> On Sep 17, 2021, at 8:59 AM, Sean Donelan wrote: > > It is possible to design a data center WITHOUT using those electrical code > exceptions, and WITHOUT a "Big Red Button." > > You can check, because my data center ideas were copied by several tech > companies world-wide (you know who

Re: Never push the Big Red Button (New York City subway failure)

2021-09-17 Thread Sean Donelan
Sigh, people often mis-hear this when I say it, so I will try to say it carefully. If you have an Emergency Power Off (EPO), the electrical code (and life-safety code) allows use of several alternative wiring methods. Some people mistakenly believe the allowed alternatives are the rule, but

Re: Never push the Big Red Button (New York City subway failure)

2021-09-17 Thread Lady Benjamin Cannon of Glencoe, ASCE
7-6824 or 1-800-430-6404 (MB only) > athomp...@merlin.mb.ca <mailto:athomp...@merlin.mb.ca> > www.merlin.mb.ca <http://www.merlin.mb.ca/> > From: NANOG on behalf of Jay > R. Ashworth > Sent: September 11, 2021 22:23 > To: nanog > Subject: Re: Never push the Big Red Button (N

Re: Never push the Big Red Button

2021-09-16 Thread Robert Taylor
We had a new fire suppression guy testing our system for our computer room, and unbeknownst to him, one of the tests that he did triggered the EPO. One of my co-workers was in the room, which had about 20 racks of equipment, and he told me afterwards that for a quick second he thought he died. He

Re: Never push the Big Red Button (New York City subway failure)

2021-09-16 Thread richey goldberg
to restart everything if we ever had to hit our red button. -richey From: NANOG on behalf of Roy Date: Thursday, September 16, 2021 at 12:41 AM To: nanog Subject: Re: Never push the Big Red Button (New York City subway failure) Miy story in the late 1970s I was working in a large computer

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Sabri Berisha
- On Sep 15, 2021, at 9:08 PM, bzs b...@theworld.com wrote: Hi, > People don't suffocate from Halon dumps, I've been thru a couple (not > me personally but staff, I was in my office but arrived quickly.) > > What is somewhat dangerous about Halon (or likely more modern) fire > suppression

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Roy
Miy story in the late 1970s I was working in a large computer facility with both mainframes and mil-spec 400hz computers. Management decided that the EPO should be tested.  So we powered down the disk and tapes.  The electrician pressed the EPO button and NOTHING.  Everything kept running.

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread bzs
On September 15, 2021 at 13:31 war...@kumari.net (Warren Kumari) wrote: > Well, there is the EPO button, which generally does that, and the (variously > labeled) HALON/FM-200/GAS FIRE SUPPRESSION/GAS DISCHARGE button, which does > the > flashy lights and klangly bell and similar. This is

Re: Never push the Big Red Button

2021-09-15 Thread Callan Banner
Totally agree @billy, could've put it better myself. Though it's much more entertaining (and terrifying) to wince at the audible difference between just the hardware whirring to a silence, and all of the temp and humidity controls whirring to a halt with the hardware. The fear in the air is

Re: Never push the Big Red Button

2021-09-15 Thread Billy Croan
Indeed. Few sounds in the data center haunt me quite as much as a sensation that the decibel level has just decreased significantly. On Wed, Sep 15, 2021, 4:14 PM Keith Stokes wrote: > The bigger thing to notice is the *lack* of noise as every server, switch > and storage system spins down. > >

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Daniel Seagraves
> On Sep 15, 2021, at 2:20 PM, Fred Baker wrote: > > One of the many stories that came out of 9/11 was a switching center in NY > City that had a diesel generator as a power backup - which of course acted as > primary when the city power is off. After a few days of operation, it needed > to

Re: Never push the Big Red Button

2021-09-15 Thread Keith Stokes
The bigger thing to notice is the *lack* of noise as every server, switch and storage system spins down. --- Keith Stokes On Sep 15, 2021, at 3:50 PM, Stephen Satchell mailto:l...@satchell.net>> wrote: In the data centers I've worked in over the decades, those Big Red Buttons would

Re: Never push the Big Red Button

2021-09-15 Thread Stephen Satchell
In the data centers I've worked in over the decades, those Big Red Buttons would activate a normally-closed contactor in a breaker panel. When pushed, the contactor would open, and turn off all the circults in said breaker panel. Not affected are lights, convenience outlets, door locks, and

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread William Herrin
On Wed, Sep 15, 2021 at 12:32 PM Warren Kumari wrote: > Oooof. I've seen someone at a gas station do something similar -- > I cannot remember if it was putting diesel in their gasoline car, > or gas in their diesel pickup, but I *do* remember the sudden > yelp and look of dismay when they

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Warren Kumari
On Wed, Sep 15, 2021 at 3:20 PM Fred Baker wrote: > > > > On Sep 10, 2021, at 1:33 PM, Warren Kumari wrote: > > > > The utility let them know that they were going to be doing some > maintenance work in the area. No impact expected, but out of an abundance > of caution, they transfer over to

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Fred Baker
> On Sep 10, 2021, at 1:33 PM, Warren Kumari wrote: > > The utility let them know that they were going to be doing some maintenance > work in the area. No impact expected, but out of an abundance of caution, > they transfer over to generators. After the utility lets them know that the >

