RE: Underground Piping Under Slab

2015-02-20 Thread Bill Brooks
Highly desirable is an understatement I assume?  I'm just hoping this is a
typographical thing.  I sent an email to NFPA earlier this week on this - no
response yet.  So many more things could be done to make the online
subscription more useful like having errata noted and having TIAs noted and
linking all text changes directly to the ROP/ROC or whatever these are
called now and maybe more.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Friday, February 20, 2015 3:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Underground Piping Under Slab

NFPA has at least temporarily stopped flagging the sections that have
changed.  Not sure how long this will continue.  IT has been expressed
pretty loudly that having the changes identified is highly desirable.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov
wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and
handbook, I noticed that while the language of 10.6.3.1 has changed in the
2013 edition to clarify the 10 ft distance, but the section was not marked
as new in either the printed code, the handbook or the PDF version available
through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation, 
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on 
 SC Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.)
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire
service mains enter under the building no more than 10 ft (3 m) as measured
from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 
 categorically states not to do something, yet 10.6.2 allows it.  
 Elimination of 10.6.1 seems the thing to do and would not change the 
 intent.  After all it's impossible to meet 10.6.1 unless you put the 
 stub up in an exterior enclosure and route it through the exterior 
 wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too
much?
 
 If this is important it should be submitted as a Building, Plumbing,
Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to
say what you really meant was that as long as the plumbing inspector is OK
with the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building 
 slab but if it's a must there are some precautions that must be taken 
 as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned
all required or as a bare minimum? I'm working on a project and the
architect has located the riser room in the center of the building,
approximately 15'
 from the outside wall. I brought it to their attention that it's not the
best idea and provided them the above code reference. Instead of
appreciating the heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http

RE: Underground Piping Under Slab

2015-02-20 Thread Fairchild, Jack
A line at some of the changes, but not all?!?!?  SMH

Jack Fairchild

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matthew J Willis
Sent: Friday, February 20, 2015 3:13 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Underground Piping Under Slab

Was there a reason given?

R/
Matt

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Friday, February 20, 2015 1:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Underground Piping Under Slab

NFPA has at least temporarily stopped flagging the sections that have changed.  
Not sure how long this will continue.  IT has been expressed pretty loudly that 
having the changes identified is highly desirable.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov 
 wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and 
 handbook, I noticed that while the language of 10.6.3.1 has changed in the 
 2013 edition to clarify the 10 ft distance, but the section was not marked as 
 new in either the printed code, the handbook or the PDF version available 
 through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation,
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on 
 SC Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.)
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire 
 service mains enter under the building no more than 10 ft (3 m) as measured 
 from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 
 categorically states not to do something, yet 10.6.2 allows it.
 Elimination of 10.6.1 seems the thing to do and would not change the 
 intent.  After all it's impossible to meet 10.6.1 unless you put the 
 stub up in an exterior enclosure and route it through the exterior 
 wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too much?
 
 If this is important it should be submitted as a Building, Plumbing, 
 Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to say 
 what you really meant was that as long as the plumbing inspector is OK with 
 the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building 
 slab but if it's a must there are some precautions that must be taken 
 as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
 required or as a bare minimum? I'm working on a project and the architect has 
 located the riser room in the center of the building, approximately 15'
 from the outside wall. I brought it to their attention that it's not the best 
 idea and provided them the above code reference. Instead of appreciating the 
 heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi

RE: Underground Piping Under Slab

2015-02-20 Thread David Blackwell
Just to clarify - the 2013 editions of NFPA 13 do have markings, it's just that 
this particular section was missed.  

Roland is correct - I previously found that the newest NFPA 54 edition was 
published by NFPA without the markings of changes traditionally found in their 
standards as called for by the NFPA Manual of Style, so I called and got 
confirmation from NFPA staff that it was intentional and expected for future 
editions of NFPA standards.  I indicated my preference for continuing to use 
notations of some sort that that would help all users understand when changes 
have been made.

Respectfully,


David W. S. Blackwell, II, PE, CFPE, CFI I
Chief Engineer
Office of State Fire Marshal
SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail, 
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   david.blackw...@llr.sc.gov
Website:  http://www.scfiremarshal.llronline.com/


Please note that you can sign up to receive automatic information on SC 
Division of Fire and Life Safety current events, policies, laws and procedures 
by visiting our Web site at:  http://www.scfiremarshal.llronline.com/


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Friday, February 20, 2015 3:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Underground Piping Under Slab

NFPA has at least temporarily stopped flagging the sections that have changed.  
Not sure how long this will continue.  IT has been expressed pretty loudly that 
having the changes identified is highly desirable.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov 
 wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and 
 handbook, I noticed that while the language of 10.6.3.1 has changed in the 
 2013 edition to clarify the 10 ft distance, but the section was not marked as 
 new in either the printed code, the handbook or the PDF version available 
 through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation, 
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on 
 SC Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.)
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire 
 service mains enter under the building no more than 10 ft (3 m) as measured 
 from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 
 categorically states not to do something, yet 10.6.2 allows it.  
 Elimination of 10.6.1 seems the thing to do and would not change the 
 intent.  After all it's impossible to meet 10.6.1 unless you put the 
 stub up in an exterior enclosure and route it through the exterior 
 wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too much?
 
 If this is important it should be submitted as a Building, Plumbing, 
 Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to say 
 what you really meant was that as long as the plumbing inspector is OK with 
 the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building 
 slab but if it's a must there are some precautions that must be taken 
 as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
 required or as a bare minimum? I'm working

RE: Underground Piping Under Slab

2015-02-20 Thread David Blackwell
When comparing NFPA 10.6.3.1 in my hard copy versions of the code and handbook, 
I noticed that while the language of 10.6.3.1 has changed in the 2013 edition 
to clarify the 10 ft distance, but the section was not marked as new in either 
the printed code, the handbook or the PDF version available through NFPA 
All-Access...  

Respectfully,


David W. S. Blackwell, II, PE, CFPE, CFI I
Chief Engineer
Office of State Fire Marshal
SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail, 
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   david.blackw...@llr.sc.gov
Website:  http://www.scfiremarshal.llronline.com/


Please note that you can sign up to receive automatic information on SC 
Division of Fire and Life Safety current events, policies, laws and procedures 
by visiting our Web site at:  http://www.scfiremarshal.llronline.com/

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rfletc...@aerofire.com
Sent: Friday, February 13, 2015 9:33 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Underground Piping Under Slab

10.6.3.1*  (13 Ed.) 
The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire service 
mains enter under the building no more than 10 ft (3 m) as measured from the 
outside edge of the building to the center of the vertical pipe.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Brooks
Sent: Friday, February 13, 2015 6:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Underground Piping Under Slab

The new NFPA exception formatting is interesting.  10.6.1 categorically states 
not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1 seems the 
thing to do and would not change the intent.  After all it's impossible to meet 
10.6.1 unless you put the stub up in an exterior enclosure and route it through 
the exterior wall.  Even the language in
10.6.3 is an exception to 10.6.1.  How much inside the building is too much?

If this is important it should be submitted as a Building, Plumbing, Mechanical 
Code change and removed from NFPA 13.

So, like we see on TV, you should now clarify your meeting comments to say 
what you really meant was that as long as the plumbing inspector is OK with the 
special precautions so are you.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, February 12, 2015 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Piping Under Slab

I understand it's not typical to run the fire main under the building slab but 
if it's a must there are some precautions that must be taken as shown in
10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
required or as a bare minimum? I'm working on a project and the architect has 
located the riser room in the center of the building, approximately 15'
from the outside wall. I brought it to their attention that it's not the best 
idea and provided them the above code reference. Instead of appreciating the 
heads up I'm now the redheaded step child, go figure.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Underground Piping Under Slab

2015-02-20 Thread Roland Huggins
NFPA has at least temporarily stopped flagging the sections that have changed.  
Not sure how long this will continue.  IT has been expressed pretty loudly that 
having the changes identified is highly desirable.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov 
 wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and 
 handbook, I noticed that while the language of 10.6.3.1 has changed in the 
 2013 edition to clarify the 10 ft distance, but the section was not marked as 
 new in either the printed code, the handbook or the PDF version available 
 through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I
 Chief Engineer
 Office of State Fire Marshal
 SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail, 
 Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on SC 
 Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.) 
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire 
 service mains enter under the building no more than 10 ft (3 m) as measured 
 from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 categorically 
 states not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1 
 seems the thing to do and would not change the intent.  After all it's 
 impossible to meet 10.6.1 unless you put the stub up in an exterior enclosure 
 and route it through the exterior wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too much?
 
