Re: [RE-wrenches] question about pole mount interconnection

2013-10-09 Thread Benn At DayStarSolar
William,
With Tech90 regardless of the conductor size it always comes with a bare #8 
included.  A 3 conductor #10 (aka 10/3) will have red, white, and black #10 
plus the bare#8. 
A four conductor will have red, white, black and blue. 

 I have only ever seen or been made aware by my suppliers that the bare is a 
#8, however would not be surprised if a different size bare could be ordered, 
if you were willing to pay extra and wait a bit longer. 

We typically pay $15-18ea for the outdoor rated tech connector, which are 
required outdoors for weatherproofing, however inspectors are fine with an 
indoor rated flex-connector ($2-3 bucks ea) where weather/moisture will not be 
an issue. 

For surface runs you may want to support it at more frequent intervals, 
especially on horizontal runs as it is not rigid and can look sloppy if not 
adequately supported. 

benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and 
typos. 

On 2013-10-08, at 9:40 PM, William Miller will...@millersolar.com wrote:

 Hilton:
 
 Can you get this cable with mixed wire gauges, i.e. 3 #10 (white and two
 colors) and 1 #8(green or bare)?
 
 How does this material look on surface runs?  Can you get it to run nice and
 straight?
 
 Thanks in advance.
 
 William
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Hilton Dier
 III
 Sent: Tuesday, October 08, 2013 4:28 PM
 To: re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] question about pole mount interconnection
 
 We just did a 4 pole installation using DPW top-of-pole mounts. We used
 Teck-90 armored watertight cable between the poles and from the poles to the
 house. The Teck-90 spiral wound metal flex conduit with an
 everything-resistant black sheath on it pre-stuffed with just about any
 combo of wires you might want. We cast 2 PVC sweeps into the 36 dia. 
 sonotubes so the cable could enter underground and come up next to the pole.
 We put PVC end caps on the tops of the sweeps with cable holes in them, just
 for neatness.
 
 Teck-90 is a revelation. We laid out and buried a double run of 100 feet of
 the stuff in the time it took the excavator to go along the trench. 
 He never got out of the cab. We get it on a 500' spool and mount the spool
 in the back of a pickup. Then we just run off however much we need, cut it
 to length, and throw dirt on it.
 
 We got it from Graybar for slightly less than the price per foot of the
 equivalent wire and PVC conduit. I had been meaning to write a post on here
 about it.
 
 We also just did PV on a barn roof and did the spool-it-off-and-clip-it-up
 routine. Made the run from the roof to the inverter on the north side first
 floor in about 40 minutes. No conduit bending. The end connectors are kind
 of pricey, but the time saved is huge.
 
 Hilton
 
 --
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 -
 No virus found in this message.
 Checked by AVG - www.avg.com
 Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13
 
 -
 No virus found in this message.
 Checked by AVG - www.avg.com
 Version: 2014.0.4142 / Virus Database: 3604/6722 - Release Date: 10/04/13
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-09 Thread Benn At DayStarSolar
I would like to retract the part of my last post on this thread where I was 
referring to the bare conductor size. My bad, I wasn't thinking clearly when 
writing that last email. Lots of numbers in my head today. A #8 bare with #10 
conductors is way out to lunch :/
The bare conductors are indeed always included and are available in different 
sizes, to an extent. 

benn
Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts and 
typos. 

On 2013-10-09, at 1:31 PM, Benn At DayStarSolar b...@daystarsolar.ca wrote:

 William,
 With Tech90 regardless of the conductor size it always comes with a bare #8 
 included.  A 3 conductor #10 (aka 10/3) will have red, white, and black #10 
 plus the bare#8. 
 A four conductor will have red, white, black and blue. 
 
 I have only ever seen or been made aware by my suppliers that the bare is a 
 #8, however would not be surprised if a different size bare could be ordered, 
 if you were willing to pay extra and wait a bit longer. 
 
 We typically pay $15-18ea for the outdoor rated tech connector, which are 
 required outdoors for weatherproofing, however inspectors are fine with an 
 indoor rated flex-connector ($2-3 bucks ea) where weather/moisture will not 
 be an issue. 
 
