Dear Pete,
Unfortunately the IEC 62368-1 language does not conform the to surge protection terms established by the IEC surge protection subcommittees SC 37A (Low-voltage surge protective devices) and SC 37B (Components for low-voltage surge protection). Notice one subcommittee deals with Devices and the other Components. What's the difference?

component: constituent part of a device which cannot be physically divided into smaller parts without losing its particular function
(IEV 151-11-21)
device: material element or assembly of such elements intended to perform a required function
(IEV 151-11-20)

I'm not in love with the device definition as there is nothing about components used in creating the device. TC 77 did a better job with

device: combination of components having a given function, forming part of a piece of equipment, apparatus, or system
IEC 61000-5-6, ed. 1.0 (2002-06)

Turning to SC 37A (Devices) the generic surge protective device definition is

surge protective device, SPD: device that restricts the voltage of a designated port or ports, caused by a surge, when it exceeds a predetermined level NOTE 1 Secondary functions may be incorporated, such as a current-limiting to restrict a terminal current. NOTE 2 Typically the protective circuit has at least one non-linear voltage-limiting surge protective component. NOTE 3 An SPD is a complete assembly, having terminals to connect to the circuit conductors.

For those SC 37A working groups purely concerned with AC and DC power protection the definition becomes

surge protective device, SPD: device that contains at least one nonlinear component that is intended to limit surge voltages and divert surge currents
NOTE An SPD is a complete assembly, having appropriate connecting means.

In both cases a surge protective device contains a surge protective component or components that give the surge protective device its surge protective function.

SC 37B (Components) are laggardly and have yet to produce a surge protective component definition. For that we must look to the ITU-T and IEEE.

surge protective component (SPC): component specifically included in a device or equipment for the mitigation of the onward propagation of overvoltages or overcurrents or both. ITU-T Recommendation K.96: Surge protective components: Overview of surge mitigation functions and technologies

surge-protective component (SPC): Component specifically included in a device or equipment for the mitigation of the onward propagation of overvoltages or overcurrents or both. C62.42.0 IEEE Guide for the Application of Surge-Protective Components in Surge-Protective Devices and Equipment Ports—Overview

Thus clear-thinking surge protection people get confused when IEC 62368-1 uses surge protective device when what is really meant is a surge protective component (e.g. gas discharge tubes, metal-oxide varistors, Zener diodes, avalanche diodes, punch-through diodes and positive temperature coefficient thermistors). The correction is obvious — replace "device" with "component".

Regards,

Mick Maytum

Safety and Telecom
Standards

mjmay...@gmail.com

https://ictsp-essays.info/


------ Original Message ------
From: "Pete Perkins" <00000061f3f32d0c-dmarc-requ...@ieee.org>
To: EMC-PSTC@listserv.ieee.org
Sent: 02/11/2017 06:04:38
Subject: Re: [PSES] Regulatory requirements for MOVs - 62368 side issues

Ralph, et al,

IEC 62368-1, the Hazard Based Standard, is developed in a way that it is intended to provide more complete coverage of the hazards encountered from electrical equipment in its scope and provide more options for manufacturers in meeting those requirements (albeit this will require looking at the details more to take advantage of some of the benefits). In 62368 MOVs are part of the class of Surge Protector Devices (SPDs) for which requirements are covered in some detail as discussed in this thread.

IN 62368 there are three levels of users for which differing protection is provided; they are ) ordinary person, an everyday user, perhaps your 8 yr old daughter, ) instructed person = person instructed or supervised by a skilled person as to energy sources and who can responsibly use equipment safeguards and precautionary safeguards with respect those energy sources, and ) skilled person = person with relevant education or experience to enable them to identify hazards and to take appropriate actions to reduce the risks of injury to themselves and others.
        This differentiation seems reasonable based upon my experience.
Perhaps for TV repair you are not skilled but might be instructed; on the other hand perhaps you are neither. Where do you fit yourself on this scale?

:>)     br,      Pete

Peter E Perkins, PE
Principal Product Safety & Regulatory Affairs Consultant
PO Box 23427
Tigard, ORe  97281-3427

503/452-1201

p.perk...@ieee.org



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc discussion 
list. To post a message to the list, send your e-mail to <emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>