Client gave me the float readings from the MX and they look ok but there's been
no float in the last couple of weeks. I've been thinking an electrical contact
problem either inside the E-panel, the inverter or the battery causing the
unexplained voltage drop. Brian and Mark you may be spot on. I
What is a common "toaster heating element" tester?
On Tue, Oct 11, 2011 at 6:05 PM, Brian Teitelbaum
wrote:
> I once saw a brand new L16 battery that would read the proper voltage (6.3
> VDC) and had good hydrometer readings, but the voltage would drop to zero
> when a load was applied. We were e
I once saw a brand new L16 battery that would read the proper voltage (6.3 VDC)
and had good hydrometer readings, but the voltage would drop to zero when a
load was applied. We were even able to do a dead short with a piece of #10 wire
with only a faint spark visible upon connection, and then no
I would load test each battery individually using a common "toaster heating element" tester.I'm betting on a bum battery in the string.
Original Message
Subject: Re: [RE-wrenches] intermittent battery problem
From: Ron Young
Date: Tue, October 11, 201
Ron,
Sounds like you might have a voltage drop in the system at point of
measurement.
A large voltage drop can happen for a few valid reasons.
1. High current demand. > Trimetric or better yet PentaMetric can show this
demand.
2. Poor Cable connection. Visual / Thermal inspection or local Vdc
Hey Wrenches,
I know it has been discussed on this list, but i'm not having any luck finding
any threads on how to deal with re-shingling an asphalt shingle roof with a PV
array already on it.
I have a potential client who is asking (somewhat concerned) about this
scenario and i'm loo
Wrenches,
I received some additional info from the customer this morning. They have asked
me to hold off my visit until they get a few more clues but some of what they
are telling me doesn't necessarily jive with a sulphated battery. Would
appreciate comments - here's a quote from their email:
James:
I do not have any experience with this system but I always read up on any
new racking system. I reviewed the manufacturer's specs and installation
instructions and here is what jumped out at me:. This system lacks what
almost all of the systems lack: a means to safely, reliably and
Wrenches,
Does anybody out there have experience with the new Renusol CS60 flat roof
racking system. We are about to install some, and I was hoping to get some
feedback on how it went. It seems like its going to be challenging to get
these things to look good.
Mucho Gracias in advance!
Sunny Reg
Thanks for the input guys.
On Mon, Oct 10, 2011 at 2:15 PM, Allan Sindelar <
al...@positiveenergysolar.com> wrote:
> **
> Mac,
> Adding to Dan's sage advice:
> No inverters have amp-hour meters built directly into them.
>
> Magnum and Outback have the ability through their respective BOS
> periph