Re: [RE-wrenches] Inverter for fire protection pump

2010-08-29 Thread R Ray Walters
HI Daryl;

Your experiences with the water pump got me to thinking that a water pump has a 
MaxPowerPoint as well. (Flow rate x head) 
As you varied the flow rate, you were also MPPT ing the pump- inverter system. 
You found max current at the middle of the pump's range, just like a solar 
module. 

Also, on batteries, I found as you did, that a single string of L16s or T105s 
could not deliver the required current for very long to either start or run a 
large load like a pump. I currently ( no pun intended) think that  two battery 
strings are optimum, for this and other reasons.

I'd third the others input, that a generator is the best choice for a fire 
suppression pump. It won't be used at all most of the time, and then it needs 
to run continuously for hours in a very critical application.
Instead of a huge battery bank and wall of inverters, the money might be better 
spent on a quality generator with reliable fuel supply (underground propane?) 
and more PV with a nice grid tie system.

Loads that can't be interrupted for a few seconds while the generator comes up 
to speed, (computers) could be on their own UPS, or have a smaller Outback 
system.
The efficiency of a grid tie system diminishes with increased battery size, 
though. 

R. Walters
r...@solarray.com
Solar Engineer




On Aug 28, 2010, at 5:24 AM, Darryl Thayer wrote:

 Sorry this could be more helpful if I had a better memory, I don't mean to 
 ramble, but some wrenches may find value.
 
 I am working on a standalone system now and I am in testing.  Normally I use 
 OUtback, (and I am very happy)  and this time I decided to use Magnum 4024 
 AE.  The job has both a large motor and is AC coupled to DGI inverter.  The 
 large motor draws over 120 amp (120 volt) surge when connected to a grid 
 source.  I have started this motor in test repeatedly My Greenlee amp clamp 
 says it is surging at 90 amps! The VOM says the min voltage is 97 volts. This 
 is on ONE 4024 AE,  Magnum is getting close to release of the paralled 
 version The test battery set is Trojan T105 single string, and the surge DC 
 measured by Ideal DC clamp on is 280 amps.  Voltage and minimum battery 
 voltage is 21 volts Ideal VOM.  I would think that the parrellel version 
 could handle your motor.  
 
 Old system
 I did a fire pump install in a large residence, I think back in 2004?  the 
 specs were similar except the starting surge was higher and the running was 
 almost the same (maximum of 20 amps and less depending upon flow).  I used an 
 Odd number of OUtback inverters (5) but not all were to this task.  First the 
 starting surge measured by my greenlee clamp-on amp meter was higher on the 
 grid than it is on the inverters.  I did a lot of field tests, however I do 
 not know where I put the data.  I noticed that if I had fully charged 
 batteries the starting was 100% reliable but on batteries at near 50% SoC the 
 system started to fault on low AC during start-up The batteries were L-16 
 Surrette 48 volt string. If the system was started every five minutes it 
 would fault, but if a longer waiting period  I remember during the course of 
 the job I started the pump over 100 times in test mode with out a failure.  
 (this system gets annual tests and no problems so far)
 
 Pumps:  We found that the pump current draw depended upon the flow rate we 
 allowed..  If we had one head open, the current draw was less than all heads 
 open.  The maximum curent draw was at some flow rate in the middle flow 
 range! The starting surge was independent of whether the valve was open or 
 closed.  If it would be possible to use a SQflex this would be a good choise. 
  Finally this system is grid tied and has a relay to Outback if the Grid 
 should fail and it has a generator inlet box if a generator is avaiable to 
 take the load.  
 
 --- On Fri, 8/27/10, Joel Davidson joel.david...@sbcglobal.net wrote:
 
 From: Joel Davidson joel.david...@sbcglobal.net
 Subject: Re: [RE-wrenches] Inverter for fire protection pump
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Friday, August 27, 2010, 9:50 PM
 Hi Ray,
 
 Thank you for your input. The pump is part of a fire
 protection system that sucks water out of the swimming pool
 and pumps it to roof sprinklers with fire retardant added to
 the water. I'll forward your email to my colleague who has
 the details.
 
