I have done projects where they had to do the same at those same facilities. It 
is unusual to hang for sure.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Senior Engineering Manager

MFP Design

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com/>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>


From: Henry Fontana 
Sent: Tuesday, April 26, 2022 12:05:45 PM
To: tston...@comcast.net ; 'Tom Wellen' 
; sprinklerforum@lists.firesprinkler.org 

Subject: [Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger


We have done many document storage facilities like an Iron mountain.  With over 
10 levels of isle protection.  All our pipe hangs off the grate from the floor 
above.  When I call my supplier I call the “subway clips” but doing a google 
search I am not getting them.  If you send me an email I will share the spec 
sheet.



Henry Fontana

Operations Manager (NYC)

Johnson Controls Fire Protection

100 Lighting Way Secaucus, NJ 07094

Cell: 201-210-9873

henry.font...@jci.com<mailto:henry.font...@jci.com>

[cid:image001.jpg@01D8597F.19B46100]



From: tston...@comcast.net 
Sent: Tuesday, April 26, 2022 3:01 PM
To: 'Tom Wellen' ; sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger



The Hanger chapter in NFPA 13 only mentions the structure. I don’t believe it 
was the intention to allow attachments to grated floor systems.



Regards,

G. Tim Stone



G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services



   117 Old Stage Rd. - Essex Jct., VT. 05452

 CELL: (802) 373-0638

 tston...@comcast.net<mailto:tston...@comcast.net>



From: Tom Wellen mailto:tgwel...@gmail.com>>
Sent: Tuesday, April 26, 2022 1:45 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe Hanger





I ran into an installation where the ring hanger was attached to the metal 
grating to support sprinkler pipe below. I'm trying to find the right way to 
support the fire sprinkler pipe. I searched several manufacturers, but I don't 
see a metal grating clip that accepts all thread for fire protection. Most 
hangers were attached to structural steel using Sammys.



Are there any listed attachments to metal grating for hangers supporting fire 
sprinkler pipe?





Tom Wellen

McKinney Fire Marshal's Office

972-547-2854

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

2022-04-26 Thread Henry Fontana
We have done many document storage facilities like an Iron mountain.  With over 
10 levels of isle protection.  All our pipe hangs off the grate from the floor 
above.  When I call my supplier I call the “subway clips” but doing a google 
search I am not getting them.  If you send me an email I will share the spec 
sheet.

Henry Fontana
Operations Manager (NYC)
Johnson Controls Fire Protection
100 Lighting Way Secaucus, NJ 07094
Cell: 201-210-9873
henry.font...@jci.com<mailto:henry.font...@jci.com>
[cid:image001.jpg@01D8597F.19B46100]

From: tston...@comcast.net 
Sent: Tuesday, April 26, 2022 3:01 PM
To: 'Tom Wellen' ; sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

The Hanger chapter in NFPA 13 only mentions the structure. I don’t believe it 
was the intention to allow attachments to grated floor systems.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
 CELL: (802) 373-0638
 tston...@comcast.net<mailto:tston...@comcast.net>

From: Tom Wellen mailto:tgwel...@gmail.com>>
Sent: Tuesday, April 26, 2022 1:45 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe Hanger


I ran into an installation where the ring hanger was attached to the metal 
grating to support sprinkler pipe below. I'm trying to find the right way to 
support the fire sprinkler pipe. I searched several manufacturers, but I don't 
see a metal grating clip that accepts all thread for fire protection. Most 
hangers were attached to structural steel using Sammys.

Are there any listed attachments to metal grating for hangers supporting fire 
sprinkler pipe?


Tom Wellen
McKinney Fire Marshal's Office
972-547-2854

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

2022-04-26 Thread tstone52
The Hanger chapter in NFPA 13 only mentions the structure. I don’t believe it 
was the intention to allow attachments to grated floor systems.

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

 CELL: (802) 373-0638  

   tston...@comcast.net

 

From: Tom Wellen  
Sent: Tuesday, April 26, 2022 1:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe Hanger

 

 

I ran into an installation where the ring hanger was attached to the metal 
grating to support sprinkler pipe below. I'm trying to find the right way to 
support the fire sprinkler pipe. I searched several manufacturers, but I don't 
see a metal grating clip that accepts all thread for fire protection. Most 
hangers were attached to structural steel using Sammys. 