 If this is important it should be submitted as a Building, Plumbing, 
 Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to say 
 what you really meant was that as long as the plumbing inspector is OK with 
 the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building slab 
 but if it's a must there are some precautions that must be taken as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
 required or as a bare minimum? I'm working on a project and the architect has 
 located the riser room in the center of the building, approximately 15'
 from the outside wall. I brought it to their attention that it's not the best 
 idea and provided them the above code reference. Instead of appreciating the 
 heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Underground Piping Under Slab

2015-02-20 Thread RFletcher
Makes it more fun proving to a contractor that it's a NEW change.

Ron fletcher Sent from my iPhone

 On Feb 20, 2015, at 3:01 PM, Roland Huggins rhugg...@firesprinkler.org 
 wrote:
 
 NFPA has at least temporarily stopped flagging the sections that have 
 changed.  Not sure how long this will continue.  IT has been expressed pretty 
 loudly that having the changes identified is highly desirable.
 
 
 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org http://www.firesprinkler.org/
 
 
 
 
 
 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov 
 wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and 
 handbook, I noticed that while the language of 10.6.3.1 has changed in the 
 2013 edition to clarify the 10 ft distance, but the section was not marked 
 as new in either the printed code, the handbook or the PDF version available 
 through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I
 Chief Engineer
 Office of State Fire Marshal
 SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail, 
 Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on SC 
 Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.) 
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire 
 service mains enter under the building no more than 10 ft (3 m) as measured 
 from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 categorically 
 states not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1 
 seems the thing to do and would not change the intent.  After all it's 
 impossible to meet 10.6.1 unless you put the stub up in an exterior 
 enclosure and route it through the exterior wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too much?
 
 If this is important it should be submitted as a Building, Plumbing, 
 Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to say 
 what you really meant was that as long as the plumbing inspector is OK with 
 the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building slab 
 but if it's a must there are some precautions that must be taken as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
 required or as a bare minimum? I'm working on a project and the architect 
 has located the riser room in the center of the building, approximately 15'
 from the outside wall. I brought it to their attention that it's not the 
 best idea and provided them the above code reference. Instead of 
 appreciating the heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

RE: Underground Piping Under Slab

2015-02-20 Thread Matthew J Willis
Was there a reason given?

R/
Matt

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Friday, February 20, 2015 1:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Underground Piping Under Slab

NFPA has at least temporarily stopped flagging the sections that have changed.  
Not sure how long this will continue.  IT has been expressed pretty loudly that 
having the changes identified is highly desirable.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov 
 wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and 
 handbook, I noticed that while the language of 10.6.3.1 has changed in the 
 2013 edition to clarify the 10 ft distance, but the section was not marked as 
 new in either the printed code, the handbook or the PDF version available 
 through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of 
 State Fire Marshal SC Department of Labor, Licensing,  Regulation, 
 141 Monticello Trail, Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on 
 SC Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.)
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire 
 service mains enter under the building no more than 10 ft (3 m) as measured 
 from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 
 categorically states not to do something, yet 10.6.2 allows it.  
 Elimination of 10.6.1 seems the thing to do and would not change the 
 intent.  After all it's impossible to meet 10.6.1 unless you put the 
 stub up in an exterior enclosure and route it through the exterior 
 wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too much?
 
