Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Paul McCall
OK, that makes sense Forrest.  That demystifies things a bit

From: Af <af-boun...@afmug.com> On Behalf Of Forrest Christian (List Account)
Sent: Tuesday, April 10, 2018 1:56 PM
To: af <af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Depends on the load and how you wire it.

For smaller sites I've been known to use a small 24VDC fan for ventilation 
which consumes less than 1A, so I switch it directly with the relay.

If you get closer to the relay rating you should use an off board relay,  and 
then you use the on board relay to control the power for the coil of the off 
board relay.   The on board relay just carries enough current to power the coil 
which isn't that much except for very large relays.

On Tue, Apr 10, 2018, 11:45 AM Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
But, is the relay switching in the Packetflux bearing any of the load at any 
point?   I would think not, but the answers are a bit confusing, as though it 
is.

I would think most basic relays could be triggered successfully with much less 
than 2A

From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of 
Forrest Christian (List Account)
Sent: Tuesday, April 10, 2018 1:44 PM
To: af <af@afmug.com<mailto:af@afmug.com>>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The relay is rated for 2A@30V, and 60W above that.

See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure 1 on 
page 3 for a visual of this.

I'd recommend that you test the relay operation with an ohm meter before trying 
a circuit.  There should be conductivity between C and NC and none between C 
and NO when the value is set to zero, and opposite  that when it's set to a one.

If it doesn't work,  upgrade the firmware to the latest and try again. There 
have been a couple of relay bugs fixed in recent memory.   Also make sure that 
the relay on above and below rows  are set to a very high and low number since 
if that is enabled it will override the relay.

On Tue, Apr 10, 2018, 11:22 AM Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yeah,  I thought this would be the case, for some reason, Packetflux support 
led my guy to realize that it didn’t work that way.

SMH

From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of Bill 
Prince
Sent: Tuesday, April 10, 2018 12:38 PM
To: Motorola III <af@afmug.com<mailto:af@afmug.com>>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The typical solution with a light-duty relay is to use it to control a heavier 
relay that carries the actual load.
-bp

--
bp
part15sbs{at}gmail{dot}com

On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yes, we know that, and have used it on lighter loads.  But, apparently there is 
a challenge on a heavier load as we described below.  Wanting to know if we can 
do what we want and maybe we just have the wrong external relay

-Original Message-
From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of 
Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
To: af@afmug.com<mailto:af@afmug.com>
Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net><mailto:pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
www.pdmnet.com<http://www.pdmnet.com><http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com><http://www.floridabroadband.com>



Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Forrest Christian (List Account)
Give me a few minutes and I'll send a drawing which might help even more.
(Need to move to a different machine)

On Tue, Apr 10, 2018, 11:52 AM Christopher Tyler <ch...@totalhighspeed.net>
wrote:

