Re: Rack rails on network equipment

2021-09-27 Thread Doug McIntyre
On Mon, Sep 27, 2021 at 03:38:15PM -0400, William Allen Simpson wrote: > Anyway, wasn't the Open Compute Project supposed to fix all this? > Why not just require OCP in all RFPs? https://xkcd.com/927/

Re: Rack rails on network equipment

2021-09-27 Thread Mel Beckman
I think the primary issue for front- vs rear-mounted switches is cooling. As long as you use switches that can pull cooling air from either the front or the back, it’s feasible to mount the TOR switches in the back. For example, I think these are parts I used to order for Cisco Catalyst

Re: Rack rails on network equipment

2021-09-27 Thread Andrey Khomyakov
Folks, I kind of started to doubt my perception (we don't officially calculate it) of our failure rates until Mel provided this: "That’s about the right failure rate for a population of 1000 switches. Enterprise switches typically have an MTBF of 700,000 hours or so, and 1000 switches operating

Re: Rack rails on network equipment

2021-09-27 Thread William Allen Simpson
On 9/25/21 7:52 PM, Joe Greco wrote: On Sat, Sep 25, 2021 at 04:23:38PM -0700, Jay Hennigan wrote: On 9/25/21 16:14, George Herbert wrote: (Crying, thinking about racks and racks and racks of AT 56k modems strapped to shelves above PM-2E-30s???) And all of their wall-warts [...] You were

Re: Rack rails on network equipment

2021-09-27 Thread Mel Beckman
That’s about the right failure rate for a population of 1000 switches. Enterprise switches typically have an MTBF of 700,000 hours or so, and 1000 switches operating 8760 hours (24x7) a year would be 8,760,000 hours. Divided by 12 failures (one a month), yields an MTBF of 730,000 hours. -mel

Re: Rack rails on network equipment

2021-09-27 Thread Doug McIntyre
On Sat, Sep 25, 2021 at 12:48:38PM -0700, Andrey Khomyakov wrote: > We operate over 1000 switches in our data centers, and hardware failures > that require a switch swap are common enough where the speed of swap starts > to matter to some extent. We probably swap a switch or two a month. ... This

Re: Rack rails on network equipment

2021-09-27 Thread Tore Anderson
* Andrey Khomyakov > Interesting tidbit is that we actually used to manufacture custom rails for > our Juniper EX4500 switches so the switch can be actually inserted from the > back of the rack (you know, where most of your server ports are...) and not > be blocked by the zero-U PDUs and all

Re: Rack rails on network equipment

2021-09-26 Thread Lady Benjamin Cannon
, they’ll probably slow things down compared with basic (good, bad ones exist) rack rails. I write all of this from the perspective of a network engineer, businesswoman, and telecom carrier - not necessarily that of a hyperscale cloud compute provider, although we are becoming one of those too

Re: Rack rails on network equipment

2021-09-26 Thread Alan Buxey
> We operate over 1000 switches in our data centers, and hardware failures that > require a switch swap are common enough where the speed of swap starts to > matter to some extent. We probably swap a switch or two a month. having operated a network of over 2000 switches, where we would see

Re: Rack rails on network equipment

2021-09-25 Thread Joe Greco
On Sat, Sep 25, 2021 at 04:23:38PM -0700, Jay Hennigan wrote: > On 9/25/21 16:14, George Herbert wrote: > >(Crying, thinking about racks and racks and racks of AT 56k modems > >strapped to shelves above PM-2E-30s???) > > And all of their wall-warts [...] You were doing it wrong, then. :-)

Re: Rack rails on network equipment

2021-09-25 Thread Jay Hennigan
On 9/25/21 16:14, George Herbert wrote: (Crying, thinking about racks and racks and racks of AT 56k modems strapped to shelves above PM-2E-30s…) And all of their wall-warts and serial cables The early 90s were a dangerous place, man. Yes, but the good news is that shortly thereafter

