Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
See below. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2018-03-13 19:57, John Woodgate wrote: I suspect that the SELV circuits of an electricity meter never leave the enclosure, so SELV is OK, but PELV would still be equally safe or better, even if a very low probability open-circuit earth occurred. John Woodgate OOO-Own Opinions Only J M Woodgate and Associateswww.woodjohn.uk Rayleigh, Essex UK On 2018-03-13 19:17, Ted Eckert wrote: Part of the reason why two levels of protection are required is because of what happens if one level fails. If the protective earth bonding connection fails, and the exposed metal is no longer earthed, the product will typically continue to operate normally. There is no indication to the user that a failure has occurred. If a second failure occurs that bridges the insulation gap between hazardous voltage and that exposed metal, the chassis will become energized. The user may still have no obvious indication of a failure until they contact that energized chassis. Different standards committees have different ways of addressing this issue. TC 108 generally requires that the protective earth bonding be designed and tested in such a way to prove that it is robust enough. In many ITE products, the user accessible circuits are earth ground references, so providing basic insulation between SELV and earth ground is not possible. Other standards committees may have chosen other methods of protection based on the products they cover. TC 13 may have decided that basic insulation between SELV and earthed parts may be the best way to provide protection in their products. In this case, if the earth bonding fails, the basic insulation may be need to reduce the risk or arcing between hazardous voltage and the exposed metal. Ted Eckert Microsoft Corporation The opinions expressed are my own and do not necessarily reflect those of my employer, TC 13 or TC 108. *From:* Scott Aldous <0220f70c299a-dmarc-requ...@ieee.org <mailto:0220f70c299a-dmarc-requ...@ieee.org>> *Sent:* Tuesday, March 13, 2018 8:57 AM *To:* EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> *Subject:* Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 Hi Vyas, I'm not familiar with this standard, but the general principle is that 2 levels of protection are required to protect operators from hazards. In the case of the "protective earthed accessible part", I imagine the standard assumes that a single fault could compromise the protective earthing, so Basic or Supplementary Insulation is also required between such a circuit and SELV. In the same vein, the table requires Double or Reinforced Insulation between an "unearthed accessible part" and SELV. On Tue, Mar 13, 2018 at 5:56 AM, Balmukund Vyas <balmukund.v...@ymllabs.com <mailto:balmukund.v...@ymllabs.com>> wrote: Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org <mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org>> Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com>> - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http:/
Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
Thanks for your comments. The definitions of SEL and PELV in IEC 62052-31 are as below. Do you find it different? Regards B M Vyas SELV system An electrical system in which the voltage cannot exceed ELV: · under normal conditions; and · under single-fault conditions, including earth faults in other circuits [IEC 61140 3.26.1] 1.1 PELV system an electrical system in which the voltage cannot exceed ELV: · under normal conditions, and · under single-fault conditions, except earth faults in other circuits [IEC 61140 3.26.1] From: John Woodgate [mailto:j...@woodjohn.uk] Sent: 14 March 2018 00:58 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 I agree: SELV as a low-voltage earth-free supply is not actually a safe concept. It's OK for short connections in the same space, because the probability of 'power cross' is extremely remote. But if SELV is extended into several spaces, including, for example, a void, the chance of power-cross is larger and it will remain undetected until someone touches both the SELV and earth. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk<http://www.woodjohn.uk> Rayleigh, Essex UK On 2018-03-13 19:13, Richard Nute wrote: Dear Mr. Vyas: I suggest you review the definitions for SELV and PELV in IEC 62052. These definitions are not the same throughout IEC standards. (I don’t have IEC 62052.) In some standards, SELV is isolated from protective earth, and PELV is connected to protective earth. If these are the definitions in IEC 62052, then SELV must be isolated from earth by Basic Insulation. (I have never understood why we have both SELV and PELV as only the voltage and the isolation are the essential parameters for protection against electric shock.) In other standards, SELV is determined by the voltage and the isolation from higher voltages; earthing (or not) of SELV does not enter into this determination. Good luck and best regards, Rich From: Balmukund Vyas <balmukund.v...