 

Are there any listed attachments to metal grating for hangers supporting fire 
sprinkler pipe?

 

 

Tom Wellen

McKinney Fire Marshal's Office

972-547-2854


_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

2022-04-26 Thread Brett Peters
We've used a carriage bolt and fender washers

Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca




On Tue, Apr 26, 2022 at 12:47 PM Chris Dorn <
chris.d...@dornfireprotection.com> wrote:

> We have used stove bolts with a large head and a long thread. That
> minimizes the possibility of a trip hazard as there is only a small bump on
> top of the grating.
>
> Christopher Dorn
> Dorn Fire Protection LLC
> 4132 Dumont Street #4
> Cincinnati, Ohio 45226
> (513) 295-2499
>
> On Apr 26, 2022, at 2:46 PM, Joe Burtell  wrote:
>
> 
> In the past, I have done (2) ceiling flanges, one on the top and one on
> the bottom of the grate to make a sandwich.
>
>
> Best regards,
>
> *Joe Burtell, SET, CFPS*
>
> [image: Burtell Fire_Small]
>
> Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
>
> 116 N. 11th Street | Billings, MT 59101
>
> Email: j...@burtellfire.com
>
> Web Site: http://www.burtellfire.com
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
> *NOTICE:*  The information contained in this e-mail transmission is
> intended only for use of the individual or entity named above.  This e-mail
> transmission, and any documents, files, previous e-mail transmissions or
> other information attached to it, may contain confidential information that
> is legally privileged.  If you are not the intended recipient of this
> e-mail transmission, or the employee or agent responsible for delivering it
> to the intended recipient, you are hereby notified that any disclosure,
> dissemination, distribution, copying or other use of this transmission or
> any of the information contained in or attached to this e-mail is strictly
> prohibited.  If you have received this e-mail transmission in error, please
> immediately notify us by return e-mail transmission and destroy the
> original e-mail transmission as well as its attachments without reading or
> saving it in any manner.  Thank you.
>
>
> On Tue, Apr 26, 2022 at 12:12 PM Taylor Schumacher 
> wrote:
>
>> Not sure you will find one. How did they attach to the grating? Toggle
>> hangers?
>>
>>
>>
>>
>>
>> *Taylor Schumacher CET*
>>
>>
>>
>>
>>
>>
>>
>> *From:* Tom Wellen 
>> *Sent:* Tuesday, April 26, 2022 12:45 PM
>> *To:* sprinklerforum@lists.firesprinkler.org
>> *Subject:* [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe
>> Hanger
>>
>>
>>
>>
>>
>> I ran into an installation where the ring hanger was attached to the
>> metal grating to support sprinkler pipe below. I'm trying to find the right
>> way to support the fire sprinkler pipe. I searched several manufacturers,
>> but I don't see a metal grating clip that accepts all thread for fire
>> protection. Most hangers were attached to structural steel using Sammys.
>>
>>
>>
>> Are there any listed attachments to metal grating for hangers supporting
>> fire sprinkler pipe?
>>
>>
>>
>>
>>
>> Tom Wellen
>>
>> McKinney Fire Marshal's Office
>>
>> 972-547-2854
>>
>> _
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> sprinklerforum-le...@lists.firesprinkler.org
>
> [image: image001.jpg]
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
>
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

2022-04-26 Thread Chris Dorn
We have used stove bolts with a large head and a long thread. That minimizes 
the possibility of a trip hazard as there is only a small bump on top of the 
grating.

Christopher Dorn
Dorn Fire Protection LLC
4132 Dumont Street #4
Cincinnati, Ohio 45226
(513) 295-2499

On Apr 26, 2022, at 2:46 PM, Joe Burtell  wrote:


In the past, I have done (2) ceiling flanges, one on the top and one on the 
bottom of the grate to make a sandwich.