Re: Rack rails on network equipment

2021-09-25 Thread George Herbert
(Crying, thinking about racks and racks and racks of AT 56k modems strapped to shelves above PM-2E-30s…) The early 90s were a dangerous place, man. -George Sent from my iPhone > On Sep 24, 2021, at 8:05 PM, Wayne Bouchard wrote: > > Didn't require any additional time at all when equipment

Re: Rack rails on network equipment

2021-09-25 Thread Shawn L via NANOG
Why about thinks like the Cisco 4500 switch series that are almost as long as a 1u server. But yet only has mounts for a relay type rack. As far as boot times, try a Asr920. Wait 15 minutes and decide if it’s time to power cycle again or wait 5 more minutes Sent from my iPhone > On Sep

Re: Rack rails on network equipment

2021-09-25 Thread Michael Thomas
On 9/25/21 2:08 PM, Jay Hennigan wrote: On 9/25/21 13:55, Baldur Norddahl wrote: My personal itch is how new equipment seems to have even worse boot time than previous generations. I am currently installing juniper acx710 and while they are nice, they also make me wait 15 minutes to boot.

Re: Rack rails on network equipment

2021-09-25 Thread Brandon Butterworth
On Sat Sep 25, 2021 at 12:48:38PM -0700, Andrey Khomyakov wrote: > We are looking at Nvidia (former Mellanox) switches If I was going to rule any out based on rails it'd be their half width model. Craziest rails I've seen. It's actually a frame that sits inside the rack rails so you need qu

Re: Rack rails on network equipment

2021-09-25 Thread Owen DeLong via NANOG
> On Sep 25, 2021, at 12:48 , Andrey Khomyakov > wrote: > Let me just say from the get go that no one is making toolless rails a > priority to the point of shutting vendors out of the evaluation process. I am > not quite sure why that assumption was made by at least a few folks. With >

Re: Rack rails on network equipment

2021-09-25 Thread Jay Hennigan
On 9/25/21 13:55, Baldur Norddahl wrote: My personal itch is how new equipment seems to have even worse boot time than previous generations. I am currently installing juniper acx710 and while they are nice, they also make me wait 15 minutes to boot. This is a tremendous waste of time during

Re: Rack rails on network equipment

2021-09-25 Thread Baldur Norddahl
The "niceness" of equipment does factor in but it might be invisible. For example if you like junipers cli environment, you will look at their stuff first even if you do not have it explicitly in your requirement list. Better rack rails will make slightly more people prefer your gear

Re: Rack rails on network equipment

2021-09-25 Thread Andrey Khomyakov
Well, folks, the replies have certainly been interesting. I did get my answer, which seems to be "no one cares", which, in turn, explains why network equipment manufacturers give very little to no attention to this problem. A point of clarification is I'm talking about the problem in the context

Re: Rack rails on network equipment

2021-09-25 Thread ic
Hi, > On 24 Sep 2021, at 12:37, Andrey Khomyakov wrote: > > (you know, where most of your server ports are…) Port side intake (switch at the front of the rack) is generally better for cooling the optical modules. The extra cabling difficulty is worth it. Also, as others said, choosing an

Re: Rack rails on network equipment

2021-09-25 Thread Sabri Berisha
- On Sep 24, 2021, at 11:19 AM, William Herrin b...@herrin.us wrote: Hi, > Seriously, the physical build of network equipment is not entirely > competent. Except, sometimes there is little choice. Look at 400G QSFP-DD for example. Those optics can generate up to 20 watts of heat that needs

Re: Rack rails on network equipment

2021-09-24 Thread Bryan Fields
On 9/24/21 10:58 PM, Owen DeLong via NANOG wrote: > Meh… Turn off power supply input switch, open chassis carefully, apply > high-wattage 1Ω resistor across capacitor terminals for 10 seconds. > If dealing with a charged capacitor, do not use a low resistance such as a ohm. This is the same as

Re: Rack rails on network equipment

2021-09-24 Thread Wayne Bouchard
Didn't require any additional time at all when equipment wasn't bulky enough to need rails in the first place I've never been happy about that change. On Fri, Sep 24, 2021 at 09:37:58AM -0700, Andrey Khomyakov wrote: > Hi folks, > Happy Friday! > > Would you, please, share your thoughts