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Jay R. Ashworth
- Original Message - > From: "Adam Thompson" > Now I'm curious... in all of the DCs and COs I've worked in - to the best of > my > knowledge, I haven't personally tested this! - the EPO button does not switch > to emergency power. It turns off ALL equipment power in the space - no >

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Tom Beecher
very long pause…then some mumbling off phone, then the manager >>> got on the line and said someone would be flying out and be onsite within >>> 12 hours. We were down for 3 days, and got fined $250,000 by the insurance >>> regulators since we couldn’t pay claims. >>> >>> >>> >>> *Matthew Huff* | Director of Technical Operations

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Warren Kumari
On Wed, Sep 15, 2021 at 12:23 PM Daniel Seagraves < dseag...@humancapitaldev.com> wrote: > > On Sep 15, 2021, at 10:58 AM, Adam Thompson > wrote: > > Now I'm curious... in all of the DCs and COs I've worked in - to the best > of my knowledge, I haven't personally tested this! - the EPO button

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread William Herrin
On Wed, Sep 15, 2021 at 9:21 AM Daniel Seagraves wrote: > It was always my understanding EPO was to be used for > “We have an electrical fire and need to remove the source RFN”, > not “we need to be on the redundant power instead of city power > and don’t want to wait for the automatic transfer”.

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Jay Hennigan
On 9/15/21 08:58, Adam Thompson wrote: Now I'm curious... in all of the DCs and COs I've worked in - to the best of my knowledge, I haven't personally tested this! - the EPO button does *not*​ switch to emergency power.  It turns off ALL equipment power in the space - no lights, no klaxons,

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Daniel Seagraves
> On Sep 15, 2021, at 10:58 AM, Adam Thompson wrote: > > Now I'm curious... in all of the DCs and COs I've worked in - to the best of > my knowledge, I haven't personally tested this! - the EPO button does not​ > switch to emergency power. It turns off ALL equipment power in the space - >

Re: Never push the Big Red Button (New York City subway failure)

2021-09-15 Thread Adam Thompson
ehalf of Jay R. Ashworth Sent: September 11, 2021 22:23 To: nanog Subject: Re: Never push the Big Red Button (New York City subway failure) - Original Message - > From: "Sean Donelan" > NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER > OUTAGE ISSUE ON AUGUST 29, 20

Re: Never push the Big Red Button (New York City subway failure)

2021-09-11 Thread Jay R. Ashworth
- Original Message - > From: "Sean Donelan" > NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER > OUTAGE ISSUE ON AUGUST 29, 2021 > Key Findings > September 8, 2021 > > https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf > > Key Findings >

Re: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Warren Kumari
t; >> >> >> *Office: 914-460-4039* >> >> *mh...@ox.com | **www.ox.com <http://www.ox.com>* >> >> >> *.......

Re: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Baldur Norddahl
..* > > > > *From:* Chris Kane > *Sent:* Friday, September 10, 2021 3:16 PM > *To:* Christopher Morrow > *Cc:* Matthew Huff ; nanog@nanog.org > *Subject:* Re: Never push the Big Red Button (New York City subway > failure) > > > > True EPO story; main

Re: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Warren Kumari
.. >> >> -----Original Message----- >> From: NANOG On Behalf Of Sean >> Donelan >> Sent: Friday, September 10, 2021 12:38 PM >> To: nanog@nanog.org >> Subject: Never push the Big Red Button (New York City subway failure) >> >&

Re: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Mikael Abrahamsson via NANOG
On Fri, 10 Sep 2021, Sean Donelan wrote: 1. The “Emergency Power Off” button did not have a protective cover at the time of the shutdown or the following WSP investigation. Aka "molly-guard". https://en.wiktionary.org/wiki/molly-guard -- Mikael Abrahamssonemail: swm...@swm.pp.se

RE: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Matthew Huff
... -Original Message- From: NANOG mailto:ox@nanog.org>> On Behalf Of Sean Donelan Sent: Friday, September 10, 2021 12:38 PM To: nanog@nanog.org<mailto:nanog@nanog.org> Subject: Never push the Big Red Button (New York City subway failure) NEW YORK CITY TRANSIT RAIL CONTROL

Re: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Chris Kane
t;> >> -Original Message- >> From: NANOG On Behalf Of Sean >> Donelan >> Sent: Friday, September 10, 2021 12:38 PM >> To: nanog@nanog.org >> Subject: Never push the Big Red Button (New York City subway failure) >> >> NEW YORK CITY TRANS

Re: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Christopher Morrow
Friday, September 10, 2021 12:38 PM > To: nanog@nanog.org > Subject: Never push the Big Red Button (New York City subway failure) > > NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER > OUTAGE ISSUE ON AUGUST 29, 2021 > Key Findings > September 8, 2021 > > > >

RE: Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Matthew Huff
Donelan Sent: Friday, September 10, 2021 12:38 PM To: nanog@nanog.org Subject: Never push the Big Red Button (New York City subway failure) NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER OUTAGE ISSUE ON AUGUST 29, 2021 Key Findings September 8, 2021 https://www.governor.ny.gov/sites/default/files

Never push the Big Red Button (New York City subway failure)

2021-09-10 Thread Sean Donelan
NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER OUTAGE ISSUE ON AUGUST 29, 2021 Key Findings September 8, 2021 https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf Key Findings [...] 3. Based on the electrical equipment log readings and the