> Generally the tirgger is measured in milliamps. Your load shouldn't be
> running through it. But rather through the remote relay.
> See the attached image for a quick wiring diagram. I think I drew the
> diode backwards, I was in a hurry.
>
> --
> Christopher Tyler
> MTCRE/MTCNA/MTCTCE/MTCWE
> Total Highspeed Internet Services
> 417.851.1107
>
> - Original Message -
> From: "Paul McCall" <pa...@pdmnet.net>
> To: af@afmug.com
> Sent: Tuesday, April 10, 2018 12:45:48 PM
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> But, is the relay switching in the Packetflux bearing any of the load at
> any point?   I would think not, but the answers are a bit confusing, as
> though it is.
>
> I would think most basic relays could be triggered successfully with much
> less than 2A
>
> From: Af <af-boun...@afmug.com> On Behalf Of Forrest Christian (List
> Account)
> Sent: Tuesday, April 10, 2018 1:44 PM
> To: af <af@afmug.com>
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> The relay is rated for 2A@30V, and 60W above that.
>
> See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure
> 1 on page 3 for a visual of this.
>
> I'd recommend that you test the relay operation with an ohm meter before
> trying a circuit.  There should be conductivity between C and NC and none
> between C and NO when the value is set to zero, and opposite  that when
> it's set to a one.
>
> If it doesn't work,  upgrade the firmware to the latest and try again.
> There have been a couple of relay bugs fixed in recent memory.   Also make
> sure that the relay on above and below rows  are set to a very high and low
> number since if that is enabled it will override the relay.
>
> On Tue, Apr 10, 2018, 11:22 AM Paul McCall <pa...@pdmnet.net pa...@pdmnet.net>> wrote:
> Yeah,  I thought this would be the case, for some reason, Packetflux
> support led my guy to realize that it didn’t work that way.
>
> SMH
>
> From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of
> Bill Prince
> Sent: Tuesday, April 10, 2018 12:38 PM
> To: Motorola III <af@afmug.com<mailto:af@afmug.com>>
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> The typical solution with a light-duty relay is to use it to control a
> heavier relay that carries the actual load.
> -bp
>
> --
> bp
> part15sbs{at}gmail{dot}com
>
> On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net pa...@pdmnet.net>> wrote:
> Yes, we know that, and have used it on lighter loads.  But, apparently
> there is a challenge on a heavier load as we described below.  Wanting to
> know if we can do what we want and maybe we just have the wrong external
> relay
>
> -Original Message-
> From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of
> Christopher Tyler
> Sent: Tuesday, April 10, 2018 12:20 PM
> To: af@afmug.com<mailto:af@afmug.com>
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> Yes, there is a relay output on the siteMonitor II that you can trigger
> via SNMP or web interface.
>
> --
> Christopher Tyler
> MTCRE/MTCNA/MTCTCE/MTCWE
> Total Highspeed Internet Services
> 417.851.1107
>
> - Original Message -
> From: "Paul McCall" <pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
> To: af@afmug.com<mailto:af@afmug.com>
> Sent: Tuesday, April 10, 2018 11:11:20 AM
> Subject: [AFMUG] Sitemonitor Question with Relay
>
> My service manager seems to be struggling with using the Sitemonitor Relay
> contact to trigger a 48 Relay that we want to use to power cycle the whole
> tower if necessary.  So, Packetflux states that the Relay control is
> maximum. 30v 1amp.  So a little more than half the amps at 48v.
>
> So, in the past (lighter loads on towers) we used this to trigger an
> external relay and "open" the ground to the main power feed going up the
> tower.  At 48v, we sometimes are around 2amp on the bigger towers, some
> perhaps a bit higher still.  (with a 48v relay).
>
> We should be able to use the Sitemonitor to somehow accomplish it.
>
> Can anybody comment on this?
>
> Thanks!
>
> Paul McCall, President
> PDMNet, Inc. / Florida Broadband, Inc.
> 658 Old Dixie Highway
> Vero Beach, FL 32962
> 772-564-6800
> pa...@pdmnet.net<mailto:pa...@pdmnet.net><mailto:pa...@pdmnet.net pa...@pdmnet.net>>
> www.pdmnet.com<http://www.pdmnet.com><http://www.pdmnet.com>
> www.floridabroadband.com<http://www.floridabroadband.com><
> http://www.floridabroadband.com>
>
>


Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Forrest Christian (List Account)
Depends on the load and how you wire it.

For smaller sites I've been known to use a small 24VDC fan for ventilation
which consumes less than 1A, so I switch it directly with the relay.

If you get closer to the relay rating you should use an off board relay,
 and then you use the on board relay to control the power for the coil of
the off board relay.   The on board relay just carries enough current to
power the coil which isn't that much except for very large relays.

On Tue, Apr 10, 2018, 11:45 AM Paul McCall <pa...@pdmnet.net> wrote:

> But, is the relay switching in the Packetflux bearing any of the load at
> any point?   I would think not, but the answers are a bit confusing, as
> though it is.
>
>
>
> I would think most basic relays could be triggered successfully with much
> less than 2A
>
>
>
> *From:* Af <af-boun...@afmug.com> *On Behalf Of *Forrest Christian (List
> Account)
> *Sent:* Tuesday, April 10, 2018 1:44 PM
> *To:* af <af@afmug.com>
> *Subject:* Re: [AFMUG] Sitemonitor Question with Relay
>
>
>
> The relay is rated for 2A@30V, and 60W above that.
>
>
>
> See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure
> 1 on page 3 for a visual of this.
>
>
>
> I'd recommend that you test the relay operation with an ohm meter before
> trying a circuit.  There should be conductivity between C and NC and none
> between C and NO when the value is set to zero, and opposite  that when
> it's set to a one.
>
>
>
> If it doesn't work,  upgrade the firmware to the latest and try again.
> There have been a couple of relay bugs fixed in recent memory.   Also make
> sure that the relay on above and below rows  are set to a very high and low
> number since if that is enabled it will override the relay.
>
>
>
> On Tue, Apr 10, 2018, 11:22 AM Paul McCall <pa...@pdmnet.net> wrote:
>
> Yeah,  I thought this would be the case, for some reason, Packetflux
> support led my guy to realize that it didn’t work that way.
>
>
>
> SMH
>
>
>
> *From:* Af <af-boun...@afmug.com> *On Behalf Of *Bill Prince
> *Sent:* Tuesday, April 10, 2018 12:38 PM
> *To:* Motorola III <af@afmug.com>
> *Subject:* Re: [AFMUG] Sitemonitor Question with Relay
>
>
>
> The typical solution with a light-duty relay is to use it to control a
> heavier relay that carries the actual load.
>
> -bp
>
>
> --
>
> bp
>
> part15sbs{at}gmail{dot}com
>
>
>
> On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net> wrote:
>
> Yes, we know that, and have used it on lighter loads.  But, apparently
> there is a challenge on a heavier load as we described below.  Wanting to
> know if we can do what we want and maybe we just have the wrong external
> relay
>
>
> -Original Message-
> From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
> Sent: Tuesday, April 10, 2018 12:20 PM
> To: af@afmug.com
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> Yes, there is a relay output on the siteMonitor II that you can trigger
> via SNMP or web interface.
>
> --
> Christopher Tyler
> MTCRE/MTCNA/MTCTCE/MTCWE
> Total Highspeed Internet Services
> 417.851.1107
>
> - Original Message -
> From: "Paul McCall" <pa...@pdmnet.net>
> To: af@afmug.com
> Sent: Tuesday, April 10, 2018 11:11:20 AM
> Subject: [AFMUG] Sitemonitor Question with Relay
>
> My service manager seems to be struggling with using the Sitemonitor Relay
> contact to trigger a 48 Relay that we want to use to power cycle the whole
> tower if necessary.  So, Packetflux states that the Relay control is
> maximum. 30v 1amp.  So a little more than half the amps at 48v.
>
> So, in the past (lighter loads on towers) we used this to trigger an
> external relay and "open" the ground to the main power feed going up the
> tower.  At 48v, we sometimes are around 2amp on the bigger towers, some
> perhaps a bit higher still.  (with a 48v relay).
>
> We should be able to use the Sitemonitor to somehow accomplish it.
>
> Can anybody comment on this?
>
> Thanks!
>
> Paul McCall, President
> PDMNet, Inc. / Florida Broadband, Inc.
> 658 Old Dixie Highway
> Vero Beach, FL 32962
> 772-564-6800
> pa...@pdmnet.net<mailto:pa...@pdmnet.net>
> www.pdmnet.com<http://www.pdmnet.com>
> www.floridabroadband.com<http://www.floridabroadband.com>
>
>
>
>


Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Chuck McCown
Solid State Relays take something like 30 mA.  

From: Paul McCall 
Sent: Tuesday, April 10, 2018 11:45 AM
To: af@afmug.com 
Subject: Re: [AFMUG] Sitemonitor Question with Relay

But, is the relay switching in the Packetflux bearing any of the load at any 
point?   I would think not, but the answers are a bit confusing, as though it 
is.

 

I would think most basic relays could be triggered successfully with much less 
than 2A

 

From: Af <af-boun...@afmug.com> On Behalf Of Forrest Christian (List Account)
Sent: Tuesday, April 10, 2018 1:44 PM
To: af <af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

 

The relay is rated for 2A@30V, and 60W above that. 

 

See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure 1 on 
page 3 for a visual of this. 

