Re: Grooved joints in pump suction main

2021-04-06 Thread John Denhardt via Sprinklerforum
I have completed hundreds of design, installations, and commissioning with
grooved connections on the suction and discharge sides of fire pumps.  I
never have seen an issue.  In fact, I use FxG adapters when I have
flanged valves or fittings.  I know it probably will not happen during my
career, but I have requested the fire pump manufacturers use groove
connections at the fire pump suction and discharge connections.

*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the **AFSA, and/or NFPA or its
technical committees.**AFSA cannot provide design or consulting engineering
services, and this opinion should therefore not be considered, nor relied
upon, as such.*

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Expand your business with ITM*
Professionalize the role of your inspection team with AFSA’s ITM Inspector
Development Program. This comprehensive 20-month program provides a blended
learning environment teamed with robust curriculum created by top industry
leaders. Plus, the first six-months of instruction is online. Now
enrolling for Spring 2021 <https://www.firesprinkler.org/itm>.


On Tue, Apr 6, 2021 at 5:22 PM Steve Leyton via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Yeah, a sucked rubber was front and center on my worry list.
>
> -Original Message-
> From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com]
> Sent: Tuesday, April 06, 2021 2:18 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matt Grise ; Steve Leyton <
> st...@protectiondesign.com>
> Subject: RE: Grooved joints in pump suction main
>
> We use grooved all the time as well (like hundreds of times) and I'm not
> aware of any issue as a result of it. I'm pretty confident that there isn't
> a rule against it. I've never seen it suck one of the gaskets through the
> pump, if that's what you're concerned about.
>
> -Kyle M
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Matt Grise via Sprinklerforum
> Sent: Tuesday, April 6, 2021 2:12 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matt Grise ; Steve Leyton <
> st...@protectiondesign.com>
> Subject: [EXTERNAL] RE: Grooved joints in pump suction main
>
> I am not aware of any prohibitions. We use grooved when we can. For
> whatever reason (tradition?) gate valves seem to always be flanged, so we
> frequently go flanged just due to availability.
>
> Matt
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Steve Leyton via Sprinklerforum
> Sent: Tuesday, April 06, 2021 4:09 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Steve Leyton 
> Subject: Grooved joints in pump suction main
>
> We've got this pump house...  Took over the design from a civil engineer
> and have been in repair mode for a couple weeks.   The original concept
> used a pre-engineered and all-inclusive pump house but the assembly won't
> be accepted by the state agency with jurisdiction because it hasn't passed
> the CA seismic testing gauntlet and is thus, not considered a
> pre-engineered/pre-approved structure.   In the course of revising this to
> slab-on-grade building, the pumps go from sitting on frames that are part
> of the floor assembly to skid-mounted and we have to furnish housekeeping
> pads that are currently really tall.   Since pump suction is 10" and we
> need a flex coupling near the floor and we have a 10" flanged ell on top of
> two flange x groove pieces, the CL of pump suction has risen to about 3'-8"
> above the floor requires a 19" concrete pad.   If I can attached the
> suction main directly to the flex coupling at about 12-14" above the FF, we
> can cut nearly a foot out of this housekeeping pad
>   so the question is:
>
> Is there any statutory prohibition or observation of good practices that
> precludes using grooved fittings and control valves on a pump suction
> main?  For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi
> pumps with high static of about 70 psi.
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>

RE: Grooved joints in pump suction main

2021-04-06 Thread Steve Leyton via Sprinklerforum
Yeah, a sucked rubber was front and center on my worry list.

-Original Message-
From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com] 
Sent: Tuesday, April 06, 2021 2:18 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise ; Steve Leyton 
Subject: RE: Grooved joints in pump suction main

We use grooved all the time as well (like hundreds of times) and I'm not aware 
of any issue as a result of it. I'm pretty confident that there isn't a rule 
against it. I've never seen it suck one of the gaskets through the pump, if 
that's what you're concerned about.

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Tuesday, April 6, 2021 2:12 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise ; Steve Leyton 
Subject: [EXTERNAL] RE: Grooved joints in pump suction main

I am not aware of any prohibitions. We use grooved when we can. For whatever 
reason (tradition?) gate valves seem to always be flanged, so we frequently go 
flanged just due to availability.