 For surface runs you may want to support it at more frequent intervals, 
 especially on horizontal runs as it is not rigid and can look sloppy if not 
 adequately supported. 
 
 benn
 Sent from a 'smart' phone, with touch screen keys. Please excuse shortcuts 
 and typos. 
 
 On 2013-10-08, at 9:40 PM, William Miller will...@millersolar.com wrote:
 
 Hilton:
 
 Can you get this cable with mixed wire gauges, i.e. 3 #10 (white and two
 colors) and 1 #8(green or bare)?
 
 How does this material look on surface runs?  Can you get it to run nice and
 straight?
 
 Thanks in advance.
 
 William
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Hilton Dier
 III
 Sent: Tuesday, October 08, 2013 4:28 PM
 To: re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] question about pole mount interconnection
 
 We just did a 4 pole installation using DPW top-of-pole mounts. We used
 Teck-90 armored watertight cable between the poles and from the poles to the
 house. The Teck-90 spiral wound metal flex conduit with an
 everything-resistant black sheath on it pre-stuffed with just about any
 combo of wires you might want. We cast 2 PVC sweeps into the 36 dia. 
 sonotubes so the cable could enter underground and come up next to the pole.
 We put PVC end caps on the tops of the sweeps with cable holes in them, just
 for neatness.
 
 Teck-90 is a revelation. We laid out and buried a double run of 100 feet of
 the stuff in the time it took the excavator to go along the trench. 
 He never got out of the cab. We get it on a 500' spool and mount the spool
 in the back of a pickup. Then we just run off however much we need, cut it
 to length, and throw dirt on it.
 
 We got it from Graybar for slightly less than the price per foot of the
 equivalent wire and PVC conduit. I had been meaning to write a post on here
 about it.
 
 We also just did PV on a barn roof and did the spool-it-off-and-clip-it-up
 routine. Made the run from the roof to the inverter on the north side first
 floor in about 40 minutes. No conduit bending. The end connectors are kind
 of pricey, but the time saved is huge.
 
 Hilton
 
 --
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 -
 No virus found in this message.
 Checked by AVG - www.avg.com
 Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13
 
 -
 No virus found in this message.
 Checked by AVG - www.avg.com
 Version: 2014.0.4142 / Virus Database: 3604/6722 - Release Date: 10/04/13
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re

Re: [RE-wrenches] question about pole mount interconnection

2013-10-09 Thread William Miller
Benn:

Thanks for the prompt correction, and no harm done, except for to dash my
hopes!  No to worry, I knew it was too good to be true.  The concept of
running #8 ground with 20 or 30 amp circuits is now and always has always
been ludicrous.  Oh well...

William




-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Benn At
DayStarSolar
Sent: Wednesday, October 09, 2013 12:43 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] question about pole mount interconnection

I would like to retract the part of my last post on this thread where I was
referring to the bare conductor size. My bad, I wasn't thinking clearly when
writing that last email. Lots of numbers in my head today. A #8 bare with
#10 conductors is way out to lunch :/ The bare conductors are indeed always
included and are available in different sizes, to an extent. 

benn

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread Ron Young
Always value the input of the group William, that's why I ask for it but I 
admit I am leaning towards the conduit between poles idea. What has your 
practice been? Kirpal, your points are valid aside from cost which is the big 
nut to crack these days it seems. Ray, would love to have gone multi-pole, 
wasn't aware of those - alas, the single pole mounts are already enroute. 

Ron

On 2013-10-07, at 8:32 PM, William Miller will...@millersolar.com wrote:

 Ron:
 
 Sounds like you have already reached a conclusion.  Good luck!
 
 William
 
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron @
 earthRight Solar
 Sent: Monday, October 07, 2013 8:08 PM
 To: RE-wrenches
 Subject: [RE-wrenches] question about pole mount interconnection
 
 Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied system.
 My question is about preference for cable run between the poles. I am
 interested in industry best practices. I have been told that running conduit
 between the poles, i.e. along the axis, will hold the cabling but the poles
 of course must be precisely aligned. The alternative is to run cabling down
 the poles, underground and up the next pole. This is wasteful of materials,
 expensive to the client and in my view presents as many safety concerns as
 the other option. Hope to hear some ideas.
 
