Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Aaron Peck
Better men then me can do it. I was hit or miss. More miss than hit. I would 
even run it by the field super to make sure I was figuring it right. 

Usually took me actually doing a small mock up in the shop to be 100% sure.

There was a guy in my office when I started. He could have the whole job 
pre-fabbed and he usually had a 97% fit rate.

God speed!

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, using
 drop-in anchors. Elevation-wise this puts me center 5 above finished
 ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Sharon Alves
Back in the day (when the earth was new) we would cut everything to fit.  That 
was our job as designers.

Thank you,

Sharon Alves
Senior Fire Sprinkler Specialist, Project Manager, SET



LP Consulting Engineers, Inc.
MEP/FS . Sustainability . CxA
1663 Eureka Rd - Roseville, CA  95661
(916) 771-0778 x114
sal...@lpengineers.com
www.lpengineers.com


This email and its attachments are the sole property of LP Consulting 
Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
communication with its contents may contain confidential and/or legally 
privileged information. It is solely for the use of the intended recipient(s). 
Unauthorized interception, review, use or disclosure is prohibited and may 
violate applicable laws including the Electronic Communications Privacy Act. If 
you are not the intended recipient, please contact the sender and destroy all 
copies of the communication.  The sender and its company do not guarantee that 
this email or its attachments is free of viruses nor does it accept any 
liability for same.

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron Peck
Sent: Thursday, March 13, 2014 9:35 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Better men then me can do it. I was hit or miss. More miss than hit. I would 
even run it by the field super to make sure I was figuring it right. 

Usually took me actually doing a small mock up in the shop to be 100% sure.

There was a guy in my office when I started. He could have the whole job 
pre-fabbed and he usually had a 97% fit rate.

God speed!

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, 
 using drop-in anchors. Elevation-wise this puts me center 5 above 
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Aaron Peck
Was that along with punchcard hydraulics? Lol 

I wish I had been better but I had my moments of very nice fit jobs. 
Coordinating around huge duct work. The foreman called me out to find out what 
I was on during this design. I just said wait and see. He was amazed when the 
duct came in and it worked perfectly. 

More proper coordination instead of prefab.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:
 
 Back in the day (when the earth was new) we would cut everything to fit.  
 That was our job as designers.
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting 
 Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
 communication with its contents may contain confidential and/or legally 
 privileged information. It is solely for the use of the intended 
 recipient(s). Unauthorized interception, review, use or disclosure is 
 prohibited and may violate applicable laws including the Electronic 
 Communications Privacy Act. If you are not the intended recipient, please 
 contact the sender and destroy all copies of the communication.  The sender 
 and its company do not guarantee that this email or its attachments is free 
 of viruses nor does it accept any liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron 
 Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Better men then me can do it. I was hit or miss. More miss than hit. I would 
 even run it by the field super to make sure I was figuring it right. 
 
 Usually took me actually doing a small mock up in the shop to be 100% sure.
 
 There was a guy in my office when I started. He could have the whole job 
 pre-fabbed and he usually had a 97% fit rate.
 
 God speed!
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, 
 using drop-in anchors. Elevation-wise this puts me center 5 above 
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
I hear you Aaron! Thanks, and you too.
35 years ago FSC stood for Fire Sprinkler Consultants. Now with MEP and Code
divisions that doesn't work. The recent thread about the rod being threaded
on the ends and smooth in the middle made me grin. It was called MT (machine
thread) Rod-- why spend the time and money threading the whole thing when
all you need is a bit on each end? :)
The first Phase of the job I'm working on now (retrofit) was hanging to the
side of concrete beams so I gave the rod length as the dim. from center of
pipe to center of beam stem, and the ring take-out put it an inch or two or
three above... straight up is a different story. I just thought someone
might know off the top of their head, i.e, i'm being lazy!
thanks again, brad

-Original Message-
From: Aaron Peck [mailto:amp...@me.com] 
Sent: Thursday, March 13, 2014 11:35 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Better men then me can do it. I was hit or miss. More miss than hit. I would
even run it by the field super to make sure I was figuring it right. 

Usually took me actually doing a small mock up in the shop to be 100% sure.

There was a guy in my office when I started. He could have the whole job
pre-fabbed and he usually had a 97% fit rate.

God speed!

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com
wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, using
 drop-in anchors. Elevation-wise this puts me center 5 above finished
 ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
Come on Sharon! We're not older than dirt, we were just the first to play in
it ;)

-Original Message-
From: Aaron Peck [mailto:amp...@me.com] 
Sent: Thursday, March 13, 2014 11:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Was that along with punchcard hydraulics? Lol 

I wish I had been better but I had my moments of very nice fit jobs.
Coordinating around huge duct work. The foreman called me out to find out
what I was on during this design. I just said wait and see. He was amazed
when the duct came in and it worked perfectly. 

