Re: [RE-wrenches] Lightning protection (was Delta LA's)

2010-09-15 Thread Darryl Thayer
If you are doing Off Grid is it enough just to drive two ground rods?  and make a connection between them?  Also what is the lowest Ohm reading your DGC 1000 meter can read? Thanks  --- On Wed, 9/15/10, R Ray Walters r...@solarray.com wrote: From: R Ray Walters r...@solarray.com Subject: Re:

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread Brian Mehalic
According to the Enphase website (/support/faqs): The Enphase Microinverter manual states that the device is positively grounded. Don't most PV modules have negative grounds? Is this a problem for Enphase? Enphase made the decision to positively ground its microinverters to minimize corrosion.

Re: [RE-wrenches] Lightning protection (was Delta LA's)

2010-09-15 Thread R Ray Walters
2 electrodes lets you off the hook for NEC, but not with the lightning hurling gods. New Mexico code has actually dropped the 2 rod rule as well, you have to install a Ufer ground in all new construction there. WIth dry rocky soil, your impedance with 2 rods can still be hundreds of Ohms. The

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread Nick Soleil
Yes, Enphase bonds the DC positive to ground in their inverters. This allows them to work with all modules, including SunPower. Nick Soleil Project Manager Advanced Alternative Energy Solutions, LLC PO Box 657 Petaluma, CA 94953 Cell: 707-321-2937 Office: 707-789-9537 Fax:707-769-9037

Re: [RE-wrenches] Accessable?

2010-09-15 Thread Andrew Truitt
Benn - I like installing j-boxes under the array as a general rule both for aesthetics and to keep them somewhat sheltered from the elements. I do not see any code issues with the location because, as you mention, they are still accessible. From NEC2008 Article 100: *Accessible (as applied to

Re: [RE-wrenches] Accessable?

2010-09-15 Thread Dave Click
And more specifically: 690.34 Access to Boxes. Junction, pull, and outlet boxes located behind modules or panels shall be so installed that the wiring contained in them can be rendered accessible directly or by displacement of a module(s) or panel(s) secured by removable fasteners and

Re: [RE-wrenches] On Demand Heaters for SDHW

2010-09-15 Thread Kristopher Schmid
Bill and Peter, I stand corrected. Tankless units do not modulate to zero. What a shame. My Takagi needs AC power to the exhaust fan in order to operate. I will be installing an aquastat relay on my solar storage tank that removes power to the Takagi when the solar tank is at or above 110

Re: [RE-wrenches] Delta LA's in or out? It's our choice.

2010-09-15 Thread Dave Palumbo
Bill, I checked with Delta and they say the LA's are designed to be mounted inside, or, outside the box. On their product sheets that came with the arrestors in years past they clearly showed the LA's inside the load center. In fact that is the way they are still showing them used on their

Re: [RE-wrenches] Accessable?

2010-09-15 Thread benn kilburn
Hey thanks for the feedback. Looks like the definition of accessible is pretty much the same for the CEC and NEC, and NEC's 690.34 gives this method the go-ahead. DayStar Renewable Energy Inc. b...@daystarsolar.ca780-906-7807 HAVE A SUNNY DAY Date: Wed, 15 Sep 2010 12:28:49 -0400 From:

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread Richard L Ratico
Brian, A GEC with no splices, or only irreversable splices, has only two ends. If you need to find them to check their integrity, you know where to look. No argument about acorn clamps. Exothermic welding might someday be required. Dick Ratico Solarwind Electric --- You wrote: Inspectors in

Re: [RE-wrenches] GEC for Enphase inverters

2010-09-15 Thread jay peltz
Hi Nick, Last time I checked Evergreen modules don't work with positive ground systems. jay peltz power On Sep 15, 2010, at 9:19 AM, Nick Soleil wrote: Yes, Enphase bonds the DC positive to ground in their inverters. This allows them to work with all modules, including SunPower. Nick

Re: [RE-wrenches] Delta LA's in or out? It's our choice.

2010-09-15 Thread Dave Click