Wrenchers,
What's the deal with mixing AC and DC conductors in a raceway? The job in
question has a 6x6 wireway under the inverters. Conductors will have their
own conduits but is it ok for them to share the wireway?
Thanks in advance for clarification on this,
Nik
--
Nicholas Ponzio
Building
No problem, so long as the insulation is rated for the highest
voltage conductor. Conductors of other systems (like premise wiring)
can not be in the raceway.
At 07:02 AM 9/24/2009, you wrote:
Wrenchers,
What's the deal with mixing AC and DC conductors in a raceway? The
job in question has
Hello Wrenches,
Typical PV modules installation instructions show modules being
supported with two supports each spaced 25% of module length in from
the short edge of the module. I'm looking for information on PV
modules which can be supported on a mounting structure using only the
short edge of
Nik, we always use 4x4 gutters when ever possible - keeps things clean and neat
- as long as insulation voltage rating is same on all wires and wires are
bundled (AC and DC - tie wraps or tape) and it's all from the same system
(house wiring is another system) then it's OK...
Max
some sharp modules, not all.
--- On Thu, 9/24/09, swingjunkie swingjun...@gmail.com wrote:
From: swingjunkie swingjun...@gmail.com
Subject: [RE-wrenches] Modules Supported only at Short End
To: RE-wrenches@lists.re-wrenches.org
Date: Thursday, September 24, 2009, 10:23 AM
Hello Wrenches,
Bundling is a good idea, I to that too. But where does it say we
have to do it?
At 09:43 AM 9/24/2009, you wrote:
Nik, we always use 4x4 gutters when ever possible - keeps things
clean and neat - as long as insulation voltage rating is same on all
wires and wires are bundled (AC and DC - tie
I am not aware of any type of installation where the NEC would require
bundling in a gutter. I have seen some non-metallic raceways with built-in
partitions for low-voltage and line-voltage wiring, but of course this type
of product wouldn't be applicable for the AC/DC separation you're looking
Hi Darryl,
For what it's worth, the '08 Handbook explains regarding 690.4(B):
For example, 690.4(B) does not permit the conductors supplying an
exterior luminaire located in close proximity to a roof-mounted PV array
to be installed in the same raceway or conductors of of PV sources
On this one we can give John Wiles some credit. He was the only one years
ago to interpret that section (690.4) as preventing, say, running landscape
lighting in the same conduit as PV array wiring. He didn't make any
distinction between PV source and output circuits, or between DC and AC
current
Thanks, but I am still concerned, the Handbook is not the code. In wire ways
it is possible to include a divider, and pass the conduit from one source
through the top half of the wire way and terminate in the lower half. Still
neat, and yes we have had AHJ demand that separation.
Darryl
---