RE: 02 storage

2012-08-13 Thread Craig.Prahl
Greg,

Jim touched on many of the issues here that go WAAY beyond the 
responsibility of a sprinkler contractor.  I'm not trying to diminish anyone's 
credibility or ability but there are a lot of issues which need to be addressed 
by several parties to be sure this building is code compliant before you even 
turn the first pipe wrench.  

I'm not sure either where the 12,000 sq. ft is coming from other than for an 
S-1 storage occupancy you have to have sprinklers if you exceed that sq. ft. 
per the IBC.   Maybe he have meant Cubic Ft since with 4 control areas that's 
the most he could get and not be forced into the H-3 occupancy.   And the high 
hazard sprinkler system?  What's that?   If you apply NFPA 55, it's only 
looking for OH2 at 3,000 sf as base line.

Either way the tenant isn't getting 20,000 cf in the warehouse without it going 
to an H-3 which then drives a whole bunch of other requirements for other 
disciplines that can get quite pricey.   

Storage occupancies are always a lot of fun, but it becomes more difficult when 
the areas have been assigned the wrong occupancy or the architect has not 
considered the actual materials used and stored within.  Then again, the owner 
may have forgotten to tell the architect what was going in there during the 
design phase.  

No matter what, this all needs to be thrown back to the architect to be sure 
the area's occupancies are properly defined based on code definitions and use.  
  


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jim Davidson
Sent: Friday, August 10, 2012 3:06 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 02 storage

What is the occupancy that is moving into the building? Per the IBC
Table 307.1(1) you are permitted to have 3,000 cubic ft of oxidizing gas
in a facility any amount greater than this amount will change the use
group to an H-3 Hazardous Use Group. NFPA 55 does not reference any of
the building code required fire separation ratings between different use
groups. Other issues will be how will the cylinders be filled? Will
there be cryogenic oxygen stored? Will there be trans-filling of
containers? What type of floor surface is in the area. If a hydrocarbon
based product oxygen-enriched atmosphere can cause these products to
ignite faster, and burn faster and hotter than usual. NFPA 55 only
requires a one hour separation while the IBC requires up to a 2 hour
fire separation between occupancies. 

Someone needs to sit down with the owner and explain that this issue is
not in the realm of the sprinkler contractor's expertise unless the
contractor would like to add to their uninsured liability potential.

This would require an engineering analysis by a FPE who has experience
in industrial gas storage facilities and Hazardous Use Group Occupancies
of the IBC. If you think Mechanical PE's practicing in the discipline of
fire protection are funny, wait until you see them perform in the
industrial gas arena.   

Have a fire safe day!

Regards

Jim

DAVIDSON ASSOCIATES

Fire Protection Engineering P. O. Box 4010
Code ConsultantsGreenville, DE  19807-0010
Medical Gas Systems Engineering (302) 994-9500
Fax (302) 234-1781

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg
McGahan
Sent: Friday, August 10, 2012 2:01 PM
To: sprinklerforum@firesprinkler.org
Subject: 02 storage

This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is
having difficulty with the AHJ who claims that even if they classify the
warehouse portion of this space as Storage Occupancy instead of
Business, The maximum cubic footage of 02 allowed to be stored in one
place is 12,000 with High Hazard Sprinkler protection. The tenant
needs to store almost 20,000 cubic feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120810/f3e9c5a0/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org

Re: 02 storage

2012-08-13 Thread Greg McGahan
All interested,

The question is regarding the building code, not fire protection per se'.
 I was just trying to educate myself and help the AHJ, who we have a great
relationship with, in case there was something he was missing. Per Florida
State Law however, this will not require an Engineer to be involved due to
the size of the system and we are qualified to use the code as it is
written and apply it. It turns out after an emergency meeting Friday
afternoon, that the AHJ has done his homework and has told the Tenant and
Architect exactly what the options are.

The options are as follows: (per the Florida Building Code and NFPA #55 and
13)

1) Max storage of 12,000 cubit feet of 02 compartmentalized into control
areas of 3,000 cuft each - separated with 2 hr separation.
2) same as above except 6,000 per control area if ventilated appropriately
3) store the remainder of the 20,000 cuft outside

OR

1) item one and 2 above and then utilize separation suffucuent to count
another area of the building as a separate building per the building code,
and store 12,000 cuft more.

