RE: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread Steve Leyton via Sprinklerforum
A live/work nuclear reactor facility, perhaps...


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



 Original message 
From: Travis Mack via Sprinklerforum 
Date: 2/6/21 1:30 PM (GMT-08:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: travis.m...@mfpdesign.com
Subject: Re: NFPA 13R & NFPA 14 - (flow rates)

But domestic demand is added at the split with domestic and fire. The domestic 
wouldn’t flow through standpipes.

It would have to be some crazy accessory use.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Engineering Manager

MFP Design

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com/>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>


From: Sprinklerforum  on behalf 
of David L. Miller, P.E. via Sprinklerforum 

Sent: Saturday, February 6, 2021 2:27:55 PM
To: 'Jose Anibal Castillo' ; 
sprinklerforum@lists.firesprinkler.org 
; st...@protectiondesign.com 
; sbi...@wenteplumbing.com 

Cc: d...@engfirepro.com 
Subject: RE: NFPA 13R & NFPA 14 - (flow rates)

I suspect that requirement is due more to the Domestic Demand in a very 
(extremely) large apartment building. Table A.9.6(b) (NFPA 13R, 2016 Edition) 
shows a Domestic Demand of 500 gpm for a building with 3500 Fixture Units.

Without a plumbing code handy I don't know where the domestic demand would get 
to 1000 gpm, but I would assume it to be in the 7000 - 8000 Fixture Unit range 
based on Table 9.6(b). How likely is it to have 7000 or 8000 Fixture Units in a 
four-story building?

It might be possibly to hit 1000 gpm domestic demand in a great big apartment 
building (250 gpm per floor) then add the 13R sprinkler demand to that to 
technically exceed the standpipe demand.


David L. Miller, P.E.
Engineered Fire Protection, LLC
11920 Richcroft Avenue
Baton Rouge, Louisiana 70814
225-273-5040

>
>
>
> In practice, probably not. As I'm sitting here today, I can't honestly
> recall how/when that section came into being or when we may have last
> tweaked it, but it's a CYA for sure. Maybe if I had a building projected
> with 13R that had an accessory use like... I dunno, boat storage. A
> marina hotel or apartment/complex with boat storage - yeah, that's the
> ticket! The boat storage is solely for use by residents and guests, so
> 13R could be applied if allowed by the AHJ and that standard prescribes
> that design shall conform to 13 outside the dwelling units, so EH2 or some
> such. But that still doesn't account for the fact that it would have to
> be a high-rise building to require an automatic water supply for a Class 1
> system, but what about a Class 2 or 3 where water supply also has to be
> automatic?
>
> I dunno, I'm just trippin' but regardless of whether this makes sense or
> not, the preceding ramble is
> my opinion only and does not represent NFPA or the NFPA 14 Technical
> Committee, nor intended to serve as an interpretation of the standard.
>
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo 
> Subject: NFPA 13R & NFPA 14
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where
> 13R system demand is higher than the standpipe demand it is supposed to be
> chosen the higher demand.
>
> Is it even possible to have a residential sprinkler system with a higher
> demand than the standpipe?
>
>
> Regards
>
>
>
> Jos? A. Castillo
>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread Travis Mack via Sprinklerforum
But domestic demand is added at the split with domestic and fire. The domestic 
wouldn’t flow through standpipes.

It would have to be some crazy accessory use.


Travis Mack, CFPS, CWBSP, RME-G, COC, SET

Engineering Manager

MFP Design

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271 ext. 700 C: 480-272-2471

travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com/>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D=0>


From: Sprinklerforum  on behalf 
of David L. Miller, P.E. via Sprinklerforum 

Sent: Saturday, February 6, 2021 2:27:55 PM
To: 'Jose Anibal Castillo' ; 
sprinklerforum@lists.firesprinkler.org 
; st...@protectiondesign.com 
; sbi...@wenteplumbing.com 

Cc: d...@engfirepro.com 
Subject: RE: NFPA 13R & NFPA 14 - (flow rates)

I suspect that requirement is due more to the Domestic Demand in a very 
(extremely) large apartment building. Table A.9.6(b) (NFPA 13R, 2016 Edition) 
shows a Domestic Demand of 500 gpm for a building with 3500 Fixture Units.