 Best regards,
 Joel Davidson
 
 - Original Message - From: R Ray Walters r...@solarray.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Friday, August 27, 2010 7:23 PM
 Subject: Re: [RE-wrenches] Inverter for fire protection
 pump
 
 
 Forgot to mention the usual info: look at the pump to
 see if a smaller or no surge Grundfos SQE might be able to
 handle the flow rate and pressure needed.
 Pumps are cheap, when you're considering multiple
 inverters..
 Given what you mentioned (110 amp surge at 240 vac), I
 don't think even a quad stack of Outbacks could do it. (
 please ignore my

Re: [RE-wrenches] Inverter for fire protection pump

2010-08-29 Thread Richard L Ratico
Maybe another possibility if the generator is a non-starter:

1) Sealed Batteries (no maintainance) appropriately sized for the running load
only, no motor starting surge
2) Single Sunny Island 5048 inverter (the most reliable IMHO)
3) 6 kVA autotransformer (boosts SI output to 240V)
4) 240V single phase input Variable Frequency Drive (programable, allows you to
slowly ramp up motor speed with little or no surge and adjust final speed)
 (VFDs are extensively used for industrial motor control) 
(adjust VFD to
operate within the Sunny Island's rating, it's at the limit here)
5) Replace the single phase pump motor with a 3 phase inverter duty unit (VFD
output is 3 phase)

Dick Ratico
Solarwind Electric


--- You wrote:
HI Daryl;

Your experiences with the water pump got me to thinking that a water pump has a
MaxPowerPoint as well. (Flow rate x head) 
As you varied the flow rate, you were also MPPT ing the pump- inverter system.
You found max current at the middle of the pump's range, just like a solar
module. 

Also, on batteries, I found as you did, that a single string of L16s or T105s
could not deliver the required current for very long to either start or run a
large load like a pump. I currently ( no pun intended) think that  two battery
strings are optimum, for this and other reasons.

I'd third the others input, that a generator is the best choice for a fire
suppression pump. It won't be used at all most of the time, and then it needs to
run continuously for hours in a very critical application.
Instead of a huge battery bank and wall of inverters, the money might be better
spent on a quality generator with reliable fuel supply (underground propane?)
and more PV with a nice grid tie system.

Loads that can't be interrupted for a few seconds while the generator comes up
to speed, (computers) could be on their own UPS, or have a smaller Outback
system.
The efficiency of a grid tie system diminishes with increased battery size,
though. 

R. Walters
r...@solarray.com
Solar Engineer




On Aug 28, 2010, at 5:24 AM, Darryl Thayer wrote:

 Sorry this could be more helpful if I had a better memory, I don't mean to
ramble, but some wrenches may find value.
 
 I am working on a standalone system now and I am in testing.  Normally I use
OUtback, (and I am very happy)  and this time I decided to use Magnum 4024 AE. 
The job has both a large motor and is AC coupled to DGI inverter.  The large
motor draws over 120 amp (120 volt) surge when connected to a grid source.  I
have started this motor in test repeatedly My Greenlee amp clamp says it is
surging at 90 amps! The VOM says the min voltage is 97 volts. This is on ONE
4024 AE,  Magnum is getting close to release of the paralled version The test
battery set is Trojan T105 single string, and the surge DC measured by Ideal DC
clamp on is 280 amps.  Voltage and minimum battery voltage is 21 volts Ideal
VOM.  I would think that the parrellel version could handle your motor.  
 
 Old system
 I did a fire pump install in a large residence, I think back in 2004?  the
specs were similar except the starting surge was higher and the running was
almost the same (maximum of 20 amps and less depending upon flow).  I used an
Odd number of OUtback inverters (5) but not all were to this task.  First the
starting surge measured by my greenlee clamp-on amp meter was higher on the grid
than it is on the inverters.  I did a lot of field tests, however I do not know
where I put the data.  I noticed that if I had fully charged batteries the
starting was 100% reliable but on batteries at near 50% SoC the system started
to fault on low AC during start-up The batteries were L-16 Surrette 48 volt
string. If the system was started every five minutes it would fault, but if a
longer waiting period  I remember during the course of the job I started the
pump over 100 times in test mode with out a failure.  (this system gets annual
tests and no problems so far)
 
 Pumps:  We found that the pump current draw depended upon the flow rate we
allowed..  If we had one head open, the current draw was less than all heads
open.  The maximum curent draw was at some flow rate in the middle flow range!
The starting surge was independent of whether the valve was open or closed.  If
it would be possible to use a SQflex this would be a good choise.  Finally this
system is grid tied and has a relay to Outback if the Grid should fail and it
has a generator inlet box if a generator is avaiable to take the load.  
 