@ymllabs.com><mailto:balmukund.v...@ymllabs.com> Sent: Tuesday, March 13, 2018 5:56 AM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Subject: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas Table 20 – Insulation requirements between circuits and between circuits and accessible parts HLV mains-circuit1) ELV circuit SELV circuit PELV circuit PEB circuit2) Protective earthed HLV non-mains-circuit2), 3) Unearthed HLV non-mains circuit3) HLV mains-circuit 1) F/B1) 6) Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B5) Table 8Table 9 B Table 8Table 9 B Table 8Table 9 ELV circuit B Table 8Table 9 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 SELV circuit D Table 8Table 9 B Table 13Table 14 F/B6) Table 13Table 14 F/B8) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PELV circuit2) D Table 8Table 9 B Table 13Table 14 F/B8) Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PEB circuit2) B5) Table 8Table 9 F/B5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B5) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Protective earthed HLV non-mains circuit2), 3) B Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B Table 8Table 9 F/B6) Table 8Table 9 B Table 8Table 9 Unearthed HLV non-mains circuit3) B Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 Protective earthed accessible part2), 7) B Table 8Table 9 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Unearthed accessible part7) D Table 8Table 9 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 B/D 4) Table 13Table 14 Abbreviations for insulations: B: Basic insulation or supplementary insulation D: double insulation or reinforced insulation F: Functional insulation S: Supplementary insulation 1)If the functional voltage (not relative to earth/ground) is greater than the
Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
I suspect that the SELV circuits of an electricity meter never leave the enclosure, so SELV is OK, but PELV would still be equally safe or better, even if a very low probability open-circuit earth occurred. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2018-03-13 19:17, Ted Eckert wrote: Part of the reason why two levels of protection are required is because of what happens if one level fails. If the protective earth bonding connection fails, and the exposed metal is no longer earthed, the product will typically continue to operate normally. There is no indication to the user that a failure has occurred. If a second failure occurs that bridges the insulation gap between hazardous voltage and that exposed metal, the chassis will become energized. The user may still have no obvious indication of a failure until they contact that energized chassis. Different standards committees have different ways of addressing this issue. TC 108 generally requires that the protective earth bonding be designed and tested in such a way to prove that it is robust enough. In many ITE products, the user accessible circuits are earth ground references, so providing basic insulation between SELV and earth ground is not possible. Other standards committees may have chosen other methods of protection based on the products they cover. TC 13 may have decided that basic insulation between SELV and earthed parts may be the best way to provide protection in their products. In this case, if the earth bonding fails, the basic insulation may be need to reduce the risk or arcing between hazardous voltage and the exposed metal. Ted Eckert Microsoft Corporation The opinions expressed are my own and do not necessarily reflect those of my employer, TC 13 or TC 108. *From:* Scott Aldous <0220f70c299a-dmarc-requ...@ieee.org <mailto:0220f70c299a-dmarc-requ...@ieee.org>> *Sent:* Tuesday, March 13, 2018 8:57 AM *To:* EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> *Subject:* Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 Hi Vyas, I'm not familiar with this standard, but the general principle is that 2 levels of protection are required to protect operators from hazards. In the case of the "protective earthed accessible part", I imagine the standard assumes that a single fault could compromise the protective earthing, so Basic or Supplementary Insulation is also required between such a circuit and SELV. In the same vein, the table requires Double or Reinforced Insulation between an "unearthed accessible part" and SELV. On Tue, Mar 13, 2018 at 5:56 AM, Balmukund Vyas <balmukund.v...@ymllabs.com <mailto:balmukund.v...@ymllabs.com>> wrote: Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org <mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org <mailto:sdoug...@ieee.org>> Mike Cantwell <mcantw...@ieee.org <mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org <mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com <mailto:dhe...@gmail.com>> - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.
Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
Part of the reason why two levels of protection are required is because of what happens if one level fails. If the protective earth bonding connection fails, and the exposed metal is no longer earthed, the product will typically continue to operate normally. There is no indication to the user that a failure has occurred. If a second failure occurs that bridges the insulation gap between hazardous voltage and that exposed metal, the chassis will become energized. The user may still have no obvious indication of a failure until they contact that energized chassis. Different standards committees have different ways of addressing this issue. TC 108 generally requires that the protective earth bonding be designed and tested in such a way to prove that it is robust enough. In many ITE products, the user accessible circuits are earth ground references, so providing basic insulation between SELV and earth ground is not possible. Other standards committees may have chosen other methods of protection based on the products they cover. TC 13 may have decided that basic insulation between SELV and earthed parts may be the best way to provide protection in their products. In this case, if the earth bonding fails, the basic insulation may be need to reduce the risk or arcing between hazardous voltage and the exposed metal. Ted Eckert Microsoft Corporation The opinions expressed are my own and do not necessarily reflect those of my employer, TC 13 or TC 108. From: Scott Aldous <0220f70c299a-dmarc-requ...@ieee.org<mailto:0220f70c299a-dmarc-requ...@ieee.org>> Sent: Tuesday, March 13, 2018 8:57 AM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Subject: Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 Hi Vyas, I'm not familiar with this standard, but the general principle is that 2 levels of protection are required to protect operators from hazards. In the case of the "protective earthed accessible part", I imagine the standard assumes that a single fault could compromise the protective earthing, so Basic or Supplementary Insulation is also required between such a circuit and SELV. In the same vein, the table requires Double or Reinforced Insulation between an "unearthed accessible part" and SELV. On Tue, Mar 13, 2018 at 5:56 AM, Balmukund Vyas <balmukund.v...@ymllabs.com<mailto:balmukund.v...@ymllabs.com>> wrote: Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas <sdoug...@ieee.org> Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com>
Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
I agree: SELV as a low-voltage earth-free supply is not actually a safe concept. It's OK for short connections in the same space, because the probability of 'power cross' is extremely remote. But if SELV is extended into several spaces, including, for example, a void, the chance of power-cross is larger and it will remain *undetected* until someone touches both the SELV and earth. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2018-03-13 19:13, Richard Nute wrote: Dear Mr. Vyas: I suggest you review the definitions for SELV and PELV in IEC 62052. These definitions are not the same throughout IEC standards. (I don’t have IEC 62052.) In some standards, SELV is isolated from protective earth, and PELV is connected to protective earth. If these are the definitions in IEC 62052, then SELV must be isolated from earth by Basic Insulation. (I have never understood why we have both SELV and PELV as only the voltage and the isolation are the essential parameters for protection against electric shock.) In other standards, SELV is determined by the voltage and the isolation from higher voltages; earthing (or not) of SELV does not enter into this determination. Good luck and best regards, Rich *From:* Balmukund Vyas <balmukund.v...@ymllabs.com> *Sent:* Tuesday, March 13, 2018 5:56 AM *To:* EMC-PSTC@LISTSERV.IEEE.ORG *Subject:* [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas Table 20 – Insulation requirements between circuits and between circuits and accessible parts HLV mains-circuit^1) ELV circuit SELV circuit PELV circuit PEB circuit^2) Protective earthed HLV non-mains-circuit^2), 3) Unearthed HLV non-mains circuit^3) HLV mains-circuit ^1) F/B^1) 6) Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B^5) Table 8Table 9 B Table 8Table 9 B Table 8Table 9 ELV circuit B Table 8Table 9 F/B^6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B^5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 SELV circuit D Table 8Table 9 B Table 13Table 14 F/B^6) Table 13Table 14 F/B^8) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PELV circuit^2) D Table 8Table 9 B Table 13Table 14 F/B^8) Table 13Table 14 F/B^6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PEB