Re: what kind of UPS will work best?

2007-10-12 Thread Olivier Nicole
Hi,

   the *why*.  Is there a best type to save me from this?  Do any of
   these power supplies come with scripts to shutdown a Unix {or
   Linux} computer?  Is there a UPS that is designed for heavy use 
   and a very short (5- to 10-second) uptime?  I'll need one that can
   interface thru the COM ports or the UBS port, if that is how
   these devices work. 

Sorry if I jump in the thread. When it comes to detecting a power
outage and shutingdown nicely your server, a cheap/easy way is for the
server (on the UPS) to check through the network for a low grade PC
(not on the UPS). If the low grade PC is down, it means the power is
off and the server should consider a shutdown.

Dirty trick, but it works.

Best regards,

Olivier
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


RE: what kind of UPS will work best?

2007-10-12 Thread Ted Mittelstaedt
Hi Gary,

  I've owned and worked with at least a dozen different UPS brands.
The best UPS I have - which I have right now powering several systems,
is a Best Power Ferrups FE series.  I don't think they make it anymore,
sorry!

  As for the APC units - the APC standby units are everyone's whore.
I have a collection of them that have failed for a variety of reasons.
They have their problems.

  The worst part about the APC units are the batteries.  If you decide
to go APC, when it comes time to replace the batteries you -must- buy
the most expensive lead acid gel cells you can find.  You cannot put in
the cheap Chinese batteries and have them last.  The reason is that
APC has deliberately calibrated their charging circuitry to fast-charge
the batteries and they use fast charge curves that will destroy the
cheap batteries very quickly.  By contrast most everyone else in the
industry uses feedback circuits that measure how fast the battery is
taking a recharge and will not boil dry the cheap batteries.  Last time
I changed batteries in my Best unit was 9/2004 and they are still going
strong and I used the cheap Chinese batteries.  By contrast all the
APC units I had which I got the same cheap batteries for, have dead
batteries in them now.

  Now, it may be in the brand new APC's they have changed things.  I
noticed in the last new APC unit we sold that APC had switched to
cheaper cells from Better Battery rather than the more spendy cells
from Panasonic that they used in their older UPSes.  But, I still think
there are better deals to be had. 

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] Behalf Of Gary Kline
 Sent: Saturday, October 06, 2007 4:12 PM
 To: FreeBSD Mailing List
 Subject: what kind of UPS will work best?
 
 
 
   Hi Folks,
   
   Recently, a storm happened and the power surge blew me 
   off-line.  Time to get serious about buying a UPS that will
   handle my four main servers for at-most, a 10-second power
   outage.  After that, shut down my computers.  It took me 90 
   minutes of up and down and crawling around last time.  That's
   the *why*.  Is there a best type to save me from this?  Do any of
   these power supplies come with scripts to shutdown a Unix {or
   Linux} computer?  Is there a UPS that is designed for heavy use 
   and a very short (5- to 10-second) uptime?  I'll need one that can
   interface thru the COM ports or the UBS port, if that is how
   these devices work. 
 
   tia, 
 
   gary
 
 
 -- 
   Gary Kline  [EMAIL PROTECTED]   www.thought.org  Public Service Unix
   http://jottings.thought.org   http://transfinite.thought.org
 
 ___
 freebsd-questions@freebsd.org mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to 
 [EMAIL PROTECTED]
 
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-10 Thread Christopher Sean Hilton
On Tue, 2007-10-09 at 11:36 +0800, Erich Dollansky wrote:
 Hi,
 
 Ray wrote:
  On Monday 08 October 2007 8:36:39 pm Erich Dollansky wrote:
  Hi,
 
  Rob wrote:
  think.  Most the draw in a residence is the HVAC.
  what is this? HVAC?
 
  Heating Ventilation Air Conditioning
  
 move the machine around to be used for heating during winter.
 
 Compared to that PCs are a minor consumer.
 
 Erich

Just my 2 cents. As others have said, go with APC. I just recently
hooked up a 2200XL rack mounted unit which is running 6 servers. A
recent calibration test showed that the unit will run these servers for
about 3 hours before it's absolutely necessary to shut down the power.
Another nice thing about the APC's is that you can find SNMP/Web modules
for some of their units which will generate SNMP traps when events occur
with the power.  

