RE: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-29 Thread Alex Rubenstein
More to the point, as I note in another reply, you don't want to be *the lineman down the road with his hands on a dead wire*. Pretty much the *first paragraph* in NEC 700 (700.6) says this: Transfer equipment shall be designed and installed to prevent the inadvertent interconnection

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-27 Thread Matthew Black
On Fri, 24 Jun 2011 18:29:14 -0400 Jay Ashworth j...@baylink.com wrote: The North American Electric Reliability Council is planning to relax the standards for how closely power utilities must hold to 60.00Hz. Here's my absolute favorite quote of all time: Tweaking the power grid's frequency

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-27 Thread Mark Radabaugh
On 6/27/11 1:19 PM, Matthew Black wrote: On Fri, 24 Jun 2011 18:29:14 -0400 Jay Ashworth j...@baylink.com wrote: The North American Electric Reliability Council is planning to relax the standards for how closely power utilities must hold to 60.00Hz. Here's my absolute favorite quote of all

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-27 Thread Owen DeLong
On Jun 25, 2011, at 4:59 PM, Joel Jaeggli wrote: On Jun 25, 2011, at 4:47 PM, Andrew D Kirch wrote: On 6/25/2011 7:43 PM, Paul Graydon wrote: Take a guess what the datacenter our equipment is currently hosted in uses. Yet another reason to be glad of a datacenter move that's coming up.

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Leo Bicknell
In a message written on Sat, Jun 25, 2011 at 03:32:09PM -0700, Seth Mattinen wrote: Most of these come in open, delayed, or closed transition models: http://www.gedigitalenergy.com/powerquality/ATSHome.htm I think we're missing something, which is where these ATS's are installed. I don't

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Jussi Peltola
On Sun, Jun 26, 2011 at 05:27:10AM -0700, Leo Bicknell wrote: It's not that you couldn't install a closed transition ATS in the ATS 1a/1b location from an electrical point of view, but I don't think codes, power companies, or common sense make it a good idea. As others have pointed out, the

RE: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Alex Rubenstein
It makes little sense to sync to the grid when the generator is only used when the grid is down - and unless you run your generators 24/7 your UPS will have to make up for the comparatively long time it takes for the generator to start, so it's rather useless to sync the generator when the

RE: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Alex Rubenstein
I think we're missing something, which is where these ATS's are installed. I don't think most utilities allow (largeish) ATS's to do a closed transition from a genset to the utility grid, but I may be wrong. There may be other ATS's in your facility that do a closed transition though. For

RE: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Matthew Huff
happened to us a few times before we switched to a delayed ATS, was a PITA to debug and resolve. -Original Message- From: Seth Mattinen [mailto:se...@rollernet.us] Sent: Saturday, June 25, 2011 8:49 PM To: nanog@nanog.org Subject: Re: Wacky Weekend: NERC to relax power grid frequency

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Jay Ashworth
- Original Message - From: Michael DeMan na...@deman.com It is my understanding also that most commercial grade gensets have built into the ATS logic that when utility power comesback online, that the transfer back to utility power is coordinated with the ATS driving the generator

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Jay Ashworth
- Original Message - From: Jeff Wheeler j...@inconcepts.biz On Sun, Jun 26, 2011 at 12:23 AM, Alex Rubenstein a...@corp.nac.net wrote: At least here in JCPL territory (northern NJ), closed transition is frowned upon. Too much risk, they think. They are correct, really, but the

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Brandon Butterworth
It makes little sense to sync to the grid when the generator is only used when the grid is down I don't know what large DC do but at our large sites we normally get power cheaper in exchange for a load shed agreement. When we got the call we ran some/all of the load on generator so the grid

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Ingo Flaschberger
Take a guess what the datacenter our equipment is currently hosted in uses. Yet another reason to be glad of a datacenter move that's coming up. Why can't we just all use DC and be happy? motors don't produce DC? dc generators produce dc. tesla vs edison? human safe dc voltage requires

RE: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Ingo Flaschberger
2) Allowing transformer fields to collapse. Even in phase, without a delayed transition ATS you can end up with a partially collapsed transformer field with a new field being created at non-ground state. This can cause a transient back wave that can snap circuit breakers. Yep, this one

Re: Wacky Weekend: NERC to relax power grid frequency strictures [OT]

2011-06-26 Thread Jussi Peltola
On Sun, Jun 26, 2011 at 11:36:24PM +0200, Ingo Flaschberger wrote: but transforming is not easy. ac/ac transformers are easy tu build and very immune against lightning strikes - inverter systems are not. Switching DC is also problematic since there is no zero crossing to extinguish the arc.