Matt 

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Tuesday, April 06, 2021 4:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton 
Subject: Grooved joints in pump suction main

We've got this pump house...  Took over the design from a civil engineer and 
have been in repair mode for a couple weeks.   The original concept used a 
pre-engineered and all-inclusive pump house but the assembly won't be accepted 
by the state agency with jurisdiction because it hasn't passed the CA seismic 
testing gauntlet and is thus, not considered a pre-engineered/pre-approved 
structure.   In the course of revising this to slab-on-grade building, the 
pumps go from sitting on frames that are part of the floor assembly to 
skid-mounted and we have to furnish housekeeping pads that are currently really 
tall.   Since pump suction is 10" and we need a flex coupling near the floor 
and we have a 10" flanged ell on top of two flange x groove pieces, the CL of 
pump suction has risen to about 3'-8" above the floor requires a 19" concrete 
pad.   If I can attached the suction main directly to the flex coupling at 
about 12-14" above the FF, we can cut nearly a foot out of this housekeeping pad
  so the question is:

Is there any statutory prohibition or observation of good practices that 
precludes using grooved fittings and control valves on a pump suction main?  
For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi pumps with 
high static of about 70 psi.

Steve Leyton
Protection Design & Consulting
San Diego, CA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252flists.firesprinkler.org-252flistinfo.cgi-252fsprinklerforum-2Dfiresprinkler.org-26c-3DE-2C1-2CNnQzlWnaYQG-5F1baqspRog4lZipjuu1qC-2DvaxML0zbRemLsolrdJFec-2DBaDtdud3LEqPl4vB4cPX1BnecsWRo2SV6VuCOY0YZdoos-5FgO38Aa3vxYvQiV-5FrUsl-2Dt5x-26typo-3D1=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8cLmSgn5hFqHpYI_MvWSgA=cYRxJJv80S71XfnU8UEmldZnkm132CKnTGHqQAbneW0=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8cLmSgn5hFqHpYI_MvWSgA=GS65IGQx-_dNIu1nxThV1C0g_zMjjs8OLZqNIThPhhQ=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Grooved joints in pump suction main

2021-04-06 Thread Steve Leyton via Sprinklerforum
We'll stop the D.I. at 6-7" AFF and go to a steel F x G spool with a flexibly 
coupling to a grooved ell.   Probably cut Sch. 40 but not ductile.   

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Duross via Sprinklerforum
Sent: Tuesday, April 06, 2021 2:20 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Tom Duross 
Subject: RE: Grooved joints in pump suction main

Cut grooved ductile I presume?  I've seen that many times.

-Original Message-
From: Sprinklerforum  On Behalf 
Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, April 06, 2021 5:18 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery ; Matt Grise 
; Steve Leyton 
Subject: RE: Grooved joints in pump suction main

We use grooved all the time as well (like hundreds of times) and I'm not aware 
of any issue as a result of it. I'm pretty confident that there isn't a rule 
against it. I've never seen it suck one of the gaskets through the pump, if 
that's what you're concerned about.

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Tuesday, April 6, 2021 2:12 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise ; Steve Leyton 
Subject: [EXTERNAL] RE: Grooved joints in pump suction main

I am not aware of any prohibitions. We use grooved when we can. For whatever 
reason (tradition?) gate valves seem to always be flanged, so we frequently go 
flanged just due to availability.

Matt 

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Tuesday, April 06, 2021 4:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton 
Subject: Grooved joints in pump suction main

We've got this pump house...  Took over the design from a civil engineer and
have been in repair mode for a couple weeks.   The original concept used a
pre-engineered and all-inclusive pump house but the assembly won't be accepted 
by the state agency with jurisdiction because it hasn't passed the CA seismic 
testing gauntlet and is thus, not considered a
pre-engineered/pre-approved structure.   In the course of revising this to
slab-on-grade building, the pumps go from sitting on frames that are part of 
the floor assembly to skid-mounted and we have to furnish housekeeping pads
that are currently really tall.   Since pump suction is 10" and we need a
flex coupling near the floor and we have a 10" flanged ell on top of two flange 
x groove pieces, the CL of pump suction has risen to about 3'-8"
above the floor requires a 19" concrete pad.   If I can attached the suction
main directly to the flex coupling at about 12-14" above the FF, we can cut 
nearly a foot out of this housekeeping pad
  so the question is:

Is there any statutory prohibition or observation of good practices that 
precludes using grooved fittings and control valves on a pump suction main?
For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi pumps with 
high static of about 70 psi.

Steve Leyton
Protection Design & Consulting
San Diego, CA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com
_url-3Fa-3Dhttp-253a-252f-252flists.firesprinkler.org-252flistinfo.cgi-252fs
prinklerforum-2Dfiresprinkler.org-26c-3DE-2C1-2CNnQzlWnaYQG-5F1baqspRog4lZip
juu1qC-2DvaxML0zbRemLsolrdJFec-2DBaDtdud3LEqPl4vB4cPX1BnecsWRo2SV6VuCOY0YZdo
os-5FgO38Aa3vxYvQiV-5FrUsl-2Dt5x-26typo-3D1=DwICAg=wn3mZQLIuInh2ClcJ0_DI
A=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8cLmS
gn5hFqHpYI_MvWSgA=cYRxJJv80S71XfnU8UEmldZnkm132CKnTGHqQAbneW0=
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ
0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8
cLmSgn5hFqHpYI_MvWSgA=GS65IGQx-_dNIu1nxThV1C0g_zMjjs8OLZqNIThPhhQ=
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Grooved joints in pump suction main

2021-04-06 Thread Tom Duross via Sprinklerforum
Cut grooved ductile I presume?  I've seen that many times.

