RE: Diesel Pump Engine RPM

2010-09-01 Thread Fletcher, Ron
For a retrofit you wouldn't do a pump test and then use the results of the test 
for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i believe. 
So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can the pressure produced at the higher rpm be used for the system
calculations? In other words can the actual pump test be used for the
system calc's or must we use the manufacturers data sheet regardless the
test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Diesel Pump Engine RPM

2010-09-01 Thread cherokeefire...@aol.com
The pumps are listed by UL per an approved, ISO registered process. 

The mfr wont guarantee a new pump to perform up to and including the safety 
margin. 

You are proposing a performance based design, using the safety margin. 

If this is not an accepted design method in new pump installations, then it is 
likely not in retro fits either. 

The pump performance test could be used to measure any degradation in 
performance against the original curve. 


Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless Phone

- Reply message -
From: Fletcher, Ron rfletc...@aerofire.com
Date: Wed, Sep 1, 2010 9:58 am
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

For a retrofit you wouldn't do a pump test and then use the results of the test 
for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i believe. 
So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can the pressure produced at the higher rpm be used for the system
calculations? In other words can the actual pump test be used for the
system calc's or must we use the manufacturers data sheet regardless the
test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Diesel Pump Engine RPM

2010-09-01 Thread George Church
NFPA 13 and 20 certainly DO allow performance-based designs under 1.5
Equivalency. 
So long as a test indicates a certain level of performance, and the AHJ
approves the use of those results and the contractor is prudent enough to
allow degradation of pump and water supply to the satisfaction of the AHJ,
or AHJs (plural) since BCO, fire official, and insurance AHJ could all be
involved, if it is APPROVED (found acceptable to the AHJs) then there is
nothing preventing the use of more than the rating of a pump if that higher
level of performance exists that I'm aware of. Written documentation by a
qualified person must be submitted to the AHJ to gain approval.

Versus the competitor who, in a proposal I just read, that their insurance
carrier wouldn't let them do anything that wasn't in the code. Well, its in
there, I just don't think they know what options are available to them, and
I sure bet they don't subscribe to this Forum where they could learn. You
get out of it what you put into it, and from the sound of their proposal,
they don't put forth much extra effort. (sigh) sometimes its like shooting
fish in a barrel, we got the job. Thanks, AFSA, for hosting the Forum.

glc 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Wednesday, September 01, 2010 11:42 AM
To: Fletcher, Ron; sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

The pumps are listed by UL per an approved, ISO registered process. 

The mfr wont guarantee a new pump to perform up to and including the safety
margin. 

You are proposing a performance based design, using the safety margin. 

If this is not an accepted design method in new pump installations, then it
is likely not in retro fits either. 

The pump performance test could be used to measure any degradation in
performance against the original curve. 


Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless Phone

- Reply message -
From: Fletcher, Ron rfletc...@aerofire.com
Date: Wed, Sep 1, 2010 9:58 am
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

For a retrofit you wouldn't do a pump test and then use the results of the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%) can
the pressure produced at the higher rpm be used for the system calculations?
In other words can the actual pump test be used for the system calc's or
must we use the manufacturers data sheet regardless the test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email

RE: Diesel Pump Engine RPM

2010-09-01 Thread Thom
Not doing pumps on a regular basis, I may be missing something but your
required to compare the actual performance with the Certified pump curve.
Now we always received the certified curve with the pump, and there were
minor diviations from the Cat. Curves. So I would say that if your design
meets the Certified curve performance your OK. Using any Actual
performance above that curve would be iffy, as you'd have to prove it's not
based upon a varied supply or other factor.

Example: Static 50 Residual 20 @ 1750, but the engineer requires that you
only use 45/2...@1575 for future supply degrading. You should exceed the
design when you run your pump test, but if you try and use that, you'll
negate the safety factor the ERO was building in.

Thom

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday, September 01, 2010 7:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

For a retrofit you wouldn't do a pump test and then use the results of the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can the pressure produced at the higher rpm be used for the system
calculations? In other words can the actual pump test be used for the
system calc's or must we use the manufacturers data sheet regardless the
test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Diesel Pump Engine RPM

2010-09-01 Thread Fletcher, Ron
That was the beauty of the PLD's. We could size the pump to compensate
for the mandatory de-rating of the supply and buy back the pressure
without going over 175 psi.


Ron Fletcher
Aero Automatic
Phoenix, AZ


 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Wednesday, September 01, 2010 8:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

Not doing pumps on a regular basis, I may be missing something but your
required to compare the actual performance with the Certified pump
curve.
Now we always received the certified curve with the pump, and there were
minor diviations from the Cat. Curves. So I would say that if your
design
meets the Certified curve performance your OK. Using any Actual
performance above that curve would be iffy, as you'd have to prove it's
not
based upon a varied supply or other factor.