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Pete Carah
On 06/26/2011 05:43 PM, Ingo Flaschberger wrote: 2) Allowing transformer fields to collapse. Even in phase, without a delayed transition ATS you can end up with a partially collapsed transformer field with a new field being created at non-ground state. This can cause a transient back wave that

Re: Wacky Weekend: NERC to relax power grid frequency strictures [OT]

2011-06-26 Thread Pete Carah
On 06/26/2011 05:55 PM, Jussi Peltola wrote: On Sun, Jun 26, 2011 at 11:36:24PM +0200, Ingo Flaschberger wrote: but transforming is not easy. ac/ac transformers are easy tu build and very immune against lightning strikes - inverter systems are not. Switching DC is also problematic since

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Gary Wardell
Hi, Yes, transforming DC is not easy. However, DC works good at long haul transmission because a lot of energy is lost in the revers EMF generated by AC a several hundred volts. Some years ago a high voltage DC line was constructed between Oregon and California to deliver power to

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-26 Thread Jussi Peltola
On Sun, Jun 26, 2011 at 06:46:09PM -0400, Pete Carah wrote: HVAC compressors have their own problems; once fully stopped you have to wait for the liquid to clear the compressor before restarting, or have LOTS of torque (like a car unit) available (and a supply of new belts :-) [begin OT

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Jay Ashworth
- Original Message - From: Jussi Peltola pe...@pelzi.net On Fri, Jun 24, 2011 at 06:29:14PM -0400, Jay Ashworth wrote: This is gonna be fun, no? If your definition of fun is spending a year watching an old microwave clock lose or gain a few minutes. I don't see how this has

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread William Herrin
On Sat, Jun 25, 2011 at 10:49 AM, Jay Ashworth j...@baylink.com wrote: Perhaps I read the piece incorrectly, but it certainly sounded to *me* like the part that was hard was not hitting 60.00, but *staying in sync with others*... Way I read it, when they occasionally run at 59.9hz for a few

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Jason Roysdon
On 06/25/2011 07:49 AM, Jay Ashworth wrote: - Original Message - From: Jussi Peltola pe...@pelzi.net On Fri, Jun 24, 2011 at 06:29:14PM -0400, Jay Ashworth wrote: This is gonna be fun, no? If your definition of fun is spending a year watching an old microwave clock lose or gain a

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Owen DeLong
On Jun 25, 2011, at 11:03 AM, Jason Roysdon wrote: On 06/25/2011 07:49 AM, Jay Ashworth wrote: - Original Message - From: Jussi Peltola pe...@pelzi.net On Fri, Jun 24, 2011 at 06:29:14PM -0400, Jay Ashworth wrote: This is gonna be fun, no? If your definition of fun is

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Jason Roysdon
On 06/25/2011 08:06 AM, William Herrin wrote: On Sat, Jun 25, 2011 at 10:49 AM, Jay Ashworth j...@baylink.com wrote: Perhaps I read the piece incorrectly, but it certainly sounded to *me* like the part that was hard was not hitting 60.00, but *staying in sync with others*... Way I read it,

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Jay Ashworth
- Original Message - From: Jason Roysdon nanog.20110...@jason.roysdon.net That's what they're doing here, opting to skip patching the time error. They're not ignoring frequency altogether, but rather only minding that aspects that have to do with grid stability, not your alarm clock.