Without a plumbing code handy I don't know where the domestic demand would get 
to 1000 gpm, but I would assume it to be in the 7000 - 8000 Fixture Unit range 
based on Table 9.6(b). How likely is it to have 7000 or 8000 Fixture Units in a 
four-story building?

It might be possibly to hit 1000 gpm domestic demand in a great big apartment 
building (250 gpm per floor) then add the 13R sprinkler demand to that to 
technically exceed the standpipe demand.


David L. Miller, P.E.
Engineered Fire Protection, LLC
11920 Richcroft Avenue
Baton Rouge, Louisiana 70814
225-273-5040

>
>
>
> In practice, probably not. As I'm sitting here today, I can't honestly
> recall how/when that section came into being or when we may have last
> tweaked it, but it's a CYA for sure. Maybe if I had a building projected
> with 13R that had an accessory use like... I dunno, boat storage. A
> marina hotel or apartment/complex with boat storage - yeah, that's the
> ticket! The boat storage is solely for use by residents and guests, so
> 13R could be applied if allowed by the AHJ and that standard prescribes
> that design shall conform to 13 outside the dwelling units, so EH2 or some
> such. But that still doesn't account for the fact that it would have to
> be a high-rise building to require an automatic water supply for a Class 1
> system, but what about a Class 2 or 3 where water supply also has to be
> automatic?
>
> I dunno, I'm just trippin' but regardless of whether this makes sense or
> not, the preceding ramble is
> my opinion only and does not represent NFPA or the NFPA 14 Technical
> Committee, nor intended to serve as an interpretation of the standard.
>
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo 
> Subject: NFPA 13R & NFPA 14
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where
> 13R system demand is higher than the standpipe demand it is supposed to be
> chosen the higher demand.
>
> Is it even possible to have a residential sprinkler system with a higher
> demand than the standpipe?
>
>
> Regards
>
>
>
> Jos? A. Castillo
>


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread David L. Miller, P.E. via Sprinklerforum
I suspect that requirement is due more to the Domestic Demand in a very 
(extremely) large apartment building.  Table A.9.6(b) (NFPA 13R, 2016 Edition) 
shows a Domestic Demand of 500 gpm for a building with 3500 Fixture Units.

Without a plumbing code handy I don't know where the domestic demand would get 
to 1000 gpm, but I would assume it to be in the 7000 - 8000 Fixture Unit range 
based on Table 9.6(b).  How likely is it to have 7000 or 8000 Fixture Units in 
a four-story building?  

It might be possibly to hit 1000 gpm domestic demand in a great big apartment 
building (250 gpm per floor) then add the 13R sprinkler demand to that to 
technically exceed the standpipe demand.


David L. Miller, P.E.
Engineered Fire Protection, LLC
11920 Richcroft Avenue
Baton Rouge, Louisiana  70814
225-273-5040

>
>
>
> In practice, probably not.   As I'm sitting here today, I can't honestly
> recall how/when that section came into being or when we may have last
> tweaked it, but it's a CYA for sure.Maybe if I had a building projected
> with 13R that had an accessory use like... I dunno, boat storage.   A
> marina hotel or apartment/complex with boat storage - yeah, that's the
> ticket!   The boat storage is solely for use by residents and guests, so
> 13R could be applied if allowed by the AHJ and that standard prescribes
> that design shall conform to 13 outside the dwelling units, so EH2 or some
> such.   But that still doesn't account for the fact that it would have to
> be a high-rise building to require an automatic water supply for a Class 1
> system, but what about a Class 2 or 3 where water supply also has to be
> automatic?
>
> I dunno, I'm just trippin' but regardless of whether this makes sense or
> not, the preceding ramble is
> my opinion only and does not represent NFPA or the NFPA 14 Technical
> Committee, nor intended to serve as an interpretation of the standard.
>
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo 
> Subject: NFPA 13R & NFPA 14
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where
> 13R system demand is higher than the standpipe demand it is supposed to be
> chosen the higher demand.
>
> Is it even possible to have a residential sprinkler system with a higher
> demand than the standpipe?
>
>
> Regards
>
>
>
> Jos? A.  Castillo
> 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA 13R & NFPA 14 - (flow rates)

2021-02-06 Thread Jose Anibal Castillo via Sprinklerforum
Thanks for the answers

Some thoughts

Section 7.10.1.3.1.1 of nfpa 14 is under 7.10.1 therefore it only applies
to Class I and Class III Systems not to class II. Also, that section is
under 7.10 flow rates therefore is not referring to pressure but flow
rates. Please correct me if I am wrong.

