RE: FM 74 Egress Sprinklre system?

2012-03-26 Thread Bill Brooks
NFPA 101A has a number of partial sprinkler system options for various
occupancies.  I recall the original development of the point systems in the
late 1970's where partial systems were given consideration in life safety
evaluations.  Perhaps the system in this case is a holdover from that time
period.  It would be instructive to take a look at past and current versions
of NFPA 101A to see how some of these systems could have been introduced
especially on the fire marshal side where NFPA could have been used in lieu
of building codes in upgrading existing buildings.  NFPA 101 has included a
provision for 6 heads off domestic for many years. 

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Sunday, March 25, 2012 5:08 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: FM 74 Egress Sprinklre system?

Douglas,

During the early eighties and maybe the seventies (I was in California until
the late eighties so I'm not sure about the when) schools K-12 were under
the jurisdiction of the State FM. There were several I've come across with
these silly partial systems protecting small areas deemed to be extra
dangerous for one reason or another, including the main building at Bates
Tech College (which was a vocational adult school in the Tacoma school
District until 1988), my own institution. In the entry to what is now the
financial aid office, but then was registration, are seven Omega heads over
the doorway. There are four along one wall in a counselor's office but that
wall used to be a pass through of some sort with a drop window arrangement.
There's an elementary school in Puyallup with two heads (and six spares)
covering a stage (platform), and a high school with four heads over the
main office counter (highly combustible paperwork no doubt).
All these systems are tapped off plumbing, and installed in, at best, a
pipe schedule, or to nothing cogent at all like your system seems to be.
I wouldn't be surprised if Washington nonsense migrated to Oregon. You may
be looking at something somebody thought was a good idea at the time,
like that six month or so surge of a single sprinkler head over a
residential cooking surface tapped off the plumbing. Or perhaps tose guys
that decided if some anti-freeze was good 100% anti-freeze would be better,
until

On Sun, Mar 25, 2012 at 12:59 PM, Douglas Hicks fire...@eoni.com wrote:

 I am looking at 2 schools that have partial sprinkler systems, 
 protecting the egress routes only.  The local Fire Marshal thinks they 
 may be installed to FM74 standards.  The 2 that I have seen are wet 
 systems, 1/2 inch drops to the heads, 1/2 garden hose fitting as an
inspector's test.
 The heads are pendant, and uprights,  as far  as 2 feet from the ceiling.
 Some of the heads are leaking, some of the heads look to be oriented 
 improperly. No one seems to know what the year of installation was.  
 Is/was there a standard for that type of sprinkler system?
 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
 hments/20120325/0cd46534/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120325/fb7364e8/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


min dist. between EC and std throw sprinklers

2012-03-26 Thread Dewayne Martinez
Can a standard throw sprinkler and extended coverage sprinkler be placed
closer than 8ft apart without a baffle?

Thanks,

Dewayne  

 

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120326/4db6b7e4/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: min dist. between EC and std throw sprinklers

2012-03-26 Thread A.P.Silva
No. If 8 ft is minimum for EC/EC the it is the same for EC/STD.

Tony 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: March 26, 2012 9:52 AM
To: SprinklerFORUM
Subject: min dist. between EC and std throw sprinklers

Can a standard throw sprinkler and extended coverage sprinkler be placed
closer than 8ft apart without a baffle?

Thanks,

Dewayne  

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120326/4db6b7e4/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: Underground FDC

2012-03-26 Thread Frank Herrick
Craig, Here is what we have been using for UG supply piping and FDC pipe  

http://www.northtowncompany.com/msdspds/Low%20density%20polywrap/northtown%20polywrap%20data%20sheet.pdf

The 8 mil minimum, group 2, linear low density, flat tube, virgin polyethylene 
film provided meets or exceeds the requirements of AWWA C105-10, ANSI A21.5-10, 
ASTM D4976 and NT4112-10. The film is marked showing trademark, year of 
manufacture, type of resin, specification conformance, applicable pipe sizes 
and a corrosion protection warning.

http://www.northtowncompany.com/polywraplow.html

Just make sure that the trench has a layer of sand or #2 fine crushed 
limestone, do not allow anyone to backfill with broken rocks or chunks of 
concrete.  You'll be guaranteed to cause a tear or rip in the polywrap and 
corrosion at that tear point. Follow the manufactures directions and I've never 
had any problems. 


Captain Frank J. Herrick 
City Of Leawood Fire Department  
14801 Mission Road
Leawood, Ks. 66224-9560
Office:    913.681.6788 x 26 
Fax:    913.681.2399
Fire Sprinklers Save Lives, Property, the Environment, and Water - Protect what 
you value most!



-Original Message-
From: Craig Leadbetter [mailto:craigleadbet...@gmail.com] 
Sent: Friday, March 23, 2012 9:38 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Underground FDC

Thanks.

I haven't found any products that I am sure will meet the NFPA 13 10.1.3.
The commentary talks about AWWA C203 standard. What I have found so far doesn't 
list this as the standard the the products meet.

Maybe I am making it more complicated than it needs to be.

--
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855
(O) 906-475-9955
(F) 906-475-5474

(C) 906-362-5393

craigleadbet...@gmail.com


On Fri, Mar 23, 2012 at 10:09 AM, lamarvau...@charter.net wrote:

 I haven't used it in a long time but 3M once produced a system package 
 of mastic coating (paint-wrap-paint) that was spec'd. on a gov't job I 
 did.I'm sure someone else may make a similar product today.



 On Fri, Mar 23, 2012 at 8:50 AM, Dewayne Martinez wrote:

  We order poly wrap and mastic coating from the local UG supplier.

