Well, that would only be true if it were a completely ideal transformer with no
impedance. Even at the nominal tap ratio of 1.0 the voltages magnitudes will
not be identical (as with a transmission line).
Ray
> On Oct 17, 2017, at 12:19 PM, Ahmad Sadiq Abubakar
>
Dear Ray,
Thanks for your response. In my case, V1 is a generator bus with 1.025 p.u.
and V2 is a known PQ bus with 1 p.u.
This implied Tap is 1.02?
On Oct 17, 2017 4:27 PM, "Ray Zimmerman" wrote:
> The tap ratio is the off-nominal tap ratio, relating per-unit voltages,
> not
The tap ratio is the off-nominal tap ratio, relating per-unit voltages, not kV
voltages. So if both voltages are at their nominal values (i.e. both at 1 p.u.)
then the TAP should be 1 and SHIFT should be 0.
Ray
> On Oct 17, 2017, at 6:23 AM, Ahmad Sadiq Abubakar
>
Hi, all
For a given case branch data r, x, b, assuming the branch is a transformer,
between bus1 and bus2, with voltages V1 and V2 KV respectively. How do I
obtain the Tap ration (column 9) and shift (column 10) of the branch matrix?
I have simply used V1/V2 as the Tap ration while the shift is