Ok, I'll bite.First, some diffnitions.. from Delmer's Standard (ISBN-13: 978-1-4180-6580-5):Apparent Power (VA) is the value found by multiplying the applied voltage by the total current of an AC circuit. Apparent power is measured in volt-amps (VA) and should not be confused with true power,

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Square-D tells me they have tested the breakers to a higher voltage (can't recall now whether it was 80V or 125 VDC) but the listing is indeed for 48 Volts. 24V battery systems are useful for a lot of applications, but the unfortunate lack of a 5A breaker means we can not use them to derive a

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Voltage is not the issue here, it is current, and battery fault currents can be staggering - far more than one would ever encounter in a typical AC system fed from a distribution transformer. I have seen a 200A Class T fail to act on an 48V inverter fault which resulted in welding the metal

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread Kurt Albershardt
Small (QO or Airpax-type) breakers in a distribution bank should be front ended with a suitable DC master breaker or fuse that has the capability to interrupt the available fault current. Ideally, the series combination should be rated but at a minimum, a coordination study should be

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread R Ray Walters
My understanding was that the din mountable QOU breakers were rated to 125 vDC, and are internally the same as the QO. The difference was the connectors, and the mounting method. I've used the QOUs reliably at 120 v nom on an EV, (but don't try this at home, kids) We still use the QOs sometimes

[RE-wrenches] Solmetric Suneye 210

2010-05-16 Thread Marco Mangelsdorf
Has anyone had any experience with the fairly new Solmetric Suneye 210 shading analysis tool? Feedback and observations? Or how about with their earlier version the Suneye 110? Thanks, marco provision_highres_solar_logo2 with C-26351 Marco Mangelsdorf, President 69 Railroad

Re: [RE-wrenches] AC breakers used in DC applications

2010-05-16 Thread William Miller
Kurt Fascinating story and valuable information. This is the kind of real world experience we need to draw on. Reality can change quickly under extreme conditions and one's education is not complete without this understanding. Thanks for this post. William Miller PS: You are fortunate