That is the AHJ's interpretation and up to others to decide what to do.

It does APPEAR to the AHJ and myself that OH2 over 3,000 sqft is the
sprinkler design criteria.

Thanks,
Greg



On Fri, Aug 10, 2012 at 1:17 PM, Todd Williams t...@fpdc.com wrote:

 Greg,

 This occupancy needs to be evaluated by an FPE and he or she needs to make
 protection recommendations. This may be covered in NFPA 55, NFPA 99 or
 similar documents, but is beyond what a contractor would normally deal with.

 Todd

 At 02:08 PM 8/10/2012, you wrote:
 Cubic Feet
 
 
 On Fri, Aug 10, 2012 at 1:02 PM, Morey, Mike mo...@bmwc.com wrote:
 
  Cubic feet or square feet?  It sounds an awful lot like he's refering to
  the IFC requirements for High Piled Combustible Storage.  They may have
  an egress or building design issue that is causing a limitation.  We've
  run into this a number of times where people just want us to make the
  sprinkler system work only to find out that the building won't work
  for what they want.
 
 
  -Mike Morey, SET
  Sprinkler Designer
  BMW Constructors, Inc
  mo...@bmwc.com
  Desk: 317-651-0596
  Cell: 317-439-2695
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg
  McGahan
  Sent: Friday, August 10, 2012 1:51 PM
  To: sprinklerforum@firesprinkler.org
  Subject: 02 storage
 
  This is a completely new area for me so any help is appreciated.
 
  Issue:  Medical Gas Storage of 02 only in various cylinders.
 
  The tenant and owner of this Commercial / Industrial Strip center is
  having difficulty with the AHJ who claims that even if they classify the
  warehouse portion of this space as Storage Occupancy instead of
  Business, The maximum cubic footage of 02 allowed to be stored in one
  place is 12,000 with High Hazard Sprinkler protection. The tenant
  needs to store almost 20,000 cubic feet.
 
  Does anyone have expertise in this area?
  Thanks,
  Greg
 
 
  --
  Greg McGahan
  Living Water Fire Protection, LLC http://www.livingwaterfp.com 1160
  McKenzie Road Cantonment, FL 32533 850-937-1850 fax 850-937-1852
  -- next part --
  An HTML attachment was scrubbed...
  URL:
  
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
 ments/20120810/f3e9c5a0/attachment.html
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
 --
 Greg McGahan
 Living Water Fire Protection, LLC http://www.livingwaterfp.com
 1160 McKenzie Road
 Cantonment, FL 32533
 850-937-1850
 fax 850-937-1852
 -- next part --
 An HTML attachment was scrubbed...
 URL: 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120810/3ed155de/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 860.535.2080
 www.fpdc.com

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120813/6f42df5c/attachment.html

RE: 02 storage

2012-08-13 Thread Craig.Prahl
 860.535.2080
 www.fpdc.com

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120813/6f42df5c/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: 02 storage (hazardous materials assessment)

2012-08-13 Thread Bill Brooks
The definition of O2 as a hazardous material is based on IBC Section 307.2
and the defined quantities in IBC Table 307.1(1).  When quantities exceed
the MAQ in Table 307.1(1), the various design options being discussed come
into play.  The concept of Control Area is defined in (2009) IBC Section
414.2. The IBC fire barrier is noted in Table 414.2.2.

I'm very surprised any AHJ would have to be educated on this, but looking
back at the messages it may be that what the AHJ said was being filtered
through a number of people who were not familiar with the process used to
deal with hazardous materials.

What I've found in the real world is the lack of correlation between
commonly generated MSDS and the various building and fire code
classification tables which does not appear to factor into this application.

I'm not familiar with the Florida Building Code, perhaps it is much more
complex than the IBC.

Keep in mind there are 13 Exceptions listed under Section 307.1, one of
which (Exception 2) is the storage of flammable and combustible liquids in
mercantile. If it were not for this exception some stores we regularly shop
in would not exist in their present form. Also Exception 6 is your
neighborhood State Store (a nod to George C.).

