Re: [time-nuts] No more 60Hz! TEC Elimination - control

2011-07-03 Thread Bill Hawkins
Group,

The effort to track power line frequency changes is laudable. I think
the effort to determine the stiffness of the network by measuring the
phase angle between GPS time and local line zero crossings is most
interesting. But the following is about the frequency control problem.

The main problem is that the amount of power that is stored in the
distribution system is negligible. The generating station has no
information about load changes until after they have happened. There
is no lag time that allows derivative action to compensate.

If the generating station is on an island with no connection to any
grid, you can use a proportional controller with integral action to
control the generator speed by manipulating the fuel valve to the
engine. This can hold the generator quite close to your desired line
frequency. But because it is feedback control, an error must be
sensed before the fuel valve moves - cycles can be lost. It is still
necessary to manually bias the fuel valve to match the error between
the cycles generated and the GPS cycles elapsed.

When generating stations are synchronously synchronized by the 
distribution network, a new problem arises. The stations can not all
use integral action and maintain stable control. In fact, only one
integral controller may be on such a network. The integral control
comes from the area dispatcher, who integrates the cycles generated
and compares them to the cycles to maintain 60.000+ cycles per second
(in the degenerate West).

I am not clear on how the dispatcher allocates frequency error to the
area stations, or how they react to commands to change. But it seems
to me that this is a control problem that can be solved without undue
stress on the generating equipment. Perhaps it is as simple as a
setpoint rate of change limit (can't be, 3000 people would have thought
of that.)

We welcome your comments with Enthusiasm.

The references below are important.

Bill Hawkins

-Original Message-
On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiec bobkup...@comcast.net wrote:

 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-07-01 Thread Francis Grosz
Folks,

 The Pacific Northwest National Laboratory has a couple of Grid Monitor
tools as part of their Gridwise program that you can download.  This gives a
pretty good high resolution look at the grid frequency.  (This is the frequency
of the Western Interconnect.)  If you're interested, check out

http://gridwise.pnnl.gov/technologies/transactive_controls.stm

The download buttons plus a link to a pdf on the program are in the
bar on the right side under Transactive.  While not the accumulated
error due to TEC elimination, it will allow you to see how far off things 
get, not to mention see any large disturbances.  There might be some
interesting viewing there this summer.  There is also more info available 
on  their Gridwise program.

 Francis Grosz
___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Oz-in-DFW


On 6/24/2011 9:20 PM, Will Matney wrote:
 However, I should have
 said, one should never run a 60 Hz transformer, or motor, on the same line
 voltage it was rated for at a lower 50 Hz.
Most modern commodity transformers for electronic power supplies are
specified for rated performance from 47 to 63 Hz.

Most power distribution system products for use in the US I've seen are
rated at 60 ± 3 Hz though some stuff from European manufacturers is
rated at ± 2.5 Hz.  I guess it's a holdover from 50 Hz specs. 

The power companies seem to spec normal variation at a max of 0.1 Hz
though I understand the max offset they use by agreement for phase
adjustment is about 0.02 Hz.

A lot of large machinery has a a great deal of independence from the AC
line frequency.  Even a 60 year old paper mill I did some work for had a
mechanical phase adjustment driven by large DC motors on the machines in
their line.  IIRC the controls guy said they could compensate for 1 Hz
line frequency variations over 10 seconds. This was a lot faster than I
expected.  Paper mills have lots of spinning mass that takes a long time
to influence.

Oz (in DFW)

-- 
mailto:o...@ozindfw.net
Oz
POB 93167 
Southlake, TX 76092 (Near DFW Airport) 





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Will Matney
Oz,

Some companies in the US are producing 50 hz transformers in their mass
produced units so they can readily sell them to the European market and
here. That is a plus for us, if we buy one, as they will run a lot cooler,
and last longer over it, when we apply 60 Hz to one. There's a bit more of
an amount of iron in a 50 Hz, which means for the applied line voltage, the
flux density will be lower, and thus, the whole thing will run cooler.
However, for a European, 50 Hz, transformer, you'll have a multiple
primary, if it's made to run here or there, as if I recall, their line
voltage is about double what ours is.

When I wrote most of the Wikibooks article on Transformer Design, I did a
major study on transformers, and probably now have 30+ books on the subject
alone. Some of the better information I read was written by Col. William T
McLyman, in his series of books on the design of transformers for NASA.
Another good book was written by engineers at MIT, and they still update
it, since it was written in the 1940's. From them, though, I learned a good
deal about their construction from wall-wart size, all they way up to the
huge oil-filled ones, now sitiing at our power stations. Plus, I used to
sell equipment to Kuhlman Electric, in Lexington, Ky., and another
transformer manufacturer in Cincinnati, Foster Transformer, and was privy
to how they built the things.

Best,

Will

*** REPLY SEPARATOR  ***

On 6/27/2011 at 6:44 AM Oz-in-DFW wrote:

On 6/24/2011 9:20 PM, Will Matney wrote:
 However, I should have
 said, one should never run a 60 Hz transformer, or motor, on the same
line
 voltage it was rated for at a lower 50 Hz.
Most modern commodity transformers for electronic power supplies are
specified for rated performance from 47 to 63 Hz.

Most power distribution system products for use in the US I've seen are
rated at 60 ± 3 Hz though some stuff from European manufacturers is
rated at ± 2.5 Hz.  I guess it's a holdover from 50 Hz specs. 

The power companies seem to spec normal variation at a max of 0.1 Hz
though I understand the max offset they use by agreement for phase
adjustment is about 0.02 Hz.

A lot of large machinery has a a great deal of independence from the AC
line frequency.  Even a 60 year old paper mill I did some work for had a
mechanical phase adjustment driven by large DC motors on the machines in
their line.  IIRC the controls guy said they could compensate for 1 Hz
line frequency variations over 10 seconds. This was a lot faster than I
expected.  Paper mills have lots of spinning mass that takes a long time
to influence.

Oz (in DFW)

-- 
mailto:o...@ozindfw.net
Oz
POB 93167 
Southlake, TX 76092 (Near DFW Airport) 





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

__ Information from ESET Smart Security, version of virus
signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Poul-Henning Kamp
In message 4e086d33.6040...@ozindfw.net, Oz-in-DFW writes:


On 6/24/2011 9:20 PM, Will Matney wrote:
 However, I should have
 said, one should never run a 60 Hz transformer, or motor, on the same line
 voltage it was rated for at a lower 50 Hz.
Most modern commodity transformers for electronic power supplies are
specified for rated performance from 47 to 63 Hz.

The only thing I know of, apart from clocks, that you should not run
on the wrong frequency are oldfashioned mechanical shavers.

If it has a motor you're fine, but if it just has a magnet and a
coil and relies on mechanical resonance: don't even think about it.

Anything else:  Just plug it in, after you checked the 110/200 V setting.

-- 
Poul-Henning Kamp   | UNIX since Zilog Zeus 3.20
p...@freebsd.org | TCP/IP since RFC 956
FreeBSD committer   | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Will Matney
Poul-Henning,

Running the transformer that way won't burn it up at that instant, it just
causes it to run hotter, because it's closer to saturation, and it shortens
the life span a good bit. A lot of the new ones now being made, are wound
to run on either frequency (wound for just under 50 Hz), so they can export
them internationally.

Best,

Will

*** REPLY SEPARATOR  ***

On 6/27/2011 at 3:39 PM Poul-Henning Kamp wrote:

In message 4e086d33.6040...@ozindfw.net, Oz-in-DFW writes:


On 6/24/2011 9:20 PM, Will Matney wrote:
 However, I should have
 said, one should never run a 60 Hz transformer, or motor, on the same
line
 voltage it was rated for at a lower 50 Hz.
Most modern commodity transformers for electronic power supplies are
specified for rated performance from 47 to 63 Hz.

The only thing I know of, apart from clocks, that you should not run
on the wrong frequency are oldfashioned mechanical shavers.

If it has a motor you're fine, but if it just has a magnet and a
coil and relies on mechanical resonance: don't even think about it.

Anything else:  Just plug it in, after you checked the 110/200 V setting.

-- 
Poul-Henning Kamp   | UNIX since Zilog Zeus 3.20
p...@freebsd.org | TCP/IP since RFC 956
FreeBSD committer   | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by
incompetence.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

__ Information from ESET Smart Security, version of virus
signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Charles P. Steinmetz



The only thing I know of, apart from clocks, that you should not run
on the wrong frequency are oldfashioned mechanical shavers.


There are lots of consumer products sold in North America that 
specify 60 Hz only, and in which the transformers will hum and 
overheat if run on 50 Hz.  I have always designed with transformers 
that will accept 47-63 Hz, but many competitors do not.  As more and 
more items move to switching power supplies, this will be less of an 
issue (of course, in many applications the switching supplies 
themselves will create new issues...).


Best regards,

Charles





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread David VanHorn



They were talking about a very small drift here. Even if the change were ten 
HOURS in a year, that's one part in 876.
I highly doubt your shaver is going to be affected by grid tolerance.

I wouldn't plug a 60 hz model into 50 hz, but that's different.


From: time-nuts-boun...@febo.com [time-nuts-boun...@febo.com] On Behalf Of 
Poul-Henning Kamp [p...@phk.freebsd.dk]
Sent: Monday, June 27, 2011 9:39 AM
To: Discussion of precise time and frequency measurement
Subject: Re: [time-nuts] No more 60Hz! TEC Elimination

In message 4e086d33.6040...@ozindfw.net, Oz-in-DFW writes:


On 6/24/2011 9:20 PM, Will Matney wrote:
 However, I should have
 said, one should never run a 60 Hz transformer, or motor, on the same line
 voltage it was rated for at a lower 50 Hz.
Most modern commodity transformers for electronic power supplies are
specified for rated performance from 47 to 63 Hz.

The only thing I know of, apart from clocks, that you should not run
on the wrong frequency are oldfashioned mechanical shavers.

If it has a motor you're fine, but if it just has a magnet and a
coil and relies on mechanical resonance: don't even think about it.

Anything else:  Just plug it in, after you checked the 110/200 V setting.

--
Poul-Henning Kamp   | UNIX since Zilog Zeus 3.20
p...@freebsd.org | TCP/IP since RFC 956
FreeBSD committer   | BSD since 4.3-tahoe
Never attribute to malice what can adequately be explained by incompetence.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Charles P. Steinmetz



Running the transformer that way won't burn it up at that instant, it just
causes it to run hotter, because it's closer to saturation, and it shortens
the life span a good bit.

I have yet to hear of any evidence for that being a problem with
US kit here in Denmark, probably because most kit is not run at
the extreme top end of its temperature specification.


I once was retained by a US manufacturer to determine why its 
high-end amps and preamps had a nearly 100% failure rate in Europe 
and Japan.  It was their power transformers, which lacked sufficient 
core for 50 Hz operation -- they overheated and opened the internal 
thermal link.  One customer had repaired his by digging out the 
thermal link and bypassing it with a short.  His got hot enough to 
cook the paper and enamel and produce smoke.


Best regards,

Charles





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-27 Thread Chuck Forsberg WA7KGX N2469R

I picked up an older stereo amp to use its parts for a project.
With no load at all, the power transformer runs uncomfortably hot.
At 50 Hz it might make a good space heater for a while.

--
Chuck Forsberg WA7KGX N2469R c...@omen.com   www.omen.com
Developer of Industrial ZMODEM(Tm) for Embedded Applications
  Omen Technology Inc  The High Reliability Software
10255 NW Old Cornelius Pass Portland OR 97231   503-614-0430


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


[time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Bob Kupiec

AP: Power grid change may disrupt clocks
-
http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


Time Error Correction Elimination
-
http://www.nerc.com/page.php?cid=6|386

NERC Report - June 14
-
http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread paul swed
change you can count on
Thanks. All those silly alarm clocks by the bed.

On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiec bobkup...@comcast.net wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread gary

I use a Logitech Squeezebox radio in the bedroom. Network timed!

I don't see how they connect grid that aren't totally in sync.

On 6/24/2011 5:50 PM, paul swed wrote:

change you can count on
Thanks. All those silly alarm clocks by the bed.

On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net  wrote:



AP: Power grid change may disrupt clocks
-
http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


Time Error Correction Elimination
-
http://www.nerc.com/page.php?cid=6|386

NERC Report - June 14
-
http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Will Matney
I predict, with all of my oracle abilities, snort, that the test won't run
no time until there's a law suit. Almost everyone uses battery powered
clocks nowdays, on the wall, and most alarms are digital with xtal
timebases. However, there are still those old foggies who still have
motorized clocks depending on 60Hz to do their duty. If this makes them
obsolete, I wonder if the government is prepared to buy folks replacement
clocks, like they provided the digital receivers for our TV's? Like I said,
I can see a courtroom battle as I write this.

Best,

Will

*** REPLY SEPARATOR  ***

On 6/24/2011 at 8:50 PM paul swed wrote:

change you can count on
Thanks. All those silly alarm clocks by the bed.

On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiec bobkup...@comcast.net wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

__ Information from ESET Smart Security, version of virus
signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread gary
It all depends where you live. I know people that get an outage a week, 
so setting clocks is a way of life.


PGE, bless their corporate hearts, is run both like a Swiss clock and 
third world nation power. If you have a fair amount of industry or malls 
nearby (i.e. customers), your power is great. Live at the edge of town, 
and things are not so good, even in Silicon Valley. Monte Sereno, Monta 
Vista (now Cupertino), etc.



On 6/24/2011 6:07 PM, Will Matney wrote:

I predict, with all of my oracle abilities, snort, that the test won't run
no time until there's a law suit. Almost everyone uses battery powered
clocks nowdays, on the wall, and most alarms are digital with xtal
timebases. However, there are still those old foggies who still have
motorized clocks depending on 60Hz to do their duty. If this makes them
obsolete, I wonder if the government is prepared to buy folks replacement
clocks, like they provided the digital receivers for our TV's? Like I said,
I can see a courtroom battle as I write this.

Best,

Will

*** REPLY SEPARATOR  ***

On 6/24/2011 at 8:50 PM paul swed wrote:


change you can count on
Thanks. All those silly alarm clocks by the bed.

On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net  wrote:



AP: Power grid change may disrupt clocks
-
http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


Time Error Correction Elimination
-
http://www.nerc.com/page.php?cid=6|386

NERC Report - June 14
-
http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to

https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts

and follow the instructions there.

__ Information from ESET Smart Security, version of virus

signature database 5851 (20110206) __


The message was checked by ESET Smart Security.

http://www.eset.com





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Hal Murray
 I don't see how they connect grid that aren't totally in sync.

Each grid is in sync with itself.  In the US, there are several grids.  They 
aren't connected except maybe by DC lines.


-- 
These are my opinions, not necessarily my employer's.  I hate spam.




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Will Matney
We have AEP here, but it's like you said, go out in the country where
Buckeye Rual Elect. is, and you have outages all the time, and you don't
want to live there in the winter.

Clocks is not what I'm concerned over as much as certain pieces of
industrial equipment that must rotate at a certain speed, or are supposed
to. Also, if they are going to allow the frequency to get slower, any
motor, or transformer, needs more iron in it, and just a 10 Hz difference
is enough to amount to a significant increase in iron. One can easily use a
50 Hz transformer on 60 Hz, but not a 60 Hz on 50 Hz. The speed difference
in motors from 50 Hz to 60 Hz would be around 1.2%, just roughly guessing
it in my head, at 1800 RPM, and we don't know how much they intend to allow
it to vary.

Best,

Will

*** REPLY SEPARATOR  ***

On 6/24/2011 at 6:33 PM gary wrote:

It all depends where you live. I know people that get an outage a week, 
so setting clocks is a way of life.

PGE, bless their corporate hearts, is run both like a Swiss clock and 
third world nation power. If you have a fair amount of industry or malls 
nearby (i.e. customers), your power is great. Live at the edge of town, 
and things are not so good, even in Silicon Valley. Monte Sereno, Monta 
Vista (now Cupertino), etc.


On 6/24/2011 6:07 PM, Will Matney wrote:
 I predict, with all of my oracle abilities, snort, that the test won't
run
 no time until there's a law suit. Almost everyone uses battery powered
 clocks nowdays, on the wall, and most alarms are digital with xtal
 timebases. However, there are still those old foggies who still have
 motorized clocks depending on 60Hz to do their duty. If this makes them
 obsolete, I wonder if the government is prepared to buy folks
replacement
 clocks, like they provided the digital receivers for our TV's? Like I
said,
 I can see a courtroom battle as I write this.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 8:50 PM paul swed wrote:

 change you can count on
 Thanks. All those silly alarm clocks by the bed.

 On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net
wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 __ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

 The message was checked by ESET Smart Security.

 http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


__ Information from ESET Smart Security, version of virus
signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread J. Forster
The network phase varies across the country. Sometime figure out the WL of
60 Hz.

-John

=


 I use a Logitech Squeezebox radio in the bedroom. Network timed!

 I don't see how they connect grid that aren't totally in sync.

 On 6/24/2011 5:50 PM, paul swed wrote:
 change you can count on
 Thanks. All those silly alarm clocks by the bed.

 On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net
 wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread J. Forster
I'd severly doubt they'd allow anything like 10%.

Also remember that the peak flux, that determins saturation, is the
integral of I dT, so you can run a 60 Hz transformer at 50 Hz if you
reduce the input to 100 VAC instead of 120 VAC.

-John

===


 We have AEP here, but it's like you said, go out in the country where
 Buckeye Rual Elect. is, and you have outages all the time, and you don't
 want to live there in the winter.

 Clocks is not what I'm concerned over as much as certain pieces of
 industrial equipment that must rotate at a certain speed, or are supposed
 to. Also, if they are going to allow the frequency to get slower, any
 motor, or transformer, needs more iron in it, and just a 10 Hz difference
 is enough to amount to a significant increase in iron. One can easily use
 a
 50 Hz transformer on 60 Hz, but not a 60 Hz on 50 Hz. The speed difference
 in motors from 50 Hz to 60 Hz would be around 1.2%, just roughly guessing
 it in my head, at 1800 RPM, and we don't know how much they intend to
 allow
 it to vary.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 6:33 PM gary wrote:

It all depends where you live. I know people that get an outage a week,
so setting clocks is a way of life.

PGE, bless their corporate hearts, is run both like a Swiss clock and
third world nation power. If you have a fair amount of industry or malls
nearby (i.e. customers), your power is great. Live at the edge of town,
and things are not so good, even in Silicon Valley. Monte Sereno, Monta
Vista (now Cupertino), etc.


On 6/24/2011 6:07 PM, Will Matney wrote:
 I predict, with all of my oracle abilities, snort, that the test won't
 run
 no time until there's a law suit. Almost everyone uses battery powered
 clocks nowdays, on the wall, and most alarms are digital with xtal
 timebases. However, there are still those old foggies who still have
 motorized clocks depending on 60Hz to do their duty. If this makes them
 obsolete, I wonder if the government is prepared to buy folks
 replacement
 clocks, like they provided the digital receivers for our TV's? Like I
 said,
 I can see a courtroom battle as I write this.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 8:50 PM paul swed wrote:

 change you can count on
 Thanks. All those silly alarm clocks by the bed.

 On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net
 wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 __ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

 The message was checked by ESET Smart Security.

 http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


__ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Will Matney
John,

That's true, but can the secondary voltage stand to drop that much? Let's
say we have a 12 volt regulated circuit, and the design engineer used the
minimum input voltage to the regulator of 13.4 volts, or 1.4 volts over the
regulated value needed (I've seen this done). Dropping the line from say
120 Vac to 100 Vac would drop the secondary DC down to around 11.2 to 11.4
Vdc, well under the minimum supply voltage of 13.4 Vdc, and under the
regulated value. When you get into plate transformers, with high winding
ratios, the voltage drop gets a good bit different. However, I should have
said, one should never run a 60 Hz transformer, or motor, on the same line
voltage it was rated for at a lower 50 Hz.

Best,

Will

*** REPLY SEPARATOR  ***

On 6/24/2011 at 7:03 PM J. Forster wrote:

I'd severly doubt they'd allow anything like 10%.

Also remember that the peak flux, that determins saturation, is the
integral of I dT, so you can run a 60 Hz transformer at 50 Hz if you
reduce the input to 100 VAC instead of 120 VAC.

-John

===


 We have AEP here, but it's like you said, go out in the country where
 Buckeye Rual Elect. is, and you have outages all the time, and you don't
 want to live there in the winter.

 Clocks is not what I'm concerned over as much as certain pieces of
 industrial equipment that must rotate at a certain speed, or are
supposed
 to. Also, if they are going to allow the frequency to get slower, any
 motor, or transformer, needs more iron in it, and just a 10 Hz
difference
 is enough to amount to a significant increase in iron. One can easily
use
 a
 50 Hz transformer on 60 Hz, but not a 60 Hz on 50 Hz. The speed
difference
 in motors from 50 Hz to 60 Hz would be around 1.2%, just roughly
guessing
 it in my head, at 1800 RPM, and we don't know how much they intend to
 allow
 it to vary.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 6:33 PM gary wrote:

It all depends where you live. I know people that get an outage a week,
so setting clocks is a way of life.

PGE, bless their corporate hearts, is run both like a Swiss clock and
third world nation power. If you have a fair amount of industry or malls
nearby (i.e. customers), your power is great. Live at the edge of town,
and things are not so good, even in Silicon Valley. Monte Sereno, Monta
Vista (now Cupertino), etc.


