RE: Transition from Outside to Inside

2011-07-13 Thread Bill Brooks
Of course the Annex is not the body as the TC already knows, and of course
this is a pretty minor point, but fixing this, even as a change to the
Annex, is not that complex.  And why, if this is how the TC rationalizes
their opinion, would they address this topic in relation to location of the
piping with respect to the foundation?   I generally use the one joint
rule which would limit the amount of underground piping to less than one
length and thereby limiting the height of the flange above the floor (just
as is shown in A.10.6.5), but I have seen multiple pieces of ductile inside
as well.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, July 12, 2011 4:47 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Transition from Outside to Inside

I agree with Mark. Some folks (including the TC at the ROP meeting)  
seem to think it is acceptable based on 13:A.10.6.5 showing part of  
the underground pipe extending above the floor.  They seem to have  
ignored that the Figure is ductile so doesn't address plastic and seem  
to have forgotten that the listing for underground plastic pipe  
applies to it being underground.  As soon as it is exposed (whether in  
a trench or as a transition piece above the floor) it has to be  
acceptable as an above ground pipe. Needless to say, this issue will  
be addressed again at the ROC meeting.

Roland

On Jul 12, 2011, at 7:16 AM, Mark Sornsin wrote:

 Bill - I'm going to go on a limb a bit and suggest there is no  
 maximum height.

 There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the  
 transition piece (23.1.6.1.1). It is implied that underground pipe  
 is only underground. An aggressive AHJ or EOR may argue that the  
 flange must be located at the floor level - so no underground pipe  
 is above-ground and vice versa. I would suggest that it really only  
 matters when dealing with plastic underground transitioning to above- 
 ground pipe. No plastic pipe should be allowed above ground, so the  
 transition should start below grade. I always spec' ductile iron  
 into the building. This meets the intent of 23.1.6.1.1 as a  
 transition.  We normally shoot for the transition to the above- 
 ground pipe to occur at 6 to 12 inches above the floor, but there is  
 nothing in 13 that mandates any particular height.

 Mark A. Sornsin, PE| Fire Protection Engineer
 Ulteig Engineers, Inc.| Fargo, ND
 mark.sorn...@ulteig.com



___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Transition from Outside to Inside

2011-07-12 Thread Mark Sornsin
Bill - I'm going to go on a limb a bit and suggest there is no maximum height. 

There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the transition 
piece (23.1.6.1.1). It is implied that underground pipe is only underground. An 
aggressive AHJ or EOR may argue that the flange must be located at the floor 
level - so no underground pipe is above-ground and vice versa. I would suggest 
that it really only matters when dealing with plastic underground transitioning 
to above-ground pipe. No plastic pipe should be allowed above ground, so the 
transition should start below grade. I always spec' ductile iron into the 
building. This meets the intent of 23.1.6.1.1 as a transition.  We normally 
shoot for the transition to the above-ground pipe to occur at 6 to 12 inches 
above the floor, but there is nothing in 13 that mandates any particular height.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, July 12, 2011 8:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Transition from Outside to Inside

Something I thought I could find but couldn't.  What is the maximum height for 
the floor flange to transition from the below ground pipe to the above ground 
pipe?  (NFPA 13-2010, 6.3  23.1.6.1.1)  Ductile and plastic are not listed in 
the Table 6.3.1.1.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Transition from Outside to Inside

2011-07-12 Thread Steve Leyton
At some point, the requirement for the flexible coupling kicks in.  Have always 
understood 9.3.2.3 (1) - 2010 edition, previous ones numbered differently - to 
include the main system riser, so the flange or adaptive fitting would have to 
be configured to allow a flex coupling at no more than 24 above the floor.

SL




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mark Sornsin
Sent: Tuesday, July 12, 2011 7:17 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Transition from Outside to Inside

Bill - I'm going to go on a limb a bit and suggest there is no maximum height. 

There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the transition 
piece (23.1.6.1.1). It is implied that underground pipe is only underground. An 
aggressive AHJ or EOR may argue that the flange must be located at the floor 
level - so no underground pipe is above-ground and vice versa. I would suggest 
that it really only matters when dealing with plastic underground transitioning 
to above-ground pipe. No plastic pipe should be allowed above ground, so the 
transition should start below grade. I always spec' ductile iron into the 
building. This meets the intent of 23.1.6.1.1 as a transition.  We normally 
shoot for the transition to the above-ground pipe to occur at 6 to 12 inches 
above the floor, but there is nothing in 13 that mandates any particular height.

Mark A. Sornsin, PE| Fire Protection Engineer 
Ulteig Engineers, Inc.| Fargo, ND  
mark.sorn...@ulteig.com 

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Tuesday, July 12, 2011 8:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Transition from Outside to Inside

Something I thought I could find but couldn't.  What is the maximum height for 
the floor flange to transition from the below ground pipe to the above ground 
pipe?  (NFPA 13-2010, 6.3  23.1.6.1.1)  Ductile and plastic are not listed in 
the Table 6.3.1.1.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146-1904
410-544-3620
410-544-3032 FAX
412-400-6528 Cell

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Transition from Outside to Inside

2011-07-12 Thread Roland Huggins
I agree with Mark. Some folks (including the TC at the ROP meeting)  
seem to think it is acceptable based on 13:A.10.6.5 showing part of  
the underground pipe extending above the floor.  They seem to have  
ignored that the Figure is ductile so doesn't address plastic and seem  
to have forgotten that the listing for underground plastic pipe  
applies to it being underground.  As soon as it is exposed (whether in  
a trench or as a transition piece above the floor) it has to be  
acceptable as an above ground pipe. Needless to say, this issue will  
be addressed again at the ROC meeting.


Roland

On Jul 12, 2011, at 7:16 AM, Mark Sornsin wrote:

Bill - I'm going to go on a limb a bit and suggest there is no  
maximum height.


There's underground pipe (CH. 10), above-ground pipe (CH. 6) and the  
transition piece (23.1.6.1.1). It is implied that underground pipe  
is only underground. An aggressive AHJ or EOR may argue that the  
flange must be located at the floor level - so no underground pipe  
is above-ground and vice versa. I would suggest that it really only  
matters when dealing with plastic underground transitioning to above- 
ground pipe. No plastic pipe should be allowed above ground, so the  
transition should start below grade. I always spec' ductile iron  
into the building. This meets the intent of 23.1.6.1.1 as a  
transition.  We normally shoot for the transition to the above- 
ground pipe to occur at 6 to 12 inches above the floor, but there is  
nothing in 13 that mandates any particular height.


Mark A. Sornsin, PE| Fire Protection Engineer
Ulteig Engineers, Inc.| Fargo, ND
mark.sorn...@ulteig.com