circuit^2) B^5) Table 8Table 9 F/B^5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B^5) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Protective earthed HLV non-mains circuit^2), 3) B Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B Table 8Table 9 F/B^6) Table 8Table 9 B Table 8Table 9 Unearthed HLV non-mains circuit^3) B Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B^6) Table 13Table 14 Protective earthed accessible part^2), 7) B Table 8Table 9 F/B^6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B^6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Unearthed accessible part^7) D Table 8Table 9 B Table 13Table 14 B Table 13Table 14 F/B^6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 B/D ^4) Table 13Table 14 Abbreviations for insulations: B: Basic insulation or supplementary insulation D: double insulation or reinforced insulation F: Functional insulation S: Supplementary insulation 1)If the functional voltage (not relative to earth/ground) is greater than the rated insulation voltage, the creepage distance for the functional insulation may be greater than that for the basic insulation. An example is a terminal block of a three-phase metering equipment with /U/_n = 230/400 V,
Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
Dear Mr. Vyas: I suggest you review the definitions for SELV and PELV in IEC 62052. These definitions are not the same throughout IEC standards. (I don’t have IEC 62052.) In some standards, SELV is isolated from protective earth, and PELV is connected to protective earth. If these are the definitions in IEC 62052, then SELV must be isolated from earth by Basic Insulation. (I have never understood why we have both SELV and PELV as only the voltage and the isolation are the essential parameters for protection against electric shock.) In other standards, SELV is determined by the voltage and the isolation from higher voltages; earthing (or not) of SELV does not enter into this determination. Good luck and best regards, Rich From: Balmukund Vyas <balmukund.v...@ymllabs.com> Sent: Tuesday, March 13, 2018 5:56 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31 Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas Table 20 – Insulation requirements between circuits and between circuits and accessible parts HLV mains-circuit1) ELV circuit SELV circuit PELV circuit PEB circuit2) Protective earthed HLV non-mains-circuit2), 3) Unearthed HLV non-mains circuit3) HLV mains-circuit 1) F/B1) 6) Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B5) Table 8Table 9 B Table 8Table 9 B Table 8Table 9 ELV circuit B Table 8Table 9 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 SELV circuit D Table 8Table 9 B Table 13Table 14 F/B6) Table 13Table 14 F/B8) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PELV circuit2) D Table 8Table 9 B Table 13Table 14 F/B8) Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PEB circuit2) B5) Table 8Table 9 F/B5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B5) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Protective earthed HLV non-mains circuit2), 3) B Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B Table 8Table 9 F/B6) Table 8Table 9 B Table 8Table 9 Unearthed HLV non-mains circuit3) B Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 Protective earthed accessible part2), 7) B Table 8Table 9 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Unearthed accessible part7) D Table 8Table 9 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 B/D 4) Table 13Table 14 Abbreviations for insulations: B: Basic insulation or supplementary insulation D: double insulation or reinforced insulation F: Functional insulation S: Supplementary insulation 1)If the functional voltage (not relative to earth/ground) is greater than the rated insulation voltage, the creepage distance for the functional insulation may be greater than that for the basic insulation. An example is a terminal block of a three-phase metering equipment with Un = 230/400 V, where the functional phase-to-phase voltage is 400 V r.m.s. For an indoor meter with material group III, the creepage distance for basic insulation from Table 9 is 3,2 mm, but the creepage distance for functional insulationfrom Table 14 is 4,0 mm. 2)Connections to the protective conductor shall comply with 6.5.2.4. Otherwise, this shall be considered to be an unearthed circuit. 3)There shall be at least basic insulation between HLV non-mains circuits and HLV mains circuits. 4)Insulation between an unearthed non-mains circuit at hazardous voltage and an unearthed accessible conductive part shall satisfy the more onerous of the following: - double/reinforced insulation, the working voltage of which is equal to the hazardous voltage; or - supplementary insulation, the working voltage of which is equal to the voltage between the non-mains circuit athazardous voltage; and * another non-mains circuit at hazardous voltage; or * a mains circuit. 5)See Annex Bfor the conditional use of basic insulation for PEB. 6)Supplementary or basic insulation shall be used if one of the circuits is an independent circuit or is ad