-Original Message-
From: Sprinklerforum  On
Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, April 06, 2021 5:18 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery ; Matt Grise
; Steve Leyton 
Subject: RE: Grooved joints in pump suction main

We use grooved all the time as well (like hundreds of times) and I'm not
aware of any issue as a result of it. I'm pretty confident that there isn't
a rule against it. I've never seen it suck one of the gaskets through the
pump, if that's what you're concerned about.

-Kyle M

-Original Message-
From: Sprinklerforum  On
Behalf Of Matt Grise via Sprinklerforum
Sent: Tuesday, April 6, 2021 2:12 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise ; Steve Leyton 
Subject: [EXTERNAL] RE: Grooved joints in pump suction main

I am not aware of any prohibitions. We use grooved when we can. For whatever
reason (tradition?) gate valves seem to always be flanged, so we frequently
go flanged just due to availability.

Matt 

-Original Message-
From: Sprinklerforum  On
Behalf Of Steve Leyton via Sprinklerforum
Sent: Tuesday, April 06, 2021 4:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton 
Subject: Grooved joints in pump suction main

We've got this pump house...  Took over the design from a civil engineer and
have been in repair mode for a couple weeks.   The original concept used a
pre-engineered and all-inclusive pump house but the assembly won't be
accepted by the state agency with jurisdiction because it hasn't passed the
CA seismic testing gauntlet and is thus, not considered a
pre-engineered/pre-approved structure.   In the course of revising this to
slab-on-grade building, the pumps go from sitting on frames that are part of
the floor assembly to skid-mounted and we have to furnish housekeeping pads
that are currently really tall.   Since pump suction is 10" and we need a
flex coupling near the floor and we have a 10" flanged ell on top of two
flange x groove pieces, the CL of pump suction has risen to about 3'-8"
above the floor requires a 19" concrete pad.   If I can attached the suction
main directly to the flex coupling at about 12-14" above the FF, we can cut
nearly a foot out of this housekeeping pad
  so the question is:

Is there any statutory prohibition or observation of good practices that
precludes using grooved fittings and control valves on a pump suction main?
For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi pumps
with high static of about 70 psi.

Steve Leyton
Protection Design & Consulting
San Diego, CA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com
_url-3Fa-3Dhttp-253a-252f-252flists.firesprinkler.org-252flistinfo.cgi-252fs
prinklerforum-2Dfiresprinkler.org-26c-3DE-2C1-2CNnQzlWnaYQG-5F1baqspRog4lZip
juu1qC-2DvaxML0zbRemLsolrdJFec-2DBaDtdud3LEqPl4vB4cPX1BnecsWRo2SV6VuCOY0YZdo
os-5FgO38Aa3vxYvQiV-5FrUsl-2Dt5x-26typo-3D1=DwICAg=wn3mZQLIuInh2ClcJ0_DI
A=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8cLmS
gn5hFqHpYI_MvWSgA=cYRxJJv80S71XfnU8UEmldZnkm132CKnTGHqQAbneW0= 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_
listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ
0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8
cLmSgn5hFqHpYI_MvWSgA=GS65IGQx-_dNIu1nxThV1C0g_zMjjs8OLZqNIThPhhQ= 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Grooved joints in pump suction main

2021-04-06 Thread Kyle.Montgomery via Sprinklerforum
We use grooved all the time as well (like hundreds of times) and I'm not aware 
of any issue as a result of it. I'm pretty confident that there isn't a rule 
against it. I've never seen it suck one of the gaskets through the pump, if 
that's what you're concerned about.

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Tuesday, April 6, 2021 2:12 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise ; Steve Leyton 
Subject: [EXTERNAL] RE: Grooved joints in pump suction main

I am not aware of any prohibitions. We use grooved when we can. For whatever 
reason (tradition?) gate valves seem to always be flanged, so we frequently go 
flanged just due to availability.

