has a higher operating voltage for 72-cell arrangements. The
> M215 is more suited for 60-cell modules and circuits.
>
> ** **
>
> Bill.
>
> ** **
>
> ** **
>
> *From:* re-wrenches-boun...@lists.re-wrenches.org [
> mailto:re-wrenches-boun...@lists.re-wrenches.org]
> *On Behalf Of *William Miller
> *Sent:* Thursday, September 26, 2013 10:01 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Using legacy modules on micro-inverters
>
> ** **
>
> Friends:
>
> ** **
>
> I am trying to upgrade a long time off-grid client to a grid-connected
> installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.
> It is my understanding that putting two of the PC4JFs in series is exactly
> one SQ-150.  I don’t have spec sheets for the PC4JFs but I am told they are
> an SP75.  If I use the data for the SP75 and multiply the voltages by two I
> get exactly a SQ-150P.
>
> ** **
>
> Anyway, putting two 36 modules together makes one 72 cell module.  This
> would likely work with an Enphase M190 but those are no longer
> manufactured.  Same with the M215.  Power One makes a micro that meets the
> predicted voltage window.
>
> ** **
>
> I did this a while ago with pairs of SR100s.  It worked great.  Anyone try
> this with even older modules, like those cited???
>
> ** **
>
> Thanks in advance.
>
> ** **
>
> William Miller
>
> ** **
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-28 Thread Jay Peltz
Hi Bill

Is there a new M250?
Enphase shows the 250 at 48vdc max and states 60 cell only modules. 

That would be nice if it did both

Jay

Peltz power. 



Sent from my iPhone

> On Sep 27, 2013, at 10:14 AM, "Bill Brooks"  wrote:
> 
> William,
>  
> Just to add one more thing. I said that the M215 does not match well, but if 
> you have them on hand, they would still work. You will probably power limit 
> in the spring and fall, but the rest of the year you will probably do fine. 
> The M250 has a higher operating voltage for 72-cell arrangements. The M215 is 
> more suited for 60-cell modules and circuits.
>  
> Bill.
>  
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
> Sent: Thursday, September 26, 2013 10:01 PM
> To: RE-wrenches
> Subject: [RE-wrenches] Using legacy modules on micro-inverters
>  
> Friends:
>  
> I am trying to upgrade a long time off-grid client to a grid-connected 
> installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.  
> It is my understanding that putting two of the PC4JFs in series is exactly 
> one SQ-150.  I don’t have spec sheets for the PC4JFs but I am told they are 
> an SP75.  If I use the data for the SP75 and multiply the voltages by two I 
> get exactly a SQ-150P.
>  
> Anyway, putting two 36 modules together makes one 72 cell module.  This would 
> likely work with an Enphase M190 but those are no longer manufactured.  Same 
> with the M215.  Power One makes a micro that meets the predicted voltage 
> window.
>  
> I did this a while ago with pairs of SR100s.  It worked great.  Anyone try 
> this with even older modules, like those cited???
>  
> Thanks in advance.
>  
> William Miller
>  
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-27 Thread Bill Brooks
William,

 

Just to add one more thing. I said that the M215 does not match well, but if
you have them on hand, they would still work. You will probably power limit
in the spring and fall, but the rest of the year you will probably do fine.
The M250 has a higher operating voltage for 72-cell arrangements. The M215
is more suited for 60-cell modules and circuits.

 

Bill.

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Thursday, September 26, 2013 10:01 PM
To: RE-wrenches
Subject: [RE-wrenches] Using legacy modules on micro-inverters

 

Friends:

 

I am trying to upgrade a long time off-grid client to a grid-connected
installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.
It is my understanding that putting two of the PC4JFs in series is exactly
one SQ-150.  I don't have spec sheets for the PC4JFs but I am told they are
an SP75.  If I use the data for the SP75 and multiply the voltages by two I
get exactly a SQ-150P.

 

Anyway, putting two 36 modules together makes one 72 cell module.  This
would likely work with an Enphase M190 but those are no longer manufactured.
Same with the M215.  Power One makes a micro that meets the predicted
voltage window.

 

I did this a while ago with pairs of SR100s.  It worked great.  Anyone try
this with even older modules, like those cited???

 

Thanks in advance.

 

William Miller

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-27 Thread Bill Brooks
William,

 

Here is what I would recommend. 

 

1.   Put pairs of SQ-150s in parallel on an M250. 

2.   Put PC4JFs as two in series by two in parallel on M250.

3.   For leftovers-two PC4JFs in series are the same as one SQ-150 so
mix and match to your heart's content.

 

The issue is either getting a paralleling cable for the MC3 connectors or
installing J-boxes with cable glands to parallel the sets. This is child's
play, but it is fun too. These are just mini PV arrays-no mystery here. You
will not overpower the M250 with this arrangement. These modules will have
lost 10-20% of their nameplate rating at STC (30% at real power) so no
problem with an M250. M215 just does not match well at all.

 

Bill.

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Thursday, September 26, 2013 10:01 PM
To: RE-wrenches
Subject: [RE-wrenches] Using legacy modules on micro-inverters

 

Friends:

 

I am trying to upgrade a long time off-grid client to a grid-connected
installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.
It is my understanding that putting two of the PC4JFs in series is exactly
one SQ-150.  I don't have spec sheets for the PC4JFs but I am told they are
an SP75.  If I use the data for the SP75 and multiply the voltages by two I
get exactly a SQ-150P.

 

Anyway, putting two 36 modules together makes one 72 cell module.  This
would likely work with an Enphase M190 but those are no longer manufactured.
Same with the M215.  Power One makes a micro that meets the predicted
voltage window.

 

I did this a while ago with pairs of SR100s.  It worked great.  Anyone try
this with even older modules, like those cited???

 

Thanks in advance.

 

William Miller

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Using legacy modules on micro-inverters

2013-09-26 Thread William Miller
Friends:

 

I am trying to upgrade a long time off-grid client to a grid-connected
installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.
It is my understanding that putting two of the PC4JFs in series is exactly
one SQ-150.  I don't have spec sheets for the PC4JFs but I am told they are
an SP75.  If I use the data for the SP75 and multiply the voltages by two I
get exactly a SQ-150P.

 

Anyway, putting two 36 modules together makes one 72 cell module.  This
would likely work with an Enphase M190 but those are no longer manufactured.
Same with the M215.  Power One makes a micro that meets the predicted
voltage window.

 

I did this a while ago with pairs of SR100s.  It worked great.  Anyone try
this with even older modules, like those cited???

 

Thanks in advance.

 

William Miller

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org