 

I'd recommend that you test the relay operation with an ohm meter before trying 
a circuit.  There should be conductivity between C and NC and none between C 
and NO when the value is set to zero, and opposite  that when it's set to a 
one. 

 

If it doesn't work,  upgrade the firmware to the latest and try again. There 
have been a couple of relay bugs fixed in recent memory.   Also make sure that 
the relay on above and below rows  are set to a very high and low number since 
if that is enabled it will override the relay.

 

On Tue, Apr 10, 2018, 11:22 AM Paul McCall <pa...@pdmnet.net> wrote:

  Yeah,  I thought this would be the case, for some reason, Packetflux support 
led my guy to realize that it didn’t work that way. 

   

  SMH

   

  From: Af <af-boun...@afmug.com> On Behalf Of Bill Prince
  Sent: Tuesday, April 10, 2018 12:38 PM
  To: Motorola III <af@afmug.com>
  Subject: Re: [AFMUG] Sitemonitor Question with Relay

   

  The typical solution with a light-duty relay is to use it to control a 
heavier relay that carries the actual load.

  -bp




  --

  bp

  part15sbs{at}gmail{dot}com

   

  On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net> wrote:

Yes, we know that, and have used it on lighter loads.  But, apparently 
there is a challenge on a heavier load as we described below.  Wanting to know 
if we can do what we want and maybe we just have the wrong external relay


-Original Message-
From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
    To: af@afmug.com
    Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net>
To: af@afmug.com
    Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an 
external relay and "open" the ground to the main power feed going up the tower. 
 At 48v, we sometimes are around 2amp on the bigger towers, some perhaps a bit 
higher still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net>
www.pdmnet.com<http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com>

   


Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Christopher Tyler
Generally the tirgger is measured in milliamps. Your load shouldn't be running 
through it. But rather through the remote relay.
See the attached image for a quick wiring diagram. I think I drew the diode 
backwards, I was in a hurry.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net>
To: af@afmug.com
Sent: Tuesday, April 10, 2018 12:45:48 PM
Subject: Re: [AFMUG] Sitemonitor Question with Relay

But, is the relay switching in the Packetflux bearing any of the load at any 
point?   I would think not, but the answers are a bit confusing, as though it 
is.

I would think most basic relays could be triggered successfully with much less 
than 2A

From: Af <af-boun...@afmug.com> On Behalf Of Forrest Christian (List Account)
Sent: Tuesday, April 10, 2018 1:44 PM
To: af <af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The relay is rated for 2A@30V, and 60W above that.

See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure 1 on 
page 3 for a visual of this.

I'd recommend that you test the relay operation with an ohm meter before trying 
a circuit.  There should be conductivity between C and NC and none between C 
and NO when the value is set to zero, and opposite  that when it's set to a one.

If it doesn't work,  upgrade the firmware to the latest and try again. There 
have been a couple of relay bugs fixed in recent memory.   Also make sure that 
the relay on above and below rows  are set to a very high and low number since 
if that is enabled it will override the relay.

On Tue, Apr 10, 2018, 11:22 AM Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yeah,  I thought this would be the case, for some reason, Packetflux support 
led my guy to realize that it didn’t work that way.

SMH

From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of Bill 
Prince
Sent: Tuesday, April 10, 2018 12:38 PM
To: Motorola III <af@afmug.com<mailto:af@afmug.com>>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The typical solution with a light-duty relay is to use it to control a heavier 
relay that carries the actual load.
-bp

--
bp
part15sbs{at}gmail{dot}com

On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yes, we know that, and have used it on lighter loads.  But, apparently there is 
a challenge on a heavier load as we described below.  Wanting to know if we can 
do what we want and maybe we just have the wrong external relay

-Original Message-
From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of 
Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
To: af@afmug.com<mailto:af@afmug.com>
Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net><mailto:pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
www.pdmnet.com<http://www.pdmnet.com><http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com><http://www.floridabroadband.com>



Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Paul McCall
But, is the relay switching in the Packetflux bearing any of the load at any 
point?   I would think not, but the answers are a bit confusing, as though it 
is.

I would think most basic relays could be triggered successfully with much less 
than 2A

From: Af <af-boun...@afmug.com> On Behalf Of Forrest Christian (List Account)
Sent: Tuesday, April 10, 2018 1:44 PM
To: af <af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The relay is rated for 2A@30V, and 60W above that.