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Friday, August 10, 2012 3:05 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 02 storage

Sounds like there are some building code issues which should not be
addressed by the sprinkler contractor. It may be your job is not so
complicated if you apply NFPA 55.  But somebody else may or may not have
done their job.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
jhoff...@kcp.com
Sent: Friday, August 10, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: 02 storage

IFC, chapter 27 and NFPA 55 have the same criteria for oxidizing gas.  It is
3000 cu ft per control area.  Don't know where the AHJ is coming up with
12000 cu ft unless he is considering the maximum of 4 control areas per
building and then you get to 12000 cu ft.  This means 4 areas that are fire
separated from each other and the rest of the building.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns  McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FMT |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
jhoff...@kcp.com



From:   Greg McGahan g...@livingwaterfp.com
To: sprinklerforum@firesprinkler.org
Date:   08/10/2012 12:50 PM
Subject:02 storage
Sent by:sprinklerforum-boun...@firesprinkler.org



This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is having
difficulty with the AHJ who claims that even if they classify the warehouse
portion of this space as Storage Occupancy instead of Business, The maximum
cubic footage of 02 allowed to be stored in one place is 12,000 with High
Hazard Sprinkler protection. The tenant needs to store almost 20,000 cubic
feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20120810/f3e9c5a0/attachment.html

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: 02 storage (hazardous materials assessment)

2012-08-13 Thread Craig.Prahl
One big problem is design professionals who don't know to ask for MSDS or who 
can't read them when they get them.

I didn't read that the scenario in question was a mercantile operation.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Monday, August 13, 2012 10:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 02 storage (hazardous materials assessment)

The definition of O2 as a hazardous material is based on IBC Section 307.2
and the defined quantities in IBC Table 307.1(1).  When quantities exceed
the MAQ in Table 307.1(1), the various design options being discussed come
into play.  The concept of Control Area is defined in (2009) IBC Section
414.2. The IBC fire barrier is noted in Table 414.2.2.

I'm very surprised any AHJ would have to be educated on this, but looking
back at the messages it may be that what the AHJ said was being filtered
through a number of people who were not familiar with the process used to
deal with hazardous materials.

What I've found in the real world is the lack of correlation between
commonly generated MSDS and the various building and fire code
classification tables which does not appear to factor into this application.

I'm not familiar with the Florida Building Code, perhaps it is much more
complex than the IBC.

Keep in mind there are 13 Exceptions listed under Section 307.1, one of
which (Exception 2) is the storage of flammable and combustible liquids in
mercantile. If it were not for this exception some stores we regularly shop
in would not exist in their present form. Also Exception 6 is your
neighborhood State Store (a nod to George C.).

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Friday, August 10, 2012 3:05 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 02 storage

Sounds like there are some building code issues which should not be
addressed by the sprinkler contractor. It may be your job is not so
complicated if you apply NFPA 55.  But somebody else may or may not have
done their job.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
jhoff...@kcp.com
Sent: Friday, August 10, 2012 2:39 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: 02 storage

IFC, chapter 27 and NFPA 55 have the same criteria for oxidizing gas.  It is
3000 cu ft per control area.  Don't know where the AHJ is coming up with
12000 cu ft unless he is considering the maximum of 4 control areas per
building and then you get to 12000 cu ft.  This means 4 areas that are fire
separated from each other and the rest of the building.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns  McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FMT |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
jhoff...@kcp.com



From:   Greg McGahan g...@livingwaterfp.com
To: sprinklerforum@firesprinkler.org
Date:   08/10/2012 12:50 PM
Subject:02 storage
Sent by:sprinklerforum-boun...@firesprinkler.org



This is a completely new area for me so any help is appreciated.

Issue:  Medical Gas Storage of 02 only in various cylinders.

The tenant and owner of this Commercial / Industrial Strip center is having
difficulty with the AHJ who claims that even if they classify the warehouse
portion of this space as Storage Occupancy instead of Business, The maximum
cubic footage of 02 allowed to be stored in one place is 12,000 with High
Hazard Sprinkler protection. The tenant needs to store almost 20,000 cubic
feet.

Does anyone have expertise in this area?
Thanks,
Greg


--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments
/20120810/f3e9c5a0/attachment.html

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum