Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-26 Thread Hugh
In an ideal world they are only hot relative to the other.  In the 
real world there will be leakage and also faults that connect one or 
other pole to the grounding system.  So then the other pole will 
thereby become hot.  So, again, they are both potentially hot.  And 
both therefore need to be fused, switched, etc...



If neither pole is grounded then both must be treated as potentially hot.

Only with regard to the other hot wire. If you do not reference one 
conductor to ground than the other one will not present any danger 
unless you are referenced to its mate... as in touching both wires 
at once.


Todd

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



--
Hugh Piggott

Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-25 Thread toddcory
If neither pole is grounded then both must be treated aspotentially hot.

Only with regard to the other hot wire. If you do not reference one conductor 
to ground than the other one will not present any danger unless you are 
referenced to its mate... as in touching both wires at once.

Todd___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-25 Thread Matt Tritt

Yay, Ray,

That's what I like to hear!

Matt T

R. Walters wrote:

I've worked on supposedly ungrounded high voltage systems on Electric 
vehicles. Got zapped when I touched the frame and a battery terminal. 
There definitely can be mA of leakage to ground, even if its not 
supposed to be there. Otherwise I welcome the move to ungrounded DC. 
Gee, red is positive, black for negative color coding is actually NEC 
compliant on an ungrounded system.


R. Walters
Solarray.com
NABCEP # 04170442



On Jul 25, 2009, at 10:03 AM, boB Gudgel wrote:


toddc...@finestplanet.com mailto:toddc...@finestplanet.com wrote:

If neither pole is grounded then both must be treated as 
potentially hot.


_Only with regard to the other hot wire._ If you do not reference 
one conductor to ground than the other one will not present any 
danger unless you are referenced to its mate... as in touching both 
wires at once.


Todd


Except of course, if there is more leakage (capacitive) from one 
ungrounded wire to ground than the other ungrounded wire to
ground.   You may still feel a tingle... The higher the voltage, 
given similar leakage, the higher the tingleage. (is that a real word?)
I am more apprehensive about touching ungrounded and live things 
(although sometimes I do). People have a larger area and

therefore a higher capacitance than birds do.

This applies for AC (mainly) of course.

boB


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org 
mailto:RE-wrenches@lists.re-wrenches.org


Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 





No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.5.392 / Virus Database: 270.13.29/2260 - Release Date: 07/25/09 01:48:00


 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-24 Thread Todd Cory




I have heard that this
requirement (to bond negative to ground) as well as bonding one of the
AC conductors to ground (neutral wire) was pushed through by wire
manufactures and unions. The wire manus sell more of their product and
the electricians get more labor in installing them. I also agree that
grounding any live conductor actually makes the system less safe.

When I have traveled over seas, I always try to open the main panel to
see how things are laid out. They never associate one of their power
conductors (usually 240 v) to ground.

Todd


Matt Tritt wrote:

  
As long as we're already on the subject, BESIDE the NEC requiring it,
why is it that we have to bond the ungrounded conductor on the battery
side of a DC system??? I believe that we are the only country in the
world that has this requirement. As long as all the system cabinets,
mounting plates, housings and etc are grounded, what is gained by
including a battery conductor? I'm not talking about HV inputs from an
array, just the battery busses.
  
I have been asking this question since forever, and the only
explanation seems to be the recital of the Code. Obvious problems can
occur when there is a + grounded piece of equipment in the mix, since -
well, it's obvious.
  
Matt T








___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-24 Thread toddcory
 Re: [RE-wrenches] Fwd: Grounding on aglacier
My understanding is that it saves cost to ground one of theconductors.  Then 
you can use single pole switches, fuses andbreakers.  If both of the circuit 
conductors are 'hot' then youwill need to use double pole everywhere.

Why? A single pole switch will stop the current regardless of whether one of 
the conductors is referenced to ground or not.


You can test whether the neutral is grounded quite easily with amultimeter.  I 
believe that everyone does ground it. Everywhere that I ask it turns out that 
it's been grounded.  Herewe lately have a new wiring system called Protective 
Multiple Earthingwhere the ground and neutral are combined into one wire 
(saving oncost).  This has the interesting side effect that the whole housewill 
become 'hot' in the event of a failure of this oneconductor.
And here, if you lose the ground/neutral, you have 240v on 120 circuits.

Todd___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-23 Thread Larry Crutcher, Starlight Solar

Hi Jay,

An interesting quandary indeed. My thoughts are to build a grid of  
radials with short ground rods at the ends, extending in all  
directions from the equipment. This approach does not use anything but  
wire, short ground rods and ground connectors so there is no equipment  
to fail or replace.


You have very low conductivity on the ice so static builds up. What  
you are trying to do is increase conductivity by equalizing  
(neutralize) the potential in the area around the communications gear.  
This is not really a grounding system but an effort to force all  
electrons to neutral in the immediate area. You want as many radials  
as possible in all directions from the comm gear. Make the radials as  
long as is practical but don't sacrifice number of radials for length,  
i.e. more is better. If you can leave materials behind, grow the  
radial network each time you have opportunity to bring in more material.


For SURE you want to bond all equipment together and test these bonds  
with a megohm meter to make sure they are potentially the same. Then  
attach the equipment stack to your radial system and megohm that bond.  
Use as wide a copper material as you can carry in.


If your problem is human contact, make sure you discharge to the  
radial network and bond yourself before touching any equipment. You  
can use a static wrist strap. A surge suppressor is useless if it has  
no ground reference to conduct to so I would not pursue that approach.


Example of radial system for RF purposes: 
http://harvesting.com/tower/photos/radials.jpg

That's my best guess on a solution. Let me know if you try this.

Kindest Regards,

Larry Crutcher
Starlight Solar
(928) 941-1660
Renewable Energy Products, Service and Installation

Mailing Address (NO SHIPPING):
11881 S Fortuna Rd.
#210
Yuma, AZ 85367

Shipping and retail store (NO MAIL):
2998 Shari Ave
Yuma, AZ 85365



On Jul 22, 2009, at 7:13 AM, jason pozner wrote:





Hey all,

I am trying to figure out how to mitigate problems found with a 12v  
500w simple DC system without a ground.  This system is at 14,500'  
on Denali (Mt McKinly).  We experienced a somewhat festive  
fireworks display on the 4th of July as static current from a storm  
seemed to travel through one of the antennae, and energized some  
radio equipment.  There is no grounded conductor, as there is no  
grounding electrode, as there is no ground to put it in.  The camp  
is situated on about 500' of glacial ice.  The conductivity of the  
ice is questionable, and to make the puzzle a bit more fun the camp  
is raised and taken down at the beginning and end of every climbing  
season (Apr-July), though the site is the same.  The loads are  
primarily for communications for search and rescue purposes, and   
reliability, and simplicity are paramount.  I have been exploring  
the avenue of a surge arrestorsThanks, and was wondering if any of  
you could make a recommendation on a product that can either be  
reset or cheap enough to have a few replacements on hand.   
Everything is flown in or carried to the site, and repair/ 
replacement needs to be simple enough so non-technical minded  
personnel can perform and re-set the system.


Thanks,

Jay Pozner
Nunatak Alternative Energy Solutions
Crested Butte, CO
(970) 349-3432
nunatakene...@gmail.com





--
Nunatak Alternative Energy Solutions
Jay Pozner and Lena Wilensky
(970)349-3432
www.nunatakenergy.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-23 Thread boB Gudgel

Larry Crutcher, Starlight Solar wrote:

Hi Jay,

An interesting quandary indeed.


This is another good example of an application that I was trying to 
grill Sunpower about --- as far as grounding their modules that need to 
be positive grounded
in order to take advantage of their higher efficiencies.   They couldn't 
answer this simple question.  How would you use one in an airplanefor 
instance ?
There are solar powered airplanes (sort  of)   Is a large faraday shield 
enough ?   Sort of like the ground radials that Larry has mentioned.  I 
would
imagine that if you get large enough radials that it ~might~ approach 
being a virtual ground. Works for antennas though.


I like questions like this one.  Sure makes one think a bit.

boB




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-23 Thread Matt Tritt
As long as we're already on the subject, BESIDE the NEC requiring it, 
why is it that we have to bond the ungrounded conductor on the battery 
side of a DC system??? I believe that we are the only country in the 
world that has this requirement. As long as all the system cabinets, 
mounting plates, housings and etc are grounded, what is gained by 
including a battery conductor? I'm not talking about HV inputs from an 
array, just the battery busses.


I have been asking this question since forever, and the only explanation 
seems to be the recital of the Code. Obvious problems can occur when 
there is a + grounded piece of equipment in the mix, since - well, it's 
obvious.


Matt T

boB Gudgel wrote:


Larry Crutcher, Starlight Solar wrote:


Hi Jay,

An interesting quandary indeed.



This is another good example of an application that I was trying to 
grill Sunpower about --- as far as grounding their modules that need 
to be positive grounded
in order to take advantage of their higher efficiencies.   They 
couldn't answer this simple question.  How would you use one in an 
airplanefor instance ?
There are solar powered airplanes (sort  of)   Is a large faraday 
shield enough ?   Sort of like the ground radials that Larry has 
mentioned.  I would
imagine that if you get large enough radials that it ~might~ approach 
being a virtual ground. Works for antennas though.


I like questions like this one.  Sure makes one think a bit.

boB




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 8.5.392 / Virus Database: 270.13.25/2256 - Release Date: 07/23/09 06:02:00


 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier, SunPower modules

2009-07-23 Thread Larry Crutcher, Starlight Solar
I have installed tons of SunPower 90's without any ground connection  
on RV's with noticeable loss of power. I believe the problem only  
occurs when you have a path to ground from the frame.


