Re: resurrecting an old system

2013-11-23 Thread Dwight Havens
I like Mr. Hill's approach.  A little quality time using his approach should 
narrow down the scope of necessary repairs fairly quickly.

Dwight





On Saturday, November 23, 2013 1:25 PM, John O'Connor jocon...@nfspk.com 
wrote:
 
Mike,
I would respectfully urge flushing prior to full 200# test, simply because
this system contains mud and other debris, that could, still in place, allow
pinhole leaks to remain undetected.  Flush to eliminate debris that could be
allowing a successful pressure test.  Once flushed, the system may still
show leaks resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike
Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1432 / Virus Database: 3629/6352 - Release Date: 11/20/13


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread RFletcher
Do an air test, fix the obvious stuff that's broken, buy a new pump and 
flush/test the existing pipe with water. An air test will get most big leaks 
it's pretty hard to find little pin hole leaks using air if it is a large 
volume system. My 2 cents.

Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 6:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread Scott A Futrell
I like the replace it all option...
How old is the system to start with?
You need to replace all the sprinklers, if some have popped you don't know 
how many others may be damaged.
What about gaskets in grooved couplings?
Is the water supply now equal to the original pump and pond? If not, pipe size 
changes, right?
You could minimize the liability by replacing everything...

Scott
 
(763) 425-1001 Office
(612) 759-5556 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 7:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: resurrecting an old system

2013-11-20 Thread Todd - Work
The owner wants to re-use the system and we have to prove to him that it needs 
to be replaced, if it does. I'm thinking after a physical inspection and air 
test, it would tell us if we have something that could be used or not. The 
building is approximately 30 ft to the peak and 25 to the hip and is wide open 
for storage and maintenance of large equipment (demolition company). However, 
working on mains around the perimeter will be difficult at best. 

My guess is that when the system was shut down, they just opened the 2 drain 
and didn't bother with low points. I think most of the low stuff will have to 
be replaced. But it would be helpful if at least the high piping could remain.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com

 On Nov 20, 2013, at 9:06 AM, Scott A Futrell sco...@ffcdi.com wrote:
 
 I like the replace it all option...
 How old is the system to start with?
 You need to replace all the sprinklers, if some have popped you don't know 
 how many others may be damaged.
 What about gaskets in grooved couplings?
 Is the water supply now equal to the original pump and pond? If not, pipe 
 size changes, right?
 You could minimize the liability by replacing everything...
 
 Scott
  
 (763) 425-1001 Office
 (612) 759-5556 Cell
 
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - 
 Work
 Sent: Wednesday, November 20, 2013 7:02 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: resurrecting an old system
 
 I am working with a company that bought a building where the sprinkler system 
 had been turned off about 10 years ago. The fire department is requiring that 
 a system be turned on. The existing system was fed from a pump taking suction 
 from a pond (disconnected and removed). There has been some cracking and 
 splitting of fittings at low points and some heads have popped. 
 
 The first step was to have a contractor come in and made a detailed visual 
 inspection of the system, including internal. That showed that all of the 
 pipe up high appears to be in good shape and could possibly be re-used. 
 However, there was some mud (not scale) that had collected in some of the 
 mains.
 
 My thought was that the next step would be to fix or cap off the broken areas 
 and do an air test to see what the integrity of the system really is, then 
 flush the system if all looks good. However, would you want to flush out the 
 mains before you do an air test? If there is a problem with the mains in the 
 area covered by the mud, would the air test not show it? On the other side, 
 flushing would create a problem since there is no public water supply. We 
 would probably have to get a fire department pumper involved. Also, you could 
 have an issue if the water finds a leak and water starts spraying down on 
 equipment
 
 Thoughts? Flush or air test first?
 
 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread Forest Wilson Fire Sprinkler Comtractor
I would air test first but I think you will need the water test to find leaks  


Sent from my Galaxy S®III

 Original message 
From: Scott A Futrell sco...@ffcdi.com 
Date: 11/20/2013  9:06 AM  (GMT-05:00) 
To: sprinklerforum@lists.firesprinkler.org 
Subject: RE: resurrecting an old system 
 
I like the replace it all option...
How old is the system to start with?
You need to replace all the sprinklers, if some have popped you don't know 
how many others may be damaged.
What about gaskets in grooved couplings?
Is the water supply now equal to the original pump and pond? If not, pipe size 
changes, right?
You could minimize the liability by replacing everything...

Scott
 
(763) 425-1001 Office
(612) 759-5556 Cell


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 7:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used. However, 
there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air test not show it? On the other side, 
flushing would create a problem since there is no public water supply. We would 
probably have to get a fire department pumper involved. Also, you could have an 
issue if the water finds a leak and water starts spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread Mike Hill
You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread John O'Connor
Mike,
I would respectfully urge flushing prior to full 200# test, simply because
this system contains mud and other debris, that could, still in place, allow
pinhole leaks to remain undetected.  Flush to eliminate debris that could be
allowing a successful pressure test.  Once flushed, the system may still
show leaks resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike
Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1432 / Virus Database: 3629/6352 - Release Date: 11/20/13

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: resurrecting an old system

2013-11-20 Thread John Denhardt
I would suggest a slightly modified approach.