More proper coordination instead of prefab.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:
 
 Back in the day (when the earth was new) we would cut everything to fit.
That was our job as designers.
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting
Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This
communication with its contents may contain confidential and/or legally
privileged information. It is solely for the use of the intended
recipient(s). Unauthorized interception, review, use or disclosure is
prohibited and may violate applicable laws including the Electronic
Communications Privacy Act. If you are not the intended recipient, please
contact the sender and destroy all copies of the communication.  The sender
and its company do not guarantee that this email or its attachments is free
of viruses nor does it accept any liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron
Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Better men then me can do it. I was hit or miss. More miss than hit. I
would even run it by the field super to make sure I was figuring it right. 
 
 Usually took me actually doing a small mock up in the shop to be 100%
sure.
 
 There was a guy in my office when I started. He could have the whole job
pre-fabbed and he usually had a 97% fit rate.
 
 God speed!
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com
wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, 
 using drop-in anchors. Elevation-wise this puts me center 5 above 
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Vince Sabolik

I think it'll work fine. Why deep plates?

Vince


On 3/13/2014 11:41 AM, Brad Casterline wrote:

My confidence level is a bit low and I would appreciate a boost:

I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, using
drop-in anchors. Elevation-wise this puts me center 5 above finished
ceiling.

I'm using 2-pc deep escutcheon.

For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?

  


Thanks,

Brad

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





--

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800Fax 440 238-4876
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Morey, Mike
Better that than the phone call of I moved that pipe up nice and tight and 
eliminated those offsets we didn't need, had that one happen a time or two.

Mike Morey, CFPS, SET
Planner Scheduler/Designer
BMWC Constructors, Inc.
1740 W. Michigan St, Indianapolis, IN 46222
O: 317.651.0596 | C: 317.586.8111
mo...@bmwc.com | www.bmwc.com


From: sprinklerforum-boun...@lists.firesprinkler.org 
[sprinklerforum-boun...@lists.firesprinkler.org] on behalf of Aaron Peck 
[amp...@me.com]
Sent: Thursday, March 13, 2014 12:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Was that along with punchcard hydraulics? Lol

I wish I had been better but I had my moments of very nice fit jobs. 
Coordinating around huge duct work. The foreman called me out to find out what 
I was on during this design. I just said wait and see. He was amazed when the 
duct came in and it worked perfectly.

More proper coordination instead of prefab.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:

 Back in the day (when the earth was new) we would cut everything to fit.  
 That was our job as designers.

 Thank you,

 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET



 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com


 This email and its attachments are the sole property of LP Consulting 
 Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
 communication with its contents may contain confidential and/or legally 
 privileged information. It is solely for the use of the intended 
 recipient(s). Unauthorized interception, review, use or disclosure is 
 prohibited and may violate applicable laws including the Electronic 
 Communications Privacy Act. If you are not the intended recipient, please 
 contact the sender and destroy all copies of the communication.  The sender 
 and its company do not guarantee that this email or its attachments is free 
 of viruses nor does it accept any liability for same.

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron 
 Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops

 Better men then me can do it. I was hit or miss. More miss than hit. I would 
 even run it by the field super to make sure I was figuring it right.

 Usually took me actually doing a small mock up in the shop to be 100% sure.

 There was a guy in my office when I started. He could have the whole job 
 pre-fabbed and he usually had a 97% fit rate.

 God speed!

 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407

 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:

 My confidence level is a bit low and I would appreciate a boost:

 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete,
 using drop-in anchors. Elevation-wise this puts me center 5 above
 finished ceiling.

 I'm using 2-pc deep escutcheon.

 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?



 Thanks,

 Brad

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
I want it to be very obvious to the students that their dormitory is
sprinklered, and if they get to horsing around too much and break one, they
will all go off and flood the place. Once they graduate I will set them
straight.
Thanks Vince, my mentor*, I knew I could count on you.
Brad

*i hope you are not ashamed of that-- I am not your fault! :) !

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net] 
Sent: Thursday, March 13, 2014 12:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

I think it'll work fine. Why deep plates?

Vince


On 3/13/2014 11:41 AM, Brad Casterline wrote:
 My confidence level is a bit low and I would appreciate a boost:

 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, using
 drop-in anchors. Elevation-wise this puts me center 5 above finished
 ceiling.

 I'm using 2-pc deep escutcheon.

 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?

   

 Thanks,

 Brad

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800Fax 440 238-4876
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Aaron Peck
*facepalm ya I've had similar things happen. Milded mannered foreman helping 
out. Sometimes good but others not so much. That's the importance of a pre-con 
meeting to go over the hows and whys of your design.