 -Original Message-
 From: 
 sprinklerforum-bounces@**firesprinkler.orgsprinklerforum-bounces@fir
 esprinkler.org 
 [mailto:sprinklerforum-**boun...@firesprinkler.orgsprinklerforum-bou
 n...@firesprinkler.org]
 On Behalf Of Craig
 Leadbetter
 Sent: Friday, March 23, 2012 7:30 AM
 To: Sprinklerforum@firesprinkler.**org 
 Sprinklerforum@firesprinkler.org
 Subject: Underground FDC

 I have a yard post FDC with underground piping. We are going to use 
 galvanized pipe so i am looking for a product that can be used to 
 protect the pipe per code for a tar based protective coating.



 --
 Craig Leadbetter
 Safeguard of Marquette
 PO Box 116
 Marquette, MI 49855
 (O) 906-475-9955
 (F) 906-475-5474

 (C) 906-362-5393

 craigleadbet...@gmail.com
 -- next part -- An HTML attachment was 
 scrubbed...
 URL:

 http://fireball.**firesprinkler.org/mailman/**
 private/sprinklerforum/attachhttp://fireball.firesprinkler.org/mailm
 an/private/sprinklerforum/attach 
 ments/20120323/3d7dc911/**attachment.html
 __**_
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.**org Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 __**_
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.**org Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 __**_
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.**org Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120323/f3270634/attachment.html

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: FM 74 Egress Sprinklre system?

2012-03-26 Thread Tom Scheidel
NFPA 101A is tied to a particular version of NFPA 101.  For example, if the 
facility is subject to the 2000 Ed of NFPA 101, then the 2001 Ed of NFPA 101A 
applies. 

This may or may not be an issue for your facility but an example of where it 
would apply would be, in very plain language:

If a complete sprinkler system (throughout) is required, then a partial 
sprinkler system would be a Negative (Bad thing). 
If a complete sprinkler system is NOT required for minimal regulatory 
compliance, then a partial sprinkler system is a Positive thing. 

How Positive and Negative are indicated in 101A forms. 

The definitions of Partial are addressed in NFPA 101A which, as you would 
expect, is tied to NFPA 13. 

The next edition of NFPA 101A comes out this year, will be labeled as the 2013 
edition, and is tied to the 2012 edition of NFPA 101. 

Hope this helps a little. 

Tom

Tom Scheidel
cms911.com
817-456-6238
Scheidel  Associates

Sent from my IPad 

On Mar 26, 2012, at 8:43, Bill Brooks bill.bro...@brooksfpe.com wrote:

 NFPA 101A has a number of partial sprinkler system options for various
 occupancies.  I recall the original development of the point systems in the
 late 1970's where partial systems were given consideration in life safety
 evaluations.  Perhaps the system in this case is a holdover from that time
 period.  It would be instructive to take a look at past and current versions
 of NFPA 101A to see how some of these systems could have been introduced
 especially on the fire marshal side where NFPA could have been used in lieu
 of building codes in upgrading existing buildings.  NFPA 101 has included a
 provision for 6 heads off domestic for many years. 
 
 Bill Brooks
 
 William N. Brooks, P.E.
 Brooks Fire Protection Engineering Inc.
 372 Wilett Drive
 Severna Park, MD 21146-1904
 410-544-3620
 410-544-3032 FAX
 412-400-6528 Cell
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
 Sent: Sunday, March 25, 2012 5:08 PM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: FM 74 Egress Sprinklre system?
 
 Douglas,
 
 During the early eighties and maybe the seventies (I was in California until
 the late eighties so I'm not sure about the when) schools K-12 were under
 the jurisdiction of the State FM. There were several I've come across with
 these silly partial systems protecting small areas deemed to be extra
 dangerous for one reason or another, including the main building at Bates
 Tech College (which was a vocational adult school in the Tacoma school
 District until 1988), my own institution. In the entry to what is now the
 financial aid office, but then was registration, are seven Omega heads over
 the doorway. There are four along one wall in a counselor's office but that
 wall used to be a pass through of some sort with a drop window arrangement.
 There's an elementary school in Puyallup with two heads (and six spares)
 covering a stage (platform), and a high school with four heads over the
 main office counter (highly combustible paperwork no doubt).
 All these systems are tapped off plumbing, and installed in, at best, a
 pipe schedule, or to nothing cogent at all like your system seems to be.
 I wouldn't be surprised if Washington nonsense migrated to Oregon. You may
 be looking at something somebody thought was a good idea at the time,
 like that six month or so surge of a single sprinkler head over a
 residential cooking surface tapped off the plumbing. Or perhaps tose guys
 that decided if some anti-freeze was good 100% anti-freeze would be better,
 until
 
 On Sun, Mar 25, 2012 at 12:59 PM, Douglas Hicks fire...@eoni.com wrote:
 
 I am looking at 2 schools that have partial sprinkler systems, 
 protecting the egress routes only.  The local Fire Marshal thinks they 
 may be installed to FM74 standards.  The 2 that I have seen are wet 
 systems, 1/2 inch drops to the heads, 1/2 garden hose fitting as an
 inspector's test.
 The heads are pendant, and uprights,  as far  as 2 feet from the ceiling.
 Some of the heads are leaking, some of the heads look to be oriented 
 improperly. No one seems to know what the year of installation was.  
 Is/was there a standard for that type of sprinkler system?
 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
 hments/20120325/0cd46534/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
 --
 Ron Greenman
 Instructor
 Fire Protection Engineering Technology
 Bates Technical College
 1101 So. Yakima Ave.
 Tacoma, WA 98405
 
 rgreen...@bates.ctc.edu
 
 http://www.bates.ctc.edu/fireprotection/
 
 253.680.7346
 253.576.9700 (cell)
 
 Member:
 ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS,