Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

2012-09-15 Thread Isaac Opalinsky
Bob, The problem with switching both conductors (in a normally grounded array) is that opening the disconnect removes the bond to ground. This takes the ground fault protection and detection system out of the scheme (which would at least have operated with the disconnect open on the normally

Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

2012-09-15 Thread Drake
This is from the 2008 NEC 690.13 All Conductors. Means shall be provided to disconnect all current-carrying conductors of a photovoltaic power source from all other conductors in a building or other structure. A switch, circuit breaker, or other device, either ac or dc, shall not be

Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

2012-09-15 Thread Jason Szumlanski
690.13 specifically states that the grounded conductor shall NOT be disconnected. All sections of Chapter III (Disconecting Means) of Article 690 specifically refers to the ungrounded conductor. Jason Szumlanski Fafco Solar On Fri, Sep 14, 2012 at 7:39 PM, Bob Clark bcl...@solar-wind.us wrote:

Re: [RE-wrenches] Disconnect BOTH positive and negative conductors from array?!?

2012-09-15 Thread Isaac Opalinsky
Disconnecting a normally grounded conductor would defeat the purpose of ground fault protection and detection. If there is anything an inspector should respect, it is ground fault protection (and 690.13). Isaac Opalinsky ___ List sponsored by Home