A general rule is if your design and pre-fab was good you won't hear anything. 
You'll only hear if something is wrong.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 14, 2014, at 12:22 AM, Morey, Mike mo...@bmwc.com wrote:
 
 Better that than the phone call of I moved that pipe up nice and tight and 
 eliminated those offsets we didn't need, had that one happen a time or two.
 
 Mike Morey, CFPS, SET
 Planner Scheduler/Designer
 BMWC Constructors, Inc.
 1740 W. Michigan St, Indianapolis, IN 46222
 O: 317.651.0596 | C: 317.586.8111
 mo...@bmwc.com | www.bmwc.com
 
 
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [sprinklerforum-boun...@lists.firesprinkler.org] on behalf of Aaron Peck 
 [amp...@me.com]
 Sent: Thursday, March 13, 2014 12:58 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Was that along with punchcard hydraulics? Lol
 
 I wish I had been better but I had my moments of very nice fit jobs. 
 Coordinating around huge duct work. The foreman called me out to find out 
 what I was on during this design. I just said wait and see. He was amazed 
 when the duct came in and it worked perfectly.
 
 More proper coordination instead of prefab.
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:
 
 Back in the day (when the earth was new) we would cut everything to fit.  
 That was our job as designers.
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting 
 Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
 communication with its contents may contain confidential and/or legally 
 privileged information. It is solely for the use of the intended 
 recipient(s). Unauthorized interception, review, use or disclosure is 
 prohibited and may violate applicable laws including the Electronic 
 Communications Privacy Act. If you are not the intended recipient, please 
 contact the sender and destroy all copies of the communication.  The sender 
 and its company do not guarantee that this email or its attachments is free 
 of viruses nor does it accept any liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron 
 Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Better men then me can do it. I was hit or miss. More miss than hit. I would 
 even run it by the field super to make sure I was figuring it right.
 
 Usually took me actually doing a small mock up in the shop to be 100% sure.
 
 There was a guy in my office when I started. He could have the whole job 
 pre-fabbed and he usually had a 97% fit rate.
 
 God speed!
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete,
 using drop-in anchors. Elevation-wise this puts me center 5 above
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org

RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Sharon Alves
I hate to admit it, but I calculated grids by hand. 

Thank you,

Sharon Alves
Senior Fire Sprinkler Specialist, Project Manager, SET



LP Consulting Engineers, Inc.
MEP/FS . Sustainability . CxA
1663 Eureka Rd - Roseville, CA  95661
(916) 771-0778 x114
sal...@lpengineers.com
www.lpengineers.com


This email and its attachments are the sole property of LP Consulting 
Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
communication with its contents may contain confidential and/or legally 
privileged information. It is solely for the use of the intended recipient(s). 
Unauthorized interception, review, use or disclosure is prohibited and may 
violate applicable laws including the Electronic Communications Privacy Act. If 
you are not the intended recipient, please contact the sender and destroy all 
copies of the communication.  The sender and its company do not guarantee that 
this email or its attachments is free of viruses nor does it accept any 
liability for same.

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron Peck
Sent: Thursday, March 13, 2014 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Was that along with punchcard hydraulics? Lol 

I wish I had been better but I had my moments of very nice fit jobs. 
Coordinating around huge duct work. The foreman called me out to find out what 
I was on during this design. I just said wait and see. He was amazed when the 
duct came in and it worked perfectly. 

More proper coordination instead of prefab.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:
 
 Back in the day (when the earth was new) we would cut everything to fit.  
 That was our job as designers.
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting 
 Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
 communication with its contents may contain confidential and/or legally 
 privileged information. It is solely for the use of the intended 
 recipient(s). Unauthorized interception, review, use or disclosure is 
 prohibited and may violate applicable laws including the Electronic 
 Communications Privacy Act. If you are not the intended recipient, please 
 contact the sender and destroy all copies of the communication.  The sender 
 and its company do not guarantee that this email or its attachments is free 
 of viruses nor does it accept any liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Aaron Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Better men then me can do it. I was hit or miss. More miss than hit. I would 
 even run it by the field super to make sure I was figuring it right. 
 
 Usually took me actually doing a small mock up in the shop to be 100% sure.
 
 There was a guy in my office when I started. He could have the whole job 
 pre-fabbed and he usually had a 97% fit rate.
 
 God speed!
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, 
 using drop-in anchors. Elevation-wise this puts me center 5 above 
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 l
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Sharon Alves
Yes, when the earth was new.  I've had fun playing in it though.