In that example, the apartment complex with the boat storage the part where
it is required to be used nfpa 13. If that is the case, then section
7.10.1.3.1.1 would not have needed to add 13R since with 13 would have been
good enough, I think.

I followed back and found that the 13R was added in 2013 edition of nfpa
14. Therefore, not sure if it was found an example where the solely use of  13R
was higher than a Class I and Class III standpipe system.

Best Regards.

On Fri, Feb 5, 2021 at 4:19 PM <
sprinklerforum-requ...@lists.firesprinkler.org> wrote:

> Send Sprinklerforum mailing list submissions to
> sprinklerforum@lists.firesprinkler.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> or, via email, send a message with subject or body 'help' to
> sprinklerforum-requ...@lists.firesprinkler.org
>
> You can reach the person managing the list at
> sprinklerforum-ow...@lists.firesprinkler.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Sprinklerforum digest..."
>
>
> Today's Topics:
>
>1. RE: NFPA 13R & NFPA 14 (Steve Leyton)
>2. RE: Existing Dry System (Chris Dorn)
>3. Re: NFPA 13R & NFPA 14 (Skyler Bilbo)
>4. Re: Existing Dry System (Skyler Bilbo)
>5. Slopes / Storage / UFC 3-600-01 change 5
>   (travis.m...@mfpdesign.com)
>6. Re: Slopes / Storage / UFC 3-600-01 change 5 (John Denhardt)
>7. RE: Slopes / Storage / UFC 3-600-01 change 5 (Cary Webber)
>8. RE: Slopes / Storage / UFC 3-600-01 change 5 (Ed Kramer)
>9. Re: Slopes / Storage / UFC 3-600-01 change 5 (John Denhardt)
>   10. Re: Slopes / Storage / UFC 3-600-01 change 5 (Tom Noble)
>   11. Re: Slopes / Storage / UFC 3-600-01 change 5 (Tom Noble)
>
>
> --
>
> Message: 1
> Date: Thu, 4 Feb 2021 21:37:02 +
> From: Steve Leyton 
> To: "sprinklerforum@lists.firesprinkler.org"
> 
> Subject: RE: NFPA 13R & NFPA 14
> Message-ID:
> <
> by5pr17mb3111ea0fed40d7eb3e31109ad5...@by5pr17mb3111.namprd17.prod.outlook.com
> >
>
> Content-Type: text/plain; charset="utf-8"
>
> In practice, probably not.   As I'm sitting here today, I can't honestly
> recall how/when that section came into being or when we may have last
> tweaked it, but it's a CYA for sure.Maybe if I had a building projected
> with 13R that had an accessory use like... I dunno, boat storage.   A
> marina hotel or apartment/complex with boat storage - yeah, that's the
> ticket!   The boat storage is solely for use by residents and guests, so
> 13R could be applied if allowed by the AHJ and that standard prescribes
> that design shall conform to 13 outside the dwelling units, so EH2 or some
> such.   But that still doesn't account for the fact that it would have to
> be a high-rise building to require an automatic water supply for a Class 1
> system, but what about a Class 2 or 3 where water supply also has to be
> automatic?
>
> I dunno, I'm just trippin' but regardless of whether this makes sense or
> not, the preceding ramble is
> my opinion only and does not represent NFPA or the NFPA 14 Technical
> Committee, nor intended to serve as an interpretation of the standard.
>
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
>
> -Original Message-----
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo 
> Subject: NFPA 13R & NFPA 14
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where
> 13R system demand is higher than the standpipe demand it is supposed to be
> chosen the higher demand.
>
> Is it even possible to have a residential sprinkler system with a higher
> demand than the standpipe?
>
>
> Regards
>
>
>
> Jos? A.  Castillo
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> --
>
> Message: 2
> Date: Thu,

Re: NFPA 13R & NFPA 14

2021-02-04 Thread Skyler Bilbo via Sprinklerforum
I could dream up a scenario where a 13R system had a higher pressure
requirement (with a lower flow) than a standpipe calculation.  Being
limited to 4 stories definitely makes this a lot less likely to occur in
the real world.  It could happen, but I have never seen it here in the real
world.