Re: Rack rails on network equipment

2021-09-24 Thread Owen DeLong via NANOG
> On Sep 24, 2021, at 3:35 PM, Niels Bakker wrote: > > * c...@cmadams.net (Chris Adams) [Sat 25 Sep 2021, 00:17 CEST]: >> Which - why do I have to order different part numbers for back to front >> airflow? It's just a fan, can't it be made reversible? Seems like that >> would be cheaper

Re: Rack rails on network equipment

2021-09-24 Thread Martin Hannigan
On Fri, Sep 24, 2021 at 1:34 PM Jay Hennigan wrote: > On 9/24/21 09:37, Andrey Khomyakov wrote: > > > *So ultimately my question to you all is how much do you care about the > > speed of racking and unracking equipment and do you tell your suppliers > > that you care? How much does the time it

Re: Rack rails on network equipment

2021-09-24 Thread Chris Adams
Once upon a time, Niels Bakker said: > * c...@cmadams.net (Chris Adams) [Sat 25 Sep 2021, 00:17 CEST]: > >Which - why do I have to order different part numbers for back to > >front airflow? It's just a fan, can't it be made reversible? > >Seems like that would be cheaper than stocking alternate

Re: Rack rails on network equipment

2021-09-24 Thread William Herrin
On Fri, Sep 24, 2021 at 3:36 PM Niels Bakker wrote: > * c...@cmadams.net (Chris Adams) [Sat 25 Sep 2021, 00:17 CEST]: > >Which - why do I have to order different part numbers for back to > >front airflow? It's just a fan, can't it be made reversible? Seems > >like that would be cheaper than

Re: Rack rails on network equipment

2021-09-24 Thread Niels Bakker
* c...@cmadams.net (Chris Adams) [Sat 25 Sep 2021, 00:17 CEST]: Which - why do I have to order different part numbers for back to front airflow? It's just a fan, can't it be made reversible? Seems like that would be cheaper than stocking alternate part numbers. The fan is inside the power

Re: Rack rails on network equipment

2021-09-24 Thread Chris Adams
Once upon a time, William Herrin said: > I care, but it bothers me less that the inconsiderate air flow > implemented in quite a bit of network gear. Side cooling? Pulling air > from the side you know will be facing the hot aisle? Seriously, the > physical build of network equipment is not

Re: Rack rails on network equipment

2021-09-24 Thread Joe Maimon
Andrey Khomyakov wrote: Hi folks, Happy Friday! Interesting tidbit is that we actually used to manufacture custom rails for our Juniper EX4500 switches so the switch can be actually inserted from the back of the rack (you know, where most of your server ports are...) and not be blocked

Re: Rack rails on network equipment

2021-09-24 Thread George Herbert
I’ve seen Dell rack equipment leap for safety (ultimately very very unsuccessfully…) in big earthquakes. Lots of rack screws for me. -George Sent from my iPhone > On Sep 24, 2021, at 9:41 AM, Andrey Khomyakov > wrote: > >  > Hi folks, > Happy Friday! > > Would you, please, share your

Re: Rack rails on network equipment

2021-09-24 Thread Joe Greco
On Fri, Sep 24, 2021 at 02:49:53PM -0500, Doug McIntyre wrote: > You mention about hardware lockin, but I wouldn't trust Dell to not switch > out the design on their "next-gen" product, when they buy from a > different OEM, as they are want to do, changing from OEM to OEM for > each new product

Re: Rack rails on network equipment

2021-09-24 Thread Doug McIntyre
On Fri, Sep 24, 2021 at 09:37:58AM -0700, Andrey Khomyakov wrote: > We selected Dell switches in part due > to Dell using "quick rails'' (sometimes known as speed rails or toolless > rails). Hmm, I haven't had any of those on any of my Dell switches, but then again, I haven't bought in in