Thank you,

Sharon Alves
Senior Fire Sprinkler Specialist, Project Manager, SET



LP Consulting Engineers, Inc.
MEP/FS . Sustainability . CxA
1663 Eureka Rd - Roseville, CA  95661
(916) 771-0778 x114
sal...@lpengineers.com
www.lpengineers.com


This email and its attachments are the sole property of LP Consulting 
Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
communication with its contents may contain confidential and/or legally 
privileged information. It is solely for the use of the intended recipient(s). 
Unauthorized interception, review, use or disclosure is prohibited and may 
violate applicable laws including the Electronic Communications Privacy Act. If 
you are not the intended recipient, please contact the sender and destroy all 
copies of the communication.  The sender and its company do not guarantee that 
this email or its attachments is free of viruses nor does it accept any 
liability for same.

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad 
Casterline
Sent: Thursday, March 13, 2014 10:09 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pre-fabbed Hangers and Drops

Come on Sharon! We're not older than dirt, we were just the first to play in it 
;)

-Original Message-
From: Aaron Peck [mailto:amp...@me.com]
Sent: Thursday, March 13, 2014 11:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Was that along with punchcard hydraulics? Lol 

I wish I had been better but I had my moments of very nice fit jobs.
Coordinating around huge duct work. The foreman called me out to find out what 
I was on during this design. I just said wait and see. He was amazed when the 
duct came in and it worked perfectly. 

More proper coordination instead of prefab.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:
 
 Back in the day (when the earth was new) we would cut everything to fit.
That was our job as designers.
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting
Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
communication with its contents may contain confidential and/or legally 
privileged information. It is solely for the use of the intended recipient(s). 
Unauthorized interception, review, use or disclosure is prohibited and may 
violate applicable laws including the Electronic Communications Privacy Act. If 
you are not the intended recipient, please contact the sender and destroy all 
copies of the communication.  The sender and its company do not guarantee that 
this email or its attachments is free of viruses nor does it accept any 
liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Better men then me can do it. I was hit or miss. More miss than hit. I
would even run it by the field super to make sure I was figuring it right. 
 
 Usually took me actually doing a small mock up in the shop to be 100%
sure.
 
 There was a guy in my office when I started. He could have the whole 
 job
pre-fabbed and he usually had a 97% fit rate.
 
 God speed!
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 10:41 PM, Brad Casterline 
 bcasterl...@fsc-inc.com
wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, 
 using drop-in anchors. Elevation-wise this puts me center 5 above 
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 l
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

http

Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Aaron Peck
I only had to hand calc grids for my NICET test of course with velocity 
pressures... Never again!

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

 On Mar 14, 2014, at 12:30 AM, Sharon Alves sal...@lpengineers.com wrote:
 
 I hate to admit it, but I calculated grids by hand. 
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting 
 Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
 communication with its contents may contain confidential and/or legally 
 privileged information. It is solely for the use of the intended 
 recipient(s). Unauthorized interception, review, use or disclosure is 
 prohibited and may violate applicable laws including the Electronic 
 Communications Privacy Act. If you are not the intended recipient, please 
 contact the sender and destroy all copies of the communication.  The sender 
 and its company do not guarantee that this email or its attachments is free 
 of viruses nor does it accept any liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Aaron 
 Peck
 Sent: Thursday, March 13, 2014 9:58 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Was that along with punchcard hydraulics? Lol 
 
 I wish I had been better but I had my moments of very nice fit jobs. 
 Coordinating around huge duct work. The foreman called me out to find out 
 what I was on during this design. I just said wait and see. He was amazed 
 when the duct came in and it worked perfectly. 
 
 More proper coordination instead of prefab.
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 11:47 PM, Sharon Alves sal...@lpengineers.com wrote:
 
 Back in the day (when the earth was new) we would cut everything to fit.  
 That was our job as designers.
 
 Thank you,
 
 Sharon Alves
 Senior Fire Sprinkler Specialist, Project Manager, SET
 
 
 
 LP Consulting Engineers, Inc.
 MEP/FS . Sustainability . CxA
 1663 Eureka Rd - Roseville, CA  95661
 (916) 771-0778 x114
 sal...@lpengineers.com
 www.lpengineers.com
 
 
 This email and its attachments are the sole property of LP Consulting 
 Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2013.  This 
 communication with its contents may contain confidential and/or legally 
 privileged information. It is solely for the use of the intended 
 recipient(s). Unauthorized interception, review, use or disclosure is 
 prohibited and may violate applicable laws including the Electronic 
 Communications Privacy Act. If you are not the intended recipient, please 
 contact the sender and destroy all copies of the communication.  The sender 
 and its company do not guarantee that this email or its attachments is free 
 of viruses nor does it accept any liability for same.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Aaron Peck
 Sent: Thursday, March 13, 2014 9:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Cc: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Better men then me can do it. I was hit or miss. More miss than hit. I would 
 even run it by the field super to make sure I was figuring it right. 
 