Matt 

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Tuesday, April 06, 2021 4:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton 
Subject: Grooved joints in pump suction main

We've got this pump house...  Took over the design from a civil engineer and 
have been in repair mode for a couple weeks.   The original concept used a 
pre-engineered and all-inclusive pump house but the assembly won't be accepted 
by the state agency with jurisdiction because it hasn't passed the CA seismic 
testing gauntlet and is thus, not considered a pre-engineered/pre-approved 
structure.   In the course of revising this to slab-on-grade building, the 
pumps go from sitting on frames that are part of the floor assembly to 
skid-mounted and we have to furnish housekeeping pads that are currently really 
tall.   Since pump suction is 10" and we need a flex coupling near the floor 
and we have a 10" flanged ell on top of two flange x groove pieces, the CL of 
pump suction has risen to about 3'-8" above the floor requires a 19" concrete 
pad.   If I can attached the suction main directly to the flex coupling at 
about 12-14" above the FF, we can cut nearly a foot out of this housekeeping pad
  so the question is:

Is there any statutory prohibition or observation of good practices that 
precludes using grooved fittings and control valves on a pump suction main?  
For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi pumps with 
high static of about 70 psi.

Steve Leyton
Protection Design & Consulting
San Diego, CA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252flists.firesprinkler.org-252flistinfo.cgi-252fsprinklerforum-2Dfiresprinkler.org-26c-3DE-2C1-2CNnQzlWnaYQG-5F1baqspRog4lZipjuu1qC-2DvaxML0zbRemLsolrdJFec-2DBaDtdud3LEqPl4vB4cPX1BnecsWRo2SV6VuCOY0YZdoos-5FgO38Aa3vxYvQiV-5FrUsl-2Dt5x-26typo-3D1=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8cLmSgn5hFqHpYI_MvWSgA=cYRxJJv80S71XfnU8UEmldZnkm132CKnTGHqQAbneW0=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwICAg=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=TAQfZmxpLkl8CBa3e20VY8cLmSgn5hFqHpYI_MvWSgA=GS65IGQx-_dNIu1nxThV1C0g_zMjjs8OLZqNIThPhhQ=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Grooved joints in pump suction main

2021-04-06 Thread Matt Grise via Sprinklerforum
I am not aware of any prohibitions. We use grooved when we can. For whatever 
reason (tradition?) gate valves seem to always be flanged, so we frequently go 
flanged just due to availability.

Matt 

-Original Message-
From: Sprinklerforum  On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Tuesday, April 06, 2021 4:09 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton 
Subject: Grooved joints in pump suction main

We've got this pump house...  Took over the design from a civil engineer and 
have been in repair mode for a couple weeks.   The original concept used a 
pre-engineered and all-inclusive pump house but the assembly won't be accepted 
by the state agency with jurisdiction because it hasn't passed the CA seismic 
testing gauntlet and is thus, not considered a pre-engineered/pre-approved 
structure.   In the course of revising this to slab-on-grade building, the 
pumps go from sitting on frames that are part of the floor assembly to 
skid-mounted and we have to furnish housekeeping pads that are currently really 
tall.   Since pump suction is 10" and we need a flex coupling near the floor 
and we have a 10" flanged ell on top of two flange x groove pieces, the CL of 
pump suction has risen to about 3'-8" above the floor requires a 19" concrete 
pad.   If I can attached the suction main directly to the flex coupling at 
about 12-14" above the FF, we can cut nearly a foot out of this housekeeping pad
  so the question is:

Is there any statutory prohibition or observation of good practices that 
precludes using grooved fittings and control valves on a pump suction main?  
For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi pumps with 
high static of about 70 psi.

Steve Leyton
Protection Design & Consulting
San Diego, CA

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org=E,1,NnQzlWnaYQG_1baqspRog4lZipjuu1qC-vaxML0zbRemLsolrdJFec-BaDtdud3LEqPl4vB4cPX1BnecsWRo2SV6VuCOY0YZdoos_gO38Aa3vxYvQiV_rUsl-t5x=1
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Grooved joints in pump suction main

2021-04-06 Thread Steve Leyton via Sprinklerforum
We've got this pump house...  Took over the design from a civil engineer and 
have been in repair mode for a couple weeks.   The original concept used a 
pre-engineered and all-inclusive pump house but the assembly won't be accepted 
by the state agency with jurisdiction because it hasn't passed the CA seismic 
testing gauntlet and is thus, not considered a pre-engineered/pre-approved 
structure.   In the course of revising this to slab-on-grade building, the 
pumps go from sitting on frames that are part of the floor assembly to 
skid-mounted and we have to furnish housekeeping pads that are currently really 
tall.   Since pump suction is 10" and we need a flex coupling near the floor 
and we have a 10" flanged ell on top of two flange x groove pieces, the CL of 
pump suction has risen to about 3'-8" above the floor requires a 19" concrete 
pad.   If I can attached the suction main directly to the flex coupling at 
about 12-14" above the FF, we can cut nearly a foot out of this housekeeping pad
  so the question is:

Is there any statutory prohibition or observation of good practices that 
precludes using grooved fittings and control valves on a pump suction main?  
For whatever it's worth, this is low pressure, 2,500 gpm at 54 psi pumps with 
high static of about 70 psi.

Steve Leyton
Protection Design & Consulting
San Diego, CA