I'm using apcupsd from the ports collection to control the servers in
the event of a long term power outage. It has a configurable
master/slave mode. You connect the master to the UPS and then slave from
the master to other servers. My UPS and server are older so the
connection between them is serial. You may get different results with
newer hardware that is USB or if you choose to go the SNMP route. 


-- Chris



-- 
   __o  All I was doing was trying to get home from work.
 _`\,_   -Rosa Parks
___(*)/_(*)___
Christopher Sean Hiltonchris | at | vindaloo.com
 pgp key: D0957A2D/f5 30 0a e1 55 76 9b 1f 47 0b 07 e9 75 0e 14

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Pieter de Goeje
On Sunday 07 October 2007, Gary Kline wrote:
   First, thank to both you and Bart for your cmments.  You were
   *right* about the price.  Can I assume that a ballpark would be
   400W for each server?  (My wife is right: I've got to cut back to
   three computers:-)  I've found one APC 2200VA with a 17minute
   uptime.  3 times 400W, yes?

I think this is overkill. Some time ago I was wondering the same thing and to 
verify my guess on the overall power usage of my servers I bought a VA/Watts 
meter (EUR. 39,-). Turns out average wattage is about 90watts per server idle 
and max 130watts under load. On powerup they will use a max. of 180watts for 
less than a second. The servers are simple dual cores with about 2 harddisks 
each. (no screens or other devices attached) Also, the powerfactor was ~0,95 
so that means that for every Watt of apparent power (VA) almost a Watt of 
real power was used. Thus, for my servers I would need something like a 
500Watt/600VA UPS.

So my advice is: don't guess but measure.

Cheers,
Pieter de Goeje
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Gary Kline
On Mon, Oct 08, 2007 at 02:36:05AM +0200, Pieter de Goeje wrote:
 On Sunday 07 October 2007, Gary Kline wrote:
  First, thank to both you and Bart for your cmments.  You were
  *right* about the price.  Can I assume that a ballpark would be
  400W for each server?  (My wife is right: I've got to cut back to
  three computers:-)  I've found one APC 2200VA with a 17minute
  uptime.  3 times 400W, yes?
 
 I think this is overkill. Some time ago I was wondering the same thing and to 
 verify my guess on the overall power usage of my servers I bought a VA/Watts 
 meter (EUR. 39,-). Turns out average wattage is about 90watts per server idle 
 and max 130watts under load. On powerup they will use a max. of 180watts for 
 less than a second. The servers are simple dual cores with about 2 harddisks 
 each. (no screens or other devices attached) Also, the powerfactor was ~0,95 
 so that means that for every Watt of apparent power (VA) almost a Watt of 
 real power was used. Thus, for my servers I would need something like a 
 500Watt/600VA UPS.
 
 So my advice is: don't guess but measure.
 


Thanks a lot.  I was thinking of doing something like this;
maybe an ammeter to see how much power each server draws; then
(possiibly add a bit for reserve).  

I'm looking at this as a long-time project.  Not rushing to do
something completely foolish.  So the more accuracy, the better!

gary



 Cheers,
 Pieter de Goeje
 ___
 freebsd-questions@freebsd.org mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to [EMAIL PROTECTED]

-- 
  Gary Kline  [EMAIL PROTECTED]   www.thought.org  Public Service Unix
  http://jottings.thought.org   http://transfinite.thought.org

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Rob

Pieter de Goeje wrote:
verify my guess on the overall power usage of my servers I bought a VA/Watts 
meter (EUR. 39,-). Turns out average wattage is about 90watts per server idle 
and max 130watts under load. On powerup they will use a max. of 180watts for 


I've got one of these:  
http://www.newegg.com/Product/Product.aspx?Item=N82E16882715001


Works nicely for measuring cumulative power usage.  APC's web site also has a 
selector with very model-specific power consumption figures:
http://www.apc.com/tools/ups_selector/index.cfm

