: [AFMUG] another grounding scenario ??
Common point neutral is a good thing.
But distributed earth grounds for the true ground circuit is good too.
The main thing you want to accomplish for safety’s sake is to allow fault
currents to find the lowest impedance path to ground as possible. It is OK to
On 5/6/15 7:32 AM, Chuck McCown wrote:
Earth ground circuits are also important to allow circuit breakers to
trip as soon as a fault happens. Again, low impedance ground circuits
help with that. I would drive ground rods. But I would also make sure
that the neutral bars are floating and not bo
neutral bars
are floating and not bonded. That would prevent ground loops for the normal
power currents.
From: Paul McCall
Sent: Tuesday, May 05, 2015 7:01 PM
To: af@afmug.com
Subject: [AFMUG] another grounding scenario ??
We are doing a new tower. Here’s the layout
Customer house
The general rule is one grounding point. However, if the sub panels are
far enough apart and/or the interconnecting ground wire is too small,
you might consider adding another ground rod. I'm guessing that the
distance to your tower is far enough away from the original ground and
the interconne
The electricians that I have spoken with say bond to existing power ground
and then pound another rod right at your connection. That is what we've
always done.
On Tue, May 5, 2015 at 7:01 PM, Paul McCall wrote:
> We are doing a new tower. Here’s the layout
>
>
>
> Customer house (Building “A”
We are doing a new tower. Here's the layout
Customer house (Building "A") has a small building (Building "B" for discussion
purposes) about 150 feet away from main house. "B" has a sub-panel and 5 live
breakers for various things. There is a 6 gauge ground wire between "B" and
the Customer h