 Ron
 _
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread penobscotsolar
Ron,
   We also install a lot of top of pole mounts and use conduit similar to
what Kirpal describes. We typically will trench and install the conduit
before we pour the concrete foundations (at least to the elbow at the
pole) as it allows for conduit to sweep up the pole instead of having
to come out of the ground and over the top of the concrete before you
sweep up. That is all I would add. We always go pole to pole with
conduit.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design



 Always value the input of the group William, that's why I ask for it but I
 admit I am leaning towards the conduit between poles idea. What has your
 practice been? Kirpal, your points are valid aside from cost which is the
 big nut to crack these days it seems. Ray, would love to have gone
 multi-pole, wasn't aware of those - alas, the single pole mounts are
 already enroute.

 Ron

 On 2013-10-07, at 8:32 PM, William Miller will...@millersolar.com wrote:

 Ron:

 Sounds like you have already reached a conclusion.  Good luck!

 William


 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron @
 earthRight Solar
 Sent: Monday, October 07, 2013 8:08 PM
 To: RE-wrenches
 Subject: [RE-wrenches] question about pole mount interconnection

 Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied
 system.
 My question is about preference for cable run between the poles. I am
 interested in industry best practices. I have been told that running
 conduit
 between the poles, i.e. along the axis, will hold the cabling but the
 poles
 of course must be precisely aligned. The alternative is to run cabling
 down
 the poles, underground and up the next pole. This is wasteful of
 materials,
 expensive to the client and in my view presents as many safety concerns
 as
 the other option. Hope to hear some ideas.

 Ron
 _

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread Chris Worcester
Hi Ron,
We do a lot of pole mounts, last one was 12' to the bottom of modules, deep
snow country. Typically in a system where there are or has the potential to
expand into more than the original pole mounted array we run a couple of
main PVC conduits underground to a concrete vault, like a C-9, C-24, or
maybe even a C-30 vault. From this vault we distribute the conduits to each
pole mount, or in a larger field like the 8 poles you're mentioning we might
go into a second vault closer to the other end of the field, then branch out
to each pole from it too. We use PVC underground, Rigid metal through the
concrete and up the pole. Hope this helps.

Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Office 530-582-4503
Cell 530-448-9692
Fax 530-582-4603
www.solarwindworks.com
ch...@solarwindworks.com

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
penobscotso...@midmaine.com
Sent: Tuesday, October 08, 2013 5:24 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] question about pole mount interconnection

Ron,
   We also install a lot of top of pole mounts and use conduit similar to
what Kirpal describes. We typically will trench and install the conduit
before we pour the concrete foundations (at least to the elbow at the
pole) as it allows for conduit to sweep up the pole instead of having to
come out of the ground and over the top of the concrete before you sweep up.
That is all I would add. We always go pole to pole with conduit.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design



 Always value the input of the group William, that's why I ask for it 
 but I admit I am leaning towards the conduit between poles idea. What 
 has your practice been? Kirpal, your points are valid aside from cost 
 which is the big nut to crack these days it seems. Ray, would love to 
 have gone multi-pole, wasn't aware of those - alas, the single pole 
 mounts are already enroute.

 Ron

 On 2013-10-07, at 8:32 PM, William Miller will...@millersolar.com wrote:

 Ron:

 Sounds like you have already reached a conclusion.  Good luck!

 William


 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron @ 
 earthRight Solar
 Sent: Monday, October 07, 2013 8:08 PM
 To: RE-wrenches
 Subject: [RE-wrenches] question about pole mount interconnection

 Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied 
 system.
 My question is about preference for cable run between the poles. I am 
 interested in industry best practices. I have been told that running 
 conduit between the poles, i.e. along the axis, will hold the cabling 
 but the poles of course must be precisely aligned. The alternative is 
 to run cabling down the poles, underground and up the next pole. This 
 is wasteful of materials, expensive to the client and in my view 
 presents as many safety concerns as the other option. Hope to hear 
 some ideas.

 Ron
 _

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread Richard L Ratico
Ron, 
How do you propose to support the conduit between the poles should you run it
above grade? At what height above grade? What type of conduit? You say you are
interested in the industry best practice. Speaking as an licensed electrician
with 20 years experience, there's no question in my mind that underground
conduit, installed as described by the other wrenches responding thus far to
your question is the best practice. Maybe you'll find a way to reinvent the
wheel. Please keep us posted on your project.

Dick Ratico
Solarwind Electric


--- You wrote:
Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied system. My
question is about preference for cable run between the poles. I am interested in
industry best practices. I have been told that running conduit between the
poles, i.e. along the axis, will hold the cabling but the poles of course must
be precisely aligned. The alternative is to run cabling down the poles,
underground and up the next pole. This is wasteful of materials, expensive to
the client and in my view presents as many safety concerns as the other option.
Hope to hear some ideas.

Ron
--- end of quote ---
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread Kirpal Khalsa
Chrisi like your design with the vaults!  Future proof! Do you make
your transition to rigid metal conduit in the concrete?  Seems solid!
Thanks for sharing...

Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o


On Tue, Oct 8, 2013 at 10:24 AM, Chris Worcester
ch...@solarwindworks.comwrote:

 Hi Ron,
 We do a lot of pole mounts, last one was 12' to the bottom of modules, deep
 snow country. Typically in a system where there are or has the potential to
 expand into more than the original pole mounted array we run a couple of
 main PVC conduits underground to a concrete vault, like a C-9, C-24, or
 maybe even a C-30 vault. From this vault we distribute the conduits to each
 pole mount, or in a larger field like the 8 poles you're mentioning we
 might
 go into a second vault closer to the other end of the field, then branch
 out
 to each pole from it too. We use PVC underground, Rigid metal through the
 concrete and up the pole. Hope this helps.

 Chris Worcester
 Solar Wind Works
 NABCEP Certified PV Installer
 Office 530-582-4503
 Cell 530-448-9692
 Fax 530-582-4603
 www.solarwindworks.com
 ch...@solarwindworks.com



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread William Miller
Ron:

If you are convinced a putting cabling underground is wasteful, then I am
curious, why even consider it as an option?  It kind of seems like your mind
is made up.

William

PS:  Our practice?  We don't run wire, unconduited or conduited through the
air or between independently moveable objects.  We put the wire in conduit
and put it in the ground.  I keeps the wire from being damaged and
electrocuting someone.  I know, it seems like a waste.

Wm


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron Young
Sent: Monday, October 07, 2013 11:17 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] question about pole mount interconnection

Always value the input of the group William, that's why I ask for it but I
admit I am leaning towards the conduit between poles idea. What has your
practice been? 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] question about pole mount interconnection

2013-10-08 Thread Hilton Dier III
We just did a 4 pole installation using DPW top-of-pole mounts. We used 
Teck-90 armored watertight cable between the poles and from the poles to 
the house. The Teck-90 spiral wound metal flex conduit with an 
everything-resistant black sheath on it pre-stuffed with just about any 
combo of wires you might want. We cast 2 PVC sweeps into the 36 dia. 
sonotubes so the cable could enter underground and come up next to the 
pole. We put PVC end caps on the tops of the sweeps with cable holes in 
them, just for neatness.


Teck-90 is a revelation. We laid out and buried a double run of 100 feet 
of the stuff in the time it took the excavator to go along the trench. 
He never got out of the cab. We get it on a 500' spool and mount the 
spool in the back of a pickup. Then we just run off however much we 
need, cut it to length, and throw dirt on it.


We got it from Graybar for slightly less than the price per foot of the 
equivalent wire and PVC conduit. I had been meaning to write a post on 
here about it.


We also just did PV on a barn roof and did the 
spool-it-off-and-clip-it-up routine. Made the run from the roof to the 
inverter on the north side first floor in about 40 minutes. No conduit 
bending. The end connectors are kind of pricey, but the time saved is huge.


Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread RM You
I use Teck a lot in my off-grid installations and I agree it is very cost 
effective and safe. It was originally designed for mining application and can 
even lay on top of the ground with vehicle traffic if necessary although I 
wouldn't recommend it as a practice. Two to three feet of supported Teck 90 
between pole mounts is easily as safe as Teck 90 or conduited wire running down 
a pole then up the next and down, then up the next. I can think of scenarios 
where idiots could find a way to defeat either practice and electrocute 
themselves (William) but maybe that's just Darwin coming to the rescue. 

I'm still weighing the pros  cons but it's been a useful discussion for the 
most part, I respect and value the depth of knowledge here as being a small 
operator I don't get the opportunity to get nearly the experience represented. 
Thank you all!