 Usually took me actually doing a small mock up in the shop to be 100% sure.
 
 There was a guy in my office when I started. He could have the whole job 
 pre-fabbed and he usually had a 97% fit rate.
 
 God speed!
 
 Sent from my iPhone
 Aaron M. Peck, SET Fire Protection
 Skype +1(202)407-9079
 Cambodia +855(0)78700407
 
 On Mar 13, 2014, at 10:41 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, 
 using drop-in anchors. Elevation-wise this puts me center 5 above 
 finished ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 l
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list

Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Vince Sabolik

Very Obvious = Target

Hell, Brad even I can remember that far back.  And no,
I'm proud of you as I am all my chillun

On 3/13/2014 1:29 PM, Brad Casterline wrote:

I want it to be very obvious to the students that their dormitory is
sprinklered, and if they get to horsing around too much and break one, they
will all go off and flood the place. Once they graduate I will set them
straight.
Thanks Vince, my mentor*, I knew I could count on you.
Brad

*i hope you are not ashamed of that-- I am not your fault! :) !

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net]
Sent: Thursday, March 13, 2014 12:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

I think it'll work fine. Why deep plates?

Vince



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
True enough! Actually, there are quite a few ceiling height changes and
surface mounted lights and other fixtures.
Thank you very much Vince. You are one of the few whom did not reply to my
Why? why? why? with DONT WORRY ABOUT IT JUST DO IT

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net] 
Sent: Thursday, March 13, 2014 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Very Obvious = Target

Hell, Brad even I can remember that far back.  And no,
I'm proud of you as I am all my chillun

On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is
 sprinklered, and if they get to horsing around too much and break one,
they
 will all go off and flood the place. Once they graduate I will set them
 straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad

 *i hope you are not ashamed of that-- I am not your fault! :) !

 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops

 I think it'll work fine. Why deep plates?

 Vince


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Bill Brooks
This is not the why group.  This is the follow-the-rules group, which
includes engineers, educators, AHJs, designers, installers, and
manufacturers, because NFPA 13 is a rule book and not an engineering guide.
If you want to reach the why group, submit Proposals to the NFPA 13
committee during the Proposal period, or begin sending Comments during the
Comment period.  By doing this you will get direct feedback in the form of
Committee Responses directly addressing your concerns.  Send them your good
ideas, then challenge them all the way to the Standards Council if you wish.
You sound like the kind of person who would enjoy the jousting.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
Casterline
Sent: Thursday, March 13, 2014 2:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pre-fabbed Hangers and Drops

True enough! Actually, there are quite a few ceiling height changes and
surface mounted lights and other fixtures.
Thank you very much Vince. You are one of the few whom did not reply to my
Why? why? why? with DONT WORRY ABOUT IT JUST DO IT

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net]
Sent: Thursday, March 13, 2014 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Very Obvious = Target

Hell, Brad even I can remember that far back.  And no, I'm proud of you as I
am all my chillun

On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is 
 sprinklered, and if they get to horsing around too much and break one,
they
 will all go off and flood the place. Once they graduate I will set 
 them straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad

 *i hope you are not ashamed of that-- I am not your fault! :) !

 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops

 I think it'll work fine. Why deep plates?

 Vince


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
Bill,
You mean this isn't the fiction writer want-to-be group? I was always better
at making things up than figuring out how things worked. I think designers
are a tad bit more unique than the other 5 you mention-- we have to start
with a blank page and fill it up. I have always admired and respected the
rules and, truth be told, I could not care less if any of them ever change,
certainly not to the point of doing battle :). The why comes from a desire
for a deeper appreciation. Thanks man!
and thanks Sharon and Mike for comments.
Brad


-Original Message-
From: Bill Brooks [mailto:bill.bro...@brooksfpe.com] 
Sent: Thursday, March 13, 2014 2:09 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pre-fabbed Hangers and Drops

This is not the why group.  This is the follow-the-rules group, which
includes engineers, educators, AHJs, designers, installers, and
manufacturers, because NFPA 13 is a rule book and not an engineering guide.
If you want to reach the why group, submit Proposals to the NFPA 13
committee during the Proposal period, or begin sending Comments during the
Comment period.  By doing this you will get direct feedback in the form of
Committee Responses directly addressing your concerns.  Send them your good
ideas, then challenge them all the way to the Standards Council if you wish.
You sound like the kind of person who would enjoy the jousting.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
Casterline
Sent: Thursday, March 13, 2014 2:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pre-fabbed Hangers and Drops

True enough! Actually, there are quite a few ceiling height changes and
surface mounted lights and other fixtures.
Thank you very much Vince. You are one of the few whom did not reply to my
Why? why? why? with DONT WORRY ABOUT IT JUST DO IT

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net]
Sent: Thursday, March 13, 2014 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Very Obvious = Target

Hell, Brad even I can remember that far back.  And no, I'm proud of you as I
am all my chillun

On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is 
 sprinklered, and if they get to horsing around too much and break one,
they
 will all go off and flood the place. Once they graduate I will set 
 them straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad

 *i hope you are not ashamed of that-- I am not your fault! :) !