Re: Rack rails on network equipment

2021-09-24 Thread Randy Carpenter
Considering that the typical $5 pieces of bent metal list for ~$500 from most vendors, can you imagine the price of fancy tool-less rack kits? Brand new switch: $2,000 Rack kit: $2,000 -Randy

RE: Rack rails on network equipment

2021-09-24 Thread Kevin Menzel via NANOG
Of Andrey Khomyakov Sent: September 24, 2021 12:38 To: Nanog Subject: Rack rails on network equipment This message was sent from outside of Sheridan College. Please be careful when opening attachments, clicking links, or responding to requests for information. Hi folks, Happy Friday! Would you

Re: Rack rails on network equipment

2021-09-24 Thread Alain Hebert
    Hi,     In my opinion:         That time you take to rack devices with classic rail can be viewed as a bounding moment and, while appreciated by the device, will reducing downtime issues on the long run that you may have if you just rack & slap 'em.     It is also Friday =D. -

Re: Rack rails on network equipment

2021-09-24 Thread richey goldberg
. The amount of time required to do the initial install is insignificant in the grand scheme of things. -richey From: NANOG on behalf of Andrey Khomyakov Date: Friday, September 24, 2021 at 12:38 PM To: Nanog Subject: Rack rails on network equipment Hi folks, Happy Friday! Would you

Re: Rack rails on network equipment

2021-09-24 Thread Mauricio Rodriguez via NANOG
Andrey, hi. The speed rails are nice, and are effective in optimizing the time it takes to rack equipment. It's pretty much par for the course on servers today (thank goodness!), and not so much on network equipment. I suppose the reasons being what others have mentioned - longevity of service

Re: Rack rails on network equipment

2021-09-24 Thread William Herrin
On Fri, Sep 24, 2021 at 9:39 AM Andrey Khomyakov wrote: > Interesting tidbit is that we actually used to manufacture custom rails for > our Juniper EX4500 switches so the switch can be actually inserted from the > back of the rack (you know, where most of your server ports are...) and not > be

Re: Rack rails on network equipment

2021-09-24 Thread Denis Fondras
> You mention a 25-minute difference between racking a no-tools rail kit and > one that requires a screwdriver. At any reasonable hourly rate for someone > to rack and stack that is a very small percentage of the cost of the > hardware. If a device that takes half an hour to rack is $50 cheaper

Re: Rack rails on network equipment

2021-09-24 Thread Jay Hennigan
On 9/24/21 09:37, Andrey Khomyakov wrote: *So ultimately my question to you all is how much do you care about the speed of racking and unracking equipment and do you tell your suppliers that you care? How much does the time it takes to install or replace a switch impact you?* Very little. I

Re: Rack rails on network equipment

2021-09-24 Thread Brandon Butterworth
On Fri Sep 24, 2021 at 09:37:58AM -0700, Andrey Khomyakov wrote: > As far as I know, Dell is the only switch vendor doing toolless rails Having fought for hours trying to get servers with those rails into some DCs racks I'd go with slightly slow but fits everywhere > *So ultimately my question

Re: Rack rails on network equipment

2021-09-24 Thread Grant Taylor via NANOG
On 9/24/21 10:37 AM, Andrey Khomyakov wrote: So ultimately my question to you all is how much do you care about the speed of racking and unracking equipment and do you tell your suppliers that you care? How much does the time it takes to install or replace a switch impact you? I was having a

Re: Rack rails on network equipment

2021-09-24 Thread Mel Beckman
We don’t care. We rack up switches maybe once or twice a year. It’s just not worth the effort to streamline. If we were installing dozens of switches a month, maybe. But personally I think it’s crazy to make rackability your primary reason for choosing a switch vendor. Do you base your

Rack rails on network equipment

2021-09-24 Thread Andrey Khomyakov
Hi folks, Happy Friday! Would you, please, share your thoughts on the following matter? Back some 5 years ago we pulled the trigger and started phasing out Cisco and Juniper switching products out of our data centers (reasons for that are not quite relevant to the topic). We selected Dell