On 6/24/2011 6:07 PM, Will Matney wrote:
 I predict, with all of my oracle abilities, snort, that the test won't
 run
 no time until there's a law suit. Almost everyone uses battery powered
 clocks nowdays, on the wall, and most alarms are digital with xtal
 timebases. However, there are still those old foggies who still have
 motorized clocks depending on 60Hz to do their duty. If this makes
them
 obsolete, I wonder if the government is prepared to buy folks
 replacement
 clocks, like they provided the digital receivers for our TV's? Like I
 said,
 I can see a courtroom battle as I write this.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 8:50 PM paul swed wrote:

 change you can count on
 Thanks. All those silly alarm clocks by the bed.

 On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net
 wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 __ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

 The message was checked by ESET Smart Security.

 http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


__ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





__ Information from ESET Smart Security, version of virus
signature database 5851 (20110206) __

The message was checked 

Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread J. Forster
Line voltage variations is why reglated power supplies were invented.

The point is that a small frequency change is not going to blow transformers.

-John

===


 John,

 That's true, but can the secondary voltage stand to drop that much? Let's
 say we have a 12 volt regulated circuit, and the design engineer used the
 minimum input voltage to the regulator of 13.4 volts, or 1.4 volts over
 the
 regulated value needed (I've seen this done). Dropping the line from say
 120 Vac to 100 Vac would drop the secondary DC down to around 11.2 to 11.4
 Vdc, well under the minimum supply voltage of 13.4 Vdc, and under the
 regulated value. When you get into plate transformers, with high winding
 ratios, the voltage drop gets a good bit different. However, I should have
 said, one should never run a 60 Hz transformer, or motor, on the same line
 voltage it was rated for at a lower 50 Hz.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 7:03 PM J. Forster wrote:

I'd severly doubt they'd allow anything like 10%.

Also remember that the peak flux, that determins saturation, is the
integral of I dT, so you can run a 60 Hz transformer at 50 Hz if you
reduce the input to 100 VAC instead of 120 VAC.

-John

===


 We have AEP here, but it's like you said, go out in the country where
 Buckeye Rual Elect. is, and you have outages all the time, and you
 don't
 want to live there in the winter.

 Clocks is not what I'm concerned over as much as certain pieces of
 industrial equipment that must rotate at a certain speed, or are
 supposed
 to. Also, if they are going to allow the frequency to get slower, any
 motor, or transformer, needs more iron in it, and just a 10 Hz
 difference
 is enough to amount to a significant increase in iron. One can easily
 use
 a
 50 Hz transformer on 60 Hz, but not a 60 Hz on 50 Hz. The speed
 difference
 in motors from 50 Hz to 60 Hz would be around 1.2%, just roughly
 guessing
 it in my head, at 1800 RPM, and we don't know how much they intend to
 allow
 it to vary.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 6:33 PM gary wrote:

It all depends where you live. I know people that get an outage a week,
so setting clocks is a way of life.

PGE, bless their corporate hearts, is run both like a Swiss clock and
third world nation power. If you have a fair amount of industry or
 malls
nearby (i.e. customers), your power is great. Live at the edge of town,
and things are not so good, even in Silicon Valley. Monte Sereno, Monta
Vista (now Cupertino), etc.


On 6/24/2011 6:07 PM, Will Matney wrote:
 I predict, with all of my oracle abilities, snort, that the test
 won't
 run
 no time until there's a law suit. Almost everyone uses battery
 powered
 clocks nowdays, on the wall, and most alarms are digital with xtal
 timebases. However, there are still those old foggies who still have
 motorized clocks depending on 60Hz to do their duty. If this makes
 them
 obsolete, I wonder if the government is prepared to buy folks
 replacement
 clocks, like they provided the digital receivers for our TV's? Like I
 said,
 I can see a courtroom battle as I write this.

 Best,

 Will

 *** REPLY SEPARATOR  ***

 On 6/24/2011 at 8:50 PM paul swed wrote:

 change you can count on
 Thanks. All those silly alarm clocks by the bed.

 On Fri, Jun 24, 2011 at 7:02 PM, Bob Kupiecbobkup...@comcast.net
 wrote:


 AP: Power grid change may disrupt clocks
 -
 http://news.yahoo.com/s/ap/20110624/ap_on_hi_te/us_sci_power_clocks


 Time Error Correction Elimination
 -
 http://www.nerc.com/page.php?cid=6|386

 NERC Report - June 14
 -
 http://www.nerc.com/files/NERC_TEC_Field_Trial_Webinar_061411.pdf



 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.

 __ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

 The message was checked by ESET Smart Security.

 http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.