Example: Static 50 Residual 20 @ 1750, but the engineer requires that
you
only use 45/2...@1575 for future supply degrading. You should exceed the
design when you run your pump test, but if you try and use that, you'll
negate the safety factor the ERO was building in.

Thom

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Wednesday, September 01, 2010 7:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

For a retrofit you wouldn't do a pump test and then use the results of
the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs
according
to the engine as you approach no load.  Engines have an operating range
and
usually selected and governor set for the pump's requirements.  I
thought
there might be a disclaimer in the most recent 20 regarding PLD
controllers,
but not to my knowledge.  I know with non-PLD controllers, we always
start
at 150% and work our way back when testing engine-driven pumps as that
helps
cool-down.  Plus, you can check RPM at first flow point.  It's
unfortunate
affinity calculations are based upon constant speed (as I understand
them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can the pressure produced at the higher rpm be used for the system
calculations? In other words can the actual pump test be used for the
system calc's or must we use the manufacturers data sheet regardless the
test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp

RE: Diesel Pump Engine RPM

2010-09-01 Thread George Church
It's not as easy to retrofit one on a Tier III as it first seemed..

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday, September 01, 2010 12:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

That was the beauty of the PLD's. We could size the pump to compensate for
the mandatory de-rating of the supply and buy back the pressure without
going over 175 psi.


Ron Fletcher
Aero Automatic
Phoenix, AZ


 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Wednesday, September 01, 2010 8:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

Not doing pumps on a regular basis, I may be missing something but your
required to compare the actual performance with the Certified pump curve.
Now we always received the certified curve with the pump, and there were
minor diviations from the Cat. Curves. So I would say that if your design
meets the Certified curve performance your OK. Using any Actual
performance above that curve would be iffy, as you'd have to prove it's not
based upon a varied supply or other factor.

Example: Static 50 Residual 20 @ 1750, but the engineer requires that you
only use 45/2...@1575 for future supply degrading. You should exceed the
design when you run your pump test, but if you try and use that, you'll
negate the safety factor the ERO was building in.

Thom

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday, September 01, 2010 7:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

For a retrofit you wouldn't do a pump test and then use the results of the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%) can
the pressure produced at the higher rpm be used for the system calculations?
In other words can the actual pump test be used for the system calc's or
must we use the manufacturers data sheet regardless the test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

RE: Diesel Pump Engine RPM

2010-09-01 Thread Phelps, Mark
Can any of the pump manufacturers weigh in on this issue, and elaborate
a little on the future availability of a PLD on a Tier III?
Mark at Aero

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George
Church
Sent: Wednesday, September 01, 2010 9:24 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

It's not as easy to retrofit one on a Tier III as it first seemed..

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Wednesday, September 01, 2010 12:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

That was the beauty of the PLD's. We could size the pump to compensate
for
the mandatory de-rating of the supply and buy back the pressure without
going over 175 psi.


Ron Fletcher
Aero Automatic
Phoenix, AZ


 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Wednesday, September 01, 2010 8:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

Not doing pumps on a regular basis, I may be missing something but your
required to compare the actual performance with the Certified pump
curve.
Now we always received the certified curve with the pump, and there were
minor diviations from the Cat. Curves. So I would say that if your
design
meets the Certified curve performance your OK. Using any Actual
performance above that curve would be iffy, as you'd have to prove it's
not
based upon a varied supply or other factor.

Example: Static 50 Residual 20 @ 1750, but the engineer requires that
you
only use 45/2...@1575 for future supply degrading. You should exceed the
design when you run your pump test, but if you try and use that, you'll
negate the safety factor the ERO was building in.

Thom

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Wednesday, September 01, 2010 7:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

For a retrofit you wouldn't do a pump test and then use the results of
the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs
according
to the engine as you approach no load.  Engines have an operating range
and
usually selected and governor set for the pump's requirements.  I
thought
there might be a disclaimer in the most recent 20 regarding PLD
controllers,
but not to my knowledge.  I know with non-PLD controllers, we always
start
at 150% and work our way back when testing engine-driven pumps as that
helps
cool-down.  Plus, you can check RPM at first flow point.  It's
unfortunate
affinity calculations are based upon constant speed (as I understand
them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can
the pressure produced at the higher rpm be used for the system
calculations?
In other words can the actual pump test be used for the system calc's or
must we use the manufacturers data sheet regardless the test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send

RE: Diesel Pump Engine RPM

2010-09-01 Thread George Church
They're available now from Clarke. We're retrofitting one from 2009.

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Phelps, Mark
Sent: Wednesday, September 01, 2010 1:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

Can any of the pump manufacturers weigh in on this issue, and elaborate a
little on the future availability of a PLD on a Tier III?
Mark at Aero

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Wednesday, September 01, 2010 9:24 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

It's not as easy to retrofit one on a Tier III as it first seemed..