 --- On Fri, 8/27/10, Joel Davidson joel.david...@sbcglobal.net wrote:
 
 From: Joel Davidson joel.david...@sbcglobal.net
 Subject: Re: [RE-wrenches] Inverter for fire protection pump
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Friday, August 27, 2010, 9:50 PM
 Hi Ray,
 
 Thank you for your input. The pump is part of a fire
 protection system that sucks water out of the swimming pool
 and pumps it to roof sprinklers with fire retardant added to
 the water. I'll

Re: [RE-wrenches] Inverter for fire protection pump

2010-08-28 Thread Joel Davidson

Hi Ray,

Thank you for your input. The pump is part of a fire protection system that 
sucks water out of the swimming pool and pumps it to roof sprinklers with 
fire retardant added to the water. I'll forward your email to my colleague 
who has the details.


Best regards,
Joel Davidson

- Original Message - 
From: R Ray Walters r...@solarray.com

To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Friday, August 27, 2010 7:23 PM
Subject: Re: [RE-wrenches] Inverter for fire protection pump


Forgot to mention the usual info: look at the pump to see if a smaller or 
no surge Grundfos SQE might be able to handle the flow rate and pressure 
needed.

Pumps are cheap, when you're considering multiple inverters..
Given what you mentioned (110 amp surge at 240 vac), I don't think even a 
quad stack of Outbacks could do it. ( please ignore my earlier post)
A quad stack could run that, just not start it. Franklin makes a soft 
start controller, that might work with that pump. What is the Horse power 
rating?


R. Walters
r...@solarray.com
Solar Engineer




On Aug 27, 2010, at 3:52 PM, R Ray Walters wrote:

Little beyond  a pair of Outbacks, possibly a pair of Magnasine 
inverters, or a quad stack of Outbacks.


R. Walters
r...@solarray.com
Solar Engineer




On Aug 26, 2010, at 2:41 PM, Joel Davidson wrote:


Wrenches,
Our customer has a fire protection pumping system that operates at 
240VAC and 22 amps with a 110 amps starting surge. The pump will only be 
used for up to 4 hours in an emergency (but hopefully never). The 
customer wants an inverter and battery (no generator or PV) in case grid 
power is destroyed by fire. What inverter(s) do you recommend? Thank you 
very much for sharing your off-grid knowledge.

Joel Davidson

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Inverter for fire protection pump

2010-08-28 Thread penobscotsolar
Joel,
   We are currently in the middle of installing a 7 kw off grid system
with just these requirements. The client is a retired Chicago
firefighter and insisted on this commercial fire suppression system.
After much research the logical conclusion we reached was the same as
William's recommendation below.

Daryl DeJoy
NABCEP Certified PV installer
Penobscot  Solar Design




 Joel:

 With these requirements, the inverter I recommend is a generator.

 William



 At 05:41 PM 8/26/2010, you wrote:
Wrenches,
Our customer has a fire protection pumping system that operates at 240VAC
and 22 amps with a 110 amps starting surge. The pump will only be used
 for
up to 4 hours in an emergency (but hopefully never). The customer wants
 an
inverter and battery (no generator or PV) in case grid power is destroyed
by fire. What inverter(s) do you recommend? Thank you very much for
sharing your off-grid knowledge.
Joel Davidson

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.441 / Virus Database: 271.1.1/3096 - Release Date: 08/26/10
18:34:00

 Please note new e-mail address and domain:

 William Miller
 Miller Solar
 Voice :805-438-5600
 email: will...@millersolar.com
 http://millersolar.com
 License No. C-10-773985
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Inverter for fire protection pump

2010-08-28 Thread Darryl Thayer
Sorry this could be more helpful if I had a better memory, I don't mean to 
ramble, but some wrenches may find value.

I am working on a standalone system now and I am in testing.  Normally I use 
OUtback, (and I am very happy)  and this time I decided to use Magnum 4024 AE.  
The job has both a large motor and is AC coupled to DGI inverter.  The large 
motor draws over 120 amp (120 volt) surge when connected to a grid source.  I 
have started this motor in test repeatedly My Greenlee amp clamp says it is 
surging at 90 amps! The VOM says the min voltage is 97 volts. This is on ONE 
4024 AE,  Magnum is getting close to release of the paralled version The test 
battery set is Trojan T105 single string, and the surge DC measured by Ideal DC 
clamp on is 280 amps.  Voltage and minimum battery voltage is 21 volts Ideal 
VOM.  I would think that the parrellel version could handle your motor.  