__ Information from ESET Smart Security, version of virus
 signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 

Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Will Matney
Hal,

The speed differences below are for a two and four pole motor.

Two Pole: 50 Hz: 3,000, 60 Hz: 3,600
Four Pole: 50 Hz: 1,500, 60 Hz:1,800

Those are not loaded speeds, however, 1800 / 1500 = 1.2

I mis-stated that post, it should have been 1.2 times greater than, or less
than, the speed, but it's around 17%, I think, (17% of 1800 is 306 RPM).
Thanks for catching that. I didn't see the graph, but in the case of 59.95
Hz, it wouldn't faze working motors or transformers enough to harm them, I
would think. It would motors for clocks though, over a long time span.

Thanks,

Will

*** REPLY SEPARATOR  ***

On 6/24/2011 at 7:13 PM Hal Murray wrote:

 Clocks is not what I'm concerned over as much as certain pieces of
 industrial equipment that must rotate at a certain speed, or are
supposed
 to. Also, if they are going to allow the frequency to get slower, any
motor,
 or transformer, needs more iron in it, and just a 10 Hz difference is
enough
 to amount to a significant increase in iron. One can easily use a 50 Hz
 transformer on 60 Hz, but not a 60 Hz on 50 Hz. The speed difference in
 motors from 50 Hz to 60 Hz would be around 1.2%, just roughly guessing
it in
 my head, at 1800 RPM, and we don't know how much they intend to allow it
to
 vary.

I think you are missing the decimal point.

How do you get 1.2% from 50 to 60 Hz?  I get 16%.

The graph had events under 59.95 Hz.  That's roughly 0.1%.
  http://tinyurl.com/6ytqsx7
  http://www.nerc.com/page.php?cid=6|386




-- 
These are my opinions, not necessarily my employer's.  I hate spam.




__ Information from ESET Smart Security, version of virus
signature database 5851 (20110206) __

The message was checked by ESET Smart Security.

http://www.eset.com




___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Chris Albertson
On Fri, Jun 24, 2011 at 5:59 PM, gary li...@lazygranch.com wrote:
 I use a Logitech Squeezebox radio in the bedroom. Network timed!

 I don't see how they connect grid that aren't totally in sync.

The big long distance transmission lines are high voltage DC.


-- 

Chris Albertson
Redondo Beach, California

___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


[time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Perry Sandeen

List,

Gary wrote: PGE, bless their corporate hearts, is run both like a Swiss clock 
and third world nation power. If you have a fair amount of industry or malls 
nearby (i.e. customers), your power is great. Live at the edge of town, and 
things are not so good, even in Silicon Valley. Monte Sereno, Monta Vista (now 
Cupertino), etc.

Gary,

Now with great humility I must inform you that you are just aren’t looking at 
this from the right perspective and with the proper positive Left Coast spirit!

Over thirty years ago a co-worker told me the given name to PGE by the natives 
was Pacific Graft and Extortion.  He further asserted that they used un-marked 
corporate vehicles as this reduced obscene rants from the public as well as 
reducing keying damage and other types of vandalism to the vehicles.

Now at least 30 years later their corporate modus operandi seems to remain 
unchanged.

Just think.  We now live in a world of 24/7 changes with things changing every 
day at breakneck speed so that we run full speed to stay even.

So you should appreciate that even 30 years later, you have a constant entity 
you can count on that screws you over, just like Old Faithful in Yellowstone 
Park, with precise regularity.  What other business private can make that 
claim?  

Now I haven’t done any research but I believe no other non-governmental entity 
can claim a record like that.  Even MicroSoft doesn’t come close.

Perhaps this amazing California record should be in the Guinness records 
somewhere near Grey Davis or maybe Charles Manson.

RegardsG

Perrier 


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Jim Lux

On 6/24/11 6:47 PM, Hal Murray wrote:

I don't see how they connect grid that aren't totally in sync.


Each grid is in sync with itself.  In the US, there are several grids.  They
aren't connected except maybe by DC lines.



all of the US is interconnected, except for Texas.

That said there's not much interchange across the intermountain West 
(e.g. not much power is run from the Pacific coast across Utah and 
Colorado).  This is why the Pacific coast will have less variation than 
the east coast.


As others have pointed out, power flows are done by changing the 
relative phase of the two zones.  You can either keep the power flows 
carefully net zero or you can keep the frequency the same, but not 
both. So what they do is try to have times when they don't need to flow 
power, so they can open the switch on the intertie, change the 
frequency for a while to get back to where they think they should be, 
then carefully resynchronize and reclose the switch.


