Re: [RE-wrenches] magnum question

2020-04-02 Thread William Miller
Jay: This idea sounds wrong on many levels. Generators are designed to be loaded evenly, with some allowance for normal deviations. Having separate loads that can vary independently is asking for regulation problems. You did not state if the generator was wound Wye or Delta. This makes a

Re: [RE-wrenches] Trimetric TM 2020

2020-04-02 Thread Dan Fink
Drake, I have a TM 2025 I'd sell you for cheap. No shunt or 48v kit. Contact me off list. Dan Fink Executive Director, Buckville Energy Consulting NABCEP PV Associate NABCEP Certified PV System Inspector IREC Certified Instructor™ for: ~ PV Installation Professional ~ Small Wind Installer NABCEP

Re: [RE-wrenches] magnum question

2020-04-02 Thread Lones Tuss
Hi Jay The FXR inverters do have the ability to run 2 legs of a 3phase system on a single Mate3(s)and a Hub10.3 Inside the Hub10.3 is a header containing 5 jumpers. These jumpers can be arranged so the inverters are set to a 3 phase configuration. Up to 9 inverters can be used per system, up to

Re: [RE-wrenches] magnum question

2020-04-02 Thread Jay
Hi Dana, That depends on the unit. In my case its a large generator with large loads, the inverters being just one of the loads. I can’t load one phase with 8kw, that would overload one phase. Splitting the load to 2 phases, is within the capacity of the generator and within the total