Larry

On Jul 23, 2009, at 12:58 PM, boB Gudgel wrote:


Larry Crutcher, Starlight Solar wrote:

Hi Jay,

An interesting quandary indeed.


This is another good example of an application that I was trying to  
grill Sunpower about --- as far as grounding their modules that need  
to be positive grounded
in order to take advantage of their higher efficiencies.   They  
couldn't answer this simple question.  How would you use one in an  
airplanefor instance ?
There are solar powered airplanes (sort  of)   Is a large faraday  
shield enough ?   Sort of like the ground radials that Larry has  
mentioned.  I would
imagine that if you get large enough radials that it ~might~  
approach being a virtual ground. Works for antennas though.


I like questions like this one.  Sure makes one think a bit.

boB




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier, SunPower modules

2009-07-23 Thread boB Gudgel

Larry Crutcher, Starlight Solar wrote:

I meant to type ...NO noticeable loss of power.


Hi Larry   But how do you ~really~ know you weren't losing power 
because of their lower efficiency unless there was
a comparison made ?  :) I'm not sure that I believe it's all that 
much of a problem, either.


But seriously, I think that  what Sunpower ~really~ means is that they 
have a problem with their lower efficiency on high voltage strings.
I don't imagine that an RV installation would be that high of voltage ? 


I would just like Sunpower to explain this all a bit better.

boB







On Jul 23, 2009, at 7:27 PM, Larry Crutcher, Starlight Solar wrote:

I have installed tons of SunPower 90's without any ground connection 
on RV's with noticeable loss of power. I believe the problem only 
occurs when you have a path to ground from the frame.


Larry

On Jul 23, 2009, at 12:58 PM, boB Gudgel wrote:


Larry Crutcher, Starlight Solar wrote:

Hi Jay,

An interesting quandary indeed.


This is another good example of an application that I was trying to 
grill Sunpower about --- as far as grounding their modules that need 
to be positive grounded
in order to take advantage of their higher efficiencies.   They 
couldn't answer this simple question.  How would you use one in an 
airplanefor instance ?
There are solar powered airplanes (sort  of)   Is a large faraday 
shield enough ?   Sort of like the ground radials that Larry has 
mentioned.  I would
imagine that if you get large enough radials that it ~might~ 
approach being a virtual ground. Works for antennas though.


I like questions like this one.  Sure makes one think a bit.

boB




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Fwd: Grounding on a glacier, SunPower modules

2009-07-23 Thread Larry Crutcher, Starlight Solar

boB,

I usually put only two in series and use MPPT to down convert to 12  
volts. Some RV customers have 6~8 modules, series/parallel. I promote  
the use of battery monitors in all systems so if there was a  
performance issue, I would have seen or heard of it by now. RV  
customers have nothing better to do than to stare at the monitors.  
Really though, most RV full-timers are a dedicated group of off- 
gridders conserving energy and water resources.


Now that you and Dan mention it, I did hear that the polarization  
effect did not occur at low string voltages. I have never installed  
any high voltage strings with SP.


Larry

On Jul 23, 2009, at 7:56 PM, boB Gudgel wrote:


Larry Crutcher, Starlight Solar wrote:

I meant to type ...NO noticeable loss of power.


Hi Larry   But how do you ~really~ know you weren't losing power  
because of their lower efficiency unless there was
a comparison made ?  :) I'm not sure that I believe it's all  
that much of a problem, either.


But seriously, I think that  what Sunpower ~really~ means is that  
they have a problem with their lower efficiency on high voltage  
strings.
I don't imagine that an RV installation would be that high of  
voltage ?

I would just like Sunpower to explain this all a bit better.

boB







On Jul 23, 2009, at 7:27 PM, Larry Crutcher, Starlight Solar wrote:

I have installed tons of SunPower 90's without any ground  
connection on RV's with noticeable loss of power. I believe the  
problem only occurs when you have a path to ground from the frame.


Larry

On Jul 23, 2009, at 12:58 PM, boB Gudgel wrote:


Larry Crutcher, Starlight Solar wrote:

Hi Jay,

An interesting quandary indeed.


This is another good example of an application that I was trying  
to grill Sunpower about --- as far as grounding their modules  
that need to be positive grounded
in order to take advantage of their higher efficiencies.   They  
couldn't answer this simple question.  How would you use one in  
an airplanefor instance ?
There are solar powered airplanes (sort  of)   Is a large faraday  
shield enough ?   Sort of like the ground radials that Larry has  
mentioned.  I would
imagine that if you get large enough radials that it ~might~  
approach being a virtual ground. Works for antennas though.


I like questions like this one.  Sure makes one think a bit.

boB




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re- 
wrenches.org


List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org