See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure 1 on 
page 3 for a visual of this.

I'd recommend that you test the relay operation with an ohm meter before trying 
a circuit.  There should be conductivity between C and NC and none between C 
and NO when the value is set to zero, and opposite  that when it's set to a one.

If it doesn't work,  upgrade the firmware to the latest and try again. There 
have been a couple of relay bugs fixed in recent memory.   Also make sure that 
the relay on above and below rows  are set to a very high and low number since 
if that is enabled it will override the relay.

On Tue, Apr 10, 2018, 11:22 AM Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yeah,  I thought this would be the case, for some reason, Packetflux support 
led my guy to realize that it didn’t work that way.

SMH

From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of Bill 
Prince
Sent: Tuesday, April 10, 2018 12:38 PM
To: Motorola III <af@afmug.com<mailto:af@afmug.com>>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The typical solution with a light-duty relay is to use it to control a heavier 
relay that carries the actual load.
-bp

--
bp
part15sbs{at}gmail{dot}com

On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yes, we know that, and have used it on lighter loads.  But, apparently there is 
a challenge on a heavier load as we described below.  Wanting to know if we can 
do what we want and maybe we just have the wrong external relay

-Original Message-
From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of 
Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
To: af@afmug.com<mailto:af@afmug.com>
Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net><mailto:pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
www.pdmnet.com<http://www.pdmnet.com><http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com><http://www.floridabroadband.com>



Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Forrest Christian (List Account)
The relay is rated for 2A@30V, and 60W above that.

See https://www.mouser.com/datasheet/2/315/mech_eng_tx-1075670.pdf figure 1
on page 3 for a visual of this.

I'd recommend that you test the relay operation with an ohm meter before
trying a circuit.  There should be conductivity between C and NC and none
between C and NO when the value is set to zero, and opposite  that when
it's set to a one.

If it doesn't work,  upgrade the firmware to the latest and try again.
There have been a couple of relay bugs fixed in recent memory.   Also make
sure that the relay on above and below rows  are set to a very high and low
number since if that is enabled it will override the relay.

On Tue, Apr 10, 2018, 11:22 AM Paul McCall <pa...@pdmnet.net> wrote:

> Yeah,  I thought this would be the case, for some reason, Packetflux
> support led my guy to realize that it didn’t work that way.
>
>
>
> SMH
>
>
>
> *From:* Af <af-boun...@afmug.com> *On Behalf Of *Bill Prince
> *Sent:* Tuesday, April 10, 2018 12:38 PM
> *To:* Motorola III <af@afmug.com>
> *Subject:* Re: [AFMUG] Sitemonitor Question with Relay
>
>
>
> The typical solution with a light-duty relay is to use it to control a
> heavier relay that carries the actual load.
>
> -bp
>
>
> --
>
> bp
>
> part15sbs{at}gmail{dot}com
>
>
>
> On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net> wrote:
>
> Yes, we know that, and have used it on lighter loads.  But, apparently
> there is a challenge on a heavier load as we described below.  Wanting to
> know if we can do what we want and maybe we just have the wrong external
> relay
>
>
> -Original Message-
> From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
> Sent: Tuesday, April 10, 2018 12:20 PM
> To: af@afmug.com
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> Yes, there is a relay output on the siteMonitor II that you can trigger
> via SNMP or web interface.
>
> --
> Christopher Tyler
> MTCRE/MTCNA/MTCTCE/MTCWE
> Total Highspeed Internet Services
> 417.851.1107
>
> - Original Message -
> From: "Paul McCall" <pa...@pdmnet.net>
> To: af@afmug.com
> Sent: Tuesday, April 10, 2018 11:11:20 AM
> Subject: [AFMUG] Sitemonitor Question with Relay
>
> My service manager seems to be struggling with using the Sitemonitor Relay
> contact to trigger a 48 Relay that we want to use to power cycle the whole
> tower if necessary.  So, Packetflux states that the Relay control is
> maximum. 30v 1amp.  So a little more than half the amps at 48v.
>
> So, in the past (lighter loads on towers) we used this to trigger an
> external relay and "open" the ground to the main power feed going up the
> tower.  At 48v, we sometimes are around 2amp on the bigger towers, some
> perhaps a bit higher still.  (with a 48v relay).
>
> We should be able to use the Sitemonitor to somehow accomplish it.
>
> Can anybody comment on this?
>
> Thanks!
>
> Paul McCall, President
> PDMNet, Inc. / Florida Broadband, Inc.
> 658 Old Dixie Highway
> Vero Beach, FL 32962
> 772-564-6800
> pa...@pdmnet.net<mailto:pa...@pdmnet.net>
> www.pdmnet.com<http://www.pdmnet.com>
> www.floridabroadband.com<http://www.floridabroadband.com>
>
>
>


Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Paul McCall
Yeah,  I thought this would be the case, for some reason, Packetflux support 
led my guy to realize that it didn’t work that way.

SMH

From: Af <af-boun...@afmug.com> On Behalf Of Bill Prince
Sent: Tuesday, April 10, 2018 12:38 PM
To: Motorola III <af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The typical solution with a light-duty relay is to use it to control a heavier 
relay that carries the actual load.
-bp

--
bp
part15sbs{at}gmail{dot}com

On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall 
<pa...@pdmnet.net<mailto:pa...@pdmnet.net>> wrote:
Yes, we know that, and have used it on lighter loads.  But, apparently there is 
a challenge on a heavier load as we described below.  Wanting to know if we can 
do what we want and maybe we just have the wrong external relay

-Original Message-
From: Af <af-boun...@afmug.com<mailto:af-boun...@afmug.com>> On Behalf Of 
Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
To: af@afmug.com<mailto:af@afmug.com>
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
To: af@afmug.com<mailto:af@afmug.com>
Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net><mailto:pa...@pdmnet.net<mailto:pa...@pdmnet.net>>
www.pdmnet.com<http://www.pdmnet.com><http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com><http://www.floridabroadband.com>




Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Chuck McCown
Or a triac if it is an AC load.  

From: Bill Prince 
Sent: Tuesday, April 10, 2018 10:38 AM
To: Motorola III 
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The typical solution with a light-duty relay is to use it to control a heavier 
relay that carries the actual load.


-bp


--

bp

part15sbs{at}gmail{dot}com


On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net> wrote:

  Yes, we know that, and have used it on lighter loads.  But, apparently there 
is a challenge on a heavier load as we described below.  Wanting to know if we 
can do what we want and maybe we just have the wrong external relay


  -Original Message-
  From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
  Sent: Tuesday, April 10, 2018 12:20 PM
  To: af@afmug.com
  Subject: Re: [AFMUG] Sitemonitor Question with Relay

  Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107

  - Original Message -
  From: "Paul McCall" <pa...@pdmnet.net>
  To: af@afmug.com
  Sent: Tuesday, April 10, 2018 11:11:20 AM
  Subject: [AFMUG] Sitemonitor Question with Relay

  My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

  So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

  We should be able to use the Sitemonitor to somehow accomplish it.

  Can anybody comment on this?

  Thanks!

  Paul McCall, President
  PDMNet, Inc. / Florida Broadband, Inc.
  658 Old Dixie Highway
  Vero Beach, FL 32962
  772-564-6800
  pa...@pdmnet.net<mailto:pa...@pdmnet.net>
  www.pdmnet.com<http://www.pdmnet.com>
  www.floridabroadband.com<http://www.floridabroadband.com>





Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Christopher Tyler
If you are using an external relay the load shouldn't matter to the SiteMonitor 
at all. The load would only matter for the extrenal relay itself. The 
SiteMonitor doesn't supply power accross the relay output so you would have to 
supply the external relays coil voltage across the site monitor contacts. You 
would only have to ensure that your coil volts and amps don't exceed the Site 
Monitor rating. And that should work just fine.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: "Bill Prince" <part15...@gmail.com>
To: "Motorola III" <af@afmug.com>
Sent: Tuesday, April 10, 2018 11:38:29 AM
Subject: Re: [AFMUG] Sitemonitor Question with Relay

The typical solution with a light-duty relay is to use it to control a
heavier relay that carries the actual load.

