Re: [EVDL] EV familiarity

2019-02-18 Thread Michael Ross via EV
The issue of wire size is ALWAYS dependent on what sort of current MAY occur even in a fault condition. The wire must be increased in cross section if there are heat retaining conditions such as conduit, insulation, limited possibility of convective cooling. So you don't size the wire based on an

Re: [EVDL] EV familiarity

2019-02-18 Thread Lee Hart via EV
Robert Bruninga via EV wrote: Right now, a negligible number of people drive EVs. The public at large still considers them golf carts, or rich yuppie toys. But each of us can make a huge difference. Back in 2011, I bought some professional EV charging Outlet signs and hung them on the two

Re: [EVDL] EV familiarity

2019-02-18 Thread EVDL Administrator via EV
On 17 Feb 2019 at 18:02, Robert Bruninga via EV wrote: > Is this legal under the NEC? On a 20 amp breaker, definitely. On a 30 amp breaker, probably not. I don't have a copy of the NEC handy, and I'm not a code expert, but IIRC the code has (or had) a provision for using a size smaller

Re: [EVDL] EV familiarity

2019-02-18 Thread EVDL Administrator via EV
I'm not a code expert, but as I understand it, in the addition to what Jay Summet said, the NEC generally prohibits connecting either 15 or 20 amp receptacles to a 30 amp branch circuit. Receptacles must be 30 amp. The fact that you're allowed to connect 15 amp 120v recepts to a 20 amp branch

Re: [EVDL] EV familiarity

2019-02-17 Thread Cor van de Water via EV
Correct, a 240v circuit can overload one leg and the ganged breakers will trip. That is why it has a pair of ganged breakers. Cor. On Sun, Feb 17, 2019, 7:41 PM Robert Bruninga via EV Thanks for your insight. Yes, the breaker will be 20 amps so if anyone > tries to do anything other than a

Re: [EVDL] EV familiarity

2019-02-17 Thread Robert Bruninga via EV
Thanks for your insight. Yes, the breaker will be 20 amps so if anyone tries to do anything other than a single L2 or two L1's they will loose both as the breaker will trip. I do assume that a 20A 2 pole breaker actually will trip based on an overload on either of the two sides independently of

Re: [EVDL] EV familiarity

2019-02-17 Thread Jay Summet via EV
I install two 120v outlets on each post along with a single 240v outlet. And then a small note says, "Either one L2 or two L1's but not both". Each post has properly rated #10 conductors for the 16 amps on Line1 and Line2 and Ground and a #12 for Neutral since the Neutral carries either zero

[EVDL] EV familiarity

2019-02-17 Thread Robert Bruninga via EV
> Right now, a negligible number of people drive EVs. > The public at large still considers them golf carts, or rich yuppie toys. But each of us can make a huge difference. Back in 2011, I bought some professional EV charging Outlet signs and hung them on the two light poles in the church