 If this is important it should be submitted as a Building, Plumbing, 
 Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to say 
 what you really meant was that as long as the plumbing inspector is OK with 
 the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building 
 slab but if it's a must there are some precautions that must be taken 
 as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
 required or as a bare minimum? I'm working on a project and the architect has 
 located the riser room in the center of the building, approximately 15'
 from the outside wall. I brought it to their attention that it's not the best 
 idea and provided them the above code reference. Instead of appreciating the 
 heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list

RE: Underground Piping Under Slab

2015-02-13 Thread Bill Brooks
The new NFPA exception formatting is interesting.  10.6.1 categorically
states not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1
seems the thing to do and would not change the intent.  After all it's
impossible to meet 10.6.1 unless you put the stub up in an exterior
enclosure and route it through the exterior wall.  Even the language in
10.6.3 is an exception to 10.6.1.  How much inside the building is too much?

If this is important it should be submitted as a Building, Plumbing,
Mechanical Code change and removed from NFPA 13.

So, like we see on TV, you should now clarify your meeting comments to say
what you really meant was that as long as the plumbing inspector is OK with
the special precautions so are you.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, February 12, 2015 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Piping Under Slab

I understand it's not typical to run the fire main under the building slab
but if it's a must there are some precautions that must be taken as shown in
10.6.2 (2007). My question is are the (3) provisions that are mentioned all
required or as a bare minimum? I'm working on a project and the architect
has located the riser room in the center of the building, approximately 15'
from the outside wall. I brought it to their attention that it's not the
best idea and provided them the above code reference. Instead of
appreciating the heads up I'm now the redheaded step child, go figure.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Underground Piping Under Slab

2015-02-13 Thread RFletcher
10.6.3.1*  (13 Ed.) 
The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire service 
mains enter under the building no more than 10 ft (3 m) as measured from the 
outside edge of the building to the center of the vertical pipe.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Brooks
Sent: Friday, February 13, 2015 6:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Underground Piping Under Slab

The new NFPA exception formatting is interesting.  10.6.1 categorically states 
not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1 seems the 
thing to do and would not change the intent.  After all it's impossible to meet 
10.6.1 unless you put the stub up in an exterior enclosure and route it through 
the exterior wall.  Even the language in
10.6.3 is an exception to 10.6.1.  How much inside the building is too much?

If this is important it should be submitted as a Building, Plumbing, Mechanical 
Code change and removed from NFPA 13.

So, like we see on TV, you should now clarify your meeting comments to say 
what you really meant was that as long as the plumbing inspector is OK with the 
special precautions so are you.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, February 12, 2015 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Piping Under Slab

I understand it's not typical to run the fire main under the building slab but 
if it's a must there are some precautions that must be taken as shown in
10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
required or as a bare minimum? I'm working on a project and the architect has 
located the riser room in the center of the building, approximately 15'
from the outside wall. I brought it to their attention that it's not the best 
idea and provided them the above code reference. Instead of appreciating the 
heads up I'm now the redheaded step child, go figure.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Underground Piping Under Slab

2015-02-12 Thread Mark A. Sornsin, P.E.
No - the primary reason is that fire service mains - combined or not - are 
large diameter pipes that would cause devastating damage if they (or their 
joints) were to fail below the slab. Along with the extensive damage is the 
additional damage that would be required to repair them after they failed, as 
well as the long period of down time without fire protection. It's just bad 
practice.

Not to mention the fact that you are supposed to be able to run a full-flow 
main drain test regularly at the sprinkler riser. So there needs to be a plan 
for piping that drain back out to the exterior wall, or a provision for a large 
diameter sump/drain. But I'm sure the ME addressed that...

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dewayne Martinez
Sent: Thursday, February 12, 2015 4:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Underground Piping Under Slab

I have had this happen too and the GC did not seem to care because it was a 
combined water service and the plumbing inspector said it was fine.
Could it be that it does not fall under fire protection rules until after the 
BFP for a combined service?

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian 
Harris
Sent: Thursday, February 12, 2015 3:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Piping Under Slab

I understand it's not typical to run the fire main under the building slab but 
if it's a must there are some precautions that must be taken as shown in 10.6.2 
(2007). My question is are the (3) provisions that are mentioned all required 
or as a bare minimum? I'm working on a project and the architect has located 
the riser room in the center of the building, approximately 15' from the 
outside wall. I brought it to their attention that it's not the best idea and 
provided them the above code reference.
Instead of appreciating the heads up I'm now the redheaded step child, go 
figure.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org