-bp

--
bp
part15sbs{at}gmail{dot}com

On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net> wrote:

> Yes, we know that, and have used it on lighter loads.  But, apparently
> there is a challenge on a heavier load as we described below.  Wanting to
> know if we can do what we want and maybe we just have the wrong external
> relay
>
> -Original Message-
> From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
> Sent: Tuesday, April 10, 2018 12:20 PM
> To: af@afmug.com
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> Yes, there is a relay output on the siteMonitor II that you can trigger
> via SNMP or web interface.
>
> --
> Christopher Tyler
> MTCRE/MTCNA/MTCTCE/MTCWE
> Total Highspeed Internet Services
> 417.851.1107
>
> - Original Message -
> From: "Paul McCall" <pa...@pdmnet.net>
> To: af@afmug.com
> Sent: Tuesday, April 10, 2018 11:11:20 AM
> Subject: [AFMUG] Sitemonitor Question with Relay
>
> My service manager seems to be struggling with using the Sitemonitor Relay
> contact to trigger a 48 Relay that we want to use to power cycle the whole
> tower if necessary.  So, Packetflux states that the Relay control is
> maximum. 30v 1amp.  So a little more than half the amps at 48v.
>
> So, in the past (lighter loads on towers) we used this to trigger an
> external relay and "open" the ground to the main power feed going up the
> tower.  At 48v, we sometimes are around 2amp on the bigger towers, some
> perhaps a bit higher still.  (with a 48v relay).
>
> We should be able to use the Sitemonitor to somehow accomplish it.
>
> Can anybody comment on this?
>
> Thanks!
>
> Paul McCall, President
> PDMNet, Inc. / Florida Broadband, Inc.
> 658 Old Dixie Highway
> Vero Beach, FL 32962
> 772-564-6800
> pa...@pdmnet.net<mailto:pa...@pdmnet.net>
> www.pdmnet.com<http://www.pdmnet.com>
> www.floridabroadband.com<http://www.floridabroadband.com>
>
>
>


Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Adam Moffett
Get a DIN mount DPDT, wire it so your load is on the normally closed 
contacts.  Run the control circuit on the DPDT through the normally open 
contact on the Site Monitor.


I'd bet a Google search can give you diagrams.


-- Original Message --
From: "Paul McCall" <pa...@pdmnet.net>
To: "af@afmug.com" <af@afmug.com>
Sent: 4/10/2018 12:11:21 PM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor 
Relay contact to trigger a 48 Relay that we want to use to power cycle 
the whole tower if necessary.  So, Packetflux states that the Relay 
control is maximum. 30v 1amp.  So a little more than half the amps at 
48v.




So, in the past (lighter loads on towers) we used this to trigger an 
external relay and “open” the ground to the main power feed going up 
the tower.  At 48v, we sometimes are around 2amp on the bigger towers, 
some perhaps a bit higher still.  (with a 48v relay).




We should be able to use the Sitemonitor to somehow accomplish it.



Can anybody comment on this?



Thanks!



Paul McCall, President

PDMNet, Inc. / Florida Broadband, Inc.

658 Old Dixie Highway

Vero Beach, FL 32962

772-564-6800

pa...@pdmnet.net

www.pdmnet.com

www.floridabroadband.com






Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread George Skorup
I use the temp control module for heaters and fans. Same concept. The 
external relays are 24VDC coil. Contacts rated for 125VAC/10A. The load 
is on the normally-open side. The temp module calls for heating or 
cooling and triggers the correct device. e.g. turn on the fan if TempA>30C.


You're just using the contacts on one smaller relay to control the coil 
on another larger relay. Pretty simple.


On 4/10/2018 11:24 AM, Paul McCall wrote:

Yes, we know that, and have used it on lighter loads.  But, apparently there is 
a challenge on a heavier load as we described below.  Wanting to know if we can 
do what we want and maybe we just have the wrong external relay

-Original Message-
From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
To: af@afmug.com
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.





Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Bill Prince
The typical solution with a light-duty relay is to use it to control a
heavier relay that carries the actual load.