 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops

 I think it'll work fine. Why deep plates?

 Vince


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread John Drucker
Well said Bill.  As AHJ we make every attempt to explain why based on 
commentary, annexes and records of code hearings. However there comes a point 
where we simply move beyond the banter and enforce the rule, if someone doesnt 
agree then take it to the next level thru appeal and or the courts, a new group 
of people will begin the rule enforcement process. Arguing with us ahjs 
wouldn't change the rule. As for the standards council, been there and done 
that once by way of a NITMAM. A year of research work, comments, more comments 
culminating travelling to Chicago to change one word in a standard that I, and 
apparently others, felt strongly about. In the time since tens of thousands of 
words have changed. I've accepted that others have a say. So the next time 
someone wants to continue beyond the printed why explanation I point in the 
direction of Chicago.   
John Drucker - Mobile Email

- Original Message -
From: sprinklerforum-boun...@lists.firesprinkler.org 
sprinklerforum-boun...@lists.firesprinkler.org
To: sprinklerforum@lists.firesprinkler.org 
sprinklerforum@lists.firesprinkler.org
Sent: Thu Mar 13 15:08:45 2014
Subject: RE: Pre-fabbed Hangers and Drops

This is not the why group.  This is the follow-the-rules group, which
includes engineers, educators, AHJs, designers, installers, and
manufacturers, because NFPA 13 is a rule book and not an engineering guide.
If you want to reach the why group, submit Proposals to the NFPA 13
committee during the Proposal period, or begin sending Comments during the
Comment period.  By doing this you will get direct feedback in the form of
Committee Responses directly addressing your concerns.  Send them your good
ideas, then challenge them all the way to the Standards Council if you wish.
You sound like the kind of person who would enjoy the jousting.

Bill Brooks

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
Casterline
Sent: Thursday, March 13, 2014 2:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pre-fabbed Hangers and Drops

True enough! Actually, there are quite a few ceiling height changes and
surface mounted lights and other fixtures.
Thank you very much Vince. You are one of the few whom did not reply to my
Why? why? why? with DONT WORRY ABOUT IT JUST DO IT

-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net]
Sent: Thursday, March 13, 2014 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Pre-fabbed Hangers and Drops

Very Obvious = Target

Hell, Brad even I can remember that far back.  And no, I'm proud of you as I
am all my chillun

On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is 
 sprinklered, and if they get to horsing around too much and break one,
they
 will all go off and flood the place. Once they graduate I will set 
 them straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad

 *i hope you are not ashamed of that-- I am not your fault! :) !

 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops

 I think it'll work fine. Why deep plates?

 Vince


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
Hey John this is Brad. My first thought was also well said Bill. Then I 
pictured the commentary in the handbooks, the different color text/fonts after 
the statements in the Body ALL saying DON'T WORRY ABOUT IT JUST DO IT. It was 
a depressing image and since this is my thread I decided to get goofy instead. 
Thanks!

 On Mar 13, 2014, at 5:58 PM, John Drucker jdruc...@redbanknj.org wrote:
 
 Well said Bill.  As AHJ we make every attempt to explain why based on 
 commentary, annexes and records of code hearings. However there comes a point 
 where we simply move beyond the banter and enforce the rule, if someone 
 doesnt agree then take it to the next level thru appeal and or the courts, a 
 new group of people will begin the rule enforcement process. Arguing with us 
 ahjs wouldn't change the rule. As for the standards council, been there and 
 done that once by way of a NITMAM. A year of research work, comments, more 
 comments culminating travelling to Chicago to change one word in a standard 
 that I, and apparently others, felt strongly about. In the time since tens of 
 thousands of words have changed. I've accepted that others have a say. So the 
 next time someone wants to continue beyond the printed why explanation I 
 point in the direction of Chicago.   
 John Drucker - Mobile Email
 
 - Original Message -
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 sprinklerforum-boun...@lists.firesprinkler.org
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Sent: Thu Mar 13 15:08:45 2014
 Subject: RE: Pre-fabbed Hangers and Drops
 
 This is not the why group.  This is the follow-the-rules group, which
 includes engineers, educators, AHJs, designers, installers, and
 manufacturers, because NFPA 13 is a rule book and not an engineering guide.
 If you want to reach the why group, submit Proposals to the NFPA 13
 committee during the Proposal period, or begin sending Comments during the
 Comment period.  By doing this you will get direct feedback in the form of
 Committee Responses directly addressing your concerns.  Send them your good
 ideas, then challenge them all the way to the Standards Council if you wish.
 You sound like the kind of person who would enjoy the jousting.
 