Test and repair as needed until tight.  Flush and then retest.

You really need to flush and retest due to the leaks that might be uncovered 
after proper flushing.  I agree with Scott on cost.  Given the total cost in 
the end, it might be wiser for the owner to spend the money on replacing the 
system.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John 
O'Connor
Sent: Wednesday, November 20, 2013 11:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

Mike,
I would respectfully urge flushing prior to full 200# test, simply because
this system contains mud and other debris, that could, still in place, allow
pinhole leaks to remain undetected.  Flush to eliminate debris that could be
allowing a successful pressure test.  Once flushed, the system may still
show leaks resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike
Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System
froze and there were lots of issues. The occupant's first indication of a
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much
longer, so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street
pressure, we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also
separated the system into smaller sections before we started testing, so as
to help us locate leaks.

I would try to salvage as much of the existing system as possible, if only
to help the owner save some money. Why discard the system because of what
you think might be wrong.
Find out what is actually wrong. System may be easily and confidently
repaired or you may find enough issues or concerns spread out through the
entire building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd -
Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler
system had been turned off about 10 years ago. The fire department is
requiring that a system be turned on. The existing system was fed from a
pump taking suction from a pond (disconnected and removed). There has been
some cracking and splitting of fittings at low points and some heads have
popped. 

The first step was to have a contractor come in and made a detailed visual
inspection of the system, including internal. That showed that all of the
pipe up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the
mains.

My thought was that the next step would be to fix or cap off the broken
areas and do an air test to see what the integrity of the system really is,
then flush the system if all looks good. However, would you want to flush
out the mains before you do an air test? If there is a problem with the
mains in the area covered by the mud, would the air test not show it? On the
other side, flushing would create a problem since there is no public water
supply. We would probably have to get a fire department pumper involved.
Also, you could have an issue if the water finds a leak and water starts
spraying down on equipment

Thoughts? Flush or air test first?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1432 / Virus

RE: resurrecting an old system

2013-11-20 Thread Matt Grise
The other benefit to the owner with replacement is a warranty. If the system is 
patched back together, then it could end up being a source of constant 
headaches and expense if leaks start to show up. 

Replacing the system could end up being a faster option depending on how many 
rounds of testing, flushing, and patching are needed.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John 
Denhardt
Sent: Wednesday, November 20, 2013 10:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

I would suggest a slightly modified approach.

Test and repair as needed until tight.  Flush and then retest.

You really need to flush and retest due to the leaks that might be uncovered 
after proper flushing.  I agree with Scott on cost.  Given the total cost in 
the end, it might be wiser for the owner to spend the money on replacing the 
system.

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John 
O'Connor
Sent: Wednesday, November 20, 2013 11:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

Mike,
I would respectfully urge flushing prior to full 200# test, simply because this 
system contains mud and other debris, that could, still in place, allow pinhole 
leaks to remain undetected.  Flush to eliminate debris that could be allowing a 
successful pressure test.  Once flushed, the system may still show leaks 
resulting from the debris removal internally.
John

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Hill
Sent: Wednesday, November 20, 2013 9:58 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: resurrecting an old system

You are on the right track. Test and repair as needed, then flush.

I had a similar situation in an aircraft hangar about 15 years ago. System 
froze and there were lots of issues. The occupant's first indication of a 
problem was falling debris, broken fittings.
We went in and fixed the obvious issues. We then put air on the system and 
found several large leaks. 
Put air on it again and still had leaks but the pressure drop took much longer, 
so we felt confident to put water on the system (street pressure).
Found several small leaks and repaired them. When system held street pressure, 
we pumped it up gradually to 200 psi.
I think the whole process took 3 days. If I remember correctly, we also 
separated the system into smaller sections before we started testing, so as to 
help us locate leaks.

I would try to salvage as much of the existing system as possible, if only to 
help the owner save some money. Why discard the system because of what you 
think might be wrong.
Find out what is actually wrong. System may be easily and confidently repaired 
or you may find enough issues or concerns spread out through the entire 
building to warrant total replacement.
By proving this one way or the other you will be helping out the new owner.

Mike Hill

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd - Work
Sent: Wednesday, November 20, 2013 8:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: resurrecting an old system

I am working with a company that bought a building where the sprinkler system 
had been turned off about 10 years ago. The fire department is requiring that a 
system be turned on. The existing system was fed from a pump taking suction 
from a pond (disconnected and removed). There has been some cracking and 
splitting of fittings at low points and some heads have popped. 

The first step was to have a contractor come in and made a detailed visual 
inspection of the system, including internal. That showed that all of the pipe 
up high appears to be in good shape and could possibly be re-used.
However, there was some mud (not scale) that had collected in some of the mains.

My thought was that the next step would be to fix or cap off the broken areas 
and do an air test to see what the integrity of the system really is, then 
flush the system if all looks good. However, would you want to flush out the 
mains before you do an air test? If there is a problem with the mains in the 
area covered by the mud, would the air