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Jason Roysdon
On 06/25/2011 02:02 PM, Jay Ashworth wrote: - Original Message - From: Jason Roysdon nanog.20110...@jason.roysdon.net That's what they're doing here, opting to skip patching the time error. They're not ignoring frequency altogether, but rather only minding that aspects that have to

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Pete Carah
On 06/25/2011 03:52 PM, Jason Roysdon wrote: On 06/25/2011 08:06 AM, William Herrin wrote: On Sat, Jun 25, 2011 at 10:49 AM, Jay Ashworth j...@baylink.com wrote: Perhaps I read the piece incorrectly, but it certainly sounded to *me* like the part that was hard was not hitting 60.00, but

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Leo Bicknell
In a message written on Fri, Jun 24, 2011 at 06:29:14PM -0400, Jay Ashworth wrote: I believe the answer to that question is contained here: http://yarchive.net/car/rv/generator_synchronization.html [1] I wouldn't use a colo that had to sync their generator to the grid. That is a bad

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Seth Mattinen
On 6/25/2011 15:12, Leo Bicknell wrote: I have never seen a generator that syncs to the utility for live, no break transfer. I'm sure such a thing exists, but that sounds crazy dangerous to me. Generators sync to each other, not the utility. Most of these come in open, delayed, or closed

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Ingo Flaschberger
Generators all stay in sync. Generator owners have expensive devices that sync the phase before the generator is connected to the grid. Once a generator is connected to the gird, it will stay in sync - in fact that is why they have the expensive devices to make sure that they are in sync before

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Paul Graydon
On 6/25/2011 12:32 PM, Seth Mattinen wrote: On 6/25/2011 15:12, Leo Bicknell wrote: I have never seen a generator that syncs to the utility for live, no break transfer. I'm sure such a thing exists, but that sounds crazy dangerous to me. Generators sync to each other, not the utility. Most

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Andrew D Kirch
On 6/25/2011 7:43 PM, Paul Graydon wrote: Take a guess what the datacenter our equipment is currently hosted in uses. Yet another reason to be glad of a datacenter move that's coming up. Why can't we just all use DC and be happy?

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Joel Jaeggli
On Jun 25, 2011, at 4:47 PM, Andrew D Kirch wrote: On 6/25/2011 7:43 PM, Paul Graydon wrote: Take a guess what the datacenter our equipment is currently hosted in uses. Yet another reason to be glad of a datacenter move that's coming up. Why can't we just all use DC and be happy? motors

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Seth Mattinen
On 6/25/2011 16:43, Paul Graydon wrote: On 6/25/2011 12:32 PM, Seth Mattinen wrote: For open and closed transitions you'll most certainly want to sync to utility to transition between the two. For the delayed transition model it'll stop at the intermediate open point for a configurable amount

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Jay Ashworth
- Original Message - From: Seth Mattinen se...@rollernet.us On 6/25/2011 15:12, Leo Bicknell wrote: I have never seen a generator that syncs to the utility for live, no break transfer. I'm sure such a thing exists, but that sounds crazy dangerous to me. Generators sync to each

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Michael DeMan
It ismy understanding also that most commercial grade gensets have built into the ATS logic that when utility power comesback online, that the transfer back to utility power is coordinated with the ATS driving the generator until both frequency and phases are within a user specified range? -

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Michael DeMan
On Jun 25, 2011, at 4:47 PM, Andrew D Kirch trel...@trelane.net wrote: On 6/25/2011 7:43 PM, Paul Graydon wrote: Take a guess what the datacenter our equipment is currently hosted in uses. Yet another reason to be glad of a datacenter move that's coming up. Why can't we just all use DC

RE: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-25 Thread Alex Rubenstein
It ismy understanding also that most commercial grade gensets have built into the ATS logic that when utility power comesback online, that the transfer back to utility power is coordinated with the ATS driving the generator until both frequency and phases are within a user specified range?

Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-24 Thread Jay Ashworth
The North American Electric Reliability Council is planning to relax the standards for how closely power utilities must hold to 60.00Hz. Here's my absolute favorite quote of all time: Tweaking the power grid's frequency is expensive and takes a lot of effort, said Joe McClelland, head of

Re: Wacky Weekend: NERC to relax power grid frequency strictures

2011-06-24 Thread Jussi Peltola
On Fri, Jun 24, 2011 at 06:29:14PM -0400, Jay Ashworth wrote: This is gonna be fun, no? If your definition of fun is spending a year watching an old microwave clock lose or gain a few minutes. I don't see how this has anything to do with syncing two generators. The grid is in sync, and if the