There are remarkably few DC interties to help.  the big Pacific DC 
intertie is done not so much to flow power both ways (it's almost 
entirely southbound), but to make it even feasible to send power several 
thousand km.  The alternate (AC) path down through the middle of 
California is a apparently a bear to keep stable, and transients can 
take tens of hours to die out.


After all, that transmission line is starting to be a significant 
fraction of a wavelength at 60 Hz. (lambda in free space is 5000km.. 
prop velocity on a power line is quite a bit slower)


___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Jim Lux

On 6/24/11 8:20 PM, Chris Albertson wrote:

On Fri, Jun 24, 2011 at 5:59 PM, garyli...@lazygranch.com  wrote:

I use a Logitech Squeezebox radio in the bedroom. Network timed!

I don't see how they connect grid that aren't totally in sync.


The big long distance transmission lines are high voltage DC.


Most aren't. I don't recall the exact number, but less than half of the 
power flowing down the Pacific coast is carried by DC. (3-4 GW on the DC 
link..  3000A at 1 MV..yeah, baby... that's a power line)



___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread J. Forster
Mostly correct, but:

 As others have pointed out, power flows are done by changing the
 relative phase of the two zones.  You can either keep the power flows
 carefully net zero or you can keep the frequency the same, but not
 both.

When two parts of the system are interconnected, the frequency must be the
same, except very briefly when the relative phase is being changed. The
direction and size of the power flow over the link is controlled by the
differential phase.

 So what they do is try to have times when they don't need to flow
 power, so they can open the switch on the intertie, change the
 frequency for a while to get back to where they think they should be,
 then carefully resynchronize and reclose the switch.

And adjust the voltages to be equal. Bth phase and voltage have to be
equal to avoid transients.

 There are remarkably few DC interties to help.  the big Pacific DC
 intertie is done not so much to flow power both ways (it's almost
 entirely southbound), but to make it even feasible to send power several
 thousand km.  The alternate (AC) path down through the middle of
 California is a apparently a bear to keep stable, and transients can
 take tens of hours to die out.

The transients are very lightly damped, unless the generator rotors have
quadrature windings with active controls.

-John

=

 After all, that transmission line is starting to be a significant
 fraction of a wavelength at 60 Hz. (lambda in free space is 5000km..
 prop velocity on a power line is quite a bit slower)

 ___
 time-nuts mailing list -- time-nuts@febo.com
 To unsubscribe, go to
 https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
 and follow the instructions there.





___
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


Re: [time-nuts] No more 60Hz! TEC Elimination

2011-06-24 Thread Jim Lux

On 6/24/11 9:22 PM, Jim Lux wrote:

On 6/24/11 8:20 PM, Chris Albertson wrote:

On Fri, Jun 24, 2011 at 5:59 PM, garyli...@lazygranch.com wrote:

I use a Logitech Squeezebox radio in the bedroom. Network timed!

I don't see how they connect grid that aren't totally in sync.


The big long distance transmission lines are high voltage DC.


Most aren't. I don't recall the exact number, but less than half of the
power flowing down the Pacific coast is carried by DC. (3-4 GW on the DC
link.. 3000A at 1 MV..yeah, baby... that's a power line)



Just looked it up..4.8GW on AC, 3.1GW on DC.

Stabilizing the 3 AC links is quite the chore.. (my dad's PhD advisor 
was involved in this.. it was one of the very early uses of computers, 
calculating loads and sources and stabilizing the networks)


If you've ever seen that video of the huge drawn arc at a electrical 
substation during a test (the arc must be 50 feet long, at least), that 
was shot at Lugo substation, which is where the 500kV AC links terminate.



The advent of GPS timing apparently made the whole controlling the 
network much easier, because it allowed high performance measurements of 
the phase at the ends of the links, which can then factor in to controls 
on things like synchronous condensors and the throttle on power 
plants. When they started to move away from mercury pool to solid state 
thyristors, that made life even easier.  There are some enormous 
cycloconverters to do small frequency/phase changes.


I find the scale of this stuff amazing, and the level of control needed 
to keep it all working is quite impressive. Sure, keeping measurement 
systems stable to 1 part in 1E15 over 20 minutes is a challenge... but 
at least all that stuff fits in one rack.


Doing 1 degree kind of control on gigawatts of power is something I find 
really impressive.