 -Rob
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Gary Kline
On Mon, Oct 08, 2007 at 02:05:17PM -0400, Rob wrote:
 Pieter de Goeje wrote:
 verify my guess on the overall power usage of my servers I bought a 
 VA/Watts meter (EUR. 39,-). Turns out average wattage is about 90watts per 
 server idle and max 130watts under load. On powerup they will use a max. 
 of 180watts for 
 
 I've got one of these:  
 http://www.newegg.com/Product/Product.aspx?Item=N82E16882715001
 
 Works nicely for measuring cumulative power usage.  APC's web site also has 
 a selector with very model-specific power consumption figures:
 http://www.apc.com/tools/ups_selector/index.cfm
 

Outstanding; thanks++ for the URL for the watt/amp/volt/Hz/VA
meter.  I just ordred one.   Also for the  ups_selector page.  
I'll need help getting the daemon and getting everything squared
away, but that's months away.

gary


  -Rob
 ___
 freebsd-questions@freebsd.org mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to [EMAIL PROTECTED]

-- 
  Gary Kline  [EMAIL PROTECTED]   www.thought.org  Public Service Unix
  http://jottings.thought.org   http://transfinite.thought.org

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Rob

Gary Kline wrote:

Outstanding; thanks++ for the URL for the watt/amp/volt/Hz/VA
	meter.  I just ordred one.   Also for the  ups_selector page.  


Glad to help.  When you're experimenting with the meter, remember that 
for many devices you need to plug it in for a couple days to average out 
the load.  Like a refrigerator, where the defrost only kicks in every 
few days.  No so big a deal on computers, but you'll still get more 
accurate numbers.  I saw one online review of the thing where the author 
was testing devices for less than an hour at a time, which is NOT going 
to give any accurate results.


Some of my discoveries:  CRTs that don't go into low power mode suck 
obscene amounts of power.  Refrigerators aren't as bad a you might 
think.  Most the draw in a residence is the HVAC.


I'll send you (off list) a spreadsheet I was using to track stuff.

  -Rob
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Erich Dollansky

Hi,

Rob wrote:


think.  Most the draw in a residence is the HVAC.


what is this? HVAC?

Erich
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Bart Silverstrim



Erich Dollansky wrote:

Hi,

Rob wrote:


think.  Most the draw in a residence is the HVAC.


what is this? HVAC?


Heating and air conditioning, I believe.  No?
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Ray
On Monday 08 October 2007 8:36:39 pm Erich Dollansky wrote:
 Hi,

 Rob wrote:
  think.  Most the draw in a residence is the HVAC.

 what is this? HVAC?

Heating Ventilation Air Conditioning

 Erich
 ___
 freebsd-questions@freebsd.org mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to
 [EMAIL PROTECTED]


___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-08 Thread Erich Dollansky

Hi,

Ray wrote:

On Monday 08 October 2007 8:36:39 pm Erich Dollansky wrote:

Hi,

Rob wrote:

think.  Most the draw in a residence is the HVAC.

what is this? HVAC?


Heating Ventilation Air Conditioning


move the machine around to be used for heating during winter.

Compared to that PCs are a minor consumer.

Erich
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-07 Thread Gary Kline
On Sun, Oct 07, 2007 at 11:12:00AM +0800, Erich Dollansky wrote:
 Hi,
 
 there are basically two types of UPS' around: online and stand-by or fly-by.
 
 The online version is much more expensive but also much better in 
 critical conditions.
 
 Gary Kline wrote:
  Hi Folks,
  
  Recently, a storm happened and the power surge blew me 
  off-line.  Time to get serious about buying a UPS that will
  handle my four main servers for at-most, a 10-second power
 
 You have the choice between four individual boxes or one big box.
 
 Cases like this let the online version shine. Stand-by versions fail 
 pretty often especially if you have a neighbour around running big 
 engines powered directly from the power lines.
 
 Even big air-cons can cause the problems.
 
  Linux} computer?  Is there a UPS that is designed for heavy use 
  and a very short (5- to 10-second) uptime?  I'll need one that can
 
 I do not think that it is a good advice to go for 10 second uptime. Take 
 a rating fitting your machines (400W power rating for the machine, 600VA 
 for the UPS) with at least 10 minutes uptime.
 