Skyler Bilbo


On Thu, Feb 4, 2021 at 3:37 PM Steve Leyton via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> In practice, probably not.   As I'm sitting here today, I can't honestly
> recall how/when that section came into being or when we may have last
> tweaked it, but it's a CYA for sure.Maybe if I had a building projected
> with 13R that had an accessory use like... I dunno, boat storage.   A
> marina hotel or apartment/complex with boat storage - yeah, that's the
> ticket!   The boat storage is solely for use by residents and guests, so
> 13R could be applied if allowed by the AHJ and that standard prescribes
> that design shall conform to 13 outside the dwelling units, so EH2 or some
> such.   But that still doesn't account for the fact that it would have to
> be a high-rise building to require an automatic water supply for a Class 1
> system, but what about a Class 2 or 3 where water supply also has to be
> automatic?
>
> I dunno, I'm just trippin' but regardless of whether this makes sense or
> not, the preceding ramble is
> my opinion only and does not represent NFPA or the NFPA 14 Technical
> Committee, nor intended to serve as an interpretation of the standard.
>
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
>
> -Original Message-
> From: Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Jose Anibal
> Castillo via Sprinklerforum
> Sent: Thursday, February 04, 2021 7:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo 
> Subject: NFPA 13R & NFPA 14
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where
> 13R system demand is higher than the standpipe demand it is supposed to be
> chosen the higher demand.
>
> Is it even possible to have a residential sprinkler system with a higher
> demand than the standpipe?
>
>
> Regards
>
>
>
> José A.  Castillo
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13R & NFPA 14

2021-02-04 Thread Steve Leyton via Sprinklerforum
In practice, probably not.   As I'm sitting here today, I can't honestly recall 
how/when that section came into being or when we may have last tweaked it, but 
it's a CYA for sure.Maybe if I had a building projected with 13R that had 
an accessory use like... I dunno, boat storage.   A marina hotel or 
apartment/complex with boat storage - yeah, that's the ticket!   The boat 
storage is solely for use by residents and guests, so 13R could be applied if 
allowed by the AHJ and that standard prescribes that design shall conform to 13 
outside the dwelling units, so EH2 or some such.   But that still doesn't 
account for the fact that it would have to be a high-rise building to require 
an automatic water supply for a Class 1 system, but what about a Class 2 or 3 
where water supply also has to be automatic?   

I dunno, I'm just trippin' but regardless of whether this makes sense or not, 
the preceding ramble is 
my opinion only and does not represent NFPA or the NFPA 14 Technical Committee, 
nor intended to serve as an interpretation of the standard.


Steve Leyton
Protection Design & Consulting
San Diego, CA 





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jose Anibal Castillo via Sprinklerforum
Sent: Thursday, February 04, 2021 7:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Jose Anibal Castillo 
Subject: NFPA 13R & NFPA 14

In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R 
system demand is higher than the standpipe demand it is supposed to be chosen 
the higher demand.

Is it even possible to have a residential sprinkler system with a higher demand 
than the standpipe?


Regards



José A.  Castillo
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA 13R & NFPA 14

2021-02-04 Thread John Denhardt via Sprinklerforum
Agree - anything could be possible!  But very hard indeed.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Our members are at the heart of everything we do*


*Be a Member, Get a Member*

We’re introducing many new programs to help meet your team’s business
needs. AFSA is offering a six-month trial membership for contractors and a
12-month trial membership for municipal AHJs. Let’s help potential members
see what they’re missing! Current members who recruit a new contractor
member will receive a $100 gift card and the new member gets a free
webinar.  Let’s grow stronger together! Join AFSA
<http://www.firesprinkler.org/join>.




