I read
I read in !emc-pstc that Kevin Richardson kevin.richard...@ieee.org
wrote (in nebbihdflagbliikmlbkgeabdnaa.kevin.richard...@ieee.org)
about 'Surge Protection EN 60439-1' on Tue, 3 Dec 2002:
Can anyone please advise if EN 60439-1 allows the practice of placing a
surge protection device (eg an MOV
Can anyone please advise if EN 60439-1 allows the practice of placing a
surge protection device (eg an MOV) across the mains input (active to earth)
is accepted.
The MOV would probably be set at something like 420 vAC or RMS so probably
about 600 peak.
The equipment is a professional lighting
Dichirico
Sent: Friday, January 12, 2001 3:33 PM
To: IEEE EMC List; Mike Cantwell
Subject: Re: EN 60439-1 ???
Hi Mike!
EN 60439-1 applies to to low-voltage (up to 1000 VAC and 1500 VDC)
switchgear and controlgear assemblies.
Coming to diesel-generator sets, IMO it applies to all
Hi Mike!
EN 60439-1 applies to to low-voltage (up to 1000 VAC and 1500 VDC) switchgear
and controlgear assemblies.
Coming to diesel-generator sets, IMO it applies to all the assemblies
(cabinets) that contain switching devices (circuit-breakers,
switch-disconnectors, fuses, etc
To: emc-pstc (E-mail)
emc-p...@majordomo.ieee.org
onics.com cc:
Sent by:Subject: EN 60439-1
All,
EN 60439-1 is titled Low-voltage switchgear and control gear asemblies -
Part 1: Type-tested and partially type-tested assemblies and is listed as a
harmonized standard under the EMC Directive.
Does any one know the scope of this standard ???
If you know the scope, does it apply