RE: PA LI - UCC Sprinkler Design Data Sheet
The UCC is the PA Uniform Construction Code, the ICC as adopted by PA. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom Sent: Thursday, September 30, 2010 2:18 PM To: sprinklerforum@firesprinkler.org Subject: RE: PA LI - UCC Sprinkler Design Data Sheet Ken: Doesn't PA switch over to ICC on Oct 1, 2010? UCC plan review would no longer apply. Pa members of the forum: The UCC plan review checklist requires a sprinkler design data sheet to be included on the first plan of the sprinkler drawings. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)
RE: PA LI - UCC Sprinkler Design Data Sheet
Jack, The hydraulic summary sheet from the calcs has always sufficed for our submittals. This, of course, combined with the required NFPA 13 list of what should be on the drawings. I have asked several AHJs about this and they have no idea what it is either. If you happen to come across oneplease shoot me a copy. The UCC checklist in question also lists a 10 psi safety factor on all hydraulic calculations. I've asked AHJs to show me where in the Uniform Construction Code and the NFPA standards that this is a requirement. No one has given me an answer yet. I only know of one jurisdiction around the Harrisburg area that has a legally adopted amendment. Best Regards, Ken Holsopple Rowe Sprinkler Systems Inc. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)
RE: PA LI - UCC Sprinkler Design Data Sheet
Two things could apply here. See chapter 24. See figure A.24.6 Sprinkler system- general information and the Hydraulic Design information sign. There is also a occupancy inforamtion sheet that I could not find quickly. These describe what the owner intends for the building use and occupancy. Art Tiroly Tiroly and Associates -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fairchild, Jack Sent: Thursday, September 30, 2010 9:22 AM To: sprinklerforum@firesprinkler.org Subject: PA LI - UCC Sprinkler Design Data Sheet Pa members of the forum: The UCC plan review checklist requires a sprinkler design data sheet to be included on the first plan of the sprinkler drawings. Is there a form somewhere which show the specific information they are looking for or is this just the hydraulic summary sheet from NFPA 13? Jack Fairchild, CFPS | Senior Fire Protection Designer | Ballinger | v 215.446.0596 | f 215.446.0597 | 833 Chestnut Street Suite 1400 Philadelphia, PA 19107 | www.ballinger-ae.com ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)
RE: PA LI - UCC Sprinkler Design Data Sheet
Ken: Doesn't PA switch over to ICC on Oct 1, 2010? UCC plan review would no longer apply. Pa members of the forum: The UCC plan review checklist requires a sprinkler design data sheet to be included on the first plan of the sprinkler drawings. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)