-bp

--
bp
part15sbs{at}gmail{dot}com

On Tue, Apr 10, 2018 at 9:24 AM, Paul McCall <pa...@pdmnet.net> wrote:

> Yes, we know that, and have used it on lighter loads.  But, apparently
> there is a challenge on a heavier load as we described below.  Wanting to
> know if we can do what we want and maybe we just have the wrong external
> relay
>
> -Original Message-
> From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
> Sent: Tuesday, April 10, 2018 12:20 PM
> To: af@afmug.com
> Subject: Re: [AFMUG] Sitemonitor Question with Relay
>
> Yes, there is a relay output on the siteMonitor II that you can trigger
> via SNMP or web interface.
>
> --
> Christopher Tyler
> MTCRE/MTCNA/MTCTCE/MTCWE
> Total Highspeed Internet Services
> 417.851.1107
>
> - Original Message -
> From: "Paul McCall" <pa...@pdmnet.net>
> To: af@afmug.com
> Sent: Tuesday, April 10, 2018 11:11:20 AM
> Subject: [AFMUG] Sitemonitor Question with Relay
>
> My service manager seems to be struggling with using the Sitemonitor Relay
> contact to trigger a 48 Relay that we want to use to power cycle the whole
> tower if necessary.  So, Packetflux states that the Relay control is
> maximum. 30v 1amp.  So a little more than half the amps at 48v.
>
> So, in the past (lighter loads on towers) we used this to trigger an
> external relay and "open" the ground to the main power feed going up the
> tower.  At 48v, we sometimes are around 2amp on the bigger towers, some
> perhaps a bit higher still.  (with a 48v relay).
>
> We should be able to use the Sitemonitor to somehow accomplish it.
>
> Can anybody comment on this?
>
> Thanks!
>
> Paul McCall, President
> PDMNet, Inc. / Florida Broadband, Inc.
> 658 Old Dixie Highway
> Vero Beach, FL 32962
> 772-564-6800
> pa...@pdmnet.net<mailto:pa...@pdmnet.net>
> www.pdmnet.com<http://www.pdmnet.com>
> www.floridabroadband.com<http://www.floridabroadband.com>
>
>
>


Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Paul McCall
Yes, we know that, and have used it on lighter loads.  But, apparently there is 
a challenge on a heavier load as we described below.  Wanting to know if we can 
do what we want and maybe we just have the wrong external relay

-Original Message-
From: Af <af-boun...@afmug.com> On Behalf Of Christopher Tyler
Sent: Tuesday, April 10, 2018 12:20 PM
To: af@afmug.com
Subject: Re: [AFMUG] Sitemonitor Question with Relay

Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net>
To: af@afmug.com
Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net>
www.pdmnet.com<http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com>




Re: [AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Christopher Tyler
Yes, there is a relay output on the siteMonitor II that you can trigger via 
SNMP or web interface.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: "Paul McCall" <pa...@pdmnet.net>
To: af@afmug.com
Sent: Tuesday, April 10, 2018 11:11:20 AM
Subject: [AFMUG] Sitemonitor Question with Relay

My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net<mailto:pa...@pdmnet.net>
www.pdmnet.com<http://www.pdmnet.com>
www.floridabroadband.com<http://www.floridabroadband.com>




[AFMUG] Sitemonitor Question with Relay

2018-04-10 Thread Paul McCall
My service manager seems to be struggling with using the Sitemonitor Relay 
contact to trigger a 48 Relay that we want to use to power cycle the whole 
tower if necessary.  So, Packetflux states that the Relay control is maximum. 
30v 1amp.  So a little more than half the amps at 48v.

So, in the past (lighter loads on towers) we used this to trigger an external 
relay and "open" the ground to the main power feed going up the tower.  At 48v, 
we sometimes are around 2amp on the bigger towers, some perhaps a bit higher 
still.  (with a 48v relay).

We should be able to use the Sitemonitor to somehow accomplish it.

Can anybody comment on this?

Thanks!

Paul McCall, President
PDMNet, Inc. / Florida Broadband, Inc.
658 Old Dixie Highway
Vero Beach, FL 32962
772-564-6800
pa...@pdmnet.net
www.pdmnet.com
www.floridabroadband.com