Thanks for your help.

   From: Charles Lepple <clep...@gmail.com>
   Date: Mon, 18 Dec 2017 19:26:56 -0500

   This may sound like an apples-to-oranges comparison, but we did uncover an 
issue with CyberPower UPSes where the delay values needed to be greater than or 
equal to 60 (seconds), since they were being rounded down to integer numbers of 
minutes internally:

   What was the largest delay you tried?

I have now tried 200 seconds without any change.  The offdelay setting
does appear in the status as ups.delay.shutdown, but seems to have no effect.

   > ups.timer.reboot: 65535
   > ups.timer.shutdown: 65535
   > 

   I seem to remember that these values should change to e.g. -60 if you
   set the delay to 60, and then they should begin counting down after
   the shutdown command is sent. It has been a while since I messed with
   that code, though.

No matter what settings I use, the UPS seems to turn off the load
immediately in response to the shutdown command.  I have never seen
ups.timer.shutdown change from the value above.  After shutting off the
load, ups.timer.reboot changes to 10, regardless of the setting of
driver.parameter.ondelay.  It then counts down to 0 and turns the load
back on.

   What log messages do you get with "/lib/nut/usbhid-ups -DD -a
   bcpers450 -k"?

See below.

   For future reference, was this UPS manufactured recently? 

I have just purchased it new, so presumably yes.