 APC supplies you with both types of UPS.
 
 All APC I have seen failing were of the fly-by type, all other were the 
 online version. I think, it will be the same for any other brand.
 
 But do not drop dead when you see the price difference. This will be 
 money well spend.
 

First, thank to both you and Bart for your cmments.  You were 
*right* about the price.  Can I assume that a ballpark would be
400W for each server?  (My wife is right: I've got to cut back to
three computers:-)  I've found one APC 2200VA with a 17minute
uptime.  3 times 400W, yes?

The first thing is to be sure of getting  large enough UPS to
bridge the few-seconds power outtages or fraction/section surges.
So I need help there.   Another question or two can wait.

thanks for any further clues!

gary

 Erich

-- 
  Gary Kline  [EMAIL PROTECTED]   www.thought.org  Public Service Unix
  http://jottings.thought.org   http://transfinite.thought.org

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-07 Thread Erich Dollansky

Hi,

Gary Kline wrote:

On Sun, Oct 07, 2007 at 11:12:00AM +0800, Erich Dollansky wrote:
*right* about the price.  Can I assume that a ballpark would be
400W for each server?  (My wife is right: I've got to cut back to
three computers:-)  I've found one APC 2200VA with a 17minute
uptime.  3 times 400W, yes?

there are other factors which affect this. It is the current peak when a 
PC starts and the phase shift it causes. The phase shift should not be a 
problem but the peak.


I would not bother as long as you do not switch the computers on in 
parallel.



The first thing is to be sure of getting  large enough UPS to
bridge the few-seconds power outtages or fraction/section surges.


If they define 17 minutes, this device will be good for you.

Just get the online version to avoid surprises later.

Erich
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-06 Thread Bart Silverstrim



Gary Kline wrote:

Hi Folks,

	Recently, a storm happened and the power surge blew me 
	off-line.  Time to get serious about buying a UPS that will

handle my four main servers for at-most, a 10-second power
	outage.  After that, shut down my computers.  It took me 90 
	minutes of up and down and crawling around last time.  That's
	the *why*.  Is there a best type to save me from this? 


APC makes GREAT UPS's and have good support.  I once blew out an APC by 
miswiring a switch on a computer (don't ask).  I called tech support, 
they agreed that what I told them had happened shouldn't have happened, 
and shipped me a new UPS for free, without any hassle.  From that point 
on, I swore I'd go APC first.



Do any of
these power supplies come with scripts to shutdown a Unix {or
	Linux} computer?  


Not that I know of...there's daemons you can install for that purpose, 
though.


Is there a UPS that is designed for heavy use 
	and a very short (5- to 10-second) uptime?  


Generally you need to add up your power requirements and match the load 
to the UPS's power rating.



I'll need one that can
interface thru the COM ports or the UBS port, if that is how
	these devices work. 


Today it's common to have a USB interface.
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: what kind of UPS will work best?

2007-10-06 Thread Erich Dollansky

Hi,

there are basically two types of UPS' around: online and stand-by or fly-by.

The online version is much more expensive but also much better in 
critical conditions.


Gary Kline wrote:

Hi Folks,

	Recently, a storm happened and the power surge blew me 
	off-line.  Time to get serious about buying a UPS that will

handle my four main servers for at-most, a 10-second power


You have the choice between four individual boxes or one big box.

Cases like this let the online version shine. Stand-by versions fail 
pretty often especially if you have a neighbour around running big 
engines powered directly from the power lines.


Even big air-cons can cause the problems.

	Linux} computer?  Is there a UPS that is designed for heavy use 
	and a very short (5- to 10-second) uptime?  I'll need one that can


I do not think that it is a good advice to go for 10 second uptime. Take 
a rating fitting your machines (400W power rating for the machine, 600VA 
for the UPS) with at least 10 minutes uptime.


APC supplies you with both types of UPS.

All APC I have seen failing were of the fly-by type, all other were the 
online version. I think, it will be the same for any other brand.


But do not drop dead when you see the price difference. This will be 
money well spend.


Erich
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]