> Hi Barry,
>
> First question about the extension cord.  An extension cord is considered 
> a
> temporary installation.  A power strip is not an extension cord.  We have
> power strips we offer in our rack systems, and also have MicroPODs which 
> are
> distribution with bypass options.  If someone asks us about additional
> surge, we suggest it goes before the UPS.  Surge strips are less expensive
> than the UPS and generally have better surge protection.
>
> The UPS is tested to UL-1778 standard.  This requires some surge 
> protection,
> but not as much as you get from a quality surge strip.  This is why the
> surge strip would come first.  The concern with putting a power strip on 
> the
> output of a UPS is that many outlets are now available.  If someone plugs 
> a
> device into the strip that overloads it, then the UPS could shut down.  
> This
> would be like a cleaning crew plugging in a floor cleaner.
>
> I do not understand the statement, either, by Tripplite about the UPS 
> output
> causing the surge to "short-circuit the UPS"
>
> There are two basic types of UPS: (1) off-line and (2) on-line.  The off
> line models can also be line-interactive models with buck-and-boost modes,
> but they are in the off-line type.
>
> (1) The off-line UPS basically lets utility power pass through it (through
> filtering and surge protection) and has to switch on the UPS electronics 
> to
> go to battery mode.  There is a relay that has to change state to change 
> to
> battery mode.  This is a fast transfer time (~6 mSec), but there is the
> break.  I have not ever experienced a transient due to this transfer.  
> Since
> this type lets utility power pass through, the output voltage and 
> frequency
> will vary as the utility power fluctuates until the UPS goes to battery
> mode.
>
> (2) The on-line UPS goes through a double-conversion process.  The 
> incoming
> utility AC power is rectified to DC, then the UPS inverter circuit is 
> always
> generating the output power.  Because of this double conversion the output
> power is a steady voltage and frequency.  When changing to or from battery
> mode there is no interruption of output power.
>
> I hope I have answered your questions, but if you have any more please let
> us know.
> Thank you,
> John Ufferman, Liebert Corporation
> Hardware Applications Engineer
> upst...@liebert.com
> 1-800-222-5877, opt.3, opt.2.
>



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               emc_p...@symbol.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to