                                        Ken

----------------------------------------------------------------------

# /lib/nut/usbhid-ups -DD -a bcpers450 -k
Network UPS Tools - Generic HID driver 0.38 (2.7.2)
USB communication driver 0.32
   0.000000     debug level is '2'
   0.000852     upsdrv_initups...
   0.014448     Checking device (1D6B/0003) (002/001)
   0.030206     - VendorID: 1d6b
   0.030219     - ProductID: 0003
   0.030239     - Manufacturer: unknown
   0.030242     - Product: unknown
   0.030246     - Serial Number: unknown
   0.030249     - Bus: 002
   0.030253     Trying to match device
   0.030259     Device does not match - skipping
   0.030304     Checking device (09AE/2010) (001/009)
   0.034107     - VendorID: 09ae
   0.034120     - ProductID: 2010
   0.034122     - Manufacturer: Tripp Lite 
   0.034153     - Product: Tripp Lite UPS 
   0.034156     - Serial Number: unknown
   0.034159     - Bus: 001
   0.034162     Trying to match device
   0.034179     Device matches
   0.034195     failed to claim USB device: could not claim interface 0: Device 
or resource busy
   0.034209     detached kernel driver from USB device...
   0.035773     HID descriptor length 613
   0.054980     Report Descriptor size = 613
   0.055190     Using subdriver: TrippLite HID 0.81
   0.055810     Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, 
Offset: 0, Size: 8, Value: 2
   0.056434     Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 
0x29, Offset: 0, Size: 8, Value: 3
   0.056913     Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 
0x2b, Offset: 0, Size: 8, Value: 1
   0.057431     Path: UPS.PowerSummary.ffff00d9, Type: Feature, ReportID: 0xc0, 
Offset: 0, Size: 8, Value: 5
   0.057855     Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, 
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.058533     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.059163     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
   0.059667     Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 
0x33, Offset: 0, Size: 8, Value: 2
   0.060193     Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 
0x2c, Offset: 0, Size: 8, Value: 1
   0.060733     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 
0x35, Offset: 0, Size: 16, Value: 5740
   0.060755     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 
0x35, Offset: 0, Size: 16, Value: 5740
   0.061271     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.061291     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.061896     Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, 
ReportID: 0x37, Offset: 0, Size: 8, Value: 100
   0.062368     Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 
0x36, Offset: 0, Size: 8, Value: 100
   0.062904     Path: UPS.PowerSummary.PresentStatus.Voltage, Type: Feature, 
ReportID: 0x31, Offset: 0, Size: 16, Value: 0
   0.063470     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: 
Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
   0.063512     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, 
ReportID: 0x32, Offset: 1, Size: 1, Value: 0
   0.063539     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x32, Offset: 2, Size: 1, Value: 0
   0.063558     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, 
ReportID: 0x32, Offset: 3, Size: 1, Value: 1
   0.063577     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
   0.063595     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x32, Offset: 5, Size: 1, Value: 0
   0.063616     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, 
ReportID: 0x32, Offset: 6, Size: 1, Value: 1
   0.063636     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: 
Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.063657     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: 
Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
   0.063679     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, 
ReportID: 0x32, Offset: 1, Size: 1, Value: 0
   0.063703     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, 
ReportID: 0x32, Offset: 2, Size: 1, Value: 0
   0.063727     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 1
   0.063749     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
   0.063769     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
ReportID: 0x32, Offset: 5, Size: 1, Value: 0
   0.063792     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
   0.063814     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: 
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.064263     Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, 
ReportID: 0x04, Offset: 0, Size: 16, Value: 12
   0.064738     Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: 
Feature, ReportID: 0x23, Offset: 0, Size: 1, Value: 0
   0.064761     Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, 
Type: Feature, ReportID: 0x23, Offset: 1, Size: 1, Value: 1
   0.064782     Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, 
Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
   0.065251     Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, 
Offset: 0, Size: 8, Value: 0
   0.065790     Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, 
Offset: 0, Size: 8, Value: 120
   0.066320     Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, 
Offset: 0, Size: 8, Value: 60
   0.066955     Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 
0x03, Offset: 0, Size: 16, Value: 450
   0.067583     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: 
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.068231     Path: UPS.OutletSystem.Outlet.ffff00bc, Type: Feature, 
ReportID: 0xe0, Offset: 0, Size: 16, Value: 0
   0.068757     Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, 
ReportID: 0x51, Offset: 0, Size: 8, Value: 1
   0.069251     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, 
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.069779     Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, 
ReportID: 0xb6, Offset: 0, Size: 8, Value: 1
   0.070327     Path: UPS.TLCustom.[1].CommunicationProtocolVersion, Type: 
Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 8208
   0.070953     Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID: 0x96, 
Offset: 0, Size: 8, Value: 255
   0.071418     refresh_report_buffer: expected 5 bytes, but got 2 instead
   0.071462     Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID: 0xb4, 
Offset: 0, Size: 32, Value: 255
   0.072034     refresh_report_buffer: expected 5 bytes, but got 2 instead
   0.072077     Path: UPS.ffff0015.[1].ffff00d3, Type: Feature, ReportID: 0xb5, 
Offset: 0, Size: 32, Value: 255
   0.072671     Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID: 0x97, 
Offset: 0, Size: 16, Value: 255
   0.073152     Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID: 0x98, 
Offset: 0, Size: 8, Value: 255
   0.073668     Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID: 0x99, 
Offset: 0, Size: 16, Value: 255
   0.078695     Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID: 0x9b, 
Offset: 0, Size: 16, Value: 3
   0.079245     Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID: 0xc2, 
Offset: 0, Size: 32, Value: 14
   0.079703     libusb_get_report: could not claim interface 0: Device or 
resource busy
   0.079755     Can't retrieve Report c1: Device or resource busy
   0.079781     Path: UPS.ffff0015.[1].ffff00d8, Type: Feature, ReportID: 0xc1, 
Offset: 0, Size: 32
   0.080340     Path: UPS.ffff0015.[1].ffff00d7, Type: Feature, ReportID: 0xc3, 
Offset: 0, Size: 32, Value: 1
   0.080865     libusb_get_report: could not claim interface 0: Device or 
resource busy
   0.080897     Can't retrieve Report 9a: Device or resource busy
   0.080919     Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, 
Offset: 0, Size: 32
   0.081587     Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, 
ReportID: 0x20, Offset: 0, Size: 16, Value: 124
   0.082168     Path: UPS.PowerConverter.Input.Voltage, Type: Feature, 
ReportID: 0x18, Offset: 0, Size: 16, Value: 0
   0.082724     Path: UPS.PowerConverter.Input.Frequency, Type: Feature, 
ReportID: 0x19, Offset: 0, Size: 16, Value: 0
   0.083265     Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: 
Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 1
   0.083304     Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, 
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.083327     Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, 
ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.083349     Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, 
ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.083368     Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, 
ReportID: 0x22, Offset: 5, Size: 1, Value: 0
   0.083388     Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: 
Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.083408     Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: 
Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.083427     Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: 
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.083917     Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, 
ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.083952     Report descriptor retrieved (Reportlen = 613)
   0.083962     Found HID device
   0.083975     Detected a UPS: Tripp Lite /Tripp Lite UPS 
   0.084049     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.084108     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 
0x35, Offset: 0, Size: 16, Value: 5740
   0.084137     Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, 
ReportID: 0x04, Offset: 0, Size: 16, Value: 12
   0.084166     Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, 
ReportID: 0x20, Offset: 0, Size: 16, Value: 124
   0.084196     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
   0.085345     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: 
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.085377     Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, 
ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.085404     Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, 
Offset: 0, Size: 8, Value: 0
   0.085426     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.085453     Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 
0x03, Offset: 0, Size: 16, Value: 450
   0.085507     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, 
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.085546     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: 
Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
   0.085573     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, 
ReportID: 0x32, Offset: 1, Size: 1, Value: 0
   0.085598     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
ReportID: 0x32, Offset: 5, Size: 1, Value: 0
   0.085623     Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: 
Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
   0.085648     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, 
ReportID: 0x32, Offset: 2, Size: 1, Value: 0
   0.085672     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 1
   0.085696     Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: 
Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.085720     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
   0.085770     Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: 
Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 1
   0.085795     Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, 
ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.085819     Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, 
ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.085843     Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, 
ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.085866     Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: 
Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.085890     Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: 
Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.085913     Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: 
Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.085937     Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, 
ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.085972     Path: UPS.PowerConverter.Input.Voltage, Type: Feature, 
ReportID: 0x18, Offset: 0, Size: 16, Value: 0
   0.085997     Path: UPS.PowerConverter.Input.Frequency, Type: Feature, 
ReportID: 0x19, Offset: 0, Size: 16, Value: 0
   0.086053     Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, 
Offset: 0, Size: 8, Value: 120
   0.086094     Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, 
Offset: 0, Size: 8, Value: 60
   0.090270     Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, 
Offset: 0, Size: 8, Value: 0
   0.090329     Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, 
Offset: 0, Size: 8, Value: 0
   0.090349     Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, 
Offset: 0, Size: 8, Value: 0
   0.090375     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: 
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.090407     Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: 
Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.090426     Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, 
ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.090443     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, 
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.090458     Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, 
ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.090477     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.090493     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.090508     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.090523     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.090539     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.090564     find_nut_info: unknown info type: load.on.delay
   0.090577     find_nut_info: unknown info type: load.on.delay
   0.090585     Initiating UPS shutdown
   0.090593     upsdrv_shutdown...
   0.090601     instcmd(shutdown.return, [NULL])
   0.090614     find_nut_info: unknown info type: shutdown.return
   0.090624     instcmd(load.on.delay, [NULL])
   0.090633     find_nut_info: unknown info type: load.on.delay
   0.090641     instcmd: info element unavailable load.on.delay

   0.090649     instcmd(shutdown.reboot, [NULL])
   0.091107     upsdrv_cleanup...