On Thu, Feb 4, 2021 at 12:28 PM Cary Webber via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> One would have to try very hard...but nothing is impossible!
>
>
>
> Cary Webber CFPS Director, Technical Services
> Reliable Automatic Sprinkler Co., Inc.
> 1470 Smith Grove Road, Liberty, SC  29657
> Tel: 864-843-5161
>
>
>
> -Original Message-
> From: Sprinklerforum  On
> Behalf Of Jose Anibal Castillo via Sprinklerforum
> Sent: Thursday, February 4, 2021 10:43 AM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Jose Anibal Castillo 
> Subject: NFPA 13R & NFPA 14
>
> CAUTION: This email originated from outside of the organization. Do not
> click links or open attachments unless you can confirm the sender and know
> the content is safe.
>
>
> In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where
> 13R system demand is higher than the standpipe demand it is supposed to be
> chosen the higher demand.
>
> Is it even possible to have a residential sprinkler system with a higher
> demand than the standpipe?
>
>
> Regards
>
>
>
> José A.  Castillo
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.orgdata=04%7C01%7Ccwebber%40reliablesprinkler.com%7Ce8bb25665c444e3c4b4108d8c923a6e9%7C361f92efbca442cdaf0d8099acee2244%7C0%7C0%7C637480502547341878%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000sdata=oYvWE517JhGg0d0mdIxRXBxa1UIGQo%2FlGyt0fzc3Nmg%3Dreserved=0
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13R & NFPA 14

2021-02-04 Thread Cary Webber via Sprinklerforum
One would have to try very hard...but nothing is impossible!



Cary Webber CFPS Director, Technical Services
Reliable Automatic Sprinkler Co., Inc.
1470 Smith Grove Road, Liberty, SC  29657 
Tel: 864-843-5161 



-Original Message-
From: Sprinklerforum  On Behalf 
Of Jose Anibal Castillo via Sprinklerforum
Sent: Thursday, February 4, 2021 10:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Jose Anibal Castillo 
Subject: NFPA 13R & NFPA 14

CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you can confirm the sender and know the 
content is safe.


In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R 
system demand is higher than the standpipe demand it is supposed to be chosen 
the higher demand.

Is it even possible to have a residential sprinkler system with a higher demand 
than the standpipe?


Regards



José A.  Castillo
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.firesprinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.orgdata=04%7C01%7Ccwebber%40reliablesprinkler.com%7Ce8bb25665c444e3c4b4108d8c923a6e9%7C361f92efbca442cdaf0d8099acee2244%7C0%7C0%7C637480502547341878%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000sdata=oYvWE517JhGg0d0mdIxRXBxa1UIGQo%2FlGyt0fzc3Nmg%3Dreserved=0
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: [EXTERNAL] NFPA 13R & NFPA 14

2021-02-04 Thread Kyle.Montgomery via Sprinklerforum
It is if there is no requirement for a standpipe.

-Kyle M

-Original Message-
From: Sprinklerforum  On Behalf 
Of Jose Anibal Castillo via Sprinklerforum
Sent: Thursday, February 4, 2021 8:43 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Jose Anibal Castillo 
Subject: [EXTERNAL] NFPA 13R & NFPA 14

In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R 
system demand is higher than the standpipe demand it is supposed to be chosen 
the higher demand.

Is it even possible to have a residential sprinkler system with a higher demand 
than the standpipe?


Regards



José A.  Castillo
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org=DwIGaQ=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=rYQ1ksDj1zRZnWzsq-WD8_4Y8idQ1MgYekE5tZTca8w=Ax0UOb5CK1LXIqOhcVuDUV8oA4vTKBRhY-rYrvkCFgg=
 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA 13R & NFPA 14

2021-02-04 Thread Jose Anibal Castillo via Sprinklerforum
In section 7.10.1.3.1.1 of the nfpa 14, 2019 states that in cases where 13R
system demand is higher than the standpipe demand it is supposed to be
chosen the higher demand.

Is it even possible to have a residential sprinkler system with a higher
demand than the standpipe?


Regards



José A.  Castillo
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org