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday, September 01, 2010 12:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

That was the beauty of the PLD's. We could size the pump to compensate for
the mandatory de-rating of the supply and buy back the pressure without
going over 175 psi.


Ron Fletcher
Aero Automatic
Phoenix, AZ


 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Wednesday, September 01, 2010 8:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

Not doing pumps on a regular basis, I may be missing something but your
required to compare the actual performance with the Certified pump curve.
Now we always received the certified curve with the pump, and there were
minor diviations from the Cat. Curves. So I would say that if your design
meets the Certified curve performance your OK. Using any Actual
performance above that curve would be iffy, as you'd have to prove it's not
based upon a varied supply or other factor.

Example: Static 50 Residual 20 @ 1750, but the engineer requires that you
only use 45/2...@1575 for future supply degrading. You should exceed the
design when you run your pump test, but if you try and use that, you'll
negate the safety factor the ERO was building in.

Thom

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday, September 01, 2010 7:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM

For a retrofit you wouldn't do a pump test and then use the results of the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
cherokeefire...@aol.com
Sent: Tuesday, August 31, 2010 6:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%) can
the pressure produced at the higher rpm be used for the system calculations?
In other words can the actual pump test be used for the system calc's or
must we use the manufacturers data sheet regardless the test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp

RE: Diesel Pump Engine RPM

2010-09-01 Thread Tom Duross
I meant to mention Tier 3's, not a lot of experience on the new ones as yet
and nothing a year down the road and so on..  Should be interesting.
From what I know, bench drivers are only used on HSC electrics and verticals
with motors.  I posted about this once.  Look at the 'certified' curve and
see if the new pump was tested with a shop driver (adjustable for BHP and
speed) or the actual driver that came bolted to it.  I haven't seen too many
engine driven pump done at the factory with other than the designed engine.
Sometimes, in expediting the pump, the factory will use one of their
adjustable drives and pump from the break tank to get a curve done and out
to the salesman, mostly motor driven units.  I don't think I'm giving away
any secrets here, they all do it.  I will say on start-up of an engine
driven unit, I always have the engine guy (or me) back off the governor and
set it to PUMP nameplate requirements at 150%, tested like I posted before.
It's the pump that sets the requirement and the driver is matched (sometimes
not too well) to its needs.
Hope this helps.
Tom


Can any of the pump manufacturers weigh in on this issue, and elaborate
a little on the future availability of a PLD on a Tier III?
Mark at Aero


It's not as easy to retrofit one on a Tier III as it first seemed..


That was the beauty of the PLD's. We could size the pump to compensate
for
the mandatory de-rating of the supply and buy back the pressure without
going over 175 psi.


Ron Fletcher

Not doing pumps on a regular basis, I may be missing something but your
required to compare the actual performance with the Certified pump
curve.
Now we always received the certified curve with the pump, and there were
minor diviations from the Cat. Curves. So I would say that if your
design
meets the Certified curve performance your OK. Using any Actual
performance above that curve would be iffy, as you'd have to prove it's
not
based upon a varied supply or other factor.

Example: Static 50 Residual 20 @ 1750, but the engineer requires that
you
only use 45/2...@1575 for future supply degrading. You should exceed the
design when you run your pump test, but if you try and use that, you'll
negate the safety factor the ERO was building in.

Thom


For a retrofit you wouldn't do a pump test and then use the results of
the
test for the calculations?


Ron Fletcher

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs
according
to the engine as you approach no load.  Engines have an operating range
and
usually selected and governor set for the pump's requirements.  I
thought
there might be a disclaimer in the most recent 20 regarding PLD
controllers,
but not to my knowledge.  I know with non-PLD controllers, we always
start
at 150% and work our way back when testing engine-driven pumps as that
helps
cool-down.  Plus, you can check RPM at first flow point.  It's
unfortunate
affinity calculations are based upon constant speed (as I understand
them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can
the pressure produced at the higher rpm be used for the system
calculations?
In other words can the actual pump test be used for the system calc's or
must we use the manufacturers data sheet regardless the test results?

The pump is a PLD if that matters.

Ron Fletcher


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Diesel Pump Engine RPM

2010-08-31 Thread Tom Duross
Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can the pressure produced at the higher rpm be used for the system
calculations? In other words can the actual pump test be used for the
system calc's or must we use the manufacturers data sheet regardless the
test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Diesel Pump Engine RPM

2010-08-31 Thread cherokeefire...@aol.com
I would contact the mfr. The listing is based on their data sheets i believe. 
So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

- Reply message -
From: Tom Duross tduro...@comcast.net
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: sprinklerforum@firesprinkler.org

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%)
can the pressure produced at the higher rpm be used for the system
calculations? In other words can the actual pump test be used for the
system calc's or must we use the manufacturers data sheet regardless the
test results?

The pump is a PLD if that matters.

Ron Fletcher

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)