RE: Short circuit tests in GR-1089

2002-11-26 Thread Dave Spencer
Hi All, My $.02 worth... I strongly disagree with what has been said regarding operation of output fuses. You may have a case for input fuses/circuit breakers. It is my belief that the purpose of this test, which is a cross referenced follow through to the design requirements now contained in

Re: DC Input Power Conducted Emissions

2002-11-26 Thread Ron Pickard
Bob, Clause 6.2 of EN 300386 states The artificial network to be used is the one described in CISPR 16-1 [1], clause 5: - 0,15 MHz to 30 MHz: (50 ohms // 50 µH). Also if you wish, you can download this standard for free from ETSI's website. IHTH. Best regards, Ron Pickard

RE: Ferrite clamps

2002-11-26 Thread Don_Borowski
S11 is the ratio of the reflected voltage to the forward voltage on a transmission line. It is a phasor quantity, so it has magnitude and phase. The in case of a ferrite clamp, one would put the clamp over the center conductor of a transmission line, and then short the transmission line just

RE: DC Input Power Conducted Emissions

2002-11-26 Thread ari.honkala
No. -Original Message- From: ext rehel...@mmm.com [mailto:rehel...@mmm.com] Sent: Tuesday, November 26, 2002 2:08 PM To: Ron Pickard Cc: emc-p...@majordomo.ieee.org Subject: Re: DC Input Power Conducted Emissions Does this require a different LISN other than the standard

RE: Ferrite clamps

2002-11-26 Thread reheller
What is S11? Bob Heller 3M Product Safety, 76-1-01 St. Paul, MN 55107-1208 Tel: 651- 778-6336 Fax: 651-778-6252 === Ghery, You are right. The parameters for S11 and ferrite are

Re: DC Input Power Conducted Emissions

2002-11-26 Thread reheller
Does this require a different LISN other than the standard LISN? Bob Heller 3M Product Safety, 76-1-01 St. Paul, MN 55107-1208 Tel: 651- 778-6336 Fax: 651-778-6252 ===

EMCD Dates

2002-11-26 Thread Alan E Hutley
Hi All Re-implementation dates,below is the best information available. But it comes with a warning notice there are many variables to be sorted and it does not appear to be very high on the EU priority list. So do not be surprised if these dates slip or change. When the cost implications are

Re: ReIssue: RE: When CE doesn't pass

2002-11-26 Thread John Woodgate
I read in !emc-pstc that Scott Douglas dougl...@naradnetworks.com wrote (in 5.0.2.1.2.20021122131840.00a58...@pop.business.earthlink.net ) about 'ReIssue: RE: When CE doesn't pass' on Fri, 22 Nov 2002: An alternative to this is have your company order all the Products from their various sources

Re: Short circuit tests in GR-1089

2002-11-26 Thread Lou Aiken
I'd like to add that the product need not operate correctly after a fault condition causes a fuse to open, it must only remain safe - within the meaning of the standard. Regards, Lou Aiken, LaMer LLC 27109 Palmetto Drive Orange Beach, AL 36561 USA tel ++ 1 251 981 6786 fax ++ 1 251 981 3054

RE: EMC EH close field probes / Mindcruiser

2002-11-26 Thread neven11
Agreeing with both, I wish to add that while the probes are very useful in locating the source and are not (very) useful in predicting the absolute level of far-field emission they may be also useful to predict relative far-field difference in emission, because with all other things equal the

Position Available

2002-11-26 Thread Barbara Judge
Compliance Certification Services, a TCB, CAB, and independent test lab specializing in domestic and international Wireless regulatory compliance testing and certification, has an opening for a Sales Professional. The person we are looking for will have, at a minimum: * TWO years

Re: Ferrite clamps

2002-11-26 Thread Lfresearch
In a message dated 11/25/2002 2:48:34 PM Central Standard Time, ghery.pet...@intel.com writes: Fischer Custom Communications has developed a small clamp that meets the CISPR 22 requirements while costing significantly less money than an IEC 61000-4-6 isolation clamp. I guess time to

Re: ReIssue: RE: When CE doesn't pass

2002-11-26 Thread Scott Douglas
Brian, Is there any way to replace the offending Product D with another vendor? If so, do it. If not, can you configure the system without Product D? If so, do it. If not, buy one Product D for your use in configuring complete systems. Then have your customer buy your system less Product D