Re: rack rails

2020-03-31 Thread Baldur Norddahl
's > adapters and things, but they're a pain as well. At least with a 4-post > square-hole rack you can get 80% of what you want to fit. > > > -----Original Message- > From: "Coy Hile" > Sent: Monday, March 30, 2020 5:31pm > To: "Karsten Elfenbein"

Re: rack rails

2020-03-30 Thread Shawn L via NANOG
tyle rack and put them in a 2-post neatly. There's adapters and things, but they're a pain as well. At least with a 4-post square-hole rack you can get 80% of what you want to fit. -Original Message- From: "Coy Hile" Sent: Monday, March 30, 2020 5:31pm To: "Karsten Elfe

Re: rack rails

2020-03-30 Thread Ben Cannon
2-post racks (typically 23" not 19” however 19 is making a dent) are still very common in MPOE rooms and OSP plant termination.Minimal space consumption is the prime reason. Frankly most fiber patch panels are a foot deep and DWDM gear has been designed to be that profile too. Many

Re: rack rails

2020-03-30 Thread Coy Hile
> On Mar 30, 2020, at 5:24 PM, Karsten Elfenbein > wrote: > > Hi, > > something like https://www.opencompute.org/projects/rack-and-power > comes into my mind for that. > Mounting on 4 posts should be the default. It is insane what some > vendors want to mount on 2 posts only. > That

Re: rack rails

2020-03-30 Thread Karsten Elfenbein
Hi, something like https://www.opencompute.org/projects/rack-and-power comes into my mind for that. Mounting on 4 posts should be the default. It is insane what some vendors want to mount on 2 posts only. Regards, Karsten Am Mo., 30. März 2020 um 19:46 Uhr schrieb Baldur Norddahl : >> >> > > I

Re: rack rails

2020-03-30 Thread Baldur Norddahl
> > > I have considered making my own rails using a laser cutting service. I have done this before where I created 500 mm to 19 inch rack adapters and had them laser cut at lasergist.com. Fairly simple really, just make a drawing in Fusion360 and upload the drawing. A few days later the adapters

Re: rack rails

2020-03-30 Thread Luke Guillory
Not sure to be honest, I see the following though which may work just not sure how thin this one is. I noticed in the DOCs it says not to use if placing directly on top of another device, which you could assume might mean it's too thick. BTI7801 Chassis Support Bracket Kit (BT8A78SSB3)

Re: [EXT] Re: rack rails

2020-03-30 Thread Chuck Anderson
On Mon, Mar 30, 2020 at 07:09:48PM +0300, Nitzan Tzelniker wrote: > We tried to flip the sides of rails in QFX5120 and it cause two problems > that prevent us from keeping it this way > 1. The switch was 2 cm from the rear post line > 2. The switch vibrate as you can see in the video >

Re: [EXT] Re: rack rails

2020-03-30 Thread Nitzan Tzelniker
We tried to flip the sides of rails in QFX5120 and it cause two problems that prevent us from keeping it this way 1. The switch was 2 cm from the rear post line 2. The switch vibrate as you can see in the video https://photos.app.goo.gl/WQwcE9vcPjSiEi9N9 Nitzan On Mon, Mar 30, 2020 at 6:54 PM

Re: [EXT] Re: rack rails

2020-03-30 Thread Tore Anderson
* Cummings, Chris > Now that you say that, I think you're right. I am referring specifically to > the EX4650 and they are the cheesy type where the rear half of the rail stays > screwed in to the rack and the front half of the rail is attached to the > switch. I assume it is the same on the

Re: [EXT] Re: rack rails

2020-03-30 Thread Chuck Anderson
On Mon, Mar 30, 2020 at 05:27:44PM +0200, Tore Anderson wrote: > * Chuck Anderson > > > The point is that the switches need to be removable without empty > > space above/below, and ideally from the rear side of the rack. By > > having extending/sliding rails, you can lift out or drop in the

Re: [EXT] Re: rack rails

2020-03-30 Thread Cummings, Chris
Now that you say that, I think you're right. I am referring specifically to the EX4650 and they are the cheesy type where the rear half of the rail stays screwed in to the rack and the front half of the rail is attached to the switch. I assume it is the same on the QFX since they are very