Old system
I did a fire pump install in a large residence, I think back in 2004?  the 
specs were similar except the starting surge was higher and the running was 
almost the same (maximum of 20 amps and less depending upon flow).  I used an 
Odd number of OUtback inverters (5) but not all were to this task.  First the 
starting surge measured by my greenlee clamp-on amp meter was higher on the 
grid than it is on the inverters.  I did a lot of field tests, however I do not 
know where I put the data.  I noticed that if I had fully charged batteries the 
starting was 100% reliable but on batteries at near 50% SoC the system started 
to fault on low AC during start-up The batteries were L-16 Surrette 48 volt 
string. If the system was started every five minutes it would fault, but if a 
longer waiting period  I remember during the course of the job I started the 
pump over 100 times in test mode with out a failure.  (this system gets annual 
tests and no problems so far)

Pumps:  We found that the pump current draw depended upon the flow rate we 
allowed..  If we had one head open, the current draw was less than all heads 
open.  The maximum curent draw was at some flow rate in the middle flow range! 
The starting surge was independent of whether the valve was open or closed.  If 
it would be possible to use a SQflex this would be a good choise.  Finally this 
system is grid tied and has a relay to Outback if the Grid should fail and it 
has a generator inlet box if a generator is avaiable to take the load.  

--- On Fri, 8/27/10, Joel Davidson joel.david...@sbcglobal.net wrote:

 From: Joel Davidson joel.david...@sbcglobal.net
 Subject: Re: [RE-wrenches] Inverter for fire protection pump
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Friday, August 27, 2010, 9:50 PM
 Hi Ray,
 
 Thank you for your input. The pump is part of a fire
 protection system that sucks water out of the swimming pool
 and pumps it to roof sprinklers with fire retardant added to
 the water. I'll forward your email to my colleague who has
 the details.
 
 Best regards,
 Joel Davidson
 
 - Original Message - From: R Ray Walters r...@solarray.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Friday, August 27, 2010 7:23 PM
 Subject: Re: [RE-wrenches] Inverter for fire protection
 pump
 
 
  Forgot to mention the usual info: look at the pump to
 see if a smaller or no surge Grundfos SQE might be able to
 handle the flow rate and pressure needed.
  Pumps are cheap, when you're considering multiple
 inverters..
  Given what you mentioned (110 amp surge at 240 vac), I
 don't think even a quad stack of Outbacks could do it. (
 please ignore my earlier post)
  A quad stack could run that, just not start it.
 Franklin makes a soft start controller, that might work with
 that pump. What is the Horse power rating?
  
  R. Walters
  r...@solarray.com
  Solar Engineer
  
  
  
  
  On Aug 27, 2010, at 3:52 PM, R Ray Walters wrote:
  
  Little beyond  a pair of Outbacks, possibly a
 pair of Magnasine inverters, or a quad stack of Outbacks.
  
  R. Walters
  r...@solarray.com
  Solar Engineer
  
  
  
  
  On Aug 26, 2010, at 2:41 PM, Joel Davidson wrote:
  
  Wrenches,
  Our customer has a fire protection pumping
 system that operates at 240VAC and 22 amps with a 110 amps
 starting surge. The pump will only be used for up to 4 hours
 in an emergency (but hopefully never). The customer wants an
 inverter and battery (no generator or PV) in case grid power
 is destroyed by fire. What inverter(s) do you recommend?
 Thank you very much for sharing your off-grid knowledge.
  Joel Davidson
  
 
 ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm
  
  Check out participant bios:
  www.members.re

Re: [RE-wrenches] Inverter for fire protection pump

2010-08-28 Thread Joel Davidson

Wrenches,

This group's experience, collective wisdom, and willingness to share 
practical knowledge and interesting ideas are how I envision higher 
education in the future. Thank you all for your helpful information. I'll 
report back what the customer decides to do.


Joel Davidson

- Original Message - 
From: Darryl Thayer daryl_so...@yahoo.com

To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Saturday, August 28, 2010 8:24 AM
Subject: Re: [RE-wrenches] Inverter for fire protection pump


Sorry this could be more helpful if I had a better memory, I don't mean to 
ramble, but some wrenches may find value.


I am working on a standalone system now and I am in testing.  Normally I use 
OUtback, (and I am very happy)  and this time I decided to use Magnum 4024 
AE.  The job has both a large motor and is AC coupled to DGI inverter.  The 
large motor draws over 120 amp (120 volt) surge when connected to a grid 
source.  I have started this motor in test repeatedly My Greenlee amp clamp 
says it is surging at 90 amps! The VOM says the min voltage is 97 volts. 
This is on ONE 4024 AE,  Magnum is getting close to release of the paralled 
version The test battery set is Trojan T105 single string, and the surge DC 
measured by Ideal DC clamp on is 280 amps.  Voltage and minimum battery 
voltage is 21 volts Ideal VOM.  I would think that the parrellel version 
could handle your motor.