Best regards,

Joe Burtell, SET, CFPS

[Burtell Fire_Small]

Phone | Fax | Mobile| Text 406-204-4653

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com

Web Site: http://www.burtellfire.com

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

NOTICE:  The information contained in this e-mail transmission is intended only 
for use of the individual or entity named above.  This e-mail transmission, and 
any documents, files, previous e-mail transmissions or other information 
attached to it, may contain confidential information that is legally 
privileged.  If you are not the intended recipient of this e-mail transmission, 
or the employee or agent responsible for delivering it to the intended 
recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.


On Tue, Apr 26, 2022 at 12:12 PM Taylor Schumacher 
mailto:tay...@sfsprinkler.com>> wrote:
Not sure you will find one. How did they attach to the grating? Toggle hangers?


Taylor Schumacher CET



From: Tom Wellen mailto:tgwel...@gmail.com>>
Sent: Tuesday, April 26, 2022 12:45 PM
To: 
sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe Hanger


I ran into an installation where the ring hanger was attached to the metal 
grating to support sprinkler pipe below. I'm trying to find the right way to 
support the fire sprinkler pipe. I searched several manufacturers, but I don't 
see a metal grating clip that accepts all thread for fire protection. Most 
hangers were attached to structural steel using Sammys.

Are there any listed attachments to metal grating for hangers supporting fire 
sprinkler pipe?


Tom Wellen
McKinney Fire Marshal's Office
972-547-2854

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org
[image001.jpg]
_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

2022-04-26 Thread Joe Burtell
In the past, I have done (2) ceiling flanges, one on the top and one on the
bottom of the grate to make a sandwich.


Best regards,

*Joe Burtell, SET, CFPS*

[image: Burtell Fire_Small]

Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com

Web Site: http://www.burtellfire.com

*“**The bitterness of poor quality remains long after the sweetness of low
price is forgotten.**”*

*NOTICE:*  The information contained in this e-mail transmission is
intended only for use of the individual or entity named above.  This e-mail
transmission, and any documents, files, previous e-mail transmissions or
other information attached to it, may contain confidential information that
is legally privileged.  If you are not the intended recipient of this
e-mail transmission, or the employee or agent responsible for delivering it
to the intended recipient, you are hereby notified that any disclosure,
dissemination, distribution, copying or other use of this transmission or
any of the information contained in or attached to this e-mail is strictly
prohibited.  If you have received this e-mail transmission in error, please
immediately notify us by return e-mail transmission and destroy the
original e-mail transmission as well as its attachments without reading or
saving it in any manner.  Thank you.


On Tue, Apr 26, 2022 at 12:12 PM Taylor Schumacher 
wrote:

> Not sure you will find one. How did they attach to the grating? Toggle
> hangers?
>
>
>
>
>
> *Taylor Schumacher CET*
>
>
>
>
>
>
>
> *From:* Tom Wellen 
> *Sent:* Tuesday, April 26, 2022 12:45 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe
> Hanger
>
>
>
>
>
> I ran into an installation where the ring hanger was attached to the metal
> grating to support sprinkler pipe below. I'm trying to find the right way
> to support the fire sprinkler pipe. I searched several manufacturers, but I
> don't see a metal grating clip that accepts all thread for fire protection.
> Most hangers were attached to structural steel using Sammys.
>
>
>
> Are there any listed attachments to metal grating for hangers supporting
> fire sprinkler pipe?
>
>
>
>
>
> Tom Wellen
>
> McKinney Fire Marshal's Office
>
> 972-547-2854
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org

_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Metal Grating Clip for Fire Sprinkler Pipe Hanger

2022-04-26 Thread Taylor Schumacher
Not sure you will find one. How did they attach to the grating? Toggle hangers?


Taylor Schumacher CET



From: Tom Wellen 
Sent: Tuesday, April 26, 2022 12:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Metal Grating Clip for Fire Sprinkler Pipe Hanger


I ran into an installation where the ring hanger was attached to the metal 
grating to support sprinkler pipe below. I'm trying to find the right way to 
support the fire sprinkler pipe. I searched several manufacturers, but I don't 
see a metal grating clip that accepts all thread for fire protection. Most 
hangers were attached to structural steel using Sammys.

Are there any listed attachments to metal grating for hangers supporting fire 
sprinkler pipe?


Tom Wellen
McKinney Fire Marshal's Office
972-547-2854