Re: [EXT] Re: rack rails

2020-03-30 Thread Chuck Anderson
On Mon, Mar 30, 2020 at 03:15:54PM +, Cummings, Chris wrote: > Juniper's ToR switches have slide in rails. They are a bit frustrating > compared to Dell easy rails, but they do the trick. You can slide the switch in/out while attached securely to the rails? That is news to me and my QFX5k

Re: [EXT] Re: rack rails

2020-03-30 Thread Tore Anderson
* Chuck Anderson > The point is that the switches need to be removable without empty > space above/below, and ideally from the rear side of the rack. By > having extending/sliding rails, you can lift out or drop in the switch > after you slide it out. Then you can remove the rails. > > With

Re: [EXT] Re: rack rails

2020-03-30 Thread Ethan O'Toole
I've been asking manufacturers for proper server-like slide-rails for their switches for years. Now they've started making the switches as deep or even deeper than servers, but they still use the same old rack ear mounting method. The Arista 4 post rack kits are pretty good. Toolless as

Re: rack rails

2020-03-30 Thread Cummings, Chris
Juniper's ToR switches have slide in rails. They are a bit frustrating compared to Dell easy rails, but they do the trick. -- Chris On 3/30/20, 10:14, "NANOG on behalf of Tore Anderson" wrote: * Luke Guillory > I've had gear that came with a small rear support shelf that didn't

Re: [EXT] Re: rack rails

2020-03-30 Thread Chuck Anderson
On Mon, Mar 30, 2020 at 10:09:25AM -0500, Chris Adams wrote: > Once upon a time, Chuck Anderson said: > > I've been asking manufacturers for proper server-like slide-rails for their > > switches for years. Now they've started making the switches as deep or > > even deeper than servers, but

Re: rack rails

2020-03-30 Thread Tore Anderson
* Luke Guillory > I've had gear that came with a small rear support shelf that didn't had to > the height, RGB Networks BNPs for example. I'm pretty sure we've used these > with the BNPs one on top of the other. > > Page 16 in this PDF shows the shelf. > >

Re: [EXT] Re: rack rails

2020-03-30 Thread Chris Adams
Once upon a time, Chuck Anderson said: > I've been asking manufacturers for proper server-like slide-rails for their > switches for years. Now they've started making the switches as deep or even > deeper than servers, but they still use the same old rack ear mounting method. Maybe it's

Re: rack rails

2020-03-30 Thread Luke Guillory
I've had gear that came with a small rear support shelf that didn't had to the height, RGB Networks BNPs for example. I'm pretty sure we've used these with the BNPs one on top of the other. Page 16 in this PDF shows the shelf.

Re: [EXT] Re: rack rails

2020-03-30 Thread Chuck Anderson
On Mon, Mar 30, 2020 at 04:18:18PM +0200, Tore Anderson wrote: > When a rack has been filled up, removal/insertion through the rear will often > be essentially impossible due to cables, vertical PDUs and stuff like that > that gets in the way. > > Explained in pictures here: >

Re: rack rails

2020-03-30 Thread Tore Anderson
* David Funderburk > 2 - Do you know of any universal rail kits for 1U, 2U and 3U servers, > routers, switches that work well?  The brand names are nice but expensive. > Thought I'd explore some cheaper options first. We use a lot of MikroTik, HP, > Dell and some CISCO with a few other things

Re: rack rails

2020-03-30 Thread Blake Hudson
. --Blake On 3/30/2020 7:14 AM, David Funderburk wrote: 1 - We now have some time on our hands to do some things in our storage area which includes identifying  a # of rack rails found in a box. Does anyone have any tips or tricks for identifying what equipment rails might match? 2 - Do you

rack rails

2020-03-30 Thread David Funderburk
1 - We now have some time on our hands to do some things in our storage area which includes identifying a # of rack rails found in a box. Does anyone have any tips or tricks for identifying what equipment rails might match? 2 - Do you know of any universal rail kits for 1U, 2U and 3U servers