 Bill Brooks
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
 Casterline
 Sent: Thursday, March 13, 2014 2:02 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Pre-fabbed Hangers and Drops
 
 True enough! Actually, there are quite a few ceiling height changes and
 surface mounted lights and other fixtures.
 Thank you very much Vince. You are one of the few whom did not reply to my
 Why? why? why? with DONT WORRY ABOUT IT JUST DO IT
 
 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:49 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Very Obvious = Target
 
 Hell, Brad even I can remember that far back.  And no, I'm proud of you as I
 am all my chillun
 
 On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is 
 sprinklered, and if they get to horsing around too much and break one,
 they
 will all go off and flood the place. Once they graduate I will set 
 them straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad
 
 *i hope you are not ashamed of that-- I am not your fault! :) !
 
 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 I think it'll work fine. Why deep plates?
 
 Vince
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 CONFIDENTIAL AND PROPRIETARY:
 This email message is intended only for the use of the individual or entity 
 to which it is addressed and may contain information that is privileged and 
 confidential, nor is it, unless specifically stated, intended to be relied 
 upon by any person or persons other than the individual or entity named above 
 and no warranties or representations are made or intended to persons or 
 entities not named above.  If the reader is not the intended recipient, you 
 are hereby notified that any dissemination, distribution or copying

Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
And I cannot imagine a better why group than this Forum. When I discovered it 
a few years ago, after having worn friends and family completely out with 
incessant sprinkler talk, I stood up and shouted my God, I'm home!

 On Mar 13, 2014, at 6:15 PM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 Hey John this is Brad. My first thought was also well said Bill. Then I 
 pictured the commentary in the handbooks, the different color text/fonts 
 after the statements in the Body ALL saying DON'T WORRY ABOUT IT JUST DO 
 IT. It was a depressing image and since this is my thread I decided to get 
 goofy instead. Thanks!
 
 On Mar 13, 2014, at 5:58 PM, John Drucker jdruc...@redbanknj.org wrote:
 
 Well said Bill.  As AHJ we make every attempt to explain why based on 
 commentary, annexes and records of code hearings. However there comes a 
 point where we simply move beyond the banter and enforce the rule, if 
 someone doesnt agree then take it to the next level thru appeal and or the 
 courts, a new group of people will begin the rule enforcement process. 
 Arguing with us ahjs wouldn't change the rule. As for the standards council, 
 been there and done that once by way of a NITMAM. A year of research work, 
 comments, more comments culminating travelling to Chicago to change one word 
 in a standard that I, and apparently others, felt strongly about. In the 
 time since tens of thousands of words have changed. I've accepted that 
 others have a say. So the next time someone wants to continue beyond the 
 printed why explanation I point in the direction of Chicago.   
 John Drucker - Mobile Email
 
 - Original Message -
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 sprinklerforum-boun...@lists.firesprinkler.org
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Sent: Thu Mar 13 15:08:45 2014
 Subject: RE: Pre-fabbed Hangers and Drops
 
 This is not the why group.  This is the follow-the-rules group, which
 includes engineers, educators, AHJs, designers, installers, and
 manufacturers, because NFPA 13 is a rule book and not an engineering guide.
 If you want to reach the why group, submit Proposals to the NFPA 13
 committee during the Proposal period, or begin sending Comments during the
 Comment period.  By doing this you will get direct feedback in the form of
 Committee Responses directly addressing your concerns.  Send them your good
 ideas, then challenge them all the way to the Standards Council if you wish.
 You sound like the kind of person who would enjoy the jousting.
 
 Bill Brooks
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad
 Casterline
 Sent: Thursday, March 13, 2014 2:02 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Pre-fabbed Hangers and Drops
 
 True enough! Actually, there are quite a few ceiling height changes and
 surface mounted lights and other fixtures.
 Thank you very much Vince. You are one of the few whom did not reply to my
 Why? why? why? with DONT WORRY ABOUT IT JUST DO IT
 
 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:49 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 Very Obvious = Target
 
 Hell, Brad even I can remember that far back.  And no, I'm proud of you as I
 am all my chillun
 
 On 3/13/2014 1:29 PM, Brad Casterline wrote:
 I want it to be very obvious to the students that their dormitory is 
 sprinklered, and if they get to horsing around too much and break one,
 they
 will all go off and flood the place. Once they graduate I will set 
 them straight.
 Thanks Vince, my mentor*, I knew I could count on you.
 Brad
 
 *i hope you are not ashamed of that-- I am not your fault! :) !
 
 -Original Message-
 From: Vince Sabolik [mailto:vi...@wtfp.net]
 Sent: Thursday, March 13, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Pre-fabbed Hangers and Drops
 
 I think it'll work fine. Why deep plates?
 
 Vince
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 CONFIDENTIAL AND PROPRIETARY:
 This email message is intended only for the use of the individual or entity 
 to which it is addressed and may contain information that is privileged and 
 confidential, nor is it, unless specifically stated, intended to be relied

Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Jamie Seidl
Brad, First question, are you running your rod down to the top of pipe?  Second 
have you surveyed the job?  More often than not smooth concrete will not be 
smooth when it is poured due to deflections in the forms. (You might want to 
leave some play in your hanger length.) Where is the ceiling guy setting up his 
rotary level?  Is he using a datum elevation marked on a column? How level is 
the concrete floor?  Center of tile project? Are there dimensions for the 
ceiling guy to start his grid border? The list can go on and on. We cut rods 
and drops on the vast majority of projects, and things work to an extent +/- 
80%?  The issue is trying to control for factors that are out of your control, 
and that's where a survey can help a lot.  I've worked on too many BIM 
projects that don't leave an appropriate level of field variation or 
tolerance (+/- 2) and everything devolves into subs arguing with subs, GC 
arguing with subs ect. 
Bottom line, add hanger length for drop-ins, take out for hangers, takeout for 
fittings/head recess and you should hit 80% plus.  
Good luck, and good for you trying, because there isn't much of a better 
feeling than having a foreman say that thing fit like a glove!


Sent from my iPhone
Jamie Seidl 

 On Mar 13, 2014, at 11:41 AM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, using
 drop-in anchors. Elevation-wise this puts me center 5 above finished
 ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pre-fabbed Hangers and Drops

2014-03-13 Thread Brad Casterline
Rod does not have to be run down to top of pipe. Retrofit, survey, available 
plans ~20 years behind modifications that were never recorded. 10 story college 
dormitory. The good news is structure is concrete and steel- hand drawn in an 
era when we all took the time to do things right. Cut-up, congested, but that's 
ok. The last one I worked on to a similar level of detail was new with full 
coordination (revit/navis). Mortenson has really got their $hit together- it is 
nice to miss even the rod supporting the unistrut supporting the cable trays. 
On this one, ceiling height varies more than structure- it sags here and there- 
but I think with the tolerance of ring take-outs and 2-piece deep (401s I used 
to call them), for 1 thru 2when the length is the same it pulls the 1 at the 
end up a bit and pushes the 1 1/2 starter down a bit, which is cool, I think, 
like Vince, it'll be fine.
Thanks Jamie, Brad

 On Mar 13, 2014, at 7:07 PM, Jamie Seidl jamie.se...@gmail.com wrote:
 
 Brad, First question, are you running your rod down to the top of pipe?  
 Second have you surveyed the job?  More often than not smooth concrete will 
 not be smooth when it is poured due to deflections in the forms. (You might 
 want to leave some play in your hanger length.) Where is the ceiling guy 
 setting up his rotary level?  Is he using a datum elevation marked on a 
 column? How level is the concrete floor?  Center of tile project? Are there 
 dimensions for the ceiling guy to start his grid border? The list can go on 
 and on. We cut rods and drops on the vast majority of projects, and things 
 work to an extent +/- 80%?  The issue is trying to control for factors that 
 are out of your control, and that's where a survey can help a lot.  I've 
 worked on too many BIM projects that don't leave an appropriate level of 
 field variation or tolerance (+/- 2) and everything devolves into subs 
 arguing with subs, GC arguing with subs ect. 
 Bottom line, add hanger length for drop-ins, take out for hangers, takeout 
 for fittings/head recess and you should hit 80% plus.  
 Good luck, and good for you trying, because there isn't much of a better 
 feeling than having a foreman say that thing fit like a glove!
 
 
 Sent from my iPhone
 Jamie Seidl 
 
 On Mar 13, 2014, at 11:41 AM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 My confidence level is a bit low and I would appreciate a boost:
 
 I'm hanging 1 thru 2 pipe at center of 19 below smooth concrete, using
 drop-in anchors. Elevation-wise this puts me center 5 above finished
 ceiling.
 
 I'm using 2-pc deep escutcheon.
 
 For simplicity I'm thinking 3/8x18 A.T.R. and 5 drops should work?
 
 
 
 Thanks,
 
 Brad 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org