Old system
I did a fire pump install in a large residence, I think back in 2004?  the 
specs were similar except the starting surge was higher and the running was 
almost the same (maximum of 20 amps and less depending upon flow).  I used 
an Odd number of OUtback inverters (5) but not all were to this task.  First 
the starting surge measured by my greenlee clamp-on amp meter was higher on 
the grid than it is on the inverters.  I did a lot of field tests, however I 
do not know where I put the data.  I noticed that if I had fully charged 
batteries the starting was 100% reliable but on batteries at near 50% SoC 
the system started to fault on low AC during start-up The batteries were 
L-16 Surrette 48 volt string. If the system was started every five minutes 
it would fault, but if a longer waiting period  I remember during the course 
of the job I started the pump over 100 times in test mode with out a 
failure.  (this system gets annual tests and no problems so far)


Pumps:  We found that the pump current draw depended upon the flow rate we 
allowed..  If we had one head open, the current draw was less than all heads 
open.  The maximum curent draw was at some flow rate in the middle flow 
range! The starting surge was independent of whether the valve was open or 
closed.  If it would be possible to use a SQflex this would be a good 
choise.  Finally this system is grid tied and has a relay to Outback if the 
Grid should fail and it has a generator inlet box if a generator is avaiable 
to take the load.


--- On Fri, 8/27/10, Joel Davidson joel.david...@sbcglobal.net wrote:


From: Joel Davidson joel.david...@sbcglobal.net
Subject: Re: [RE-wrenches] Inverter for fire protection pump
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Friday, August 27, 2010, 9:50 PM
Hi Ray,

Thank you for your input. The pump is part of a fire
protection system that sucks water out of the swimming pool
and pumps it to roof sprinklers with fire retardant added to
the water. I'll forward your email to my colleague who has
the details.

Best regards,
Joel Davidson

- Original Message - From: R Ray Walters r...@solarray.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Friday, August 27, 2010 7:23 PM
Subject: Re: [RE-wrenches] Inverter for fire protection
pump


 Forgot to mention the usual info: look at the pump to
see if a smaller or no surge Grundfos SQE might be able to
handle the flow rate and pressure needed.
 Pumps are cheap, when you're considering multiple
inverters..
 Given what you mentioned (110 amp surge at 240 vac), I
don't think even a quad stack of Outbacks could do it. (
please ignore my earlier post)
 A quad stack could run that, just not start it.
Franklin makes a soft start controller, that might work with
that pump. What is the Horse power rating?

 R. Walters
 r...@solarray.com
 Solar Engineer




 On Aug 27, 2010, at 3:52 PM, R Ray Walters wrote:

 Little beyond a pair of Outbacks, possibly a
pair of Magnasine inverters, or a quad stack of Outbacks.

 R. Walters
 r...@solarray.com
 Solar Engineer




 On Aug 26, 2010, at 2:41 PM, Joel Davidson wrote:

 Wrenches,
 Our customer has a fire protection pumping
system that operates at 240VAC and 22 amps with a 110 amps
starting surge. The pump will only be used for up to 4 hours
in an emergency (but hopefully never). The customer wants an
inverter and battery (no generator or PV) in case grid power
is destroyed by fire. What inverter(s) do you recommend?
Thank you very much for sharing your off-grid knowledge.
 Joel Davidson

Re: [RE-wrenches] Inverter for fire protection pump

2010-08-27 Thread R Ray Walters
Little beyond  a pair of Outbacks, possibly a pair of Magnasine inverters, or a 
quad stack of Outbacks.

R. Walters
r...@solarray.com
Solar Engineer




On Aug 26, 2010, at 2:41 PM, Joel Davidson wrote:

 Wrenches,
 Our customer has a fire protection pumping system that operates at 240VAC and 
 22 amps with a 110 amps starting surge. The pump will only be used for up to 
 4 hours in an emergency (but hopefully never). The customer wants an inverter 
 and battery (no generator or PV) in case grid power is destroyed by fire. 
 What inverter(s) do you recommend? Thank you very much for sharing your 
 off-grid knowledge.
 Joel Davidson
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org