Re: [PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
Hi Vyas, I'm not familiar with this standard, but the general principle is that 2 levels of protection are required to protect operators from hazards. In the case of the "protective earthed accessible part", I imagine the standard assumes that a single fault could compromise the protective earthing, so Basic or Supplementary Insulation is also required between such a circuit and SELV. In the same vein, the table requires Double or Reinforced Insulation between an "unearthed accessible part" and SELV. On Tue, Mar 13, 2018 at 5:56 AM, Balmukund Vyaswrote: > > > > > Dear All, > > IEC 62052-31 is standard for product safety requirements for electricity > metering equipment. It has a table 20 (given below) which details out > insulation requirements between various types of circuits. > > My question is, why Basic insulation is required between SELV circuit and > protective earthed accessible parts? Isn’t a functional insulation is > sufficient for this? > > > > Thanks > > > > B M Vyas > > > > Table 20 – Insulation requirements between circuits and between circuits > and accessible parts > > > > HLV > mains-circuit1) > > ELV circuit > > SELV circuit > > PELV circuit > > PEB circuit2) > > Protective earthed HLV non-mains-circuit2), 3) > > Unearthed HLV non-mains circuit3) > > HLV mains-circuit 1) > > F/B1) 6) > > Table 8Table 9 > > B > > Table 8Table 9 > > D > > Table 8Table 9 > > D > > Table 8Table 9 > > B5) > > Table 8Table 9 > > B > > Table 8Table 9 > > B > > Table 8Table 9 > > ELV circuit > > B > > Table 8Table 9 > > F/B6) > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > F/B5), 6) > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > SELV circuit > > D > > Table 8Table 9 > > B > > Table 13Table 14 > > F/B6) > > Table 13Table 14 > > F/B8) > > Table 13Table 14 > > B > > Table 13Table 14 > > D > > Table 13Table 14 > > D > > Table 13Table 14 > > PELV circuit2) > > D > > Table 8Table 9 > > B > > Table 13Table 14 > > F/B8) > > Table 13Table 14 > > F/B6) > > Table 13Table 14 > > B > > Table 13Table 14 > > D > > Table 13Table 14 > > D > > Table 13Table 14 > > PEB circuit2) > > B5) > > Table 8Table 9 > > F/B5), 6) > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > F/B5) > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > Protective earthed HLV non-mains circuit2), 3) > > B > > Table 8Table 9 > > B > > Table 8Table 9 > > D > > Table 8Table 9 > > D > > Table 8Table 9 > > B > > Table 8Table 9 > > F/B6) > > Table 8Table 9 > > B > > Table 8Table 9 > > Unearthed HLV non-mains circuit3) > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > D > > Table 13Table 14 > > D > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > F/B6) > > Table 13Table 14 > > Protective earthed accessible part2), 7) > > B > > Table 8Table 9 > > F/B6) > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > F/B6) > > Table 13Table 14 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > Unearthed accessible part7) > > D > > Table 8Table 9 > > B > > Table 13Table 14 > > B > > Table 13Table 14 > > F/B6) > > Table 13Table 14 > > B > > Table 13Table 14 > > D > > Table 13Table 14 > > B/D 4) > > Table 13Table 14 > > Abbreviations for insulations: > > B: Basic insulation or supplementary insulation > > D: double insulation or reinforced insulation > > F: Functional insulation > > S: Supplementary insulation > > 1)If the functional voltage (not relative to earth/ground) is > greater than the rated insulation voltage, the creepage distance for the > functional insulation may be greater than that for the basic insulation. An > example is a terminal block of a three-phase metering equipment with *U*n > = 230/400 V, where the functional phase-to-phase voltage is 400 V r.m.s. > For an indoor meter with material group III, the creepage distance for > basic insulation from Table 9 is 3,2 mm, but the creepage distance for > functional insulationfrom Table 14 is 4,0 mm. > > 2)Connections to the protective conductor shall comply with > 6.5.2.4. Otherwise, this shall be considered to be an unearthed circuit. > > 3)There shall be at least basic insulation between HLV > non-mains circuits and HLV mains circuits. > > 4)Insulation between an unearthed non-mains circuit at > hazardous voltage and an unearthed accessible conductive part shall satisfy > the more onerous of the following: > > - double/reinforced insulation, the working voltage of which is > equal to the hazardous voltage; or > > - supplementary insulation, the working voltage of which is equal > to the voltage between the non-mains circuit athazardous voltage; and > > · another non-mains circuit at hazardous voltage; or > > · a mains circuit. > > 5)See Annex Bfor the conditional use of basic insulation for > PEB. > > 6)