Ron Young

On 2013-10-08, at 4:28 PM, Hilton Dier III hiltond...@gmail.com wrote:

 We just did a 4 pole installation using DPW top-of-pole mounts. We used 
 Teck-90 armored watertight cable between the poles and from the poles to the 
 house. The Teck-90 spiral wound metal flex conduit with an 
 everything-resistant black sheath on it pre-stuffed with just about any combo 
 of wires you might want. We cast 2 PVC sweeps into the 36 dia. sonotubes so 
 the cable could enter underground and come up next to the pole. We put PVC 
 end caps on the tops of the sweeps with cable holes in them, just for 
 neatness.
 
 Teck-90 is a revelation. We laid out and buried a double run of 100 feet of 
 the stuff in the time it took the excavator to go along the trench. He never 
 got out of the cab. We get it on a 500' spool and mount the spool in the back 
 of a pickup. Then we just run off however much we need, cut it to length, and 
 throw dirt on it.
 
 We got it from Graybar for slightly less than the price per foot of the 
 equivalent wire and PVC conduit. I had been meaning to write a post on here 
 about it.
 
 We also just did PV on a barn roof and did the spool-it-off-and-clip-it-up 
 routine. Made the run from the roof to the inverter on the north side first 
 floor in about 40 minutes. No conduit bending. The end connectors are kind of 
 pricey, but the time saved is huge.
 
 Hilton
 
 -- 
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread William Miller
Hilton:

Can you get this cable with mixed wire gauges, i.e. 3 #10 (white and two
colors) and 1 #8(green or bare)?

How does this material look on surface runs?  Can you get it to run nice and
straight?

Thanks in advance.

William
 
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Hilton Dier
III
Sent: Tuesday, October 08, 2013 4:28 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] question about pole mount interconnection

We just did a 4 pole installation using DPW top-of-pole mounts. We used
Teck-90 armored watertight cable between the poles and from the poles to the
house. The Teck-90 spiral wound metal flex conduit with an
everything-resistant black sheath on it pre-stuffed with just about any
combo of wires you might want. We cast 2 PVC sweeps into the 36 dia. 
sonotubes so the cable could enter underground and come up next to the pole.
We put PVC end caps on the tops of the sweeps with cable holes in them, just
for neatness.

Teck-90 is a revelation. We laid out and buried a double run of 100 feet of
the stuff in the time it took the excavator to go along the trench. 
He never got out of the cab. We get it on a 500' spool and mount the spool
in the back of a pickup. Then we just run off however much we need, cut it
to length, and throw dirt on it.

We got it from Graybar for slightly less than the price per foot of the
equivalent wire and PVC conduit. I had been meaning to write a post on here
about it.

We also just did PV on a barn roof and did the spool-it-off-and-clip-it-up
routine. Made the run from the roof to the inverter on the north side first
floor in about 40 minutes. No conduit bending. The end connectors are kind
of pricey, but the time saved is huge.

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4142 / Virus Database: 3604/6704 - Release Date: 09/27/13

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4142 / Virus Database: 3604/6722 - Release Date: 10/04/13

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-08 Thread Chris Worcester
Hi Kirpal,

We do go to Sch 80 PVC into the concrete to a rigid steel (RMC) sweep 90,
then up the pole with the RMC to the disco. We run  Sch 40 PVC underground,
unless we are going under a road or through a lot of rock, then it's back to
the Sch 80. We also run a #4 bare solid copper next to the conduit, more
earth contact the better, it is nice to set the ground rod in the vault too.
Then you tie off to it with future arrays also, easily. 

 

Chris Worcester

Solar Wind Works

NABCEP Certified PV Installer

Office 530-582-4503

Cell 530-448-9692

Fax 530-582-4603

www.solarwindworks.com

ch...@solarwindworks.com

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal
Khalsa
Sent: Tuesday, October 08, 2013 2:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] question about pole mount interconnection

 

Chrisi like your design with the vaults!  Future proof! Do you make your
transition to rigid metal conduit in the concrete?  Seems solid!

Thanks for sharing...




Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o

 

On Tue, Oct 8, 2013 at 10:24 AM, Chris Worcester ch...@solarwindworks.com
wrote:

Hi Ron,
We do a lot of pole mounts, last one was 12' to the bottom of modules, deep
snow country. Typically in a system where there are or has the potential to
expand into more than the original pole mounted array we run a couple of
main PVC conduits underground to a concrete vault, like a C-9, C-24, or
maybe even a C-30 vault. From this vault we distribute the conduits to each
pole mount, or in a larger field like the 8 poles you're mentioning we might
go into a second vault closer to the other end of the field, then branch out
to each pole from it too. We use PVC underground, Rigid metal through the
concrete and up the pole. Hope this helps.

Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Office 530-582-4503
Cell 530-448-9692
Fax 530-582-4603
www.solarwindworks.com
ch...@solarwindworks.com



 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] question about pole mount interconnection

2013-10-07 Thread Ron @ earthRight Solar
Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied system. My 
question is about preference for cable run between the poles. I am interested 
in industry best practices. I have been told that running conduit between the 
poles, i.e. along the axis, will hold the cabling but the poles of course must 
be precisely aligned. The alternative is to run cabling down the poles, 
underground and up the next pole. This is wasteful of materials, expensive to 
the client and in my view presents as many safety concerns as the other option. 
Hope to hear some ideas.

Ron
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-07 Thread William Miller
Ron:

Sounds like you have already reached a conclusion.  Good luck!

William


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ron @
earthRight Solar
Sent: Monday, October 07, 2013 8:08 PM
To: RE-wrenches
Subject: [RE-wrenches] question about pole mount interconnection

Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied system.
My question is about preference for cable run between the poles. I am
interested in industry best practices. I have been told that running conduit
between the poles, i.e. along the axis, will hold the cabling but the poles
of course must be precisely aligned. The alternative is to run cabling down
the poles, underground and up the next pole. This is wasteful of materials,
expensive to the client and in my view presents as many safety concerns as
the other option. Hope to hear some ideas.

Ron
_

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-07 Thread Kirpal Khalsa
Ronwe do a lot of pole mount installations and we always run down each
pole and up the nextschedule 80 pvc conduit and a junction box at the
top.  It is solid, and should last as long as the array---at least 25+
yearsobviously to do this right the conduit should be installed prior
to the concrete as it then comes up vertically right along the
pole.definitely takes a bit longer to set up but you can be assured
that it is going to last for the long hauladditionally if you are ever
going to have the arrays adjustable on the top of pole mounts it will be
tricky to adjust if the cabling is in free air spanning from one sub array
to the next.as each array will be dependent on the positioning of the
other
Good luck


Sunny Regards,
Kirpal Khalsa
NABCEP Certified PV Installation Professional
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o


On Mon, Oct 7, 2013 at 8:08 PM, Ron @ earthRight Solar 
solarea...@solareagle.com wrote:

 Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied
 system. My question is about preference for cable run between the poles. I
 am interested in industry best practices. I have been told that running
 conduit between the poles, i.e. along the axis, will hold the cabling but
 the poles of course must be precisely aligned. The alternative is to run
 cabling down the poles, underground and up the next pole. This is wasteful
 of materials, expensive to the client and in my view presents as many
 safety concerns as the other option. Hope to hear some ideas.

 Ron
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] question about pole mount interconnection

2013-10-07 Thread Ray Walters
That's too many separate  poles, they get to be a real hassle at more 
than two (and costly too).  I'd go to a multipole mount arrangement, 
(here's 
one:http://www.dpwsolar.com/index.php/applications/commercial/9-commercial/17-multi-pole-mounts-g2-mpm-g2
and then all your cabling won't have to jump up and down, it can just 
run the length of the array framing.  This is more how all large ground 
mount systems are going these days.  Otherwise, you need to bring all 
the poles into a centrally located combiner, possibly at one of the poles.


R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 10/7/2013 9:08 PM, Ron @ earthRight Solar wrote:

Hi Wrenches, I am installing six 8 panel pole mounts in a grid tied system. My 
question is about preference for cable run between the poles. I am interested 
in industry best practices. I have been told that running conduit between the 
poles, i.e. along the axis, will hold the cabling but the poles of course must 
be precisely aligned. The alternative is to run cabling down the poles, 
underground and up the next pole. This is wasteful of materials, expensive to 
the client and in my view presents as many safety concerns as the other option. 
Hope to hear some ideas.

Ron
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org