[PSES] insulation between SELV and protective earthed accessible part- IEC 62052-31
Dear All, IEC 62052-31 is standard for product safety requirements for electricity metering equipment. It has a table 20 (given below) which details out insulation requirements between various types of circuits. My question is, why Basic insulation is required between SELV circuit and protective earthed accessible parts? Isn’t a functional insulation is sufficient for this? Thanks B M Vyas Table 20 – Insulation requirements between circuits and between circuits and accessible parts HLV mains-circuit1) ELV circuit SELV circuit PELV circuit PEB circuit2) Protective earthed HLV non-mains-circuit2), 3) Unearthed HLV non-mains circuit3) HLV mains-circuit 1) F/B1) 6) Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B5) Table 8Table 9 B Table 8Table 9 B Table 8Table 9 ELV circuit B Table 8Table 9 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 SELV circuit D Table 8Table 9 B Table 13Table 14 F/B6) Table 13Table 14 F/B8) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PELV circuit2) D Table 8Table 9 B Table 13Table 14 F/B8) Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 PEB circuit2) B5) Table 8Table 9 F/B5), 6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B5) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Protective earthed HLV non-mains circuit2), 3) B Table 8Table 9 B Table 8Table 9 D Table 8Table 9 D Table 8Table 9 B Table 8Table 9 F/B6) Table 8Table 9 B Table 8Table 9 Unearthed HLV non-mains circuit3) B Table 13Table 14 B Table 13Table 14 D Table 13Table 14 D Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 Protective earthed accessible part2), 7) B Table 8Table 9 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 B Table 13Table 14 Unearthed accessible part7) D Table 8Table 9 B Table 13Table 14 B Table 13Table 14 F/B6) Table 13Table 14 B Table 13Table 14 D Table 13Table 14 B/D 4) Table 13Table 14 Abbreviations for insulations: B: Basic insulation or supplementary insulation D: double insulation or reinforced insulation F: Functional insulation S: Supplementary insulation 1)If the functional voltage (not relative to earth/ground) is greater than the rated insulation voltage, the creepage distance for the functional insulation may be greater than that for the basic insulation. An example is a terminal block of a three-phase metering equipment with Un = 230/400 V, where the functional phase-to-phase voltage is 400 V r.m.s. For an indoor meter with material group III, the creepage distance for basic insulation from Table 9 is 3,2 mm, but the creepage distance for functional insulationfrom Table 14 is 4,0 mm. 2)Connections to the protective conductor shall comply with 6.5.2.4. Otherwise, this shall be considered to be an unearthed circuit. 3)There shall be at least basic insulation between HLV non-mains circuits and HLV mains circuits. 4)Insulation between an unearthed non-mains circuit at hazardous voltage and an unearthed accessible conductive part shall satisfy the more onerous of the following: - double/reinforced insulation, the working voltage of which is equal to the hazardous voltage; or - supplementary insulation, the working voltage of which is equal to the voltage between the non-mains circuit athazardous voltage; and · another non-mains circuit at hazardous voltage; or · a mains circuit. 5)See Annex Bfor the conditional use of basic insulation for PEB. 6)Supplementary or basic insulation shall be used if one of the circuits is an independent circuit or is adjacent to a conductive part which may be earthed when the equipment is installed. 7)A functional earthed circuit shall be treated as an unearthed accessible part. The exception is where the functional earth is bonded to the protective conductor and this meets the relevant requirements, then it may be treated as an earthed accessible part. 8)For a PELV system earthed at one end of a cable run, it would be permissible to connect a SELV system at the other end. NOTEReference is made to the respective tables specifying clearances and creepage distances. This e-mail and any files transmitted with it are for the sole use of the intended recipient(s) and may contain confidential and privileged information. If you are not the intended recipient, please contact the sender by reply e-mail and destroy all copies and the original message. Any unauthorized review, use, disclosure, dissemination,